    Dear All,

    I am using EtherCat Master in my project, and I am testing it. My problem is, that I can not catch any status. In the input assistant, I could find the following:
    IoConfig_Globals.EtherCAT_Master.xError -> it is boolean, and according to the explanation:
    "The output is TRUE when

    • an error occurs when starting the EtherCAT stack, or
    • communication with the slaves is interrupted because no more messages can be received (for example, due to a damaged cable)."

    Based on it, I have added to my ST this one:
    e:=IoConfig_Globals.EtherCAT_Master.xError;

    Where e is boolean variables.

    But it always FALSE. If the program is running, I unplug the EtherCat EK1100 from the power, and in the Codesys I can see the red triangles next to the EtherCat master etc., but the variable is still FALSE.

    How can I check it during the run? Is there any other solution to check does the Master run properly or not?

    Thank You in advance!

     
  • eschwellinger

    eschwellinger - 2022-01-18

    Hi,
    you need to call the global Master instance in your code to have these variables up to date.

    Ethercat_Master();
    xconfigfinished:=Ethercat_Master.xConfigFinished;
    xError:=Ethercat_Master.xError;
    
     
    πŸ‘
    1
  • skalakope - 2022-01-18

    Dear eschwellinger!

    Thank You for your rapid help! It works now.

     