Post by mp9876 on Device logon problem following fresh install
CODESYS Forge
talk
(Post)
All screenshots are enclosed in MS Word document. NOTE; 4 questions features at the end. Any assistance would be greatly appreciated! Hi everyone, I am still having device logon problem following a fresh install Here are the STEPS I went through following a FRESH CODESYS Win 64 3.5.19.60 install on a different computer. ‘Gateway not configured properly’ when attempting to REFRESH from the Users and Groups. Then did Gateway manage and confirmed it was ok: This message popped out as it was a fresh install: YES then: Initially went with Administrator twice (user & password) but it did not like it. No device is responding to …: Continued by setting a new user Pressed OK and obtained the following message: Stopped and Restarted PLC at that point: Obtained the following: Attempted to login a 2nd time without success. Then I scanned the network to see if matching device can be detected: Only way to get it detected was to remove the tick in the ‘Hide non-matching devices…’ Attempted a WINK but got a return like this one: REFRESH either @ Users and Groups or @ Access Rights returns: Then created user ‘mp’ at Project level ang logged in: Understandably device user mp9876 was not valid for the Project. Device information A few questions comes to my mind following these connection attempts: 1- Gateway not configured properly message pops out because of a non-compatible device ? 2- Why would the device not be compatible ? 3- Any way to make the device compatible ? 4- Any ideas on how to get this connectivity problem to the device solved ?
Last updated: 2024-03-17
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by vstrom on Codesys v3.5.22.10 - Internal error:System.AggregateException...Value cannot be null...Parameter name: expLValue
CODESYS Forge
talk
(Post)
Hi to all, I receive an error when I try to compile a project that in v.3.5.21.50 have no problem. The error seems to comes out when I add the Visualization part into the project. The complete error is: [ERROR] Internal error:System.AggregateException: One or more errors occurred. ---> System.Exception: Internal error in Code ---> System.ArgumentNullException: Value cannot be null. Parameter name: expLValue at _3S.CoDeSys.LanguageModelManager.LanguageModelBuilder.CreateAssignmentExpression(IExprementPosition pos, IExpression expLValue, IExpression expRValue, Operator kindof) at _3S.CoDeSys.LanguageModelManager.LanguageModelBuilder.CreateAssignmentStatement(IExprementPosition pos, IExpression expLeft, IExpression expRight) at ..(IExpression , IExpression ) at ..(_IAssignmentExpression , ) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Optimization.AssignmentStatementReplacer.ReplaceExpressionStatement(_IExpressionStatement expressionStatement, _ICompiledPOU cpou) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Optimization.ExpressionStatementReplacerVisitor.visit(_ISequenceStatement sequenceStatement) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Optimization.ExpressionStatementReplacerVisitor.visit(_IIfStatement ifst) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Optimization.ExpressionStatementReplacerVisitor.visit(_ISequenceStatement sequenceStatement) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Optimization.ExpressionStatementReplacerVisitor.visit(_IIfStatement ifst) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Optimization.ExpressionStatementReplacerVisitor.visit(_ISequenceStatement sequenceStatement) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Optimization.ExpressionStatementReplacerVisitor.visit(_IForStatement forloop) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Optimization.ExpressionStatementReplacerVisitor.visit(_ISequenceStatement sequenceStatement) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Optimization.ExpressionStatementReplacerVisitor.visit(_ISequenceStatement sequenceStatement) at ..(_ICompiledPOU ) at ..(_ICompiledPOU ) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Codegeneration.(_ICompiledPOU , _ISignature ) at ..(_ICompiledPOU ) at ..(_ICompiledPOU& ) at ..() --- End of inner exception stack trace --- --- End of inner exception stack trace --- at _3S.CoDeSys.Compiler35220.CompilerPhases.CompilerPhase5_Codegenerator.(IList1 ) at _3S.CoDeSys.Compiler35220.CompilerPhases.CompilerPhase5_Codegenerator.(IScope5 , IList1 ) at _3S.CoDeSys.Compiler35220.CompilerPhases.CompilerPhase5_Codegenerator.(ICodegenerator ) at _3S.CoDeSys.Compiler35220.CompilerPhases.CompilerPhaseControllerGenerateCode.() at _3S.CoDeSys.Compiler35220.CompilerPhases.CompilerPhaseControllerGenerateCode.() ---> (Inner Exception #0) System.Exception: Internal error in Code ---> System.ArgumentNullException: Value cannot be null. Parameter name: expLValue at _3S.CoDeSys.LanguageModelManager.LanguageModelBuilder.CreateAssignmentExpression(IExprementPosition pos, IExpression expLValue, IExpression expRValue, Operator kindof) at _3S.CoDeSys.LanguageModelManager.LanguageModelBuilder.CreateAssignmentStatement(IExprementPosition pos, IExpression expLeft, IExpression expRight) at ..(IExpression , IExpression ) at ..(_IAssignmentExpression , ) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Optimization.AssignmentStatementReplacer.ReplaceExpressionStatement(_IExpressionStatement expressionStatement, _ICompiledPOU cpou) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Optimization.ExpressionStatementReplacerVisitor.visit(_ISequenceStatement sequenceStatement) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Optimization.ExpressionStatementReplacerVisitor.visit(_IIfStatement ifst) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Optimization.ExpressionStatementReplacerVisitor.visit(_ISequenceStatement sequenceStatement) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Optimization.ExpressionStatementReplacerVisitor.visit(_IIfStatement ifst) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Optimization.ExpressionStatementReplacerVisitor.visit(_ISequenceStatement sequenceStatement) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Optimization.ExpressionStatementReplacerVisitor.visit(_IForStatement forloop) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Optimization.ExpressionStatementReplacerVisitor.visit(_ISequenceStatement sequenceStatement) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Optimization.ExpressionStatementReplacerVisitor.visit(_ISequenceStatement sequenceStatement) at ..(_ICompiledPOU ) at ..(_ICompiledPOU ) at _3S.CoDeSys.Compiler35220.Phase5_Codegeneration.Codegeneration.(_ICompiledPOU , _ISignature ) at ..(_ICompiledPOU ) at ..(_ICompiledPOU& ) at ..() --- End of inner exception stack trace ---<---
Last updated: 2026-04-22
Post by gilad on CODESYS SoftMotion Generic DSP402 on WAGO PFC200 + Festo CMMT-AS: MC_Power stays Busy, Controlword remains 0
CODESYS Forge
talk
(Post)
Hello, I am trying to connect a Festo CMMT-AS-C4-3A-MP-S1 servo drive to a WAGO PFC200 (750-8210) using EtherCAT and CODESYS SoftMotion. Hardware PLC: WAGO PFC200 750-8210 Drive: Festo CMMT-AS-C4-3A-MP-S1 Communication: EtherCAT CODESYS version: Device description version 6.3.1.1 Drive firmware: 36.10.3 Current Status EtherCAT communication is working correctly: EtherCAT master = Running Drive detected and operational PDO input and output mapping is active Statusword, position and velocity are updating correctly Current PDO mapping: Outputs: 6040 Controlword -> %QW0 6060 Modes of operation -> %QB2 607A Target position -> %QD1 60FF Target velocity -> %QD3 Inputs: 6041 Statusword -> %IW2 6061 Modes of operation display -> %IB6 6064 Position actual value -> %ID2 606C Velocity actual value -> %ID3 SoftMotion Axis I added a SoftMotion CiA402 axis under the EtherCAT slave: Axis type: SM_Drive_GenericDSP402 Axis communication state: operational (100) No SoftMotion mapping errors anymore Problem MC_Power is executed with: Enable = TRUE bRegulatorOn = TRUE bDriveStart = TRUE but: Status = FALSE Busy = TRUE Error = FALSE ErrorID = SMC_NO_ERROR The axis remains in: SMC_AXIS_STATE.power_off DSP402 state = SWITCH_ON_DISABLED The most important observation: Statusword = 32784 (0x8010) Controlword (%QW0) remains 0 all the time SoftMotion never writes 6, 7, or 15 to the Controlword. Additional Information The axis status page reports: "The license is missing or invalid. The PLC runs in demo mode." I am not sure whether: The missing SoftMotion license prevents Controlword generation completely. The axis is still not correctly connected to the EtherCAT slave despite operational communication. There is an additional CiA402 configuration step required for the Festo CMMT-AS drive. Has anyone successfully used a Festo CMMT-AS MP drive with CODESYS SoftMotion Generic DSP402 on a WAGO PFC200? Any suggestions on what should be checked next would be greatly appreciated.
Last updated: 2026-06-24
Post by kreisfilho on Stop raspberry from executing a plc program
CODESYS Forge
talk
(Post)
Hi guys, Can someone inform where in a raspberry pi are stored the codesys programs? I´ve been training the use of a RPI as PLC, which works pretty well, however while both the RPI and PC (running codesys) remain connected to the same network. The question is: how to run the codesys program downloaded to the RPI as a stand alone device (disconnected from the PC)? Thanks! Kreis
Last updated: 2023-08-23
Post by arnog on Two drives on one axis, Gantry Robot
CODESYS Forge
talk
(Post)
Hi TK_Jenssen did you found a solution I am setting up the samelike gantry only with two z-axes which are mounted on fix position with an X axes between the two z-axes. The movement and position of both z-axes must be very well aligned and calibrated. Maybe also to be adjusted by programming. Can you sent an example of your solution?
Last updated: 2023-08-25
Post by fabian on v3.5 SP19 - Modbus TCP Devices - Channel Limit?
CODESYS Forge
talk
(Post)
Hi all, Is there an update on this topic? Same problem here, I can not add more than 10 Modbus-Slave channels. Is there a workaround? Many thanks! Fabian Codesys 3.5.19 SP2, Modbus 4.3.0.0, Name: Modbus TCP Slave Hersteller: 3S - Smart Software Solutions GmbH Kategorien: Modbus TCP Slave Typ: 89 ID: 0000 0005 Version: 4.1.0.0 Bestellnummer: - Beschreibung: Ein Geraet, das als Slave für einen Modbus TCP Master konfiguriert ist. Version Konfiguration 3.5.11.0
Last updated: 2023-08-28
Post by dasch on eCockpit - unable to start simulation
CODESYS Forge
talk
(Post)
This is a known bug in e!Cockpit. See Release notes of V 1.11: 1 e!Cockpit Release Version 1.11 (2022-07) ATTENTION: If a library that uses asynchronous tasks (e.g. WagoAppConfigTool, WagoAppCloud or function modules such as Dali-Master) is dragged into the project, the simulation cannot be started. It is already sufficient to add the library to the project (an FB does not even have to be instantiated). I guess you are using one of these libraries/modules in your project. We e.G. often use PWM modules, these are also affected.
Last updated: 2023-09-05
Post by nico01 on Integer with comma in visualization
CODESYS Forge
talk
(Post)
Hello everyone, I created a visualization with a lot of REAL, with one or two digits after the decimal point. This causes me problems in terms of rounding and memory... is it possible to display an integer with a comma, like with PROFACE or SIEMENS? It's just an "abuse" of display, the comma is just on the visualization. This limits the memory (16 versus 64 bytes) and rounding is easier to manage... See print screen on proface software THANKS
Last updated: 2023-09-20
Post by sukrit on What licenses are required for runtime on raspberry pi cm4
CODESYS Forge
talk
(Post)
We have developed a project for 2 servo motors using raspberry pi computemodule 4 on ethercat master. we are using web visualization for display different screens. project is running well in demo. we want to implement it in production envoirment. being new still wondering which licences i need. Can We get this information in codesys devlopment software. code size is approx 5 mb, 1 instance of etharcat master and aproox 100 variables in visaualization.
Last updated: 2023-10-17
Post by rcaponi on Codesys 3.5 SP19 Patch 4. Trace context menu does not work
CODESYS Forge
talk
(Post)
Hello, I'm using the new Codesys 3.5 SP19 Patch 4 version with CODESYS Control for Raspberry Pi MC SL v4.8. Compared to the Codesys 3.5 SP19 Patch 1 version, the context menu on a Trace object no longer works. So I can no longer run the Downloader Trace command. Do any options need to be enabled with the new version? Best regards Roberto Caponi
Last updated: 2023-10-24
Post by snhatton on Running webvisu with Codesys Control Win V3 in Simulation Mode
CODESYS Forge
talk
(Post)
Yes, you can use the CODESYS ControlWin V3 Soft PLC. However, if simulation is enabled on the device this will disable all communication, so you need to turn off simulation to view the visualization in a web browser. In simulation mode, all IO and communication is disabled for standalone testing. In addition, make sure to set the start visualization in the WebVisu object in the application tree. I hope this helps!
Last updated: 2023-12-04
Post by installwhat on What is the solution for "Application stopped on recovery switch request"?
CODESYS Forge
talk
(Post)
<Entry severity="information" component="<10>" user="nobody" timestamp="2024-07-04 ?? 5:10:47" infoId="1">Axis#=121 , Error=30014 , Emergency 2 <Entry severity="information" component="<10>" user="nobody" timestamp="2024-07-04 ?? 5:10:23" infoId="1">TCP Server : WaitClient <Entry severity="information" component="<10>" user="nobody" timestamp="2024-07-04 ?? 5:10:23" infoId="1">TCP Server : Init What is "component="<10>"? Is this system a vanilla CODESYS RTE or is it a modified installation. I think more details are required.
Last updated: 2024-07-08
Post by mubeta on Some 'pathetic' errors in SoftMotion program
CODESYS Forge
talk
(Post)
Yes, this point is part of my misunderstanding. Why, after the execution ot the motion FBs is set to FALSE and exsecuted at lest one time, it must be continuosly called, even if the motion control it's take from another subsequent instruction. This is what I really don't undertand, but what in fact it's happening. For example, in case of stopping a MoveVelocity FB, then Halting the motion by the related FB, the axis at spot goes into error. If there was bad trigger management, the various instructions would NEVER work.
Last updated: 2024-07-18
Post by mgabryel on Problems with CAN 2.0 comunication on Wago PLC (Codesys 3.5)
CODESYS Forge
talk
(Post)
Hello, I am trying to program CAN Bus comunication on WAGO PLC (more precisely on WAGO Touch Monitor model TP600). I am using for this purpose library "WagoAppCanLayer2" from Wago company. My IDE for programming this device is CODESYS V3.5 SP19 Patch 2 + (64-bit). My program is written in Structured text using function blocks from previously mentioned library. Here is code of this program: 1) Variables declarations: PROGRAM PLC_PRG VAR oOpenInterface : WagoAppCanLayer2.FbCanL2Open :=( udiBaudrate := 125000 ); xInterfaceIsOpen : BOOL; sInterfaceInfo : STRING; oReceive : WagoAppCanLayer2.FbCanRx29BitFrame :=( xBufferMode := FALSE, wCanId := 16#181 ); xRecv : BOOL; sReceiveInfo : STRING; oSend : WagoAppCanLayer2.FbCanTx29BitFrame :=( dwCanId := 16#100, //was 16#201 xRtrFrame := FALSE ); xSend : BOOL; sSendInfo : STRING; oCanDiag : WagoAppCanLayer2.FbCanErrorInfo; xRst : BOOL; aSendData : ARRAY [1..8] OF BYTE; bSendLen : BYTE; TON_0 : TON; TON_1 : TON; END_VAR 2) Program body: oOpenInterface( xEnable := NOT xInterfaceIsOpen, I_Port := IoConfig_Globals.WAGO_CAN_LAYER2_DEVICE ); sInterfaceInfo := oOpenInterface.oStatus.GetDescription(); xInterfaceIsOpen S= oOpenInterface.xValid AND NOT oOpenInterface.xError; oReceive( xEnable := xInterfaceIsOpen, I_Port := IoConfig_Globals.WAGO_CAN_LAYER2_DEVICE, xRxTrigger := xRecv ); sReceiveInfo := oReceive.oStatus.GetDescription(); IF NOT xRecv THEN IF oReceive.bRxNBytes > 0 THEN oReceive.aRxBuffer[1]; oReceive.aRxBuffer[2]; oReceive.aRxBuffer[3]; oReceive.aRxBuffer[4]; oReceive.aRxBuffer[5]; oReceive.aRxBuffer[6]; oReceive.aRxBuffer[7]; oReceive.aRxBuffer[8]; END_IF xRecv := TRUE; END_IF aSendData[1] := 224; aSendData[2] := 13; aSendData[3] := 14; aSendData[4] := 15; aSendData[5] := 222; aSendData[6] := 13; aSendData[7] := 14; aSendData[8] := 15; bSendLen := 8; TON_0(IN:= NOT TON_1.Q, PT:= T#2S , Q=>xSend, ET=> ); TON_1(IN:= TON_0.Q, PT:= T#2S , Q=>, ET=> ); oSend( xEnable := xInterfaceIsOpen, I_Port := IoConfig_Globals.WAGO_CAN_LAYER2_DEVICE, aTxBuffer := aSendData, bTxNBytes := bSendLen, xTxTrigger := xSend ); sSendInfo := oSend.oStatus.GetDescription(); oCanDiag( xEnable := TRUE, I_Port := IoConfig_Globals.WAGO_CAN_LAYER2_DEVICE, xTriggerResetCounter := xRst, xValid=> , xError=> , oStatus=> , wBusState=> , wBusDiag=> , uiRxOverflowsL2=> , uiTxOverflowsL2=> , uiRxOverflows=> , uiMsgTimeouts=> , uiBusOffs=> , uiBusWarnings=> ); Program first opens comunication on CAN 2 device and then periodically try send one CAN data frame. After starting program CAN 2 interface is properly open. The xSend variable is toggling with period 2s. When program sends data an "Tx overflow" error appears. When I am watching CAN_H line on DSub 9 socket i am not able to see proper CAN frames - see screenshot attached to this message. Could somebody help me determine what is wrong with this program. Best regards
Last updated: 2024-08-02
Post by pavanifm on Test a manager script (.tsd file{xml document}) not starting from Git CI heedlessly/ without ui
CODESYS Forge
talk
(Post)
'--noUI' option of Command line interface for test manager test script not executing when triggered from CI as well as from Local PC however is it working for execution of python scripts from CLI. can we start codesys test manager scripts from CLI interface without any GUI in background process of windows? i can see simlillar questions asked but no answer yet. otherwise, what is the solution to built test automation framework using Test Manager & GIT CI/CD?
Last updated: 2024-08-07
Post by pavanifm on Test a manager script (.tsd file{xml document}) not starting from Git CI heedlessly/ without ui
CODESYS Forge
talk
(Post)
'--noUI' option of Command line interface for test manager test script not executing when triggered from CI as well as from Local PC however is it working for execution of python scripts from CLI. can we start codesys test manager scripts from CLI interface without any GUI in background process of windows? i can see simlillar questions asked but no answer yet. otherwise, what is the solution to built test automation framework using Test Manager & GIT CI/CD?
Last updated: 2024-08-07
Post by pavanifm on Test a manager script (.tsd file{xml document}) not starting from Git CI heedlessly/ without ui
CODESYS Forge
talk
(Post)
'--noUI' option of Command line interface for test manager test script not executing when triggered from CI as well as from Local PC however is it working for execution of python scripts from CLI. can we start codesys test manager scripts from CLI interface without any GUI in background process of windows? i can see simlillar questions asked but no answer yet. otherwise, what is the solution to built test automation framework using Test Manager & GIT CI/CD?
Last updated: 2024-08-07
Post by pavanifm on Test a manager script (.tsd file{xml document}) not starting from Git CI heedlessly/ without ui
CODESYS Forge
talk
(Post)
'--noUI' option of Command line interface for test manager test script not executing when triggered from CI as well as from Local PC however is it working for execution of python scripts from CLI. can we start codesys test manager scripts from CLI interface without any GUI in background process of windows? i can see simlillar questions asked but no answer yet. otherwise, what is the solution to built test automation framework using Test Manager & GIT CI/CD?
Last updated: 2024-08-07
Post by liamb on Converting CANbus to Decimal from signed 2's complement
CODESYS Forge
talk
(Post)
I need to combine two 8 bit CANbus messages to 16 bits signed int then convert to decimal Decimal from signed 2's complement. I've been using the below code to read for new messages, combine them then assign them to a variable What is the best way to do this for from signed 2's complement? fbRxMessage351(Data := RxMessage351Data); IF fbRxMessage351.NewMessage THEN ChargeVoltage := (WORD_TO_REAL((RxMessage351Data[0]) + ((RxMessage351Data[1]) * 256))) * 0.1; END_IF
Last updated: 2024-08-16
Post by egau on Mutate Hash table value
CODESYS Forge
talk
(Post)
Hi, using the ElementCollections Library, why isn't it possible to mutate a value found within a HashTable? From what I understand, the only way to change a value would be to use the RemoveByKey(), followed by AddKeyValuePair(). My goal is to use a Data Structure that works like a Dictionary in Python. The HashTable seems to come close to this, except that the values themselves seem to be immutable... In python, we can mutate a dict easily (see attached picture).
Last updated: 2024-08-29
Post by mostafa-beshr on implementing continuous movement in Codesys
CODESYS Forge
talk
(Post)
Hi everyone, I’m working on implementing continuous movement in Codesys, but I've run into some trouble. I've tried using ALL SM3 Basic and SML without success. I’m specifically looking for a library that supports continuous updates and can fetch values from a server in real time. Does anyone know of a library or approach that fits these requirements? Any advice or suggestions would be greatly appreciated! i read plcopen documentaion as well as codesys Thank you!
Last updated: 2024-09-11
Post by mostafa-beshr on implementing continuous movement in Codesys
CODESYS Forge
talk
(Post)
Hi everyone, I’m working on implementing continuous movement in Codesys, but I've run into some trouble. I've tried using ALL SM3 Basic and SML without success. I’m specifically looking for a library that supports continuous updates and can fetch values from a server in real time. Does anyone know of a library or approach that fits these requirements? Any advice or suggestions would be greatly appreciated! i read plcopen documentaion as well as codesys Thank you!
Last updated: 2024-09-11