Post by timvh on Device diagnosis ( EtherCAT IO card )
CODESYS Forge
talk
(Post)
You can get the state by just using the name of your node (same name as in device tree): VAR etcState: IoDrvEthercatDriverLib.ETC_SLAVE_STATE; END_VAR etcState := EJ1100.wState; Alternatively, you can iterate through the device tree to get the status of all (Ethercat) nodes. See here an example (no guarantee it works, just give as suggestion): PROGRAM P_IO_State VAR CONSTANT uiMAX_NR_OF_TERMINALS : UINT := 100; END_VAR VAR // general device diagnosis // can only be used when the Device - PLC Settings - Advanced settings - enable diagnosis for devices is enabled // this will add the DED library coupler: DED.INode; terminal: DED.INode; aDeviceState: ARRAY[0..uiMAX_NR_OF_TERMINALS - 1] OF DED.DEVICE_STATE; uiTerminalCount : UINT; uiIndex : UINT; // for each terminal check if it implements device diagnostics xQueryResult: BOOL; itfDevice : DED.IDevice2; xDiagAvailable: BOOL; eError: DED.ERROR; xEverythingOK: BOOL; END_VAR uiTerminalCount := 0; // start at the top of the device tree with the first EtherCAT coupler coupler := EtherCAT_Master.FirstChildNode; WHILE coupler <> 0 DO // for each coupler that is found start at the first terminal terminal := coupler.FirstChildNode; WHILE terminal <> 0 AND uiTerminalCount < uiMAX_NR_OF_TERMINALS - 1 DO // for each terminal that is found get the status through the device diagnosis interface xQueryResult := __QUERYINTERFACE(terminal, itfDevice); IF xQueryResult THEN aDeviceState[uiTerminalCount] := itfDevice.GetDeviceState(xDiagnosisInfoAvailable => xDiagAvailable, eError => eError); uiTerminalCount := uiTerminalCount + 1; END_IF terminal := terminal.NextSiblingNode; END_WHILE coupler := coupler.NextSiblingNode; END_WHILE uiIndex := 0; xEverythingOK := TRUE; WHILE uiIndex < uiTerminalCount DO IF aDeviceState[uiIndex] <> DED.DEVICE_STATE.RUNNING THEN xEverythingOK := FALSE; EXIT; END_IF uiIndex := uiIndex + 1; END_WHILE
Last updated: 2025-02-06
Post by rmaas on Strange Behavior on Raspberry Pi
CODESYS Forge
talk
(Post)
Hello, what you are seeing is not strange behavior. The problem is that everyting is happening in the same program cycle. After the variable Stepnumber is changed from 10 to 20 for example then you want the program to wait with the next EQ until the next program cycle. Else every EQ will be be true because in every line the variable Stepnumber is increased. When the program arrives (still in the same cycle) at the line with the timer, the Stepnumber has been increased to 30 in the meantime and the timer will allway be ON because even though the variable is written to 10 in this line in the next cycle it starts with 10 and will be 30 again before reaching the timer in line 8. Not very good at explaining stuff but i hope you get the problem. See screenshot below for an example of one way you could solve this...
Last updated: 2024-06-18
Post by cer-wa on Not able to connect multiple profinet encoder in codesys Linux ARM64
CODESYS Forge
talk
(Post)
Hello, currently im working with a RevPi connect 5 on a codesys project. Up until now I was having a blast because things were going really smooth but for like almost a day im kind of stuck on the integration of multiple profinet sensors into my project. This is kind of a bummer because that should be an easy thing to do. What I tried so far was to create and additional ethernet adapter where I then tried to connect my devices. in the beginning I tried to connect the devices directly which was not working because I could assign the IP-adress only to the ethernet adapter and not to the devices but the device was found in the device repository (this gets important in the second part) So what I tried next was to setup a PN-Controller and connect my devices subsequently to the Controller. Sadly now the devices wont show up in the device repository anymore. To me its not clear why this is happening. And the worst thing is: I went ahead and setup a device completely like I would want to have it in the project and when I then click on scan devices I can even find the device. But it can not be added to project for whatever reason eventhough im 100% certain that the gsdml file is the correct one. Can anyone help me with this. Like I said this seems like an easy thing to do and its taking me way longer than expected already. The only thing that came to my mind why this might not work is because I have codesys license which only allows one profinet instance. Could that be the case? The error message seems then pretty unfit but ok. I will be grateful for every advice. Thanks in advance! Best regards!
Last updated: 2025-09-25
Post by s1ack on Wago PFC200 Ethernet / IoDrvEthernet Issue?
CODESYS Forge
talk
(Post)
CODESYS Control for PFC200 4.13.00 CODESYS IIoT Libraries SL 1.11.0.0 Application Based License: CODESYS Control Standard M I have (2) projects with similar code base and both using Wago PFC200. On the second project I am seeing 2 things that I have not been able to resolve: 1) Errors in the log under the Ethernet Item: IoDrvEthernet: [PCI\E1Q51CE62] Could not be found on target! Please check the Ethernet settings. 2) Exception for CPU Load. "Processorload watchdog: plcload=100, maxplcload=95" I have slowed down cyclic tasks on this project, even though on the first project there is actually more code - and it does not exhibit this behavior. In looking at the CPU loading via Linux 'TOP' command there appears to be 20% idle. So plenty of headroom (my opinion). In an effort to troubleshoot I have duplicated the target hardware on my bench. It ran overnight without a CPU load exception. On the test system, I have tried (3) version of the ethernet device. 3.5.16.0 3.5.17.0 and 4.2.0.0 Presently the log does not show the error, but status says the module reports an error. I really do not know if this issue is related to the CPU load exception. The issue does not appear to effect ethernet communications (ModbusTCP or SNMP or Webvisu or PuTTy into Linux Shell). On my test bench I have ModbusTCP slave simulators for all ModbusTCP slaves, but only (1) of the (5) SNMP devices present.
Last updated: 2025-01-21
Post by khaledkhalil on Question about the hairaichy of UaExpert
CODESYS Forge
talk
(Post)
Hello, I am Examining this Example from Codesys Tutorial about OPC-UA server here https://www.youtube.com/watch?v=aJhzN3Uk-Do&list=PLWtD08CpmZcSV26aWh1axCAef5c5HxX-3&index=1&t=1167s. Now i am running to problem, when i create instances and i want them to appear directly under the object directory, However, it always appear with me under Objects >> Device set >> Device Name in CODESYS. I need to know how i can change the directory of my instances 'inst_3' and so on. So they can be under objects directly. I tried to modify the settings, but couldn't find any leads till now. Thanks in advance for helping
Last updated: 2024-09-12
Post by wbj0t on connect IDE to plc that uses modem ppp
CODESYS Forge
talk
(Post)
Hello everyone! I have an PLC device that uses modem ppp connection to the internet with white IP. Device PPP connection with modem operator established, so I can connect to this device via SSH also within Codesys IDE (check version, info, etc...) BUT, I cant establish connection to this device in the device gateway options for application upload and debugging. How can I do this? Im trying set my device remote IP and port 11740, but, as I understand, it is wrong decision, because the next logic in this connection: local W10 service (Codesys Gateway) listen on 1217, then (some how) this service scanning local networks for seeking any local IP which listening on port 11740, and then connects and writes there. OR IM WRONG?:) W10 tool 'Test-NetConnection' with parameters 'ip -Port 11740' succeeded with True. Need some help, please :)
Last updated: 2024-05-21
Post by davidbo on How to stop dhcpcd and use SysSockSetIpAddressAndNetMask to set address?
CODESYS Forge
talk
(Post)
It is stated: "Dynamic ip address, provided by DHCP, BOOTP, etc. Cannot be changed by SysSockSetIpAddressAndNetMask()" Therefore I try to stop dhcpcd and flush the eth0 like this VAR CONSTANT flushIP:STRING:='sudo ip addr flush dev eth0'; stopDHCP:STRING:='sudo systemctl stop dhcpcd'; END_VAR SysProcessExecuteCommand2(pszCommand:=stopDHCP, pszStdOut:=stdout,udiStdOutLen:= SIZEOF(stdout),pResult := ADR(Result)); SysProcessExecuteCommand2(pszCommand:=flushIP, pszStdOut:=stdout,udiStdOutLen:= SIZEOF(stdout),pResult := ADR(Result)); Besides losing the connection when flush occurs the CODESYS halts, seen on the display and I cannot see why, because I have lost the connection from my IDE. Why does the flush command halt the execution of the application?
Last updated: 2025-11-04
Post by adamrobotic on llcallback() iec exception caught cmpid=0x00000002, eventid=0x00010008
CODESYS Forge
talk
(Post)
Hi All, Recently I have been experiencing a issue in CodeSys SP16 Patch 3, with a exception which comes up after I have made several online changes. callcallback() iec exception caught cmpid=0x00000002, eventid=0x00010008, after I experience this fault then I receive a error message for any subsequent online change "online change failed, no task gap within 10000ms". To recover either the controller needs a orgin reset, which will allow online edits thereafter until falling back into the loop. I am using a TURCK TX707 product which is controlling robot trajectory, We have hard coded the coordinate data rather than using persistence variables so hence the need to do online changes consistently. I have read on the forum other people have experienced similar issue with the online task gap, but I have no task which have same priority and also monitored the CPU usage and have not seen it go above 13%. Anyones help would be much appreciated, thankyou.
Last updated: 2023-08-18
Post by rcaponi on Codesys Control RTE V3. Remote Control
CODESYS Forge
talk
(Post)
Hello, I would like to have, if possible, some clarification on this function. That is, I would like to understand if it is useful for managing, fom my development PC, the RTE runtime executed on a remote control. This is what the help says: Remote PLC: Opens the Remote Configuration dialog. By enabling or disabling the Control remote PC, not local option, you determine whether a PLC is used that is on a remote or local PC. Accordingly, the menu commands Start PLC, Stop PLC, and PLC Configuration refer to the local PC or a PC reached on the network. For the remote PC, specify the Target PC address, Port number, and a Timeout value (in ms) for the connection (Remote Timeout [ms]). But does this mean that I also need to install the RTE runtime on my development PC? Is it possible to have some more information? Best regards Roberto Caponi
Last updated: 2023-09-22
Post by janber0206 on Gateway doesn't come online, regarding a working internet connection
CODESYS Forge
talk
(Post)
Solved EN: The Problem is that the Codesys Edge-Gateways have a License with a runtime of an half year, as long the Gateways are online they will self renew themselfs. In my Case the RevPi was more than a year offline and so the Edge-Gateway was not working anymore. The solution: I accessed a laptop that was directly connected to the RevPi. I installed the Codesys service tool and renewed the certificate manual. DE: Das Propblem ist das die Codesys Edge-Gatways eine Lizenz haben die nur ein halbes Jahr gültig ist. Solange das Gateway eine Internet verbindung hat aktualisiert sich das Zertifikat von alleine. In meinem Fall war das Gateway aber über ein Jahr offline und hat somit nicht mehr funktioniert. Die Lösung: Ich hab auf einen Laptop von Kunden mit TeamViewer zugegriffen, der Laptop wurde mit Kabel direkt mit RevPi verbunden. Codesys Service Tool installiert und dann das Gatewayzertifikat aktualisiert.
Last updated: 2023-10-26
Post by climblinne on Calling OPC UA Methods from UaExpert
CODESYS Forge
talk
(Post)
Hello, I hope someone could help me. I installed the newest Codesys 3.5 SP 20 Patch 1. When loading the demo files from @i-campbell I can upgrade them to the latest version and everthing works on the OPC-UA client side as expected (object "a" is visible, I can use the "ExampleMethod"). Now I * remove the "Information Model", * delete the "OPC_UA_Symbols Objects", * Add "Information Model" again * add "TestRootObjectType" again and "Generate IEC declarations" * and search for mapped instances (to get instance "a" again) Very good still working as expected. Now I delete the OPC_UA_Symbols and add it again referring to the "objecttest" from 16.9.2020. Also I redo the steps from above. The result is now, that I can't see the "a" object in the "Root/Objects" folder. Why ist this and how can I make it running? I think, it could may be a different version of the UA configuration file. I tried to build my own model definition files and got the same problem (but I am really not an expert). When someone has a actual model, which is also running in the actual Codesys I would be very grateful. Or even better, how to make the correct model in e.g. UA Modeler SW (I followed the description https://documentation.unified-automation.com/uamodeler/1.6.0/html/howprojnet_sec.html).
Last updated: 2024-07-01
Post by abauza on Image Pool using in other libraries
CODESYS Forge
talk
(Post)
Hi im Albert, im developing libraries for my PLCs and i have some issues on visualization part. First of all I have done a library that have a image pool with a list of 4 gifs "ImagePoolErrors" (i've tested in other projects and it works) but the problem comes when i create another library that in the visualization part contains images from my image pool library, when i simulate a program that includes a instance of my second library object the visualization images dont show, any of them, i've checked all the references and tried some options of the image properties but without any difference. Here is the screenshots of the first library (that contains Image Pool) and the second library (that includes images of the image pool first library) and the visualization simulation (with the missing image gif issue). Any idea of what i forgotten in the process? If you need any detail of the library or of the project or you need the library file, ask me, thank on advance
Last updated: 2024-08-19
Post by rossanoparis on Clarifications regarding the appropriate runtime system to use
CODESYS Forge
talk
(Post)
Thank you @TimvH It is clear that licences are application based and now thanks to your reply I could understand the meaning of RT systems. The RT called "CODESYS Control for Linux ARM SL" can be deployed on a generic debian based ARM system. The RT called "CODESYS Control for Raspberry Pi MC SL" is more specific for Rasberry HW. Did I understand correctly? Regarding the RT called "CODESYS Virtual Control SL" despite its description it is not clear to me when to use it. It seems that a project created using such RT system can be deployed on any HW. It sound good obviously, as it means that it is possible to realize a completely abstract project from its hardware. The only limit could be represented by the need of using a specific HW or OS feature, in that case a more specific RT system should be chosen. Is my last consideration correct? Regards Rossano
Last updated: 2024-09-26
Post by cihangur on OpC UA server on Raspberry Pi 64 SL runtime
CODESYS Forge
talk
(Post)
Hello everyone, I wanted to write here because it is a similar and the most up-to-date topic. I want to connect to CoDeSys Win V3 x64 - 3.5.19.50 with OPC UA using WinCC Advanced V17. (Or to a PLC with CoDeSys Version 4.10.0.0) My settings are exactly the same as the previous comment. I even tried many different settings. I can access all CoDeSys OPC UA variables via TIA Portal IDE and add them to my HMI tags. When WinCC RT Advanced is started, it gives a warning that the connection could not be established and does not update the variables. I can connect to Inovance AM600 using CoDeSys Target version 3.5.11.50. (The same version Win x64 is also connected.) However, a security setting in the current versions prevents me. I would be very happy if those who have up-to-date experience on this issue and find a solution share it. The CoDeSys Security Settings which I can access variables with TIA Portal: CommunicationPolicy: POLICY_BASICSHA256SHA256 CommunicationMode: ALL Activation: Activated UserAuthentication: ENABLED Server Certificate: Valid until 2034 Greetings.
Last updated: 2024-12-06
Post by hyys12 on Help understanding analog in-/outputs
CODESYS Forge
talk
(Post)
Hello. I am currently working on a WAGO PLC, where I am trying to wrap my head around how the analog inputs and outputs work in codesys. I have looked far and wide on the internet, for a general introduction to the whole concept, but I have not had any luck with finding anything that helped me understand it better. The whole goal is for me to be able to read an analog input from a temperature sensor, as well as using an analog output, to control a frequency inverter. I know these have nothing to do with each other, but that is all I have on hand right now. I am trying to program this using Ladder Diagram. The only thing is, that every video/guide I have seen/read using LD, just adds a whole lot of function blocks, to do all kinds of stuff they don't explain. My general question is, how would one go ahead and read the analog input, as well as transmit an analog output? Is there some kind of specific function block I would have to use for this, or some great video I can watch, to understand the inner workings. Is it somehow possible to see the values the PLC recieved/sends? Regards.
Last updated: 2024-12-11
Post by mubeta on Strange problem with the ‘MC_SetPosition’ function
CODESYS Forge
talk
(Post)
Hi gseidel, before moving to HW implementation, I had created the same program in simulation mode with virtual drives and, as far as I remember, everything worked fine simulating process and the few useful inputs. So it does not seem to be a SoftMotion library problem, but rather a problem with dynamics or physical axis adjustments. What escapes me, however, is the fact that this function is supposed to perform a position shift virtually, in fact without interfering with the axis itself, thus independent of its adjustments. MC_SetPosition() is not a homing function, in fact it is clearly intended to be executed on the fly with the axis moving. Now I'll see if I can reduce the program, although I don't like it very much. In my life I have learned that problem searches should be done on the part, and not in a more or less similar way.
Last updated: 2025-01-10
Post by shaunvdm on Canbus Slave SDO Read from Object
CODESYS Forge
talk
(Post)
Busy testing a solution to use Canbus Slave to replace a physical device and convert to Ethercat device but keep the Canbus Master in place. Master needs to Read SDO object 5FA2. In the Master PLC if i send the SDO with 8 bytes in message IE: 60B 40 A2 5F 00 00 00 00 00 i get my expected 58B 43 A2 5F 00 00 68 36 02 containing data back. Problem is if we issue a 4 byte command can send 60B 40 A2 5F. Surely the canbus slave should respond with a 58B 43 A2 5F 00 00 68 36 02 but it comes back as 80 A2 5F 00 00 00 00 08 - meaning this OBJECT does not exist. Is there a setting in the canbus slave driver for Canbus to allow the 4 byte command to read the SDO OBJECTS ?
Last updated: 2025-05-27
Post by latassan on RaspberryPi 5 gateway problem
CODESYS Forge
talk
(Post)
Hello, I'm trying to use a raspberryPi 5 as a PLC. I fixed its IP address, I can ping it. I've also installed the CODESYS Control for Raspberry Pi 64 SL runtime on it. So I've created a gateway (IP address of the Raspberry, TCP port 1217). I see the green dot next to this gateway. When I do a network scan, I can see my raspberry (see photo). When I try to connect to it, I have to define an administrator profile, which I do. On validation, I see a message: No device is responding to the scan request. I've checked that port 1217 is listening on the raspberry, I've uninstalled the runtime then installed it again, but I can't connect. Also, when I try to configure the user groups before connecting, I see that Offline mode is not supported by the device, even though I'm connected to it in the Deploy Control SL tab. When I try to refresh, I see: Gateway not configured properly. How can I connect to my Raspberry? Have I defined my gateway incorrectly?
Last updated: 2025-06-12
Post by pouyavakili on Execute Codesys Tests with python
CODESYS Forge
talk
(Post)
❓ Issue: TestManager Not Available in Python Script (AttributeError) 🙏 Question: Why does project.get_testmanager() not work in scripting, even though Test Manager is installed and licensed, and the script runs in GUI mode? Is there a way to ensure the Test Manager interface is loaded or accessible from the scripting environment? 🧠 Summary: I'm trying to automate test execution using the CODESYS scripting engine (Python) via a script that opens a project, builds the application, and runs tests from a TestRepository.xml. Although the Test Manager works manually in the IDE, it fails when accessed via script with the following error: AttributeError: 'ScriptObject' object has no attribute 'testmanager' 🧪 Test Setup: CODESYS version: 3.5.21.10 Test Manager: Installed and licensed (works in the IDE manually) Project: Contains a test repository, which can be executed via the GUI Script execution method: powershell Start-Process -FilePath "C:\Program Files\CODESYS 3.5.21.10\CODESYS\Common\CODESYS.exe" ` -ArgumentList @( '--profile="CODESYS V3.5 SP21 Patch 1"', '--runscript="C:\Scripts\run_tests.py"' ) -Wait 📜 Script Summary: python project = projects.open(project_path) application = project.active_application application.build() This fails: testmanager = project.get_testmanager() ❗ Problem: Calling project.get_testmanager() or application.testmanager throws an AttributeError, even though the same project and test repository work in the GUI.
Last updated: 2025-07-23
Post by kurtk on Modbus TCP Server
CODESYS Forge
talk
(Post)
ditto I'm just getting my codesys wheels on and the modbus stuff is confusing. I am re-platforming an existing PLC application On that platform one could simply tag variables to register numbers and the whole shooting match could be accessed via modbus and typically holding registers and input registers were treated the same way... On codesys I see there is a modbus TCP server Device I/O mapping tab and a Modbus TCP server IEC objects tab I get the sense that one can configure the serving of variables both/either way but am unclear about the optimum/necessary path. Apparently in the IEC Objects tab one can "ADD" something or other - presumeably channels. I have created a preliminary function block but the Select Function Block window shows nothing to select WTH ? I exported the Device mapping and was surprised to see the entire Device IO map - complete with all the bit-mapped holding/input registers!! WTH!!?? Bit-mapped words are strictly a nichey special purpose application. I am targetting making a couple hundred variables available which would turn into hundreds of pages of IO/mapping Is the FUnction Block IEC objects thingy an alternative to that ? I notice that CODESYS shows the tags which the PLC used to specify the register address... are tags used in CODESYS for any specific hard-core purpose ?
Last updated: 2025-08-19
Post by leandroct on Creating Boot Application not working
CODESYS Forge
talk
(Post)
I have a Control Win V3.5 SP20 (64-bit) application, and until now, I open the program (with a password) and download it. However, I need to give the client the option to install the program on the Controller, without them having to open it and access the code. So, I followed these steps: 1 – In the Online => Create Boot Application menu, I saved the generated files in a directory: Application.app Application.crc PlcLogic\visu\ directory with several files 2 – In the SysTray, I ran the PLC, and it created a directory. In the root of this directory (C:\ProgramData\CODESYS\CODESYSControlWinV3x64\E84889DB), I pasted Application.app and Application.crc. Since it created a \visu directory, I pasted the PlcLogic\visu\ files generated in Create Boot Application into it. 3 - In the general Codesys directory (C:\ProgramData\CODESYS\CODESYSControlWinV3x64), I edited CodesysControl.cfg, adding: [CmpLog] Application.1=Application 4 - When running the PLC, nothing happens and the TargetVisu screen does not open. What I'm doing wrong?
Last updated: 2025-09-03
Post by alexgooi on Licensing info not available.
CODESYS Forge
talk
(Post)
Sorry for the question, but I'm not completely getting the idea here, could you be more specific, maybe give an example? I'm now in a state where I don't have a softcontainer on my license server anymore (even after reinstalling from the Codesys-IDE). I tried reaching the webserver of Codemeter but when I do that I get redirected to http://"IP":22352 This is not reachable, afterwards I installed lynx on my Debian machine (command line only). From here I could reach the webserver and toggle the network server setting, but unfortunately this did not help. I also tried to changed the remote read setting to 1 (in the Server.ini file). But after a Codemeter reboot this is overwritten to 0. I have the feeling that it should be much easier to get a license to work, am I missing some checkbox somewhere? Is there a tutorial (or manual) that explains the licensing sequence step by step, because I'm pretty stuck.
Last updated: 2025-10-01
Post by nicetuxedo on Can not activate license on Raspberry pi
CODESYS Forge
talk
(Post)
Hello everyone, I'm hoping for some assistance with a license activation issue: a software crash has left my license in a strange state. Here is the sequence of events: I purchased a new license for the Raspberry PI from the official CODESYS web store. I opened the CODESYS and started the online activation process using the ticket number I received. During the activation, the CODESYS software threw an exception and crashed. I was not able to see if the activation completed. After restarting CODESYS, I attempted to run the activation process again with the same ticket number. The License Manager now gives me an error stating that the ticket has already been activated/used. I am now stuck because my installation is not licensed, but the activation server believes my ticket has been consumed. Has anyone encountered this before? Is there a way to have the ticket status reset?
Last updated: 2025-10-08
Post by rabaggett on CODESYS control for Raspberry Pi 64 SL errors
CODESYS Forge
talk
(Post)
Hi, I am trying to create a project using a raspberry pi, I have added the modules for the Pi and MCP3008. I have encountered som errors that I don't know how to track down. 1. The GPIOs give preprocessor errors, but I read that this does not prevent compiling. This seems to be true. I can build the empty project with no errors. 2. After adding a SPI master and MCP3008, the preprocessor errors double, but seem similar and the project again builds with no errors. 3. I add a DUT and GVL, with a function, and I get the following errors. They remain even if I delete these things. ------ Build started: Application: Device.Application ------- Typify code... [ERROR] crr: C0032: Cannot convert type 'Unknown type: 'ADR(GVL_Io_17160064_c083_41f8_9e53_208be7537753_HPS_7.Io_17160064_c083_41f8_9e53_208be7537753_HPS_7)'' to type 'POINTER TO IoConfigParameter' [ERROR] crr: C0077: Unknown type: 'GVL_Io_17160064_c083_41f8_9e53_208be7537753_HPS_7.Io_17160064_c083_41f8_9e53_208be7537753_HPS_7' [ERROR] crr: C0046: Identifier 'GVL_Io_17160064_c083_41f8_9e53_208be7537753_HPS_7' not defined Compile complete -- 3 errors, 0 warnings I attach the project. What am I doing wrong? Thanks!
Last updated: 2024-05-02
Post by gediminas on Datasource OPC UA client system failure
CODESYS Forge
talk
(Post)
I am using CODESYS v3.5 SP20 Patch 3 / Control for BeagleboneBlack SL v4.13 and after some time the OPC UA Server crashes. However, Runtime still works without any issues. The events leading up to the OPC server crash are the most suspicious: 1) Mutex deadlock detected - owner thread died, and 2) Runtime received SIGABRT. And it seems very similar with this topic except used versions - issues should be fixed with previous SP's. I can't seem to find any information about these events. Need some pointers in the right direction on how I can fix this problem.
Last updated: 2024-10-25