Post by simotion on Property
CODESYS Forge
talk
(Post)
Why can't a property be of type REFERENCE TO? Plc goes to stop if I try that.
Last updated: 2023-12-14
Post by ph0010421 on How to manage variable types larger than 64 bits - Ethernet/IP
CODESYS Forge
talk
(Post)
My guess is that's a STRING, not an INT type. And it's 128 bytes, not bits
Last updated: 2024-09-23
Post by athuum on Error 'Library not found' and 'Unkown type'
CODESYS Forge
talk
(Post)
I have found the solution, the CmpEventMgr version has to correspond with the 3sLicense version.
Last updated: 2024-10-10
Post by eschwellinger on License problem gateway
CODESYS Forge
talk
(Post)
most important information are missing: Which CODESYS Version? Which runtime version? Which plc type (manufacturere).. Not all plc manufacturer already support application based licenses. From your pictures I see you have activated 4 axis Motion (which is an applications based license type) does only work on plc's which do support this.
Last updated: 2024-04-25
Post by phoward131 on Numpad decimal value requires leading zero
CODESYS Forge
talk
(Post)
I have noticed on the standard numpad dialog, if a user enters a purely decimal number (ie '.6'), the numpad will not accept the value but gives no indication. One must type a leading zero (ie '0.6') in order for it to work. Is there a way to correct this so that a user can just type the decimal value?
Last updated: 2024-04-30
Post by timvh on FB string and naming
CODESYS Forge
talk
(Post)
Really not clear what you are trying to do, but isn't a Struct enough? So add an object of the type DUT to the Application. Then create a structure TYPE ST_Sensor : STRUCT sName : STRING; uiNumber : UINT; END_STRUCT END_TYPE Then in you application add an instance of this Structure stSensor1 : ST_Sensor := (sName := 'my sensor', uiNumber := 1); or use it like this stSensor1.sName := 'my sensor';
Last updated: 2024-09-28
Post by eschwellinger on Scan Network on gateway created with Control Sl
CODESYS Forge
talk
(Post)
it seems that the device you scan, is not the same type which you have added to the project in CODESYS. Virtual Control is Arm 64 SL so please select this type in CODESYS when you generate a new Application..or right click to the device- update device - virtual Control Arm 64 SL
Last updated: 2024-10-16
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by ewi04 on Git - User identification data is lost when codesys is closed
CODESYS Forge
talk
(Post)
Hallo, it's not a big problem, but it is a bit annoying. The git user identification data is lost when codesys is closed. So I have to enter the information again and again. Is there a way to save the data? Environment: Codesys V3.5 SP19 Patch 4 (64Bit), Git 1.3.0.0 Thanks
Last updated: 2023-11-22
Post by fazlinda on AWS IoT core CODESYS
CODESYS Forge
talk
(Post)
Hi, Im having a problem sending a data from my structure text code from codesys to aws. Instead of receiving {state {reported {data: 123}}} It display {state {reported {data: 123}}}\x00 \x00 \x00 \x00 \x00 \x00 \x00 Please help me solve this issues. how to remove \x00 ?
Last updated: 2023-12-06
Post by fazlinda on AWS IoT core CODESYS
CODESYS Forge
talk
(Post)
Hi, Im having a problem sending a data from my structure text code from codesys to aws. Instead of receiving {state {reported {data: 123}}} It display {state {reported {data: 123}}}\x00 \x00 \x00 \x00 \x00 \x00 \x00 Please help me solve this issues. how to remove \x00 ?
Last updated: 2023-12-06
Post by fazlinda on AWS IoT core CODESYS
CODESYS Forge
talk
(Post)
Hi, Im having a problem sending a data from my structure text code from codesys to aws. Instead of receiving {state {reported {data: 123}}} It display {state {reported {data: 123}}}\x00 \x00 \x00 \x00 \x00 \x00 \x00 Please help me solve this issues. how to remove \x00 ?
Last updated: 2023-12-06
Post by fazlinda on AWS IoT core CODESYS
CODESYS Forge
talk
(Post)
Hi, Im having a problem sending a data from my structure text code from codesys to aws. Instead of receiving {state {reported {data: 123}}} It display {state {reported {data: 123}}}\x00 \x00 \x00 \x00 \x00 \x00 \x00 Please help me solve this issues. how to remove \x00 ?
Last updated: 2023-12-06
Post by fazlinda on AWS IoT core CODESYS
CODESYS Forge
talk
(Post)
Hi, Im having a problem sending a data from my structure text code from codesys to aws. Instead of receiving {state {reported {data: 123}}} It display {state {reported {data: 123}}}\x00 \x00 \x00 \x00 \x00 \x00 \x00 Please help me solve this issues. how to remove \x00 ?
Last updated: 2023-12-06
Post by fazlinda on AWS IoT core CODESYS
CODESYS Forge
talk
(Post)
Hi, Im having a problem sending a data from my structure text code from codesys to aws. Instead of receiving {state {reported {data: 123}}} It display {state {reported {data: 123}}}\x00 \x00 \x00 \x00 \x00 \x00 \x00 Please help me solve this issues. how to remove \x00 ?
Last updated: 2023-12-06
Post by abjha1998 on Converting UINT into bytes and converting 2Bytes into UINT
CODESYS Forge
talk
(Post)
Hi, I have been working on Codesys V3.5 with PFC200 controller and Can Gateway 750-658. I want to convert the incoming CAN data from bytes into UINT and for outgoing data bytes to UINT. Does anyone has experience with this kind of data? I tried few different ways but it doesn't seem to be working.
Last updated: 2023-12-07
Post by nima-khajehali on Data Transferring between 2 PLCs in a same PC
CODESYS Forge
talk
(Post)
Hi Guys, I want to simulate the data exchange between 2 soft PLCs on the same PC. We are trying to simulate the process and we could not see the desired result. What should I do to pass all data between these 2 PLC's correctly ? Please see attached
Last updated: 2024-02-05
Post by dengsberg on Check Connection Status of the OPC-UA Server for Data Source Manager with OPC-UA Client
CODESYS Forge
talk
(Post)
I am using the Data Source Manager with OPC-UA Client to get data from another CodeSys application in the same Project. How can I check in the PLC_PRG structured text if the connection is ok or not?
Last updated: 2024-09-07
Post by timvh on Send data to USB
CODESYS Forge
talk
(Post)
https://forge.codesys.com/prj/codesys-example/file-utilities/home/Home/
Last updated: 2024-07-22
Post by vladimirsmall on Send data to USB
CODESYS Forge
talk
(Post)
Thank you on support
Last updated: 2024-08-05
Post by robbudge on Data Source Error 418
CODESYS Forge
talk
(Post)
Same ? Did you find the Solution??
Last updated: 2024-10-11
Post by mase on Python script: Launch Codesys, Execute Script, Exit Codesys
CODESYS Forge
talk
(Post)
Hi, sorry I can´t help you with your issue, but I hope you can give me a hint on getting GUID for other objects than POUs. Your code states "Guid("6f9dac99-8de1-4efc-8465-68ac443b7d08")". We can I find the GUID / ObjectIds`? I wasn´t able to get details about the GUID of DataTypes (STRUCT/ENUM,..)m, Functions (FUN), GLOBALS and TYPES. I want to create markdown of all available project elements. Thanks for your help
Last updated: 2024-08-06
Post by macros8 on Alarm Management - latched variable represented as Text list
CODESYS Forge
talk
(Post)
Hi, I haven´t noticed you put the comment here. I thing it´s a bit different. What I want is to have detail errors of technology in data type e.g. INT. This variable I would latch to the corresponding error msg but I would like to get it convert to text from the text list and not keep it in INT form. Example. Main error Valve Error: SubErrors 1 - Both sensors 2 - Not retracted in time 3 - Not pulled out in time In HMI Main error + latch SubErrors => "Valve Error: Both sensors" The benefit is that text lists are part of translation and can be easily manipulated. I know I can create whole string msg in PLC but then, it lose advantage of Alarm management. Thanks. M.
Last updated: 2023-11-07