Post by jbcregen on Accessing parameters from a structure or function block with the web interface CODESYS Forge talk (Post)
I have a project with hundreds of OPC-UA variables available on the network. A lot of these variables are used actively in various scripts that run in background in the OS (Linux). I'm experimenting with Automation Server and I have a hard time understanding how the web interface populates its parameters list for a given PLC (<plc details="" parameters="" for="" plc="" 'xyz'="">).</plc> In this page, it looks like the only variables available are the ones that are of a "base" type : bool, TIME, String, INT, etc. All the variables that are nested into function blocks or structures are not available in the web interface, even if they are available to any OPC-UA client. Is this a limitation of the Automation Server or is there something that can be done in Codesys?
Last updated: 2025-12-01

Post by jorenbeyl on library inside library CODESYS Forge talk (Post)
I am currently developing a library that contains real‑time data. To handle this real‑time data, I am using additional libraries called SysTime and SysTypes Interfaces. When I compile my library on its own, no errors occur. However, when I use this library in a project and compile the project, I get an error indicating that the SysTime data type is not recognized. This happens even though the SysTime library is visible as a dependency under my library. Does anyone know how to correctly include a library within another library so that the project recognizes the sub‑library without causing compilation errors?
Last updated: 2026-04-23

Post by timvh on library inside library CODESYS Forge talk (Post)
1) it should be possible to access the type SysTime in the project as A_Lib.SysTime. 2) you could add the SysTimeCore library to the library manager of your library (POU Pool). This might seem as a double library, but because of the placeholder resolution only one will be used. Then, in your library manager of your library, select the SysTimeCore library, right-click, select "Properties" and enable the option "Publish all IEC symbols ...." For more information about library development, you could follow our advanced training course in Ridderkerk. The next is scheduled for 24 and 25 June 2026 https://www.extendsmartcoding.nl/codesys-training/
Last updated: 2026-04-25

Post by baotthitawat on Cloud SCADA for Industrial Energy Monitoring CODESYS Forge talk (Post)
Recently I’ve been exploring ATSCADA iEnergy Tools for SCADA-based energy monitoring systems. One thing I find interesting is how modern SCADA platforms are evolving beyond traditional machine monitoring. Many industrial systems are now using Cloud SCADA architectures for centralized energy management, remote dashboards, and operational analytics. ATSCADA iEnergy Tools supports: Real-time energy monitoring Historical data logging MySQL integration Reporting and Excel export Remote SCADA dashboards Cloud-based monitoring systems I think this type of solution is practical for factories, power monitoring applications, building management systems, and other industrial automation projects where energy optimization is becoming increasingly important. Industrial automation is clearly moving toward web-based and cloud-connected SCADA platforms, especially as more facilities focus on digital transformation and smarter energy management
Last updated: 2026-05-26

Post by baotthitawat on Cloud SCADA for Industrial Energy Monitoring CODESYS Forge talk (Post)
Recently I’ve been exploring ATSCADA iEnergy Tools for SCADA-based energy monitoring systems. One thing I find interesting is how modern SCADA platforms are evolving beyond traditional machine monitoring. Many industrial systems are now using Cloud SCADA architectures for centralized energy management, remote dashboards, and operational analytics. ATSCADA iEnergy Tools supports: Real-time energy monitoring Historical data logging MySQL integration Reporting and Excel export Remote SCADA dashboards Cloud-based monitoring systems I think this type of solution is practical for factories, power monitoring applications, building management systems, and other industrial automation projects where energy optimization is becoming increasingly important. Industrial automation is clearly moving toward web-based and cloud-connected SCADA platforms, especially as more facilities focus on digital transformation and smarter energy management
Last updated: 2026-05-26

Post by gseidel on Limit Axis CNC Jerk using SMC_Polynomial_AbsMaxLocs CODESYS Forge talk (Post)
Dear josepmariarams, this (internal) function has been removed with SoftMotion 4.17.0.0. We do not have public functions to compute the extrema of a polynomial. On which polynomials exactly did you call SMC_Polynomial_AbsMaxLocs? (Maybe if I understand better how you limit the jerk I can come up with an alternative.) There is no functionality to limit the jerk of individual axes in the CNC. With SMC_LimitDynamics, you can limit the velocity and acceleration of cartesian (X/Y/Z) and additional (P/Q/U/V/W/A/B/C) axes, but not the jerk. And with a quadratic ramp type you can limit the jerk on the path. Best regards, Georg
Last updated: 2026-06-10

Post by otbeka on CAA File Handling: "Read only" error CODESYS Forge talk (Post)
Hi, On CODESYS V3.5.19.50 I am using the latest 3S File Access library (CAA File & CAA Types) to save and retrieve configuration data from the User Data section of an SD card, via file called config.txt. The application reads the file to memory once upon initialisation, and then the only other operation is overwriting the file with the updated configuration whenever the user changes the settings. An issue is ocurring, seemingly randomly, where the config.txt file, and all surrounding directories, cannot be written to by the unit, returning a READ_ONLY_CAA error upon file open. This sometimes does not clear even after power-cycling the PLC several times, yet checking the file permissions with ls -l shows normal read, write, and execute access. I am wondering if this is caused by the PLC itself or by an issue in my application. I have included my CAA File handler function block (SD_Card_Bin(FB).txt) and any associated types/calls below: TYPE ConfigData : STRUCT Config : ARRAY[0..256] OF STRING(64); NumberOfStrings : UDINT; END_STRUCT END_TYPE TYPE Buffer : STRUCT Data : ARRAY[0..SIZEOF(ConfigData)] OF BYTE; DataLength : UDINT; END_STRUCT END_TYPE A case within my MAIN PRG: mode.WriteConfigDataToFile: VisuElems.CURRENTVISU := 'Screen_Write'; IF xModeHasChanged THEN iErrorCount := 0; iRoute := 0; END_IF CASE iRoute OF 0: inBuffer := ConfigData_To_Buffer(GVL.UnitData); xConfigError := FALSE; xDataConfigured := FALSE; iRoute := 1; 1 : //Read Data from Card SD_Card_Bin.strFileName :=FileName; SD_Card_Bin.iFileOperation := 2; SD_Card_Bin(xExecute :=TRUE, WriteBuffer := inBuffer, xDone =>xDataConfigured, xError=>xConfigError, strErrorCodes=>strError); IF xDataConfigured THEN SD_Card_Bin(xExecute :=FALSE); IF xConfigError THEN iRoute := 32767; ELSE iRoute :=100; END_IF END_IF 100: // The end bCurMode := mode.DisplayProcessVariables; 32767: // Config error iErrorCount := iErrorCount + 1; IF iErrorCount > 2 THEN // Repeats 3 times, if no progress abandons and returns error bCurMode := mode.WriteError; ELSE iRoute := 0; // Try again END_IF END_CASE I'd like to rule out my application as the cause of this bug - help via comments or criticism would be greatly appreciated.
Last updated: 2025-03-19

Post by annd on Migration von "CODESYS Control for PFC200 SL" zu WAGO FW26 "CODESYS V3.5.19.2" CODESYS Forge talk (Post)
Hallo, da Wago nun von eCockpit zum offenen "CODESYS Development System V3" wechselt, möchte ich meinen bestehenden 750-8212 von der PFC200 SL auf die Wago Firmware umstellen. Welche Schritte sind dabei notwendig? Den Controller würde ich auf die aktuelle FW 26 updaten und die 3.5.19.2 von Wago mit den Descriptions verwenden. Reicht es im Codesys Projektbaum mit "Gerät aktualisieren" auf den Wago Controller zu wechseln? Es wird dann statt dem "Pfc200Bus"ein leerer K-Bus und ein leerer Com-Port angezeigt. Müssen die einzelnen Module dann darunter neu angelegt und alle E/A Variablen manuell neu eingetragen werden? Das exportieren und danach wieder importieren funktioniert nicht, weil die Namen bzw. Adressen unterschiedlich sind. Ist das so richtig? Kann der Block "Modbus_COM_Port - Modbus_Master_COM_Port - Modbus_Slave" so bleiben wie bisher oder muss das auch unter dem neuen COM-Port neu angelegt werden? Für ein paar Hinweise wäre ich dankbar. Schöne Grüße, annD
Last updated: 2023-11-17

Post by bruceae on Ethernet/IP Scan CODESYS Forge talk (Post)
Hello, I have a robot configured as a Generic Ethernet Module under Ethernet/IP Scanner. I can not see the change of state of the outputs coming from the robot on the codesys side in real-time. (The robot has it's own internal program that would changes the values of remote outputs 0-3 off and on). Also when I send data down to the inputs of the robot it doesn't transfer over as expected. As an example I'll send to the robot's input bit 0 a value of 1. It doesn't see that value change. However, when I write that input bit 0 back to a value of 0, the robot changes state and shows a value of 1. And if I change the state of a different bit, the other bits update properly, except for the bit that I changed. Any advice would be greatly appreciated, and if anything else is needed let me know.
Last updated: 2024-09-10

Post by atcprojectteam on Modbus Function Code 15, writing multiple coils CODESYS Forge talk (Post)
Hi all, I am using an RSTI-EP I/O card along with the EPXMBE101 Modbus/TCP network adapter. I have a Control Standard L license. I successfully connected to the I/O card via Modbus and can read inputs without any issues. However, when I try to write to the digital output modules using function code 15, I am unable to make any changes. Here’s what I have done so far: I created a small project using Structured Text. I set up Modbus channels (as shown in the attached image) and mapped the pins. When I use cyclic mode, the connection results in an error. However, when I use the rising edge, the connection works, but I don’t see any changes on the I/O card. For the output module, I assigned one bit to high. After that, I ran CODESYS Control Win V3. (Should I be running the PLC as well?) I built the program, but I am not receiving any response from the I/O card. Could you please advise on what might be causing this issue?
Last updated: 2025-02-26

Post by atcprojectteam on Modbus Function Code 15, writing multiple coils CODESYS Forge talk (Post)
Hi all, I am using an RSTI-EP I/O card along with the EPXMBE101 Modbus/TCP network adapter. I have a Control Standard L license. I successfully connected to the I/O card via Modbus and can read inputs without any issues. However, when I try to write to the digital output modules using function code 15, I am unable to make any changes. Here’s what I have done so far: I created a small project using Structured Text. I set up Modbus channels (as shown in the attached image) and mapped the pins. When I use cyclic mode, the connection results in an error. However, when I use the rising edge, the connection works, but I don’t see any changes on the I/O card. For the output module, I assigned one bit to high. After that, I ran CODESYS Control Win V3. (Should I be running the PLC as well?) I built the program, but I am not receiving any response from the I/O card. Could you please advise on what might be causing this issue?
Last updated: 2025-02-26

Post by pikebuster on Help for a newbie CODESYS Forge talk (Post)
Can somebody help me with this? I have problem with the button! This task must be solved using Sequential Function Chart (SFC), IEC 61131-3. TASK Create an SFC program to control a traffic light at an intersection. Description: You will program a traffic light that has three phases: Green, Yellow, and Red. The traffic light must follow these rules: Green light is on for 10 seconds. Yellow light is on for 3 seconds. Red light is on for 10 seconds. If the pedestrian button is pressed, the system must keep the red light on for 20 seconds during the next cycle. After the pedestrian has “crossed,” the system should return to its normal cycle. Basic Steps: Initialization: Start by setting the traffic light to Red. Green Phase: After 10 seconds, switch to Green. Yellow Phase: After 10 seconds in the Green phase, switch to Yellow. Red Phase: After 3 seconds in the Yellow phase, switch back to Red. Loop: Repeat the cycle. Use, for example, lamp symbols in the visualization module to simulate the traffic light. You may also add a simple pedestrian light if desired.
Last updated: 2025-03-11

Post by fredsta on Unable to load dynamic modules (Download failed: Application=Application) CODESYS Forge talk (Post)
Hey there, I am currently trying to find a good solution for the communication between CODESYS Control on Raspberry Pi and "the rest of the world", i. e. the things apart from CODESYS on my linux. My first approach was to use the c-integration. So I created a lib, defined extern fbs, compiled the code on my Pi using the SDK and put the .so into my lib project. When I try to log into the Pi and load the program, I get the error message which you can see in the attached picture. "Die dynamischen Module der C-Integration konnten nicht auf das Laufzeitsystem geladen werden" is german and means roughly "the modules from the c-integration could not be loaded onto the runtime system." Is this normal? Am I doing something wrong? I will have a look at the unix domain socket thing next, as I am still in the process of finding the best solution for the communication.
Last updated: 2024-02-15

Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error CODESYS Forge talk (Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27

Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error CODESYS Forge talk (Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27

Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error CODESYS Forge talk (Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27

Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error CODESYS Forge talk (Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27

Post by dominggus on when going online, stuck on "Syncing file "visuelemsdatetime.tl_datetime.txt" CODESYS Forge talk (Post)
Hi, We are currently using a Raspberry Pi 4 CM4 module in a EdgeBox RPI 200 - Industrial Edge Controller running the latest CODESYS Runtime Package 4.11.0.0. On the PC (actually an Intel Macbook Pro running Windows 10 in Parallels) we run CODESYS V3.5.19.50. Yesterday end of day when I was about to logoff and head home, I wanted to send the latest build to the Raspberry I clicked the Login button to compile a new version and then sync the application and all the files, it get's stuck on the last file to sync (see attached screenshot). This takes eternally, although sometimes, when I use my SFTP client (Cyberduck) and go into the raspberry and refresh the directory /var/opt/codesys/PlcLogic/visu/, or when I open the actual file visuelemsdatetime.tl_datetime.txt, it gets un-stuck (forcing a refresh, which might fix the syncing issue) and CODESYS continues and I can click the Start button to start the application. But this SFTP force refresh trick does not always help either... What could be the issue here? network connectivity? Can someone please help me out?
Last updated: 2024-03-02

Post by rk-gaw on Unhandled exception and refactoring error CODESYS Forge talk (Post)
Hello everyone. I hope this is the right place to ask for help, this error is causing me a great amount of time loss and I really would like to end this nightmare. I don't know why but at times if I try to Browse -> Display Cross Reference on a variable Codesys just crashes. I'll attach the file with the complete crash report hoping someone can figure why it happend. I think that the unhandled exception comes from the PersisranceManager Module and is connected with the other big problem I'm facing: I cannot refactor in my project, if I'll try to refactor a POU name the whole POU will become "frozen", it's like its desynchronizing from the project and the project cannot find the pointer to the POU once I refactor it. And when I open the project a warning pop-up will show up with the frozen POUs name, but I cannot figure out what the warning is telling me. I'll attach every warning and error pop up the project is showing me, and thanks in advance to anyone who can figure something out.
Last updated: 2025-12-10

Post by salvatorethomas on Port instantiation of serial interface in WAGO PLC using Modb_L05.lib in CoDeSys v2.3 CODESYS Forge talk (Post)
Hi — good description of the problem. A few suggestions / questions that might help narrow this down: Since your first serial port (COM2) works fine but the second (COM4 + MODBUS_EXT_MASTER) never opens, check whether the two ports are truly independent — some WAGO modules share internal resources, so COM4 might conflict with other functions or modules. Make sure that the physical wiring and module configuration for the second port (baud rate, flow control, RS-485 vs RS-422, etc.) exactly match what the library expects — a mismatch in flow control or wiring could prevent port opening even if the LED signals seem OK. Try using a plain SERIAL_INTERFACE on COM4 first (like you did for COM2) without Modbus logic — if that opens, you know the hardware + port config is fine, so the issue is more likely with modb_L05.lib. If the port opens but Modbus still fails, enable debug/logging (if available) to inspect whether the port opening fails or the subsequent Modbus negotiation fails. If you like — I can share a minimal example project I used with WAGO + COM4 + Modbus that worked; you could adapt that to test your setup. Wacky Flip
Last updated: 2025-12-01

Post by bmatlove on Re-create CoE online window in Visu CODESYS Forge talk (Post)
Hello, I am trying to re-create the CoE online window within a Visu for purposes of checking and interacting with device parameters occasionally for maintenance purposes. To minimize reliance on using the IDE for misc interactions. Ideally, I would like to exactly mimic the CoE online window within the IDE. I assume that it uses a few tricks to minimize overhead, such as only polling registers which are within the visual scope, for example. I'm afraid it might be too much to ask for a pre-built drop-in Visu module to exist for this task. Do I have any options aside from manually re-creating all the logic to do this, relying heavily on SdoInfo function blocks? Is there a way for me to reference the device ESI file to shortcut the process of determining how many registers there are and getting the address for each?
Last updated: 2025-12-27

Post by chaylak on MC_ReadActualPosition with ST code CODESYS Forge talk (Post)
hi everyone, i am trying use MC_ReadActualPosition module in ST but i cant do it,( if i use CFC yes i read it) my axis is SoftMotion General Axis Pool->VirtAxisZ [Device: SoftMotion General Axis Pool] codesys V3.5 SP20 program: PROGRAM PLC_PRG VAR VirtAxisZ : AXIS_REF_VIRTUAL_SM3; fbPowerZ : MC_Power; fbReadPos : MC_ReadActualPosition; bEnable : BOOL := TRUE; lrActPos : LREAL; bValid : BOOL; bError : BOOL; fbResetZ : MC_Reset; xZ_Valid : BOOL; xZ_Busy : BOOL; xGlobalPower : BOOL; xGlobalReset : BOOL; xBtnTeachingMode : BOOL; lrGrvZ_OffsetTorque : LREAL := 0.5; lrPulseMmZ : LREAL; rPosFromBlock : LREAL; xZ_IsPowered : BOOL; xZ_PowerError : BOOL; iZ_PowerErrorID : LREAL; rZ_ActualPos : LREAL; lrTargetTorque : LREAL; sZ_ErrorString : STRING; //********** jog fbJogZ : MC_Jog; xJogForward : BOOL; xJogBackward : BOOL; rZ_ActVelocity : REAL; END_VAR fbResetZ( Axis:= VirtAxisZ, Execute:= xGlobalReset); fbPowerZ( Axis:= VirtAxisZ, Enable:= xGlobalPower, bRegulatorOn:= xGlobalPower, bDriveStart:=xGlobalPower , Status=> xZ_IsPowered, Busy=> xZ_Busy, Error=> xZ_PowerError, ErrorID=> iZ_PowerErrorID ); IF xGlobalPower THEN fbJogZ( Axis:= VirtAxisZ, JogForward:= xJogForward, JogBackward:= xJogBackward, Velocity:= 100, Acceleration:= 100, Deceleration:= 100, Jerk:= 1000); END_IF fbReadPos( Axis := VirtAxisZ, Enable := TRUE, Valid => bValid, Position => lrActPos, Error => bError ); IF VirtAxisZ.bError THEN sZ_ErrorString := 'Z Ex err'; ELSIF NOT xZ_IsPowered THEN sZ_ErrorString := 'Z Ex (Power Off)'; ELSE sZ_ErrorString := 'Z Ex Ready'; END_IF IF xBtnTeachingMode THEN lrTargetTorque := lrGrvZ_OffsetTorque; ELSE lrTargetTorque := 0; END_IF VAR_INPUT CFC_Motion: INT; END_VAR
Last updated: 2026-05-15

Post by critcho on WebVisu Numpad dialog - Dialogtitle not accepting string variable CODESYS Forge talk (Post)
I have a WebVisu page which is re-used for multiple types of gas; it displays the alarm thresholds etc. for one gas at a time. I have an array of structures holding the set-points for each of the gasses. I'm trying to change the dialog title for the value input pop-up (VisuDialogs.Numpad). The Dialogtitle is set to Gas_Alarms.HighAlarmActivationLevelDialog, which is a string(50): When the gas type is changed (page first loaded, or prev/next buttons), METHOD Gas_Alarms.Update_Display_Variables is called, to update the strings used for the dialog titles so it shows GasName High Alarm Activation Level (EngineeringUnits), e.g. CO2 High Alarm Activation Level (PPM): HighAlarmActivationLevelDialog := Insert(' High Alarm Activation Level ()', EngineeringUnits, 30); HighAlarmActivationLevelDialog := Insert(HighAlarmActivationLevelDialog, GasName, 0); (That's not where the problem is, I'm just explaining why I'm using a variable dialogue title.) The variables used are definitely strings, but i'm always getting the error: "The type of the dialog title must be either STRING or WSTRING". I've tried moving HighAlarmActivationLevelDialog etc. to the GVL and also changing them to WSTRING, I even tried adding them to the structure array, but I always get the same error. Clearing the dialog title for that element removes the error - so I'm confident it's not a phantom error caused by something else. But I should be able to add these titles, can't just nuke them all to make it work. The MinVal and MaxVal for the Numpad are called from the array, e.g. GVL.Gas_Alarm_Configs[0].ScaledValueMIN, they are not getting an error. I am using array indexes 1 - 5 for the gasses, when I load the form or change gas, I copy the selected index to index 0 of the array, and values from Gas_Alarm_Configs[0].[ALL] are displayed on the page. When they hit save, I copy Gas_Alarm_Configs[0].[ALL] to Gas_Alarm_Configs[CurrentGasIndex].[ALL]. (ALL just means every element, I can't figure out how to display an asterix in this question... :) ) I've searched online for variable title dialog, but not found anything to help. Thanks for your help!
Last updated: 2025-05-29

Post by ara32 on CODESYS 4 Linux: CODESYS Forge talk (Post)
Hello! I managed to correctly launch CODESYS Developer Studio 3.5.17, almost all functionality works. The only issue remaining is that when connecting to a device and obtaining its public key, the NCryptEncrypt function is called, which is not fully implemented in the DLL source code, resulting in the connection not being established. Currently, the code of this function in the Wine repository looks like this: SECURITY_STATUS WINAPI NCryptEncrypt(NCRYPT_KEY_HANDLE key, BYTE *input, DWORD insize, void *padding, BYTE *output, DWORD outsize, DWORD *result, DWORD flags) { struct object *key_object = (struct object *)key; TRACE("(%#Ix, %p, %lu, %p, %p, %lu, %p, %#lx)\n", key, input, insize, padding, output, outsize, result, flags); if (flags & ~(NCRYPT_NO_PADDING_FLAG | NCRYPT_PAD_OAEP_FLAG | NCRYPT_PAD_PKCS1_FLAG | NCRYPT_SILENT_FLAG)) { FIXME("Flags %lx not supported\n", flags); return NTE_BAD_FLAGS; } if (flags & NCRYPT_NO_PADDING_FLAG || flags & NCRYPT_PAD_OAEP_FLAG) { FIXME("No padding and oaep padding not supported\n"); return NTE_NOT_SUPPORTED; } if (key_object->type != KEY) return NTE_INVALID_HANDLE; return map_ntstatus(BCryptEncrypt(key_object->key.bcrypt_key, input, insize, padding, NULL, 0, output, outsize, result, flags)); } The program crashes due to the NCRYPT_PAD_OAEP_FLAG flag. I'm not proficient in C++, but I attempted to add handling myself, and here's the result: SECURITY_STATUS WINAPI NCryptEncrypt(NCRYPT_KEY_HANDLE key, BYTE *input, DWORD insize, void *padding, BYTE *output, DWORD outsize, DWORD *result, DWORD flags) { struct object *key_object = (struct object *)key; TRACE("(%#Ix, %p, %lu, %p, %p, %lu, %p, %#lx)\n", key, input, insize, padding, output, outsize, result, flags); if (flags & ~(NCRYPT_NO_PADDING_FLAG | NCRYPT_PAD_OAEP_FLAG | NCRYPT_PAD_PKCS1_FLAG | NCRYPT_SILENT_FLAG)) { FIXME("Flags %lx not supported\n", flags); return NTE_BAD_FLAGS; } if (flags & NCRYPT_NO_PADDING_FLAG) { FIXME("No padding not supported\n"); return NTE_NOT_SUPPORTED; } BCRYPT_OAEP_PADDING_INFO oaepInfo = { 0 }; oaepInfo.pszAlgId = BCRYPT_SHA1_ALGORITHM; NTSTATUS status = BCryptEncrypt(key_object->key.bcrypt_key, input, insize, &oaepInfo, NULL, 0, output, outsize, result, flags); if (key_object->type != KEY) return NTE_INVALID_HANDLE; return map_ntstatus(BCryptEncrypt(key_object->key.bcrypt_key, input, insize, padding, NULL, 0, output, outsize, result, flags)); } Now, when calling the connection, it crashes with the error "bcrypt:BCryptEncrypt flags 0x4 not implemented." Can anyone help with enhancing this functionality or at least point me in the right direction?
Last updated: 2024-03-22

Post by mariusz997 on Visualisation - internal error CODESYS Forge talk (Post)
Hi everyone. I try to reach Codesys but I have problem on the beginning. I use Codesys 3.5.18.60 and 3.5.18.30 . On both version I have this same problem - when I create new standard project with controller Control Win v3 x64, empty PLC program - I compile it and everything is ok. But when I add visualisation without any elements and compile it - I get: ~~~ ------ Build started: Application: Device.Application ------- Typify code... Generate code... Generate global initializations... [WARNING] SortingStation: HMI Device: PLC Logic: Application: Missing element configuration. Element may not be usable. [WARNING] SortingStation: fbOutletConveyour Device: PLC Logic: Application: C0196: Implicit conversion from unsigned Type 'WORD' to signed Type 'INT' : Possible change of sign [ERROR] Internal error:System.NullReferenceException: Odwołanie do obiektu nie zostało ustawione na wystąpienie obiektu (in english: Object reference not set to an instance of an object.). w _3S.CoDeSys.Codex86_64.V351500.CPUx86_64.CodeStore(TypeClass tc, Register RegBase, Register RegIndex, Int32 nOffset, Register RegSrc, Int32 nScale) w _3S.CoDeSys.Codex86_64.V351500.Codex86_64_V351500.GenerateVarAbsolut(IVariableExpression varexp, Int32 iArea, Int32 nAddress, IIndexInfo indexinfo, ICompiledType ctype, Int32 nTypeSize, IAccessMode am) w ..(_IVariableExpression ) w ..(IExprement ) w ..(IExprement ) w ..(_ICompoAccessExpression ) w ..(IExprement ) w _3S.CoDeSys.Codex86_64.V351500.Codex86_64_V351500.Generate(IAssignmentExpression assign) w ..(_IAssignmentExpression ) w ..(IExprement ) w _3S.CoDeSys.Codex86_64.V351500.Codex86_64_V351500.Generate(IExpressionStatement expstat) w ..(IExprement ) w _3S.CoDeSys.Codex86_64.V351500.Codex86_64_V351500.Generate(ISequenceStatement seq) w ..(IExprement ) w _3S.CoDeSys.Codex86_64.V351500.Codex86_64_V351500.Generate(ISequenceStatement seq) w ..(IExprement ) w _3S.CoDeSys.Codex86_64.V351500.Codex86_64_V351500.Generate(ISequenceStatement seq) w ..(IExprement ) w _3S.CoDeSys.Codex86_64.V351500.Codex86_64_V351500.Generate(ISequenceStatement seq) w ..(IExprement ) w _3S.CoDeSys.Codex86_64.V351500.Codex86_64_V351500.Generate(ISequenceStatement seq) w ..(IExprement ) w _3S.CoDeSys.Codex86_64.V351500.Codex86_64_V351500.Generate(ICompiledPOU cpou, ISequenceStatement mainRoutine, Boolean bKeepCompileInformation, IEnumerable`1 subroutines) w _3S.CoDeSys.Codex86_64.V351500.Codex86_64_V351500.Generate(ICompiledPOU cpou, Boolean bKeepCompileInformation) w ..(_ICompiledPOU ) w _3S.CoDeSys.Compiler35180.Phase5_Codegeneration.Codegeneration.(_ICompiledPOU , _ISignature ) w ..(_ICompiledPOU , Boolean , Boolean , _ICompileContext , _ICompileContext , Boolean , Codegeneration , Boolean& , Boolean , Boolean ) w ..(Boolean , Boolean , _ICompileContext , _ICompileContext , InitExitSignatureInfo , Boolean , Codegeneration , _ISignature , Boolean& , Boolean , Boolean ) w _3S.CoDeSys.Compiler35180.CompilerPhases.CompilerPhase5_Codegenerator.(Codegeneration , _ISignature , InitExitSignatureInfo& , Boolean& ) w _3S.CoDeSys.Compiler35180.CompilerPhases.CompilerPhase5_Codegenerator.(Codegeneration , _ISignature ) w _3S.CoDeSys.Compiler35180.CompilerPhases.CompilerPhase5_Codegenerator.(ICodegenerator ) w ..() w ..() Build complete -- 1 errors, 2 warnings : No download possible ~~~ Could someone help me with this problem? Thank you in advance Mariusz
Last updated: 2025-11-11