Post by timvh on OSCAT Scale_r function not working in LD 4.60 works in LAD2 on 3.5.21sp3 CODESYS Forge talk (Post)
It seems like a bug in FBD. Work-around: If you click on the small line between the box and the output variable and delete this, the variable is removed. When you then assign a variable again (Ctrl-A), then you will see that the line will be a bit longer. If you then select the previous variable, you will see that it works.
Last updated: 2025-10-26

Post by gseidel on Scara3 kinematic robot error CODESYS Forge talk (Post)
Hi aniket-b, the maximum cycle time of the EtherCAT_Task is very high, ca. 35 ms. Could you please check if this is just the first cycle after starting the application or if it happens during motion? (You can reset the times in the task configuration by right-clicking in the "monitoring" tab.) Another thing to try: put the SoftMotion_Planning task on a different core. Best regards, Georg
Last updated: 2026-01-07

Post by jgalaska on SMC_Trafo 6DOF Config Error CODESYS Forge talk (Post)
Hello, Recently I was trying to run 6DOF robot in codesys via SMC_Trafo_ArticulatedRobot_6DOF, unfortunately no matter what parameters I tried, it always outputs InvalidConfig Error. I saw the same issue in a topic: https://forge.codesys.com/forge/talk/Motion/thread/16e1f0327f/ But if I understand correctly, the user solved it by developing his own version of this block. I wanted to know if it is a bug in the library (SM3_CNC 4.20.0.0) or am I doing something wrong? Can anyone confirm that they can use the FB without it reporing the Error? Kind regards,
Last updated: 2026-01-21

Post by risele on dynamic modbus devices CODESYS Forge talk (Post)
Have the same issue: I'm making a test setup for modbus devices testing and calibration. One is run for every possible address, and it starts with minimal request: if the device is found, it continue to work with it, otherwise it's set to Disabled temporary. Those state machines are running under FOR cycle, and disabled are just skipped. Every instance have its own timer for not running too frequently and a start delay, so the actual requests are separate in time. I also check not for a single error, but have some timer to allow one-two timeouts. The small program disables and re-enables devices temporary (manually, since i could not iterate over MB devices). VAR Reset:ARRAY[1..GVL_MB.MD_COUNT] OF R_TRIG; i:INT; END_VAR {IF hasconstantvalue(GVL_MB.MD_COUNT, 1, >= )} i:=1; MD_1.Enable:=GVL_MB.MDPortsEnable[i]; Reset[i](CLK:=GVL_MB.MDPortsEnable[i]); MD_1.xReset:=Reset[i].Q; {END_IF} {IF hasconstantvalue(GVL_MB.MD_COUNT, 2, >= )} i:=2; MD_2.Enable:=GVL_MB.MDPortsEnable[i]; Reset[i](CLK:=GVL_MB.MDPortsEnable[i]); MD_2.xReset:=Reset[i].Q; {END_IF} There is also program to re-enable devices periodically. METHOD ScanBus VAR_INPUT END_VAR VAR j:INT; (*block auto scanning if calibration is running for any device since it's data-reach process that should not be interrupted with modbus timeouts *) CalibrationBusy:BOOL:=FALSE; END_VAR CalibrationBusy:=FALSE; FOR j:=1 TO GVL_MB.MD_COUNT DO CalibrationBusy:=CalibrationBusy OR MD_Calibrate.AutoTesters[j].xBusy; END_FOR; IF CalibrationBusy THEN RETURN; END_IF tBusScanSchedule(IN:=(NOT tBusScanSchedule.Q), PT:=tBusScanPeriod); IF (NOT tBusScanDelayer.Q) AND (tBusScanSchedule.Q OR (NOT xFirstScanPerforemed)) THEN xBusScanBusy:=TRUE; MissingCounter:=0; xFirstScanPerforemed:=TRUE; FOR j:=1 TO GVL_MB.MD_COUNT DO (* MD_Calibrate is main calibration program. Identifiers - is array of State machines mentioned above Phase_Faulted is a state of Identifiers where I'm sure device is missing on the bus *) IF MD_Calibrate.Identifiers[j].state=eStateMDIdentifier.Phase_Faulted THEN MD_Calibrate.Identifiers[j].Rescan(); MissingCounter:=MissingCounter+1; END_IF END_FOR END_IF tBusScanPauser(IN:=tBusScanDelayer.Q AND (MissingCounter>0),PT:=tBusScanDelay*MissingCounter); xBusScanBusy:=tBusScanPauser.Q; xFirstScanPerforemed:=xFirstScanPerforemed OR tBusScanPauser.ET>=tBusScanPauser.PT; Also the GUI have buttons for each address possible that re-enables the device if required.
Last updated: 2 days ago

Post by marekxc on Error C0521 - unknow compiler CODESYS Forge talk (Post)
Select in tree "DEVICE", right-click and select "Update Device" Select "Library manager" and Change the version of the Library (down manualy). Samoetimes "Try reload Library". If you open a project version 3.5.19 in version 3.5.16, there are difficulties.
Last updated: 2023-09-02

Post by laazik2 on v3.5 SP19 - Modbus TCP Devices - Channel Limit? CODESYS Forge talk (Post)
I am actually wondering as well if there are plans to fix it or not? As adding two modbus devices creates it's own problems with connection limits and other issues, which some slave devices have.
Last updated: 2023-09-05

Post by jinil on Import RsLogix 5000 project to Codesys CODESYS Forge talk (Post)
Hello, I am trying to do the same thing. I want my Rslogix 5000 project into Codesys. Was wondering if you have found a way to do it. Thank you.
Last updated: 2023-09-07

Post by jinil on Import RsLogix 5000 project to Codesys CODESYS Forge talk (Post)
Hello, I am trying to do the same thing. I want my Rslogix 5000 project into Codesys. Was wondering if you have found a way to do it. Thank you.
Last updated: 2023-09-07

Post by eschwellinger on Device User Logon and No device is responding.. Pi4b codesys 3.5 SP19 2 + (64-bit) CODESYS Forge talk (Post)
CODESYS runtime version 4.9.0.0 for your Pi. ssh user should be pi. This is for RasperrPi Os 32 bit. If you are on RasperryPi OS 64Bit use Arm 64bit SL product as Runtime.
Last updated: 2023-09-11

Post by wehling-h on Troubles with using CAN API CODESYS Forge talk (Post)
Hi together, I'm using a 11bit driver system which seems to work well so far. May someone here knows if i have to configure a singleID for each message i like to receive and evaluate?
Last updated: 2023-09-11

Post by danwoodlock on RPI Zero w - Edge gateway cant install CODESYS Forge talk (Post)
Hello all, First post. I recently acquired an RPI zero W from amazon, and have been using it with Codesys v3.5 SP19 patch 2. I first got it working yesterday, and after installing the runtime on the Pi, I was prompted to install the edge gateway. Installation of the edge gateway failed because of unsupported architecture, undeterred I was able to connect to the pi and program as I wanted. The issue I've noticed is that if I do not load anything to the pi overnight, I can then no longer connect to the pi and download, although I can still ping it from my pc. I found that if I power cycle the PI, I am then able to connect again, and it works as normal. I did some googling and found instances where people recommended downloading the newest edge gateway, which brings me here. Wondering if there are any suggestions, or if this is a known issue. I actually tried installing all 3 versions of edge gateway for science, but all fail with the same message. Thanks -Dan
Last updated: 2023-09-13

Post by eschwellinger on PCAN serial "No CAN driver found" CODESYS Forge talk (Post)
which system are you using on the target system? If this is Linux this is different - in compare to use it on Control Win
Last updated: 2023-09-20

Post by sedoerr on Check For Open Dialogs On Client CODESYS Forge talk (Post)
FUNCTION CheckDialogOpen : BOOL VAR_INPUT sDialogName : STRING; END_VAR VAR pstClientData : POINTER TO VisuElems.VisuStructClientData; itfDialogManager : VisuElems.IDialogManager; itfMyDialog : VisuElems.IVisualisationDialog; END_VAR VisuElems.g_ClientManager.BeginIteration(); WHILE (pstClientData := VisuElems.VisuElemBase.g_ClientManager.GetNextClient()) <> 0 DO itfDialogManager := VisuElems.g_VisuManager.GetDialogManager(); itfMyDialog := itfDialogManager.GetDialog(sDialogName); CheckDialogOpen := VisuDialogs.VisuDlgUtil_IsDialogOpen(itfMyDialog,pstClientData,itfDialogManager); IF CheckDialogOpen THEN EXIT; END_IF END_WHILE
Last updated: 2023-09-26

Post by anhkdv on Motion FB Error CODESYS Forge talk (Post)
When I load the SMC_GroupWait command twice in a row into the buffer an error occurs when I try to MC_MoveLinearRelative in the dynamic coordinate system. If I use MC_MoveLinearAbsolute in the dynamic coordinate system, it still works
Last updated: 2023-10-23

Post by riccardo on VisuElems.CurrentUserGroupId is not stable CODESYS Forge talk (Post)
GoodMorning everyone. I have a system that, in case of alarm, have to block. When the operator logs in must have to acknoledge the alarm and should operate in the system freely. To perform this I detect the logged User by (VisuElems.CurrentUserGroupID <> 0) with a similar code to the the following: PROGRAM AlarmMngt VAR alarm : BOOL:= FALSE; Ack : BOOL:= TRUE; PushBottonOpening : BOOL:= FALSE; Valve : BOOL := FALSE; Flag: BOOL := FALSE; END_VAR IF alarm AND Ack AND (NOT Flag) THEN valve := FALSE; PushBottonOpening := FALSE; Ack := FALSE flag := TRUE; ELSIF (NOT alarm) AND Ack THEN flag := FALSE; END_IF (* if the system is in alarm but there is a logged operator that acknowledge the alarm the system allows the valve opening.*) IF (VisuElems.CurrentUserGroupID <> 0) AND Ack AND Alarm AND PushBottonOpening THEN Valve := TRUE; ELSIF (VisuElems.CurrentUserGroupID = 0) AND Alarm THEN valve := FALSE; END_IF The problem I have is in the last 5 lines of the code: Even if there is a logged in user, the GroupID variable is subjected to a refresh that cyclically set for an instant it to 0 and this close the valve making difficult to the user to work Now I solved it creating a time hysteresys cycle but it is not a good solution. Someone is able to explane me why the GroupID variable is sobjected to this refresh and how to stabilize to avoiding it? Thank you in advance, Riccardo
Last updated: 2023-11-10

Post by riccardo on VisuElems.CurrentUserGroupId is not stable CODESYS Forge talk (Post)
Goodmorning TimvH, Thanks for the reply. I don't know if your solution solve my trouble yet, I am going to see the link you sent me. In the mean time I try to explane better what I need to do. I have a turbine system that get in alarm under some condition (E.g low speed of turbine) and block the itself. When the system is stoped there is no speed turbine and the system cannot start. To give to the operetor the possibility to bypass the alarms, there is an acknoledgement alarm pushbutton. This bypass must not work for everyone but only for those client that perform the login by (User Management). Furthermore, if the user perform the (manual or automatic) logout in alarm conditions, the acknowlegment must be annulled and block the system again. To do this, I need to know if an operator is logged in the page and is working to fix the problem; otherwise the syste must autoturn off again. Now I go to study your solution, if I have explaned better and you have another idea tell me please.
Last updated: 2023-11-16

Post by nathant on Easiest RevPi PLC to configure HMI visualization with? CODESYS Forge talk (Post)
I'm worried that the Core SE (which I was originally going to go with) will not be straight foward in terms of setting up the HMI visualization. This is for an offline application, if that matters.
Last updated: 2023-11-28

Post by nathant on Easiest RevPi PLC to configure HMI visualization with? CODESYS Forge talk (Post)
I'm worried that the Core SE (which I was originally going to go with) will not be straightfoward in terms of setting up the HMI visualization. This is for an offline application, if that matters.
Last updated: 2023-11-28

Post by viktorr on ShareMemory library documentation CODESYS Forge talk (Post)
Hello, I was wondering if there was further documentation on the SharedMemory library in CodeSys outside of the code example provided, or maybe a way to access the source code of the shared memory implementation. Thank you in advance for any advice. - Viktor
Last updated: 2024-07-03

Post by viktorr on Shared Memory Requested Size CODESYS Forge talk (Post)
Hello Derek, I recognize this is an older post, but i was wondering if found any ways to remedy this. I am running into what i think is the same problem you had here. Thank you in advance for any information, Viktor
Last updated: 2024-07-04

Post by dekelec on Codesys 2.3 & Peak PCAN CODESYS Forge talk (Post)
IF you have an USB interface type in "Peak_USB" for CAN card driver (Name of CAN card driver). No need to add libraries for communication via CoDeSys Gateway. For other card types contact PEAK support and they will help you. Regards,
Last updated: 2024-07-08

Post by tyronnosaurus on ReceiveWatchdog FB not working on J1939 P2P PGNs CODESYS Forge talk (Post)
Hi guys. I've got a device that sends a status message over J1939 and a PLC running Codesys to receive it. This message uses a P2P PGN (as opposed to a broadcast PGN). Codesys can only read it if I mark the J1939_ECU as "Local" (see screenshot 1). The message is received correctly, that is not the problem. The problem is detecting if the message stops being received. Local ECUs have no Watchdog checkbox to detect if the message has been received in the last X seconds. In order to implement a watchdog, I've used a ReceiveWatchdog FB. The same code works well for any non-P2P message, but doesn't work for this particular P2P message I'm trying to monitor. Even if I physically disconnect the device, ReceiveWatchdog.xBusy stays True, and ReceiveWatchdog.xError never triggers due to a timeout error. Is there any caveat in the ReceiveWatchdog FB that makes it unable to monitor P2P PGNs in Local J1939_ECUs?
Last updated: 2024-07-11

Post by timvh on CanOpen write issue CODESYS Forge talk (Post)
See: https://content.helpme-codesys.com/en/CODESYS%20Examples/_ex_canopen_canopen.html SDO example: SegmentedAndBlockWriteExample: Writing if an object of any length via SDO (segmented transfer or block transfer) by means of CiA405.SDO_WRITE_DATA This help page also contains a link to a demo project.
Last updated: 2024-07-16

Post by mikek10 on Some 'pathetic' errors in SoftMotion program CODESYS Forge talk (Post)
Most FBs clock on the rising edge so if they are never called with xExecute = False then subsequent actions will not be performed.
Last updated: 2024-07-18

Post by drml on Array to String CODESYS Forge talk (Post)
If a size is not specified, CODESYS allocates 80 characters by default for a string. After 7 seconds, does your Json_string contain all of your 20000 key/values? Or is the result truncated to 80 characters?
Last updated: 2024-07-19