Post by acc00 on Main Task cycle too long leading to PLC Fail CODESYS Forge talk (Post)
I have 2 Wago PFC200 PLC, running with Runtime SP19 Patch 5, with the Redundant application. The PLC communicates as Modbus Master with at this moment 15 Modbus Slaves -later there will be 28 in total- (Drives, Power management units,...). These devices are connected in 2 rings (1 ring of Drives, 1 ring of Power Management units), with 2 Managed Moxa Switches being part of the ring. Each PLC is connected to one of these switches. The issue I'm encountering is that the Cycle time of the Active PLC goes very high when I'm closing the Drive ring (simulating an issue on one Cabinet supply, resulting in that one Drive shut down, which can happen on field quite often). As a result of this long cycle, the PLC fails and goes to Exception, and the Passive PLC does not take control of the system. A normal cycle is around 30ms for the Main task, and a few ms for the Ethercat task. When I monitor with Profiler, I see that in this Maximum Cycle, the main Task is only taking 13ms, so I'm not sure where the PLC is hanging for so long. Is the remaining cycle time the Redundant management/sync or something else? Thank you in advance.
Last updated: 2024-03-08

Post by rabaggett on Reading Named Pipes in Linux Is there a better way? CODESYS Forge talk (Post)
I have a Python program that will handle things in my application such as VISA over IP and Telnet control of instruments. I want the main control and HMI in Codesys. My problem is communication between the two. I have looked at several ways to accomplish this, and settled on having the Python program create two named pipes, one to send information to Codesys, and one for Codesys to send information to Python. The information would be packetized with \n for end of packet.. Seems simple. I think the named pipes method should work, but file reading in Codesys using the CAA file library starts to get difficult when the file is never ending, as in this case. Before I spend too much time making something that may be fundamentally flawed I want to ask. Is there a better way? Is there a way to read the file 'one line at a time' which might solve my never ending file problem? Thanks!
Last updated: 2024-05-09

Post by fizzy-bubblech on 3.5 P20 hangs - no response CODESYS Forge talk (Post)
Colleagues, i have the same problems. At the current time, I have to use the new version of the Codesys (3.5.20.10) + Control for Linux SL 4.11.0.0, but it works unstable : theree are a lot of freezes and not-respondings. I tested this on different projects: those that were created in the current version of the project, and those that were migrated from other versions of the development environment. Compiling a project without connecting to a controller is fast enough. The first downloading of the code into the controller, too. But as soon as you need to make edits and download a new code problems begin. Codesys "freezes" at the "Generation code" stage for 15-20 minutes. And only after that time loads the code into the controller. Previously, we used version 3.5.17.60 + Control for Linux SL 4.7.0.0. The process took 1-2 minutes. Do you have any ideas how can i fix it? I will be grateful for your answers.
Last updated: 2024-06-27

Post by squiggleypuff on Can't Add New Version of Modbus TCP Master CODESYS Forge talk (Post)
I'm having a tough time trying to get Modbus working on a Festo CPX-E PLC; it throws these pre-compiler errors as soon as I add in my Modbus TCP Master 3.5.12.30 to my project: I'm confused about the C0046 error, as I have IODrvModbusTCP 4.3.0.0 Library installed. So I thought maybe I needed to use the newest Modbus TCP Master 4.3.0.0, which is in my device repository: However, whenever I go to add this underneath the Ethernet adapter (which is version 4.2.0.0), the only TCP Master version available is the old 3.5.12.30 one, even if I have Display all versions checked.: I even went so far as to delete the old version, but then there were no options to add a Modbus TCP Master under my Ethernet adapter. What needs to be done to use the newest Modbus TCP Master? Or are these pre-compiler errors unrelated and I'm missing something? Any help greatly appreciated.
Last updated: 2024-04-04

Post by tariq on Using Hilscher CIFX Cards as EtherCAT Masters in CODESYS CODESYS Forge talk (Post)
Dear Codesys Support Team, I hope this message finds you well. I am currently working on a project that involves using a Hilscher CIFX card to act as an EtherCAT master within the CODESYS environment. Despite following the available documentation and setup guides, I have encountered some challenges and require assistance to ensure proper configuration and operation. Questions: 1- Could you please confirm if the Hilscher CIFX card is supported as an EtherCAT master in CODESYS? If so, are there specific drivers or configuration files that need to be installed? 2- Are there detailed setup guides or example projects available that demonstrate the integration of Hilscher CIFX cards with CODESYS for EtherCAT communication? 3- Is there any additional software or plugins required for ensuring seamless communication between the CIFX card and the EtherCAT slaves within CODESYS? Your support and guidance on these matters would be greatly appreciated, as it is crucial for the success of our project. Thank you for your time and assistance. I look forward to your prompt response. Best regards, TB
Last updated: 2024-07-02

Post by kevinrn on Github Actions CI/CD tasks - development topic CODESYS Forge talk (Post)
Hello community, I just want to inform you about our plans and the current status of automating the build process for CODESYS libraries. So it might be helpful for some people who are in the same situation. Background story: I am a software engineer at powerIO GmbH, normally I use high level languages for the products we develop and offer. Sometimes I work with my team on CODESYS libraries, which can also be found in the CODESYS store. Most of the time I spend with them on architecture tasks and tasks that are not directly related to our products. Every time I see the manual processes for releasing a library etc., I am very surprised about this time intensive process. Current situation: I know there has been a scripting interface for years. CODESYS Git was released a few years ago, but the scripting interface was only released a few months (weeks?) ago. We developed a pseudo-automated solution a few months ago, but it was all very hacky. So now there is a better Git implementation and also more modularization and installation options. For example, the CODESYS installer has a full CLI, which makes it very convenient to install CODESYS installations headless. Plans: I think it's the right time to develop a better automation solution. Most of our software projects are hosted on Github and we use Github actions very intensively for other software projects. Therefore, we have decided to use Github for our CODESYS library projects as well. Following tasks should be implemented in automation for CI/CD tasks: - Automated setup of CODESYS installation (Already released: https://github.com/marketplace/actions/setup-codesys-installation) - Checkout CODESYS libraries - Execute tests scripts - Sign CODESYS libraries - Extract Library documentation - Create CODESYS package - Sign CODESYS package Side Note: - This is mainly a side project, and we do not provide support for the CI/CD part. - This topic is here to help and also to get help from other software engineers. - This project and idea is not prioritized as I am currently the only one working on it and I hope it will help us and also others and increase productivity. - We are putting this out there as an organization, but priorities can change quickly and the CI/CD tasks I am developing are mostly done in my spare time. So please don't expect this to happen in a short time or even be fully completed. I would be very happy if some ppl will join the development process and might be open to discuss some technical details for this. I hope this topic is not to off-topic, but I think the CI/CD part is very important today and it can increase a lot of quality and push productivity. Thanks :)
Last updated: 2024-03-28

Post by hanoues on setting date and time on CPX-E CODESYS Forge talk (Post)
Hello, Can anybody here tell me how to modify the time and date on my CPX-E? I used the code I found on CODESYS online help, but it doesn't work. What am I missing? FUNCTION current_date_time : STRING VAR stUTC_Timestamp : SysTime; //utc time // ULINT#1528280694913 stLocal_TimeStamp : SysTime; //local time but is in general equal // ULINT#1528280694913 stdNow : SysTimeDate; //local time in an object to access each number (day, month...) dtNow : DATE_AND_TIME;//DT#2018-6-6-10:24:54 todNow : TIME_OF_DAY; // TOD#10:24:54.913 datNow : DATE; // D#2018-6-6 END_VAR SysTimeRtcHighResGet(stUTC_Timestamp); // ULINT#1528273494913 SysTimeRtcConvertHighResToLocal(stUTC_Timestamp, stdNow); //convert UTC ULINT to Local SysTime // stdNow.wYear = UINT#2018 // stdNow.wMonth = UINT#6 // stdNowy.wDay = UINT#6 // stdNow.wHour = UINT#10 // stdNow.wMinute = UINT#24 // stdNow.wSecond = UINT#54 // stdNow.wMilliseconds = UINT#913 // stdNow.wDayOfWeek = UINT#3 // stdNow.wYday = UINT#157 SysTimeRtcConvertDateToHighRes(stdNow, stLocal_TimeStamp); // ULINT#1528280694913 dtNow := TO_DT(stLocal_TimeStamp / 1000 ( ms )); // DT#2018-6-6-10:24:54 todNow := TO_TOD(stLocal_TimeStamp MOD TO_ULINT(T#1D)); // TOD#10:24:54.913 datNow := TO_DATE(dtNow); // D#2018-6-6 (convert to appropriate string) current_date_time := concat('$N[', TO_STRING(dtNow)); current_date_time:= concat(current_date_time,'.'); current_date_time:= concat(current_date_time, TO_STRING(stdNow.wMilliseconds)); current_date_time:= concat(current_date_time,'] - '); RETURN;
Last updated: 2024-05-21

Post by manuknecht on Opening a Dialog on a specific Client from ST CODESYS Forge talk (Post)
I managed to find a solution that seems to work reliably. As the VU.Globals.CurrentClient-filter accesses the CURRENTCLIENTID or at least a similar, internal variable it can only be used if called from a certain client (e.g. from a button in a visualization). My solution works by implementing a new client filter that compares the client ID of all clients to the ID of the last client that was used. The variable containing the data of the last client is defined as: G_LastClient : VU.IVisualizationClient; // Copy of last client that detected click This last client is then updated every time a button is pressed using the Execute ST-Code input configuration of the button: G_LastClient := VU.PublicVariables.Clients.Current; Next, I created a function block that implements the client filter interface as so: FUNCTION_BLOCK FB_LastClientFilter IMPLEMENTS VU.IVisualizationClientFilter VAR_INPUT END_VAR VAR_OUTPUT END_VAR VAR END_VAR Then i added a method to the FB called IsAccepted which is used to filter out the client. When creating the method, it should automatically be filled with the according variable declaration, as it is defined in the interface: (* For every client can be desided, if it is accepted. ``TRUE``: Client is accepted*) METHOD IsAccepted : BOOL VAR_INPUT (* The client, to check*) itfClient : VU.IVisualizationClient; END_VAR Now the client can be compared to the last used client as such: // check if clientID corresponds to clientID of last recorderd client IF itfCLient.ClientId = G_LastClient.ClientId THEN IsAccepted := TRUE; ELSE IsAccepted := FALSE; END_IF To make use of this custom client filter, initialize a variable with the client filter: LastClient : FB_LastClientFilter; // Client filter to find last used client Then use this client filter when opening or closing a dialog from ST: fbOpenMyDialog(itfClientFilter:=LastClient,xExecute:=TRUE,sDialogName:='VIS_MyDialog_DLG');
Last updated: 2023-09-27

Post by oi18ct on ARM SL Development Board Recommendation CODESYS Forge talk (Post)
Hello codesys forum, My company is looking at developing a solution with Codesys ARM SL. The requirements will not tax the capabilities of Codesys. I would like to buy an AMR 7 or 8 Dev Board for experimenting. I am looking for a recommendation as I have minimal experience with Linux. Any input from the forum would be most appreciated as the hardware requirements as provided by Codesys for ARM SL seem pretty minimal (basically a arm7 or 8 with Debian is all). Our needs are small in scale- something like 8 digital inputs, 6 digital outputs, 2 analog inputs and 1 analog output. A small gui will be published via web visualization for external display (no local display). Communications with ModbusTCP and uart/RS485. It may be necessary to access i2c and make c or python calls to some existing code that is pretty small. Something like the EMCraft STM32MP1 SOM Starter Kit or Octavo Systems OSD32MP1-RED development board? Ideally something that has a path to a SoM for production. Kontron appears to have some interesting options too. Just having a hard time deciding where to start. Thanks in advance... LC
Last updated: 2023-11-11

Post by ewi04 on Git with visu CODESYS Forge talk (Post)
Hi, I have several problems with the git extension. Situation: I am working with Codesys v3.5 SP19 Patch 1 and Git V1.2.1.0. The remote repository is GitLab Community Edition v16.1.2. I am working on a project with one other person. Problems: 1: After each start of Codesys all of the visu pages are marked as modified. So we have to discard all changes first. Otherwise the history is not clean and the merge request becomes more complex. I tested it with a new project and only local. I made the observation, that a page is not marked as modified when it is committed a second time (after a restart of codesys). But this is necessary after every change of a page. However, since we are working in a team, it seems we are playing ping-pong and so all pages are marked as modified on each startup. 2: Each image pool causes a parent child conflict. Also in my local project. The only solution that I have found, is to ignore the issue. Does anyone have the same problems? I think it looks more like bugs. Thanks ewi04
Last updated: 2023-11-22

Post by squiggleypuff on RemoteTargetVisu creates Unresolved Reference CODESYS Forge talk (Post)
I have a project with a Festo CPX-E-CEC-C1-PN PLC (Run-time version 3.5.12.50) that I have been developing on just fine using Codesys V3.5 SP19 Patch 5 (64bit). I am at the stage where I wanted to use the Festo HMI screen, and have added a RemoteTargetVisu object to my application. After adding this object, I am no longer able to log in to the PLC as I get an Unresolved Reference warning for 'USERMGRUSERGETPROPERTY' towards the end of the download process. I was able to find this post (https://forge.codesys.com/forge/talk/Visualization/thread/fc686a6cb2/) where the two possible solutions are to "set the placeholder to emtpy" or update the runtime. Problem is, I don't know how to do either of these things, as I'm still very green in Codesys land. I'd be happy to update the Festo PLC runtime, as that seems like the better option, but have not had any luck in finding a tutorial for this online. If anyone could point me in the right direction I'd appreciate it.
Last updated: 2024-03-19

Post by bruceae on Ethernet/IP Scan CODESYS Forge talk (Post)
Hello, I have a robot configured as a Generic Ethernet Module under Ethernet/IP Scanner. I can not see the change of state of the outputs coming from the robot on the codesys side in real-time. (The robot has it's own internal program that would changes the values of remote outputs 0-3 off and on). Also when I send data down to the inputs of the robot it doesn't transfer over as expected. As an example I'll send to the robot's input bit 0 a value of 1. It doesn't see that value change. However, when I write that input bit 0 back to a value of 0, the robot changes state and shows a value of 1. And if I change the state of a different bit, the other bits update properly, except for the bit that I changed. Any advice would be greatly appreciated, and if anything else is needed let me know.
Last updated: 2024-09-10

Post by davidbo on RPI can system operation like rm in a shell have an impact on a Task cycle time CODESYS Forge talk (Post)
I have noticed that a rm file1.txt command on a shell has an impact on the cycle time for a TASK writing to file2.txt. Seen in the Monitor fane of the Task configuration Furthermore if a TASK makes a system call like rm, its cycle time increases of course but it seems to have an invisible impact on other TASKs too. I have a TASK for handling communication over the CANbus (SPI) where it stops sending "Heartbeats" for many seconds when another TASK does a system rm. Why is that not seen on the Monitor fane? Is even codesyscontrol paused when system calls are made? The CPU load is about 30-40%
Last updated: 2024-09-23

Post by dkugler on TargetVisu Freezing CODESYS Forge talk (Post)
The only weird situation i remeber with particular or complete frozen target visu was after the rtc clock was fallen or set back to the past. It looked like after running a while the alarm history database crashed during writing entries at a date lot of years in the past. After setting the rtc clock to actual date/time and deleting the alarm db every thing worked fine. I don't know, if this is/was a problem of our PLC hardware/firmware? Maybe check date/time at your system?
Last updated: 2024-09-13

Post by davidbo on RPI can system operation like rm in a shell have an impact on a Task cycle time CODESYS Forge talk (Post)
CODESYS Control for Raspberry Pi MC SL v4.4.0.0 CANopen_Manager 4.2.0.0 I did not call rm directly from my TASK-i2c, it was trough the attached python script. It is not always a problem happens, but sometimes a rm takes a long time. I reduced the amount of calls to logi2c.py but I don't understand why TASK-i2c sometimes can cause problems for TASK-CAN
Last updated: 2024-09-27

Post by davidbo on RPI can system operation like rm in a shell have an impact on a Task cycle time CODESYS Forge talk (Post)
CODESYS Control for Raspberry Pi MC SL v4.4.0.0 CANopen_Manager 4.2.0.0 I did not call rm directly from my TASK-i2c, it was trough the attached python script. It is not always a problem happens, but sometimes a rm takes a long time. I reduced the amount of calls to logi2c.py but I don't understand why TASK-i2c sometimes can cause problems for TASK-CAN
Last updated: 2024-09-27

Post by niloufar on Execution Order of Function Blocks CODESYS Forge talk (Post)
Hi, Our program incorporates various function blocks and programs written in different languages such as St and SFC. They implement numerous actions and methods using different languages from their function blocks. My question is whether the execution order of function blocks is associated with the programming languages used. I understand that cycle time can be configured in the task configuration, but I'm curious if there is a specific sequence order of execution for function blocks written in different languages. For example, all function blocks in (ST) are executed first, followed by the execution of (SFC). Specifically, when the function is written in (ST) and the action is implemented in (SFC). I modified all function blocks in the main PLC program and configured a task configuration for the main program.
Last updated: 2023-12-13

Post by royw on Profinet library for C# CODESYS Forge talk (Post)
Hi, I don't know if I'm in the right place or if it's even possible... I'm looking for a way to address a Profinet device with Record Read and Write from my own PC. I actually only need very few commands to configure our device. This means setting the MAC address and a serial number. We would like to do this from a C# program. Now we are looking for a library or something similar. Since you can do it from Codesys, I thought there might be a DLL or something similar that you could use for this. As I said, we don't want real-time queries of the cyclic data but only record read/write. Does anyone have any helpful hint? Thanks in advance
Last updated: 2023-12-22

Post by i-campbell on What does CODESYS expect to do when I get such an error message CODESYS Forge talk (Post)
you need to get the addons that the person that programmed it used. I always store an .installation-config file alongside the project. If you have lost that, then it gets a bit of a headache: I think even with SP18 you can hit yes to open it anyway, and it will suggest which addons it thinks are missing, if you double click the yellow "missing-addons" in the status bar. If you know you have the right addons, you can do a "Save As.." and it will write your current addon list to the file, and you wont get the error next time.
Last updated: 2024-01-08

Post by cedriclee on RaspberryPI reconnection error CODESYS Forge talk (Post)
"Hello, I'm Cedric Lee, a PLC engineer based in Korea. I'm reaching out about an ongoing issue with the connection when attempting to control Beckhoff modules using Raspberry Pi with CODESYS for the first time. I use CODESYS to target the Raspberry Pi's IP, install version 4.10.0.0 of the CODESYS Runtime Package, and upon pressing Start in the Runtime, the target connects to the Raspberry Pi. However, within about a minute, an error window appears, stating 'no connection to the device. please rescan your network,' leading to the disconnection of the target. This cycle repeats. I've attached some pictures for your reference. I'm using CODESYS Development System V3, Raspberry Pi 4 Model B (installed as 64-bit), and Beckhoff EK1100 modules. If anyone has a solution to this issue, please help. Your assistance is greatly appreciated."
Last updated: 2024-01-11

Post by jtebokkel on Access to the path *** is denied CODESYS Forge talk (Post)
I am also having this issue. It was working fine for the first 2ish months and is now throwing this error. I can just try and go online again a second time and it works. I'm wondering if there is an environmental variable or something that isn't set that is causing it to use an empty path as a temp directory. The empty path will be the location the app is running from which is that path C:\Program Files\CODESYS 3.5.19.50\CODESYS\Common. The permissions don't allow a normal user to write to that directory which causes the error. It also only seems to happen when there are changes or the build has been cleaned.
Last updated: 2024-02-14

Post by sumit on Not able to see input data coming from eip adapter on codesys CODESYS Forge talk (Post)
dhumphries, I changed the datatype this time from BYTE to USINT (because that's what my adapter is sending: array of uint8_t). The text "New Help String" you saw in previous screenshots is just the description of the input/s (it can be anything). I also looked into the logs (see attached) for that ! sign next to the device, I found that connection is being timeout. I tried some suggestions from online such as increase the RPI but still got connection timeout issue, also by changing the datatype, I still don't see incoming data from the adapter, although its visible on wireshark. thanks,
Last updated: 2024-03-07

Post by superjojo2002 on Licensing info not available. CODESYS Forge talk (Post)
I recognized that I have to start the two services "/etc/init.d/codemeter" and "/etc/init.d/codemeter-webadmin" in the docker container as well. If I do so, then the command "cmu -x" returns root@sensoredge-field-netfield-produktmanagment:/# cmu -x cmu - CodeMeter Universal Support Tool. Version 7.60c of 2023-Aug-09 (Build 5625) for Linux/ARMHF 64-Bit Copyright (C) 2007-2023 by WIBU-SYSTEMS AG. All rights reserved. So this time there is no indication any more that "Codemeter is not running". But still we are getting the error when using the license manager in CODESYS development system.
Last updated: 2024-03-21

Post by vernon-laurence on EtherCAT fieldbus CODESYS Forge talk (Post)
The simplest way to do this would be to add a bus coupler dedicated to the expansion IO. The EtherCAT network does not fault when modules connected to the expander are not present. In the image below, nothing below the red line is present in the network - with the network working correctly. In your "base" project, simply include all of the possible modules, and then plug them in as you add pumps to the system. I would also highly recommend against the use of direct addressing. There are other methods to accomplish this, including using the "Optional" checkbox for modules and explicitly addressing them. Although, this would require more upfront work to design the network, and some additional work each time modules were added. https://content.helpme-codesys.com/en/CODESYS%20EtherCAT/_ecat_edt_slave_slave.html
Last updated: 2024-04-09

Post by wiresplus on How to Connect / Go Online without re-downloading the project CODESYS Forge talk (Post)
Hello, I have a PLC in a remote location. I can connect to it, but when I use a different PC, it asks me to re-download to the PLC - which will a) interrupt production and b) cause version issues. Codesys being open-source, if someone else has made changes, I need to be able to connect, upload the current project, compare it with mine and then decide what next. Every time I connect, it says Warning: An application 'Application' is currently in RUN mode on the PLC. As there is no matching compile information, this existing application needs to be replaced. Click 'Yes' to download the latest code or 'No' to abort. What am I doing wrong?
Last updated: 2024-04-13