Post by tvm on Web Client (HMI) Disconnects from Webvisu (Weidmuller u-OS)
CODESYS Forge
talk
(Post)
ok, that's different than our issue then. We're using Schneider Electric M262 PLCs, and we've had it where certain web browsers cause the web server to only allow https connections, but it's not recoverable with a refresh. It usually requires a power cycle or even a full firmware flash. Your issue might have more to do with the timing. I don't know if it helps you, but we normally run our visu task at 200mS, with an update rate of 200mS. Seems to work. I went through this: https://faq.codesys.com/pages/viewpage.action?pageId=112525371 but it really seems like trial and error.
Last updated: 2023-09-06
Post by derpaul on PFC200 Update to 4.9.0.0 - No Connection
CODESYS Forge
talk
(Post)
Hallo Today I decided to perform an Update on my PFC200 but after the Update the Device was not reachable anymore. I tried reseting to factory reset. Software reset and so on, but nothing helps... In my Router I can see it, I cann SSH into the PFC200 but it is not reachable. Then I try to go back to 4.8.0.0 But now I get this error: [INFORMATION] Befehl SSH auf root@192.168.1.17 ausführen: Laufzeitsystem stoppen [FEHLER] Fehlerausgabe: /etc/init.d/codesyscontrol: line 34: /opt/codesys/scripts/init-functions: No such file or directory [INFORMATION] Standardausgabe: /etc/init.d/codesyscontrol: line 34: /opt/codesys/scripts/init-functions: No such file or directory Please help, I can't get this thing working... Regards
Last updated: 2023-09-27
Post by derpaul on PFC200 Update to 4.9.0.0 - No Connection
CODESYS Forge
talk
(Post)
Hallo Today I decided to perform an Update on my PFC200 but after the Update the Device was not reachable anymore. I tried reseting to factory reset. Software reset and so on, but nothing helps... In my Router I can see it, I cann SSH into the PFC200 but it is not reachable. Then I try to go back to 4.8.0.0 But now I get this error: [INFORMATION] Befehl SSH auf root@192.168.1.17 ausführen: Laufzeitsystem stoppen [FEHLER] Fehlerausgabe: /etc/init.d/codesyscontrol: line 34: /opt/codesys/scripts/init-functions: No such file or directory [INFORMATION] Standardausgabe: /etc/init.d/codesyscontrol: line 34: /opt/codesys/scripts/init-functions: No such file or directory Please help, I can't get this thing working... Regards
Last updated: 2023-09-27
Post by ofey on Modbus TCP communication
CODESYS Forge
talk
(Post)
Hi! I tried setting up the PLC I'm working with (Beijer GN-9373) to connect to a modbus master running on a laptop. I have an ethernet connection (via USB-C to ethernet) between the laptop and the controller. I have tried following tutorial on how to set this up. I have added an ethernet device with the IP-address of the PLC. Further I added a ModbusTCP_Slave_Device with default settings. I get the error "Failed to open TCP Port: 1" when I try to go online with the PLC. Earlier I tested the exact same set up with the soft PLC from codesys. I can then read/write values correctly with the Modbus master i have running on the laptop. Hope anybody can help me with this, thanks in advance!
Last updated: 2023-10-06
Post by ewi04 on Recipe Manager - RecipeManCommands, load & write wrong values, Bug?
CODESYS Forge
talk
(Post)
Hallo, I have a strange problem with the recipe manager. ISSUE: When using RecipeManCommands not all values are loaded correctly. Saving a recipe with CreateRecipe(), ReadAndSaveRecipe() or ReadAndSaveRecipeAs() works without any problems. BUT: LoadRecipe(), WriteRecipe() or LoadFromAndWriteRecipe() do not load the data correctly. It is Interesting that we have a different error pattern with LoadRecipe() than with WriteRecipe() or LoadFromAndWriteRecipe(). LoadRecipe() does not load all data and WriteRecipe() or LoadFromAndWriteRecipe() overwrites some data or assigns it incorrectly. And it is also strange that LoadRecipe() writes the values to the PLC. Normally it doesn’t do it. It makes no difference whether the memory type is textual or binary. I have an object consisting of STRUCTs which is inserted in the recipe definition. Environment: Codesys V3.5 SP19 Patch 4 (64Bit), Recipe Management 4.2.0.0 *Add a project (reduced to the problem)
Last updated: 2023-11-15
Post by sean-barton on Function block method default arguments
CODESYS Forge
talk
(Post)
I have default arguments specified for function block methods but when calling a method, an error is produced requiring me to supply all the arguments despite there being default values. According to the online documentation, under section "Calling a Method" and subsection "argument passing" of the following link: https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_obj_method.html "Passing an argument for an input ... can be omitted ... for which a default or initial value was specified in the declaration..." I have found this to be the case for all Codesys IDEs I've used, 3.5.11, 3.5.16, 3.5.17, 3.5.19. Am I missing something?
Last updated: 2023-12-21
Post by fdmartello on Unable to compare projects containing alarm manager 4.5.0.0
CODESYS Forge
talk
(Post)
Hello. In Codesys version 3.5.19.50 when comparing two projects that have an "Alarm Configuration" obj from the Alarm Manager library vers. 4.5.0.0 the attached error pops up. This originally happened with two projects that I converted from vers. 3.5.17.30 so, thinking it was some conversion issue, I created two clean projects directly in 3.5.19.50 using the Standard Project template and only added the Alarm Configuration objects in them. The result is the same and the only way I found that allowed me to compare them is by deleting the incriminated object in one of the two projects. Has anyone else encountered this issue? Best regards
Last updated: 2024-01-19
Post by timvh on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
Are you using the Control Win SL (installed together with the development environment of CODESYS)? If yes, you might want to consider using the CODESYS RTE instead. This has real-time capabilities (running on separate core(s)). But to be able to use this, you have to install the CODESYS Ethernet driver for your network interface to be able to let the RTE access the network port also in realtime. See: https://store.codesys.com/en/codesys-control-rte-sl-bundle.html https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_windows_rts_v3.html PS, I haven't tested this myself yet, but you could try to use the SetCommunicationState method of the Profinet controller to see if you can reset and start the bus communication: result := PN_Controller.SetCommunicationState(eRequestedState := DED.DEVICE_TRANSITION_STATE.START); PS, if you are located in the Netherlands or Belgium, we could also provide the license(s) for you.
Last updated: 2024-02-28
Post by timvh on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
Are you using the Control Win SL (installed together with the development environment of CODESYS)? If yes, you might want to consider using the CODESYS RTE instead. This has real-time capabilities (running on separate core(s)). But to be able to use this, you have to install the CODESYS Ethernet driver for your network interface to be able to let the RTE access the network port also in realtime. See: https://store.codesys.com/en/codesys-control-rte-sl-bundle.html https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_windows_rts_v3.html PS, I haven't tested this myself yet, but you could try to use the SetCommunicationState method of the Profinet controller to see if you can reset and start the bus communication: result := PN_Controller.SetCommunicationState(eRequestedState := DED.DEVICE_TRANSITION_STATE.START); PS, if you are located in the Netherlands or Belgium, we could also provide the license(s) for you.
Last updated: 2024-02-28
Post by esave on Softmotion Light Problem: The license is missing or invalid
CODESYS Forge
talk
(Post)
Hello everybody I want to controll a stepper driver from Leadshine (EM3E-556E). The EtherCat slave is CiA 402 compatible. Because of this I bought the Softmotion Light Package from Codesys and implemented it in my project. I rightclicked the EtherCat slave and added the Softmotion Light axis. But now the error message shows: "The license is missing or invalid. The PLC runs in demo mode." What have i done wrong? I use Codesys 3.5.17. Is it possible that the stepper driver is not compatible with the Softmotion license? Thanks for all your help
Last updated: 2024-05-02
Post by kazuhiro on Problems using MySql Library and SysProcessExecuteCommand2 together
CODESYS Forge
talk
(Post)
I use fbMsSQL_compact(FUN) of the MySQL Library to write data to the database. There is no problem when writing data using only fbMsSQL_compact(FUN). However, when I try to write data obtained using SysProcessExecuteCommand2 to the database using fbMsSQL_compact(FUN), an error message "Dest server on ip address:xxx.xxx.xxx.xxx and port:1433 is unreachable" appears and writing is not possible. From what I have researched, it seems that writing is not completed in one cycle of fbMsSQL_compact(FUN), and when SysProcessExecuteCommand2 is executed first in the second cycle, the work done in one cycle of fbMsSQL_compact(FUN) is reset. Could you please give me some advice?
Last updated: 2024-06-18
Post by kazuhiro on Problems using MySql Library and SysProcessExecuteCommand2 together
CODESYS Forge
talk
(Post)
I use fbMsSQL_compact(FUN) of the MySQL Library to write data to the database. There is no problem when writing data using only fbMsSQL_compact(FUN). However, when I try to write data obtained using SysProcessExecuteCommand2 to the database using fbMsSQL_compact(FUN), an error message "Dest server on ip address:xxx.xxx.xxx.xxx and port:1433 is unreachable" appears and writing is not possible. From what I have researched, it seems that writing is not completed in one cycle of fbMsSQL_compact(FUN), and when SysProcessExecuteCommand2 is executed first in the second cycle, the work done in one cycle of fbMsSQL_compact(FUN) is reset. Could you please give me some advice?
Last updated: 2024-06-18
Post by ron-rp on Errors with VisuUserManagement library
CODESYS Forge
talk
(Post)
Hi all, I've played a bit with the VisuUserManagement library, and some other security option in my project, and I started getting this error when logging in - see attached pic. something to do with a specific screen in the library - VUM_Login. Also, Codesys started to ask me to log in to the library when logging in, asking to log in as user of the groups Maintainer or Owner, which I dont know either users (attached pic). when I close the login screen and try to log in to the PLC again, everything works again until I close and open Codesys. I do use user and password to login to the PLC, and this login screen is fine I know the user and pass I setup. anyone know what did I do wrong here and how to fix it?
Last updated: 2024-06-25
Post by toffeebonbon on EL7041-0052 - does it run with EL7041 SoftMotion?
CODESYS Forge
talk
(Post)
I let this project rest for a while and picked it up last week. I have been in contact with the support from beckhoff and got the information that the terminals were identical (communication wise). As the Log of the Axis (not the drive's log) shows the error when trying to write into the register 0x8012 and set the value for an encoder to a value that is the default - at least according to the manual - I was wondering if it is possible to "not write that value" to skip that part? Or am I misunderstanding the way the library communicates with the drive?
Last updated: 2024-07-24
Post by cfam on Codesys Control for PLCnext SL, Bus not running
CODESYS Forge
talk
(Post)
Good day I would appreciate it if you can give me some advice on how to fix my "Bus Not Running Error". I am Using Codesys 3.5 SP20 and Codesys Control PLCnext SL V4.12.0.0. Codesys control was installed on the device and I can log into it but it seems that it does not pick up the PLC or the IO attached (Please see attached Image). The Bus Cycle Task of the AXL F 2152 is set to Main Task and the "Always update Variable" is Enabled on each IO Module. My Main Task interval is set to 100ms and Priority is set to 0. I have tried other options and none seem to work. Your response to this issue will be highly appreciated.
Last updated: 2024-08-12
Post by cfam on Codesys Control for PLCnext SL, Bus not running
CODESYS Forge
talk
(Post)
Good day I would appreciate it if you can give me some advice on how to fix my "Bus Not Running Error". I am Using Codesys 3.5 SP20 and Codesys Control PLCnext SL V4.12.0.0. Codesys control was installed on the device and I can log into it but it seems that it does not pick up the PLC or the IO attached (Please see attached Image). The Bus Cycle Task of the AXL F 2152 is set to Main Task and the "Always update Variable" is Enabled on each IO Module. My Main Task interval is set to 100ms and Priority is set to 0. I have tried other options and none seem to work. Your response to this issue will be highly appreciated.
Last updated: 2024-08-12
Post by opineiro on Stack overflow with really simple function
CODESYS Forge
talk
(Post)
Hi, I have an issue with a function which sends a message through API Rest. I'm using a function from httpCLient library. I have tested this function inside a program and it works fine. But when I want to use it inside a function (so I can call it simultaneously from 2 different points on the main program) it gives a stack overflow error. In detail it says: "C0297 Stack Overflow on Main Task. Stack sizes... Call hierarchy:" I have simplified as much as I can the function, but I'm hitting a wall with this. Anybody has an idea of what's wrong? Thanks!
Last updated: 2024-09-16
Post by jari-koivuluoma on Newly created texlists wont appear in the selection dropdown
CODESYS Forge
talk
(Post)
When I create a new textlist in Codesys 3.5 SP19 Patch 5, it wont appear in the dropdown menu at Rectangle element > Dynamic texts > Text list. If I just type the name of the textlist to the field (in quotes), I get an error saying that some file is missing. Any good ideas what to do and what is going on. I recently updated to that version and I only now noticed this when I needed to add a new textlist so Im quite screwed with this not being able to add text lists. While im typing this, I tried copying an existing list and modifying it and it seems to show. Any ideas?
Last updated: 2024-09-19
Post by jacobwago on v3.5 SP19 - Modbus TCP Devices - Channel Limit?
CODESYS Forge
talk
(Post)
Hello, I have experienced the same issue as described above but for the Modbus Serial configurator. Looking for a solution. In v3.5 SP19 Patch 7 the Modbus Serial Master Slave configurator has a "virtual" limit of 10 channels. In v3.5 SP18 Patch 5 this virtual limit does not exist. I can successfully copy back and forth from 18 to 19 with out any build error. However, this is not a good solution for our customers. What is even more confusing is that the IoDrvModbus library is the same version (4.3.0.0) for both SP18 and SP19. Please help in providing a fix to the virtual channel limit of 10 in SP19. Thanks,
Last updated: 2024-09-29
Post by xabier on BUG CODESYS-NO WORK AUTOMATICALLY RESTARSLAVES
CODESYS Forge
talk
(Post)
I detect a Bug of Codesys....NO WORK AUTOMATICALLY RESTARSLAVES. I explain the secuence: I have click in my project the option AUTOMATICALLY RESTARSLAVES In the moment start my Ipc, the network ethercat start correctly I disconnect the wire of my first slave and later connect again the wire..(see the screen Bug Codesys restart slave1) NO work the restart automatic slaves...and is not possible execute of FB MC_REset beacuause appear this error (see the screen Bug Codesys restart slave2) The only way for resolver this problem is execute the FB SMC3ReinitDrive I replay the same with PLC BECKHOFF in Twincat3 and I havent this problem...In the moment connect the wire again in the slave the comunication of ehterCat restart and the slave comunication again with out problem
Last updated: 2024-11-07
Post by yannickasselin on MQTT QoS 1 & 2
CODESYS Forge
talk
(Post)
Hello, After some more tests, here is what I found out. It seems we have to increase the uiKeepAlive and tPingInterval parameters. If I increase the uiKeepAlive value to 60s and the tPingInterval to 30s, then if I disconnect the ethernet cable from Codesys and publish some messages to which Codesys subscribes to and then reconnect within 30s, I will get the messages. If I don't reconnect the cable within 30s (ping interval), the client goes in error with "ACKNOWLEDGE_TIMEOUT". When this happens, it will not automatically reconnect after reconnecting the cable. I have to disable and re-enable the client but I will not get the published messages. I need to do more tests because there are a lot of weird things happening when playing with the ping interval and the keep alive. It is not clear to me what does what. I even ended up not receiving messages anymore, even if I disabled and re-enabled the mqtt client. The client did not give any error. The only way I was able to get messages again was by modifying my client ID. After that, if I try to re-use one of the old client IDs, nothing works (publish, subscribe) and I get a TCP_INIT_ERROR and sometimes a TCP_READ_ERROR. I need more explanation/documentation about these weird behaviors. Maybe it is the way I use it, maybe it is related to the broker (I am using Mosquitto with default parameters). When using a Node-Red client, everything works perfectly. I am trying to achieve the same behavior with Codesys but it seems impossible so far.
Last updated: 2024-10-30
Post by scoob on ModbusFB - Slow Response Time
CODESYS Forge
talk
(Post)
Hello, I have been trying to use the ModbusFB functions so I can put some code into libraries, but it seems to be very slow for me. I have a Modbus device with 100ms registers. I previously setup 10 channels in the 'traditional' Modbus Slave with channels and mappings - and set a cyclic trigger at 100ms - this worked fine. I then tried the ModbusFB example, and setup reading the same 10 blocks of modbus addresses, copying the example and putting all of the requests into an array and triggering the requests sequentially. I timed how long the requests are taking to get round to each one, and it is around 1s 450ms. How do I speed this up to match the cyclic time? IF NOT(init) THEN init := TRUE; // Set the required IP address: ipAddress[0] := 192; ipAddress[1] := 168; ipAddress[2] := 1; ipAddress[3] := 10; // Pass the required IP address to the clinet FB: client_NetworkSwitch.aIPaddr := ipAddress; client_NetworkSwitch.udiLogOptions := (ModbusFB.LoggingOptions.ClientConnectDisconnect OR ModbusFB.LoggingOptions.ClientReceivedValidReplies); // Try to connect the client client_NetworkSwitch(xConnect:=TRUE); // Configure all the channels to read connecting them to the client: portStatus_Request(rClient := client_NetworkSwitch, uiStartItem := 4096, uiQuantity := 32, pData := ADR(portStatus), udiReplyTimeout := udiReplyTimeout); portSpeed_Request(rClient := client_NetworkSwitch, uiStartItem := 4352, uiQuantity := 32, pData := ADR(portSpeed)); flowControl_Request(rClient := client_NetworkSwitch, uiStartItem := 4608, uiQuantity := 32, pData := ADR(flowControl)); linkUpCounter_Request(rClient := client_NetworkSwitch, uiStartItem := 5888, uiQuantity := 32, pData := ADR(linkUpCounter)); txPacketCounter1_Request(rClient := client_NetworkSwitch, uiStartItem := 8192, uiQuantity := 100, pData := ADR(txPacketCounter1)); txPacketCounter2_Request(rClient := client_NetworkSwitch, uiStartItem := 8292, uiQuantity := 28, pData := ADR(txPacketCounter2)); rxPacketCounter1_Request(rClient := client_NetworkSwitch, uiStartItem := 8448, uiQuantity := 100, pData := ADR(rxPacketCounter1)); rxPacketCounter2_Request(rClient := client_NetworkSwitch, uiStartItem := 8548, uiQuantity := 28, pData := ADR(rxPacketCounter2)); txErrors_Request(rClient := client_NetworkSwitch, uiStartItem := 8704, uiQuantity := 64, pData := ADR(txErrors)); rxErrors_Request(rClient := client_NetworkSwitch, uiStartItem := 8960, uiQuantity := 64, pData := ADR(rxErrors)); // Trigger all client requests initially FOR clientRequestsCnt := 0 TO (SIZEOF(clientRequests)/SIZEOF(clientRequests[0]))-1 DO pClientRequest := clientRequests[clientRequestsCnt]; pClientRequest^.xExecute := TRUE; END_FOR // Prepare sequential trigger / control of client requests. clientRequestsCnt := 0; pClientRequest := clientRequests[clientRequestsCnt]; END_IF // Call the client to do request processing: client_NetworkSwitch(); // Now we trigger client request sequentially ... IF NOT pClientRequest^.xExecute AND NOT pClientRequest^.xDone AND run AND client_NetworkSwitch.xConnected THEN pClientRequest^.xExecute := TRUE; END_IF // .. and check result/error IF pClientRequest^.xExecute AND run AND client_NetworkSwitch.xConnected THEN IF pClientRequest^.xDone THEN // Prepare next trigger of client request (a rising edge of xExecute) pClientRequest^.xExecute := FALSE; IF clientRequestsCnt < SIZEOF(clientRequests)/SIZEOF(clientRequests[0])-1 THEN // next client request clientRequestsCnt := clientRequestsCnt + 1; ELSE clientRequestsIterationCounter := clientRequestsIterationCounter + 1; clientRequestsCnt := 0; END_IF pClientRequest := clientRequests[clientRequestsCnt]; END_IF END_IF I did try a semi-coded way using the IoDrvModbusTCP library, and setting the slave com settings, then 10 commands and 10 requests, then using a TP on xDone as a pause, before triggering another request - this is time the delay is around 120ms - so the device is fine with the speed, just something I am doing wrong in the ModbusFB method I am sure.
Last updated: 2024-04-26
Post by paulpotat on cm4 runtime problem
CODESYS Forge
talk
(Post)
Hello, I have exactly the same issue, with the following configuration : Hardware version >>> cat /proc/cpuinfo processor : 0 model name : ARMv7 Processor rev 3 (v7l) BogoMIPS : 108.00 Features : half thumb fastmult vfp edsp neon vfpv3 tls vfpv4 idiva idivt vfpd32 lpae evtstrm crc32 CPU implementer : 0x41 CPU architecture: 7 CPU variant : 0x0 CPU part : 0xd08 CPU revision : 3 processor : 1 model name : ARMv7 Processor rev 3 (v7l) BogoMIPS : 108.00 Features : half thumb fastmult vfp edsp neon vfpv3 tls vfpv4 idiva idivt vfpd32 lpae evtstrm crc32 CPU implementer : 0x41 CPU architecture: 7 CPU variant : 0x0 CPU part : 0xd08 CPU revision : 3 processor : 2 model name : ARMv7 Processor rev 3 (v7l) BogoMIPS : 108.00 Features : half thumb fastmult vfp edsp neon vfpv3 tls vfpv4 idiva idivt vfpd32 lpae evtstrm crc32 CPU implementer : 0x41 CPU architecture: 7 CPU variant : 0x0 CPU part : 0xd08 CPU revision : 3 processor : 3 model name : ARMv7 Processor rev 3 (v7l) BogoMIPS : 108.00 Features : half thumb fastmult vfp edsp neon vfpv3 tls vfpv4 idiva idivt vfpd32 lpae evtstrm crc32 CPU implementer : 0x41 CPU architecture: 7 CPU variant : 0x0 CPU part : 0xd08 CPU revision : 3 Hardware : BCM2711 Revision : a03141 Serial : 10000000d5be5b5f Model : Raspberry Pi Compute Module 4 Rev 1.1 Kernel version >>> uname -a Linux raspberrypi 6.1.21-v7l+ #1642 SMP Mon Apr 3 17:22:30 BST 2023 armv7l GNU/Linux OS Version >>> cat /etc/os-release PRETTY_NAME="Raspbian GNU/Linux 11 (bullseye)" NAME="Raspbian GNU/Linux" VERSION_ID="11" VERSION="11 (bullseye)" VERSION_CODENAME=bullseye ID=raspbian ID_LIKE=debian HOME_URL="http://www.raspbian.org/" SUPPORT_URL="http://www.raspbian.org/RaspbianForums" BUG_REPORT_URL="http://www.raspbian.org/RaspbianBugs" /boot/config.txt I added the following line : arm_64bit=0 CodeSys runtime version 4.10 Were you able to solve the issue @michelebianchi ? Any help with this would be appreciated... BR
Last updated: 2024-08-28
Post by kevinrn on CODESYS Development System V3 installation auf unter Parallells Windows 11auf MAC PRO M1 ARM Prozessor
CODESYS Forge
talk
(Post)
Hallo, das Thema ist ja etwas offtopic. Aber ich kann gerne mal von meiner Erfahrung berichten: Nachdem ich von 2020 bis 2023 immer einen MacBook Pro mit Intel CPU hatte (i9/32GB) und nun seit Januar 2024 mit dem M3 Max unterwegs bin kann ich Nachfolgendes berichten. Infos zu den Aufgaben, die ich damit erledige: Die Runtime nutze ich nicht auf dem Mac (Wenn ich von Mac rede, dann meine ich damit die Win11 ARM64 Parallels Umgebung) Ich nutze die IDE für Library development und für automatisierungs Tests von CI/CD jobs. Weiterhin öffne ich oft große Projektarchive mit teilweise 160 MB. Erfahrungen zur Installation von CODESYS Versionen: Ich habe einige Versionen installiert, unter anderem, 3.5.14.4, 3.5.17.2, 3.5.16.3, 3.5.18.4 und 3.5.19.6. Ich hatte mit keiner einizgen Installation ein Problem. Die Installation lief immer ohne Probleme durch. Runtimes (Control Win) installiere ich nicht. Ich nutze linux basierte Zielsysteme und bei bedarf eine Windows VM auf einen entfernen Host mit X64. Lokales Gateway läuft ebenso Sonstige Erfahrungen: Ich nutze viele Komponenten Querbeet: Alarming, AC Persistence, Symbol Konfiguration, CFC und ST Editor, externes Packages wie STWeep, Git für Library Entwicklung, Visu, etc. Mit keiner dieser "Komponenten" hatte ich schwierigkeiten oder einen Unterschied zu x64 systemen festgestellt. Man muss aber auch sagen, dass das alles nur ein kleiner Bruchteil ist, was die CODESYS Welt beinhaltet, deshalb sind diese Aussagen auch nur subjektiv aus meinem Erfahrungsbereich. Für das Entwickeln von Libraries sehe ich keine Performance Einschränkungen. Ganz im Gegenteil, für das, dass hier eine emulation stattfindet, ist es erstaunlich schnell. Meiner Meinung nach sind sogar einfache und kleine Projekte schneller als beim Intel Mac. Die Akku Leistung mit dem Mac und Parallels ist fantastisch. Lüfter hört man nicht mal bei der Nutzung von CODESYS. Beim Intel konnte ich sonst ein Spiegelei auf der Abdeckung zubereiten... Was evtl. etwas langsamer ist bzw. mir manchmal so vor kommt ist, der CFC Editor im Online Mode. Aber hierzu fehlt mir ein richtiger Vergleich. Fazit: Ich bin selbst erstaunt wie gut die CODESYS IDE auf einem ARM64 emuliert wird. Ich muss aber auch sagen, dass ich jederzeit eine x64 Workspace zur Verfügung habe, falls was nicht funktionieren sollte. Das habe ich mir extra zum Umstieg zu gelegt. Bisher habe ich es jedoch noch nie benötigt, da meine Anforderungen alle erfüllt werden. Es sollte einem aber bewusst sein, dass dies keine supportete Umgebung ist und man auch bei spezifischen Problemen keinen Support erwarten sollte. Ich nutze CODESYS ca. 4-12 Stunden die Woche und ich warte immer noch auf etwas, um meine X64 Cloud Workspace mal zu verwenden... Vielleicht hilft dir dies ja etwas bei der Entscheidung.
Last updated: 2024-03-21
Post by gerdkoch on Dynamic I/Os Mapping
CODESYS Forge
talk
(Post)
Hi, I assume that you have a Pfc200 G2 or something and work with the original WAGO runtime. Then I would recommend the WagoSysDynamicIoMapping. Here in the example projects there is a PDF file for the library: https://downloadcenter.wago.com/learning-material/details/ll0w3pmdunzvem83g1 There is a global functional component in a GVL of the library. I think it's called DynKbusIoManager or something. The active terminals are registered there. Then there are filter Fb's for e.g. the first clamp with a specific article number. Everything is in the PDF.
Last updated: 2023-08-18