Post by jasperclauwaert on Persistent Retain Variables Not Visible in Online View (WAGO PFC100 + CODESYS)
CODESYS Forge
talk
(Post)
Hi everyone, Iβm working on a WAGO PFC100 with CODESYS. During development everything worked fine, but in the final stage I set several variables to PERSISTENT RETAIN. When I go online, most of these persistent variables cannot be monitored. Instead, I see: <Value of the expression cannot be retrieved> Interestingly, a few variables do show their values correctly, but the majority do not. The variables are not used as pointers or in any unusual way. The application compiles and runs without errors. Has anyone experienced this before? Is this a known issue with PFC100 or CODESYS? Any ideas on what could cause this behavior? Thanks in advance! Jasper
Last updated: 2025-10-23
Post by fari on Configure J1939 I/O Mapping via Scripting
CODESYS Forge
talk
(Post)
Hi everyone, With the latest version of Codesys, itβs now possible to import DBC files directly into the J1939 Manager, which is great. However, Iβm trying to achieve the same thing programmatically and canβt find any scripting functions related to import_dbc or any host_parameter that would let me configure PGNs and signal mappings automatically. So far, Iβve managed to add the J1939 Manager and an ECU, and I can pass the DBC database to it, but Iβm stuck when it comes to adding the signals. Has anyone figured out if this can be done through scripting? (Attached is an illustration of what I am trying to accomplish programmatically). Thanks in advance.
Last updated: 2025-10-24
Post by gseidel on Can't get SMC_SmoothPath to work
CODESYS Forge
talk
(Post)
Hi bertus, I cannot see any problem in the code you posted. Just some ideas: What is the value of D_ANGLE_TOL? - Do you need the assignment bAbort := NOT bDecoder? Does it help to leave it out? Any errors (e.g. SMC_SmoothPath.Error/ErrorID) or PLC log messages? What if you comment out SMC_SmoothMerge and SMC_LimtiDynamics, is corner smoothing still not working? Is bDecode written from a different task (e.g. visu)? Then I would recommend to assign to a local variable (bDecodeLocal := bDecode) and use that for all FBs. Otherwise, FBs might see different values of bDecode in a single cycle, which will cause problems. Regards, Georg
Last updated: 2025-12-17
Post by rau00 on Touch Probe 0x60B8 writting
CODESYS Forge
talk
(Post)
Hi erveyone, Rau here, first time asking on CODESYS Forge: When working with my servodrives, a special behaviour is required on dsp402 0x60B8 object, a control that is not supported by MC_TouchProbe. For this reason, I'd like to ask: Anyone knows if there is any way to bypass or change the softmotion axis writting into 0x60B8 object? My main problem is that MC_TouchProbe.TriggerInput.iTriggerNumber only allows to choose between TP 1 and TP 2 (not both at the same time). iTriggerNumber only allows values [0, 1, 2, 3], other values triggers an error in the FB, wether SMC_TP_COMM_ERROR for values [4, 5, 6, 7] and SMC_TRIGGER_OUT_OF_RANGE with any other value. Best regards, Guillem
Last updated: 2026-04-10
Post by pernockham on Gateway in China - "Gateway not connected"
CODESYS Forge
talk
(Post)
I think I understand my problem. They are most probably related to configuration of the network. When I use DHCP for the unit to my router it all works. However when using static IP I have not managed to reach functioning state. Trying to replicate the situation on my desk. Having a static IP on the "debian host" and a connection to my computer which then routes traffic on to internet. I have entered settings for gateway and netmask. I can ping from my "debian plc host" to internet and also do "curl google.com" so traffic seems to find its way through and back, still "Automation server" will not find the gateway. Any hints how a manual configuration should be done? Is it possibly a "firewall" issue of my "normal router"? Thanks for any help! Per
Last updated: 2026-01-27
Post by konstantin on Lenze i950 Servo and WAGO PFC200
CODESYS Forge
talk
(Post)
Hello, basically the i950 drive support CiA402 Basic and CiA402 Advanced modes. I attached pictures of both mode supported functions. It also support CSP, VL, CSV and CST modes. It seems the homing mode is in CiA402 Advanced mode but how can you not have the homing mode in both modes? It is a vital part of any servo system. If I use the SoftMotion standard demo mode, I can move the servo absolute and relative but cannot home it. But in SoftMotion Light mode, I cannot execute any motion function. Here is the official manual for i950 servo drive - i950 Documentation Best Regards Konstantin Kolev
Last updated: 2026-02-13
Post by toffeebonbon on EL7041-0052 - does it run with EL7041 SoftMotion?
CODESYS Forge
talk
(Post)
Good morning everyone. In my setup I am trying to use a couple of EL7041-0052 (the EL7041 variant without terminals for an encoder) to run stepper motors without feedback. When using the softmotion drivers for the EL7041 (Rev22 and Rev24, even selecting external feedback type doesn't work) the device log shows warnings for the corresponding hardware: "SDO write error 0x1 -> 0x8012:0x08 eError 0x1 AbortCode 0x6090011". 0x8012:0x08 is the register for the Feedback Type. My best guess was setting the the register value in the start parameters to zero, but the result is the same. What else can I try to get the hardware to work? I have screenshots attatched showing the running fieldbus and the log messages. EDIT: One clarification: the "device log" that shows the error is the PLC, not the ethercat terminal. The log of the terminal itself shows neither errors nor warnings. BR Robert
Last updated: 2023-11-29
Post by mubeta on parker servo and position
CODESYS Forge
talk
(Post)
In general, drives have parameter sets to adjust behaviour in such cases: position recovery, adaptation with resistant torque, out-of-position window failure, etc. (Much depends on the type of configuration set for the axis: positioner, speed controller, torque controller, etc.). I have used that type of drive very little, in only two cases and a long time ago. To tell you what is normal is impossible. I know by reputation they are very simple objects, without too many pretensions and adjustments possible. Try running traces by monitoring actual position, motor current, torque and following error. These are the most sensible curves to understand what is going on. Maybe by fine tuning the motor tuning, the current controller or the speed controller you will get something closer to what you want. For example, from DS, the motor has a standstill torque of 3 Nm. Observe with traces whether this is effective: motor current trend. And afterwards, when you have your own accurate picture of the situation, you can also hear from the product's local support to see if you can steal a few more things from it performance-wise.
Last updated: 2024-08-05
Post by paulorb on STRUCT AT %MW1000
CODESYS Forge
talk
(Post)
Hi I am trying to use STRUCT to parse commands from Modbus/TCP, Modbus client will fill the bytes related to a specific command (type, parameters), then PLC (Codesys) will access the command parameters. A STRUCT will simplify a lot the process of parsing the data, so I don't need to parse byte per byte, address will be mapped to a struct and I can use it for parsing the data. From what I understood, the compiler does not allow me to specify the location of the struct for a %MW register. VAR_COMMAND AT %MW1002: structGenericModbusCommand; This will throw: Bad declaration, use '%ML' for 'structGenericModbusCommand' variable But If I change it to %ML, when you go online you see that it is actually allocating the struct in another memory address. When we go online, on GVL we can see: VAR_COMMAND. structGenericModbusCommand %ML1002 commandType COMMANDTYPE %MB8016 ... %MB8020 I am not specifying a pointer or a reference it is a struct type, why is it mapping to a %MW location (random one). How can I control where it is mapping to? I need a consistent way to map STRUCT to specific modbus address. Is it possible? Thanks, Paulo Note I am using a Codesys OEM: Schneider Machine Expert Logic Builder (M241)
Last updated: 2024-08-13
Post by manuknecht on High Cycle Times for SoftMotion_PlanningTask when using AxisGroup
CODESYS Forge
talk
(Post)
Hello all I am using an AxisGroup with the Gantry2 Kinematics to move a 2D-Gantry system. When creating the AxisGroup, the SoftMotion_PlanningTask is created automatically with a cycle time of 2 ms in my case. I realized that the maximum cycle time of this task can spike to very high values (up to 60 ms) at lower speeds of the motion, leading to synchronization issues and errors on the axes. The same behaviour - though not as drastic - can be observed with virtual axes too. Is this behaviour intended or to be expected? Can the cycle time or type of the SoftMotion_PlanningTask be changed to prevent these errors? Or is there another fix for this issue? I tried changing the cycle type to Freewheeling, which solved the synchronization issues, but caused an error on the AxisGroup after a while, reading SMC_CP_QUEUE_UNDERRUN. Thanks in advance and best regards Manuel
Last updated: 2024-03-07
Post by zoronoa on J1939.ReceiveWatchdog & J1939.ReceiveParameterGroup
CODESYS Forge
talk
(Post)
Hi, I'm trying to monitor a specific PGN which I have it sending a pulse every 500mS Problem: Using the Watchdog for the ECU does not really help me as I have multiple instances with separate PGNs, if a PGN goes ghost, the ECU watchdog won't be flagged as the others will be running. I found the J1939.ReceiveWatchdog & J1939.ReceiveParameterGroup function blocks and they seem like a good solution for my problem, I just can't get them to work from my understanding you just build the J1939.ReceiveParameterGroup once and then connect it's output to the J1939.ReceiveWatchdog, here's my CODE for the setup HEARTBEAT_TIMER(IN:= TRUE, PT:= T#1000MS); //turn-on delay because of initialization race IF HEARTBEAT_TIMER.Q= TRUE THEN Glob_Var.DisplayReceive.xExecute:= TRUE; Glob_Var.DisplayReceive.itfECU:= Valve_X; Glob_Var.DisplayReceive.dwPGN:= 65511; Glob_Var.DisplayWatchdog.xEnable:= TRUE; Glob_Var.DisplayWatchdog.itfParameterGroup:= Glob_Var.DisplayReceive.itfParameterGroup; Glob_Var.DisplayWatchdog.tTimeout:= T#1500MS; END_IF Notes: Glob_Var.DisplayReceive is of type J1939.ReceiveParameterGroup Glob_Var.DisplayWatchdog is of type J1939.ReceiveWatchdog The above code is done once and not cyclically I'm monitoring Glob_Var.DisplayWatchdog.xError cyclically
Last updated: 2024-03-13
Post by shamcke on Array with generic constant as persistent variable
CODESYS Forge
talk
(Post)
Hello, I have written a function block that uses a generic constant for the upper bound of an array. I wanted to have this array in the persistent memory area, thus I constructed my FB as follows: FUNCTION_BLOCK FbWithGenericArrayLength VAR_GENERIC CONSTANT uiArrayLength : UINT := 10; END_VAR VAR PERSISTENT arr : ARRAY[1..uiArrayLength] OF INT; END_VAR In my PLC_PRG I declare an instance of said FB PROGRAM PLC_PRG VAR myFb : FbWithGenericArrayLength<10>; END_VAR This compiles just fine. When I let CODESYS fill my persistent list, it adds duplicate entries {attribute 'qualified_only'} VAR_GLOBAL PERSISTENT RETAIN // Generated instance path of persistent variable PLC_PRG.myFb.arr: ARRAY [1..uiArrayLength] OF INT; // Generated instance path of persistent variable PLC_PRG.myFb.arr: ARRAY [1..uiArrayLength] OF INT; END_VAR so I manually delete the duplicate. When i now compile, I get errors ------ Build started: Application: Device.Sim.Device.Application ------- Typify code... [ERROR] Sandbox_FW31: PersistentVars [Device: PLC Logic: Application](Line 4): C0161: Border 'uiArrayLength' of array is no constant value [ERROR] Sandbox_FW31: PersistentVars [Device: PLC Logic: Application](Line 4): Type of mapped variable is not equal to original type Compile complete -- 2 errors, 0 warnings Build complete -- 2 errors, 0 warnings : No download possible Is is simply not possible to use a generic constant for the persistent array? Thanks in advance. Edit: It seems I can manually replace the uiArrayLength in the persisten list by the value 10 I used as the generic constant for this particular instance.
Last updated: 2026-05-29
Post by jegerjon on XY Chart
CODESYS Forge
talk
(Post)
I have a XY chart in a visualization that is working fine, all lines are presented correctly. When I present the XY chart visualization in a frame, it seemes as no values are recorded, all lines are zero. When i open the visualization containing the XY chart in e!cockpit i see the lines are presented correctly but still not in the frame. Any ideas?
Last updated: 2023-08-30
Post by spareparts on SPI Master not running/MCP3008 Missing driver.
CODESYS Forge
talk
(Post)
I believe I have installed the correct device descriptions and library, in an attempt to use the MCP3008 in conjunction with RPI; when project runs the MCP3008 is unable to find the correct driver. Is there anything I'm missing? Very new to this so any help is apprecated!
Last updated: 2023-09-12
Post by eschwellinger on Correct CAN Driver for EL6751
CODESYS Forge
talk
(Post)
Hi, for Control Win : add CmpEL6751CanDrv in the c:\ProgramData\CODESYS\CODESYSControlWinV3x64\E1FA7ABE\CODESYSControl.cfg [ComponentManager] Component.1=CmpTargetVisuStub Component.2=CmpWebServer Component.3=CmpWebServerHandlerV3 Component.4=SysCpuMultiCore Component.5=SysReadWriteLock Component.6=SysCpuBreakpoints Component.7=SysPipeWindows Component.8=CmpEL6751CanDrv for Linux SL or Pi or any ARM device - I think it is already static loaded as component - see plclogger on startup
Last updated: 2023-09-20
Post by transmin01 on SafetyApp - "Invalid ERR Ack input"
CODESYS Forge
talk
(Post)
Hi, I am trying to get a basic safety application to download but I keep getting an "Invalid ERR Ack input" and "The Standard Inputs Size of zero is not allowed". I am simply using 2 safety inputs through an "AND" block to 2 safety outputs. Any help would be appreciated. Regards Trevor.
Last updated: 2023-09-27
Post by transmin01 on SafetyApp - "Invalid ERR Ack input"
CODESYS Forge
talk
(Post)
Hi, I am trying to get a basic safety application to download but I keep getting an "Invalid ERR Ack input" and "The Standard Inputs Size of zero is not allowed". I am simply using 2 safety inputs through an "AND" block to 2 safety outputs. Any help would be appreciated. Regards Trevor.
Last updated: 2023-09-27
Post by tk096 on Motion FB Error
CODESYS Forge
talk
(Post)
Hi, Softmotion Robotics does not support tracking in/out to dynamic coordinate systems with relative movements. Is MC_MoveLinearAbsolute an option? See SMC_RELATIVE_MOVEMENT_TRACKING_CS in https://content.helpme-codesys.com/en/libs/SM3_Error/Current/SM3_Error/SMC_ERROR.html Concerning the other error: Do you use any motion function blocks of SM3_Basic to move a single axis of the robot in your application?
Last updated: 2023-10-20
Post by ivanmaltar on Update Raspberry Pi error
CODESYS Forge
talk
(Post)
Hello, from today, I got an error when I try to open 'Tools/Update Raspberry Pi' and I got this error: There is no value with the specified name associated with this subkey. This feature worked before. I did not do any changes to Codesys installation. Codesys version is SP19.1, and CODESYS Control For Raspberry Pi 4.8.0.0
Last updated: 2023-11-30
Post by jvfred on Display problems on Weintek's cMT3092x HMI
CODESYS Forge
talk
(Post)
Hello, I have the same issue with my cMT display. I know it's a communications issue with my Eurotherm E+PLC400 PLC using the Codesys V3 driver. Were you ever able to figure out what the problem was and if so, what was your fix. Any help would be greatly appreciated.
Last updated: 2023-12-01
Post by mybackingtracks on CODESYS 3.5 SP19 Patch 5 - missing Raspberry PI tab
CODESYS Forge
talk
(Post)
Hello, I have two virtual machines. One with CODESYS 3.5 SP19 Patch 5 installed, and second with CODESYS 3.5 SP19 Patch 1 installed. On Virtual Machine with Patch 5, I cannot to find Raspberry PI Tab witch I have visible on CODESYS with Patch 1. How can I turn it on? Thanks in advance for any feedback.
Last updated: 2023-12-05
Post by dileesha on Codesys device configuration
CODESYS Forge
talk
(Post)
I am new to this and I have a Beijer X2 Control 7 HMI and in my laptop I have installed codesys v3.5, ix developer and codesys gateway control. I have designed a simple PLC programme and Im trying to connect my PC and Beijer HMI via an ethernet cable and scanit in the codesys software. But when I scan it does not show any device.
Last updated: 2023-12-08
Post by rschwager on GVL to SHMem
CODESYS Forge
talk
(Post)
Hallo! Have some any idea to transfer whole GVL to Shared Memory? I also shared REATIN memory to shraed meory for making a Retain Backup System without USP in Linux on a FRAM. For an other Application we want to shared the whole GVL off obne part (e.g. GVL_Test). How cvan I get easy the Size and the Address for meory copy?
Last updated: 2024-07-09
Post by stiller on OPC UA RPI 4.8.0.0 Status Code / "out of range"
CODESYS Forge
talk
(Post)
Hello, I have an OPC-UA server with an information model. For many values, there is a defined range (e.g., 0 to 100). If a client enters a value outside this range (e.g., 120), the StatusCode should change to Bad. How can I accomplish this? Any help is appreciated! Thank you in advance. Best regards, Christian Stiller
Last updated: 2024-07-10
Post by mrrobot on No source code available for this object
CODESYS Forge
talk
(Post)
Hello, I have this strange error while I am adding an axis to my slave: "No source code available for this object because it is in the compiled library 'sm3_drive_etc_ds402_cyclic' ..... I looked on google/chatgpt but i cannot find a solution for this issue Any help is welcome ! Thanks in advance Mrrobot
Last updated: 2024-07-15
To search for an exact phrase, put it in quotes. Example: "getting started docs"
To exclude a word or phrase, put a dash in front of it. Example: docs -help
To search on specific fields, use these field names instead of a general text search. You can group with AND or OR.