Post by timvh on Modbus TCP & RTU with Control for Linux SL
CODESYS Forge
talk
(Post)
It seems you have 2 network interfaces. Did you try eth1? Did you already configure the IP address for this interface in Linux? If yes, then maybe undo this. - or only set eth0 in the Nic configuration without anything else (so no IP address, because this is already set in Linux). For more information about the Nic settings, see (probably already read it?): https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_obj_deploy_control_sl_configuration.html PS, if you only want to run CODESYS Control SL, you don't necessarily need the Virtual PLC variant. You could also install and run the CODESYS Control SL Runtime in the Host operating system. This way you should also be able to access the serial port and directly access all ethernet ports. Maybe this is easier?
Last updated: 2024-10-23
Post by shafiq-dsc on Beckhoff EK series cannot detect but BK1120 detect
CODESYS Forge
talk
(Post)
Dear Support, I have i950 wants to connect with Beckhoff EtherCAT coupler BK1120. There are 2 GSD files for BK1120. 1. BK1120 without MDP.(EtherCAT ESI Device Description (XML)) 2. BK1120 with MDP. (EtherCAT BKxxx (MDP) configuration files) When connecting the BK1120 with i950, scanned devices detects BK1120 without MDP from ESI No1 above. But the KL1408 & KL2408 not detect because they have ELxxxx IO type. When manually insert BK1120 with MDP, the KL1xx8 is able to add manually also but the error shows and Install Missing Descriptions appears. The questions; 1. Why the error occurs? 2. Can the i950 connect with KLxxxx IO type or not? Regards, Shafiq
Last updated: 2024-10-25
Post by wistaro on How to use PLC_Open FBs with PROFINET servodrive (PROFIdrive layer)
CODESYS Forge
talk
(Post)
Hello, I would like to know if there is a PROFIdrive layer in CODESYS. I am already familliar with Codesys's SoftMotion on CANOpen/EtherCAT (to control PLC Open FBs), and I need the same kind of stuff for PROFINET-IO devices; In my configuration, I have a CIFX board from Hischer to enable IRT, the SoftPLC "Codesys Control RTE V3 x64", and a servo-drive from INFRANOR that implements PROFINET / PROFIdrive (with IRT) protocol. This drive works well with the Object Technology of Tia Portal, but some customers use Codesys. Do you have an idea how to do that? Thanks in advance. Regards, William ROMIGUIERES INFRANOR France
Last updated: 2024-10-29
Post by r-niedermayer on OPC UA subscriber not operational
CODESYS Forge
talk
(Post)
Hi. As far as projects in "old version"s are concerned, these can be upgraded to newer versions at any time. To do this, the device must be updated accordingly and the copilers and library versions must be adapted. You can find instructions on how to proceed in the online help/FAQ: https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_changing_compiler_version.html https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_cmd_update_device.html See also 4.3.22.4 "How to open an Example Project" within the following pdf for more details on the single steps: https://forge.codesys.com/lib/counit/tickets/_discuss/thread/3e991befbc/ca97/attachment/Public%20FAQ-v13-20240610_075228.pdf Regaring your OPCUA connection state always showing just "DISABLED", without knowing both sides of the assembly in detail, one can only approach the problem theoretically. We can give a chekclist on how to proceed: Fist, please recheck the communication settings in the OPC UA connection function block to ensure that the server URL, endpoint URL, and other settings are correct and match the configuration of the OPC UA server. Verify that the OPC UA server is running and accessible. -You can try to connect to the OPC UA server using a separate client, such as UAExpert, to ensure that the issue is not related to the OPC UA server itself. Test the security settings in the OPC UA connection function block to ensure that the correct security policy and certificate are selected. If you are using a dynamic connection to the OPC UA server, probe that the connection settings are correctly configured and that the OPC UA client is able to establish a connection to the OPC UA server. Also, please loock into the log files for any errors related to the OPC UA connection function block, these should be listet there. The log files may also provide additional information about the issue and help you to further troubleshoot the problem. FYI - Please see https://content.helpme-codesys.com/en/CODESYS%20Communication/_cds_obj_data_source_communication_opc_ua_server.html: Her you can finde the Communication settings via OPC UA Server -> layout Browse Live Server: The client connects to the server and detects the existing variables and types. From Information Model The client reads the data structure (layout) of the OPC UA Server from the information model set here and as a result receives the information about available variables and types. A connection to the server is not required. The list contains the information models installed in the OPC UA Information Model Repository. "Read Connection" Settings from IEC Variable (option set): - The connection settings used by the device are not read here from the dialog, but at runtime from the IEC variable specified here. - For this possibility, please see the Using a Dynamic Connection to an OPC UA Server (https://content.helpme-codesys.com/en/CODESYS%20Communication/_comm_use_dynamic_opc_ua_server_comm_settings.html) The settings for the communication of a Client-data source to an OPC UA Server can also be dynamically configured from the IEC code and can also be changed at runtime. For such a purpose, a structure is available in the DatasourceOpcUAServer library (For a description of the OPC UA Server, there is one included in the standard installation of CODESYS, https://content.helpme-codesys.com/en/CODESYS%20Communication/_cds_encrypt_communication_data_sources_opc_ua_client.html)
Last updated: 2024-11-04
Post by arnaud on eCockpit - unable to start simulation
CODESYS Forge
talk
(Post)
Hi there! I'm using eCockpit WAGO software to develop HMI's for multiple projects. As I recently starting this, my knowledge on the software is somewhat limited (so maybe my question is a simple one). For most of my projects I can simulate the application and start it to test the code and HMI. However for two projects, I can initiate the "simulation activation" but I cannot start it. Nothing happens when I press start and the visualization shows "The online visualization is waiting for connection. please start the application". - I don't see any errors in the messages - Initially the project are made by a colleague, which moved on. I guess I'm forgetting something, like missing a setting. I appreciate any help I can get. If you need more information to help me out, let me know. Thanks!
Last updated: 2023-08-25
Post by ofey on Modbus TCP communication
CODESYS Forge
talk
(Post)
Hi! I tried setting up the PLC I'm working with (Beijer GN-9373) to connect to a modbus master running on a laptop. I have an ethernet connection (via USB-C to ethernet) between the laptop and the controller. I have tried following tutorial on how to set this up. I have added an ethernet device with the IP-address of the PLC. Further I added a ModbusTCP_Slave_Device with default settings. I get the error "Failed to open TCP Port: 1" when I try to go online with the PLC. Earlier I tested the exact same set up with the soft PLC from codesys. I can then read/write values correctly with the Modbus master i have running on the laptop. Hope anybody can help me with this, thanks in advance!
Last updated: 2023-10-06
Post by matthew on New Ladder Editor Issues
CODESYS Forge
talk
(Post)
Hi There, When using the new ladder editor there is no option for function blocks to Remove uncalled FB call parameters. I also see no update function block. When you double click the function block it no longer opens the function block. I also now get warnings if I insert FB call without a contact in front. Warning is: (Impl)): C0373: Expression or part of it has no effect I take it the new editor must work differently? The only reason for using new ladder editor is the ST execute/block editing is far better, If you have alot of text in the old ST execute the editor window is very small and when online it's even worse. The new ST block seems a lot better Thanks!
Last updated: 2023-10-10
Post by sean-barton on Function block method default arguments
CODESYS Forge
talk
(Post)
I have default arguments specified for function block methods but when calling a method, an error is produced requiring me to supply all the arguments despite there being default values. According to the online documentation, under section "Calling a Method" and subsection "argument passing" of the following link: https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_obj_method.html "Passing an argument for an input ... can be omitted ... for which a default or initial value was specified in the declaration..." I have found this to be the case for all Codesys IDEs I've used, 3.5.11, 3.5.16, 3.5.17, 3.5.19. Am I missing something?
Last updated: 2023-12-21
Post by mohammadasif on Blink Function definition is wrong in codesys online help
CODESYS Forge
talk
(Post)
https://content.helpme-codesys.com/en/libs/Util/Current/Signals/BLINK.html in the above link, please correct your website the following: "Output value, starts with FALSE and switches between TRUE and FALSE for the given high and low times" it should actually be: "Output value, starts with TRUE and switches between TRUE and FALSE for the given high and low times" if not please let me know if this has changed in a util library update, in your older website it has the right definition here: https://help.codesys.com/webapp/blink;product=codesys;version=3.5.11.0
Last updated: 2023-12-28
Post by matthew on New Ladder Diagram conversion does not work due to missing features
CODESYS Forge
talk
(Post)
Hi It looks like in the new ladder there is no way to remove unused FB call parameters or update the function block? It's quite often where you have a function block with multiple uses and not all the parameters are required. Need the ability to leave an input/output blank without getting an compile error Expression expected instead of '' Also double clicking on the FB no longer opens the underlying FB code and view what it was doing online. Dragging and dropping a variable does not work, only using the selection works. Will these be available in the V1.0 release or just best to stick to the old ladder until it's available? Thanks
Last updated: 2024-01-28
Post by alexgooi on Update boot project default unchecked
CODESYS Forge
talk
(Post)
Dear Forum, I'm currently switching to Codesys V3.5 SP19. When I want to do an online change, I get the option to update the boot project, in other (codesys based) packages this is checked on by default. In Codesys V3.5 SP19 (and maybe older versions) this is unchecked by default. We are doing a lot of remote updates with systems that almost never power cycle. In other words when this box is forgotten the system will run fine until a blackout. Is it possible to get it checked on by default? This question was asked before, but no answers where given. https://forge.codesys.com/forge/talk/Engineering/thread/ffb4ffa298/ Thank you in advance.
Last updated: 2024-02-09
Post by jtebokkel on Access to the path *** is denied
CODESYS Forge
talk
(Post)
I am also having this issue. It was working fine for the first 2ish months and is now throwing this error. I can just try and go online again a second time and it works. I'm wondering if there is an environmental variable or something that isn't set that is causing it to use an empty path as a temp directory. The empty path will be the location the app is running from which is that path C:\Program Files\CODESYS 3.5.19.50\CODESYS\Common. The permissions don't allow a normal user to write to that directory which causes the error. It also only seems to happen when there are changes or the build has been cleaned.
Last updated: 2024-02-14
Post by sumit on Not able to see input data coming from eip adapter on codesys
CODESYS Forge
talk
(Post)
dhumphries, I changed the datatype this time from BYTE to USINT (because that's what my adapter is sending: array of uint8_t). The text "New Help String" you saw in previous screenshots is just the description of the input/s (it can be anything). I also looked into the logs (see attached) for that ! sign next to the device, I found that connection is being timeout. I tried some suggestions from online such as increase the RPI but still got connection timeout issue, also by changing the datatype, I still don't see incoming data from the adapter, although its visible on wireshark. thanks,
Last updated: 2024-03-07
Post by bschraud on Zielsystem stimmt nicht mit dem verbundenen Gerät überein
CODESYS Forge
talk
(Post)
Hallo, nach einer Umrüstung des RPi auf SSD habe ich den RPi neu aufgesetzt. Nach dem Installieren der Runtime (4.11.0.0 raspberry, all) auf den RPi kann ich das Gerät nicht mehr verbinden. Die Fehlermeldung lautet "Das gewählte Zielsystem 'Codesys Control for Raspberry Pi MC SL' stimmt nicht mit dem verbundenen Gerät 'Codesys Control for Raspberry Pi 64SL' überein. ID-Diskrepanz: Ausgewählt=000 0011, Online=0000 0012" Bei der Konfiguration des Laufzeitsystems kann man nur Multicore 64-bit (Aarch64) auswählen. Beim Aktualisieren des Gerätes im Gerätebaum habe ich Raspberry Pi MC SL in der Version 4.11.0.0 ausgewählt. Diese Version habe ich auch ausgewählt, weil nur diese Version für den produktiven Einsatz zugelassen ist. Die codesys Version ist frisch installiert, also 3.5.19.60 Vielen Dank für Ihre Hilfe
Last updated: 2024-03-08
Post by bschraud on Zielsystem stimmt nicht mit dem verbundenen Gerät überein
CODESYS Forge
talk
(Post)
Dank umfangreicher Hilfe durch den Kontron Support kann ich nun wieder übersetzen. Es waren einige Bibliotheken auf einem älteren, nicht 64bit-kompatiblen Stand. Beim Öffnen des Projektes erscheint zwar ein Dialog zum Aktualisieren der Bibliotheken. Diesen hatte ich auch mit "Auf neueste setzen" bestätigt. Trotzdem waren etliche Bibliotheken im Projekt veraltet. Leider habe ich noch keine Stelle in der Online Hilfe gefunden, die die Zusammenhänge in der Bibliotheksverwaltung und das Vorgehen bei Fehlern erklärt. (Z.B. wie man vermeiden kann, dass eine Komponente automatisch eine ältere Bibliotheksversion lädt, obwohl eine aktuelle Version der gleichen Bibliothek schon hinzugefügt wurde.) Vielen Dank für die Hilfe!
Last updated: 2024-03-25
Post by fugtwad on Automation Builder V2.5 EtherCAT CM579 Master Scan for devices - >No gateway selected
CODESYS Forge
talk
(Post)
ABB Automation Builder v2.5.0.22 Premium CodeSys 2.3.9.62 Running on Win 10 VM x64 Goal: I have an EtherCAT topology issue which normally a "Scan for devices.." on the EtherCAT master would shed some light on. Issue: Upon trying such I get a "No gateway selected" error. Question: How might I point the the "scanner" at a gateway? What is working: Gateway is running in system tray. I can go online to PLC. A scan from the "Diagnostics live" tab of the EtherCAT master gives slave status. What I have tried: Restarting gateway in system tray. Exiting system tray gateway and reloading it. Turning off firewall. Contacting ABB support multiple times. Any help appreciated.
Last updated: 2024-05-20
Post by jaspergain on Non-existing identifiers
CODESYS Forge
talk
(Post)
Hello, I got a bit of a weird issue going on which is kind of annoying. So recently we switched a lot of Modbus IO to EtherCAT, as we were having issues with stability. All works fine, which is great. But sometimes when I change the program I get errors claiming that identifiers are not defined. Meaning I can't go online. See the picture below. I believe this is because some of these identifiers were used with Modbus, and they weren't properly removed/deleted? A clean all temporary fixes the issue, but it comes back again after a while of changing the code, and building. Any way to fix these non-existing required identifiers, or even find out where they are required? Thanks for the help in advance. Jasper.
Last updated: 2024-05-29
Post by danielbeers on Automation Server + Pi Gateway + PLC w/ CAN
CODESYS Forge
talk
(Post)
Hello, I have a project using some EPEC PLC's. Some of them are programmable using Ethernet and some use CAN. We currently have a Raspberry Pi that is acting as a gateway to the Codesys Automation Server and is successfully working for the PLC's communicating over ethernet. I am trying to achieve a similar result for the PLC's that have only CAN access. I have PEAKCan drivers on the Pi, and can successfully send/receive messages. But the Gateway does not recognise the PLC when scanned from the Automation server online. Is there a library or service that exists to translate the CAN messaging, to the Edge Gateway, and be able to achieve remote access with the Automation Server? Or is this not possible without creating something custom? Cheers, Daniel
Last updated: 2024-09-22
Post by sigurdrb on Codesys and error messages, warnings exceptions etc.
CODESYS Forge
talk
(Post)
Hi, I tried some different libraries (CmpApp etc.) to find some global variables that I could read out as a variable in the codesys environment. Do any one of you know which libraries are best suited for this, and how I can read it out? My goal is to send messages, warnings etc. to the system that communicates to the PLC. Currently if something goes wrong I need to see the logfiles, or go online with the controller. I think I could save a lot of time if I could read the errors from our user interface that is connected to the PLC by TCP/IP.
Last updated: 2024-11-06
Post by umdee on Error when monitoring LAD programs
CODESYS Forge
talk
(Post)
I get the following error when monitoring my program (see attached screenshots): "Unhandled exception has occured in your application. If you click Continue, the application will ignore this error and attempt to continue. If you click Quit, the application will close immediately. Value cannot be null. Parameter name: source. And the details say: See the end of this message for details on invoking just-in-time (JIT) debugging instead of this dialog box. ** Exception Text ** System.ArgumentNullException: Value cannot be null. Parameter name: source at System.Linq.Enumerable.Any[TSource] (IEnumerable1 source, Func2 predicate) at _3S.CoDeSys.NWLEditor.NWLTextCell.OnPaintCellLayer(PaintEventArgs e) at _3S.CoDeSys.Controls.Controls.GfxEdControl.PaintCellCellLayer(PaintEventArgs e, GfxCell cell) at _3S.CoDeSys.Controls.Controls.GfxEdControl.PaintCellCellLayer(PaintEventArgs e, GfxCell cell) at _3S.CoDeSys.Controls.Controls.GfxEdControl.PaintCellCellLayer(PaintEventArgs e, GfxCell cell) at _3S.CoDeSys.Controls.Controls.GfxEdControl.OnPaint(PaintEventArgs e) at System.Windows.Forms.Control.PaintWithErrorHandling(PaintEventArgs e, Int16 layer) at System.Windows.Forms.Control.WmPaint(Message& m) at System.Windows.Forms.Control.WndProc(Message& m) at System.Windows.Forms.UserControl.WndProc(Message& m) at _3S.CoDeSys.Controls.Controls.GfxEdControl.WndProc(Message& m) at System.Windows.Forms.NativeWindow.Callback(IntPtr hWnd, Int32 msg, IntPtr wparam, IntPtr lparam) ** Loaded Assemblies ** (3000 lines of assemblies) ** JIT Debugging ** To enable just-in-time (JIT) debugging, the .config file for this application or computer (machine.config) must have the jitDebugging value set in the system.windows.forms section. The application must also be compiled with debugging enabled. For example: <configuration> <system.windows.forms jitdebugging="true"> </system.windows.forms></configuration> When JIT debugging is enabled, any unhandled exception will be sent to the JIT debugger registered on the computer rather than be handled by this dialog box The windows show red X's where the networks should be. Any advice on how to fix this? Additional Information PLC used: Wago 750-8212, Firmware FW26 Startup profile: CODESYS V3.5 SP19 Patch 5 OS version: Microsoft Windows NT 10.0.22631.0 .NET version: 4.0.30319.42000 Full Version info attached as .txt
Last updated: 2024-03-17
Post by alexgooi on OPC-UA and other communication questions
CODESYS Forge
talk
(Post)
Dear forum, I currently have a big question mark above my head, and maybe this forum can shine some light on the situation. I recently updated to Codesys 3.15 SP19 Patch 6. And now I’m trying to setup the OPC-UA server, besides that I’m trying to connect to the controller with the Codesys V3 (Ethernet) protocol. OPC-UA I have installed the correct licenses on my controller (Runtime and communication). I’m able to connect to the controller with an OPC-UA client, and I’m able to browse the tags, so far so good. Therefore I’m assuming that the OPC-UA server is running on the controller. But now the strange part, in the device security settings I have set the communication Policy to BASCI256SHA256 ( I also have tried the other ones) and the communication mode is set to secure if possible (I also have tried all the other ones) (see picture). With these settings I would assume that I would only be able to login with a Basic256SHA256 policy with a client. But the opposite is true, I am able to login using the no policy mode and when I set it to Basic256SHA256 the client (UA-Expert) notes that this policy is not available on the server. I then check the certificates and I noted that there is no certificate for the OPC-UA server, I tried to generate one but it gave the error that the certificate has not been created by the device (See picture). To summarize I have no clue what is going on, and the controller does the opposite of what I would expect. Codesys Ethernet V3 driver I have a HMI connected to the same controller using the Ethernet V3 driver. But this will not connect. I tried all the Protocols (see picture), with and without the username and password enabled. But it will not connect, when I scan the available servers I can see the controller with the port number that I am expecting, so I’m assuming that the Codesys V3 ethernet driver is up on the controller. Does anyone can give me some direction, because the stuff that I tried doesn’t make sense to me. Thank you in advance
Last updated: 2024-04-02
Post by dantheman on Connecting to SoftPLC Only Works By Turning Off Modbus Ethernet Port
CODESYS Forge
talk
(Post)
I have an IPC with 2 ethernet ports and 1 Wi-Fi. I'm using ModbusTCP with the ethernet port named "enp2s0" connected to my remote I/O. This works fine when testing with Python and also works with CODESYS, but CODESYS is only able to scan for the Linux SoftPLC when I turn off the "enp2s0" interface. In other words, I can't get online with the IDE if I want my ModbusTCP comms to run with CODESYS. I'm using a Linux SoftPLC that has the following entry in CODESYSControl.cfg, hoping that this will allow me to connect with "enp1s0" or "wlp3s0", and leave "enp2s0" for field comms, but this seems to only make the source IP of the ModbusTCP comms to be bound to "enp2s0". That last point is the case only if I don't restart the service, but if I do restart the service after changing the config file, the source IP for the ModbusTCP comms then becomes the one for "enp1s0", which is very confusing to me: [SysSocket] Adapter.0.Name="enp2s0" Adapter.0.EnableSetIpAndMask=1 On the device list, I only have "enp2s0" given as the ethernet device that has the ModbusTCP master & slave beneath it, shown in Screenshot 1. On the IPC, I can ping the ModbusTCP client (remote I/O) from "enp2s0", and I've attached a Wireshark capture of running ModbusTCP from the CODESYS runtime as Screenshot 2, 3 & 4 (again, I can't get online when this is running, I have to turn off "enp2s0" to connect even when it's idle and I don't have an active TCP session with my Python tests). Like I explained above, the source IP is "enp1s0", even though the ethernet device on the project is "enp2s0". I was lucky to catch the red message that showed the source IP that makes sense to me (the one for "enp2s0"), but for some reason that connection was reset and I never saw that packet again. I've also tried this with Auto-reconnect both enabled & disabled, for the ModbusTCP Master device. I also have to turn off "enp1s0" and then turn it on, just so that I can have the ModbusTCP comms running from "enp2s0" (which is not intuitive in any way to me, I'd love some help understanding that phenomenon as well) in the weird manner that I've described above. I would be very appreciative if someone can help me figure out this pickle. I'd love to just connect to CODESYS through my Wi-Fi interface and leave my ethernet ports for field comms.
Last updated: 2024-08-01
Post by ryandmg on Web Client (HMI) Disconnects from Webvisu (Weidmuller u-OS)
CODESYS Forge
talk
(Post)
Thanks So Much for the reply! Were using the Weidmuller UV66-ADV-10-CAP-W The HMI is pointed to the URL which is assigned through u-OS. Basically when you log into the controller's webserver via browser you can view the installed apps. One of which is the Codesys runtime. When you click on that it takes you to the visualization. That corresponding url is what the HMI is looking for. I apologize I don't have that on hand as I'm in the office right now. I don't think I tried connecting using the port you mentioned and https in lieu of the u_OS URL. I can certainly try. Out of the box the u-OS is set for HTTP. Since we're isolated I havent changed that yet. When this has happened while logged on via chrome on my laptop, simply refreshing brings the visualization right back. In the case of the HMI in kiosk mode, we power cycle the HMI to force a reconnect, log back in u-OS and the visualization is back.
Last updated: 2023-09-06
Post by arundara on Variable Sync Issue In Soft Plc Redundancy
CODESYS Forge
talk
(Post)
Hello, I was trying to create a redundancy POC for our application where we read data from few modbus tcp devices. As there is a limitaion that modbus tcp device support only for single master device, we wanted to test how the variable sync happens in redundancy mode. For that i have used the redundancy sample code added a variable "b" under a condition. What i observed was while active controller is running, if passive controller is powerup, passive controller is able to sync all the data configured for redundacny. But after that the variable data which resided under a condition is not synching from active to passive controller. I have attached the image where i have highlighter the variable. Can some help me to understand how redundacny work in codesys soft plc and if there is a solution to sync variable which are under condition, please explain the same or suggestion to achieve the same. Hardware - Raspberry Pi (2 qty) Redundancy licence used - yes in both controllers. Codesys runtime - 4.9.0.0 Codesys software version - V3.5 SP19 if i have posted this question in wrong section, please do let me know in whcih section i have to post this question.
Last updated: 2023-12-01
Post by k2saki on CNC / G01 Speed is very slow (or go-stop motion) in Continuous short segment .
CODESYS Forge
talk
(Post)
I'm using CAD/CAM that outputs GCode with G01 many short segments from NURBS Curve, only X-Y axis. But CODESYS CNC motion seems much slower ( or stop-go motion ) in simulation mode than F-Value (I checked value from SMC_Interpolator - dVel ). In GCode G01, F value is F500, but movement is very slow, actual speed (dVel) is between 0 to 30 back and forth. I think very old CNC can move like that, but nowadays, a lot of CNC can move smoothly to process free curve ( somethimes option switch ) I tried to use G51 Dxx but I got the same result. My questions are 1) How do I improve CODESYS CNC motion in this case ? 2) How can I graph the sampling from dVel of SMC_Interpolate in CODESYS? From my GCode N2006 G01 X1.4364 Y-14.6847 F500 N2007 G01 X1.6759 Y-14.6768 N2008 G01 X1.9152 Y-14.6486 N2009 G01 X2.1547 Y-14.6400 N2010 G01 X2.3943 Y-14.6090 N2011 G01 X2.6336 Y-14.6002 N2012 G01 X2.8732 Y-14.5716 N2013 G01 X3.1127 Y-14.5634 N2014 G01 X3.3520 Y-14.5410 N2015 G01 X3.5915 Y-14.5336 N2016 G01 X3.8308 Y-14.5307 ... Thansk.
Last updated: 2024-04-29
To search for an exact phrase, put it in quotes. Example: "getting started docs"
To exclude a word or phrase, put a dash in front of it. Example: docs -help
To search on specific fields, use these field names instead of a general text search. You can group with AND
or OR
.