Post by jroddball79 on PM556-TP-ETH β How to change IP address without overwriting the PLC program?
CODESYS Forge
talk
(Post)
Hi, I need to change the IP address of an ABB PM556-TP-ETH using ABB Automation Builder. The situation is: I have connectivity to the PLC using the current IP (configured in Communication Settings) Online Login works fine The Network Scan does not detect the PLC IP-Configuration tool shows all fields disabled I don't have the original project source, only an empty project The PLC has no SD card inserted The Online menu does not show an Upload option When I modify the IP in the project and connect, Automation Builder shows: "The PLC configuration needs to be updated. A full PLC download is required" I'm afraid a full download will overwrite the running program. Is there any way to change only the IP address without overwriting the application? I'm also open to solutions using third-party tools, Python scripts, or any other method (DCP protocol, direct TCP communication, etc.) as long as it doesn't overwrite the running application. Thank you
Last updated: 2026-05-19
Post by toffeebonbon on EL7041-0052 - does it run with EL7041 SoftMotion?
CODESYS Forge
talk
(Post)
I let this project rest for a while and picked it up last week. I have been in contact with the support from beckhoff and got the information that the terminals were identical (communication wise). As the Log of the Axis (not the drive's log) shows the error when trying to write into the register 0x8012 and set the value for an encoder to a value that is the default - at least according to the manual - I was wondering if it is possible to "not write that value" to skip that part? Or am I misunderstanding the way the library communicates with the drive?
Last updated: 2024-07-24
Post by r-c-r on SM3RaspiStepper 0.0.0.6 issue
CODESYS Forge
talk
(Post)
Hello, I noticed that version 0.0.0.6 is now available, so I tested it using CODESYS V3.5 SP19 Patch 7 and SoftMotion 4.17.0.0. While the project compiles and downloads without issues, I encountered a problem with the 'Enable: GPIO pin number that is set when the axis is enabled (with MC_Power) (0: not used)' functionality β it no longer works (HIGH level not present at the output pin). I observed the same behavior with version 0.0.0.5, whereas version 0.0.0.4 functions correctly. Could you help me identify what might be causing this issue or suggest how to resolve it? Thanks.
Last updated: 2025-03-19
Post by esave on Softmotion Light Problem: The license is missing or invalid
CODESYS Forge
talk
(Post)
Hello everybody I want to controll a stepper driver from Leadshine (EM3E-556E). The EtherCat slave is CiA 402 compatible. Because of this I bought the Softmotion Light Package from Codesys and implemented it in my project. I rightclicked the EtherCat slave and added the Softmotion Light axis. But now the error message shows: "The license is missing or invalid. The PLC runs in demo mode." What have i done wrong? I use Codesys 3.5.17. Is it possible that the stepper driver is not compatible with the Softmotion license? Thanks for all your help
Last updated: 2024-05-02
Post by imdatatas on Unrecoverable SoftMotion state after switch to PreOp
CODESYS Forge
talk
(Post)
Dear @alimans, Additionally, As far as I know since starting from Softmotion V4.18.0.0 automatic restart behaviour for an axis has been changed for this issue. See below explanation from release notes. "With CODESYS SoftMotion 4.18.0.0, the behavior of SoftMotion axes after a loss of communication to the servo drive has changed. Now, an automatic reinitialization is performed as soon as the communication is established again. Before, an explicit call to SMC3_ReinitDrive had to be performed. An example for a loss of communication is that the cable to one of the drives is unplugged." Regards, imdatatas
Last updated: 2025-10-23
Post by gseidel on SMC_Interpolator / CNC Abort β ControlAxisByPos Sometimes Remains Busy and Axis Continues Moving
CODESYS Forge
talk
(Post)
Hi kishan, I would recommend to first execute a stop (input bSlowStop or bQuickStop of the interpolator). Only when the interpolator has stopped you should abort the interpolator and preprocessing FBs. BTW., a new rising edge of the execute input should suffice. In case preprocessing is done in a different task: take care to write the abort signal to a local variable in the path and interpolation task and use this local copy. (Otherwise, some preprocessing FBs might see an abort and others not, in the same cycle of the task.) Best regards, Georg
Last updated: 2026-10-27
Post by darwin03 on Mismatch between coordinate monitor and actual motion using SMC_GroupJog2, MC_MoveLinearAbsolute (6DOF)
CODESYS Forge
talk
(Post)
Dear Georg, Thank you for your explanation about the axis scaling. I checked the scaling of Joint6 and corrected it so that one technical unit equals one angular degree. However, I am now facing another issue. When I move all axes to zero position and then try to use SMC_GroupJog2 and MC_MoveLinearAbsolute, I receive the error SMC_CP_CONFIGS_DIFFER I already tried moving each joint manually to different positions before executing the motion command, but the error still appears. Could you please explain: What exactly causes SMC_CP_CONFIGS_DIFFER Thank you very much for your support. Best regards, darwin03
Last updated: 2026-05-04
Post by gseidel on Limit Axis CNC Jerk using SMC_Polynomial_AbsMaxLocs
CODESYS Forge
talk
(Post)
Dear josepmariarams, this (internal) function has been removed with SoftMotion 4.17.0.0. We do not have public functions to compute the extrema of a polynomial. On which polynomials exactly did you call SMC_Polynomial_AbsMaxLocs? (Maybe if I understand better how you limit the jerk I can come up with an alternative.) There is no functionality to limit the jerk of individual axes in the CNC. With SMC_LimitDynamics, you can limit the velocity and acceleration of cartesian (X/Y/Z) and additional (P/Q/U/V/W/A/B/C) axes, but not the jerk. And with a quadratic ramp type you can limit the jerk on the path. Best regards, Georg
Last updated: 2026-06-10
Post by gseidel on Mismatch between coordinate monitor and actual motion using SMC_GroupJog2, MC_MoveLinearAbsolute (6DOF)
CODESYS Forge
talk
(Post)
Hi darwin03, as can bee seen at the end of your video, the direction of rotation now seems correct for all axes. I can only guess, but the most likely reason are different denavit hartenberg parameters in the SoftMotion axis group editors and the robot used in the simulation tool. Maybe some arm lengths differ, maybe some offsets are given with opposite sign. I would again refer you to https://content.helpme-codesys.com/en/libs/SM3_Transformation/Current/SM3_Transformation/Function-Blocks/Standalone-Kinematics/Articulated-Robots/6AxisArticulated/Kin_ArticulatedRobot_6DOF.html. Please double check all parameters and the table of the DH parameters given there and compare that against the robot in the simulation tool. Also: did you configure any tool in CODESYS? I would suggest to simplify and remove any tools for finding the source of the wrong movements. Best regards, Georg
Last updated: 2026-10-16
Post by imdatatas on The default ramp type selection in SoftMotion V4.18.0.0 is Quadratic
CODESYS Forge
talk
(Post)
Dear @gseidel, Thank you for your clarification. I fully agree that the quadratic ramp type may have certain technical advantages. However, the main problem is backward compatibility and consistency across projects. In many automation projects, application developers rely on the fact that creating a new axis object will behave exactly the same way as in previous versions. With SoftMotion V4.18.0.0 and later, if an application developer adds an axis and overlooks the changed default, the motion function blocks behave differently than expected. In particular, since the Jerk value in SM3_Basic function blocks is ineffective in trapezoid ramp type, users are accustomed to leaving this parameter empty in their projects. In many existing projects, this variable has not even been assigned. When the default is changed to quadratic, the Jerk parameter suddenly becomes relevant, which can cause errors or unexpected behaviour in the field. From a user perspective, a default setting should always be the βsafeβ and βexpectedβ option, while alternative options (like quadratic) can be selected manually if desired. Keeping the default as trapezoid ensures compatibility with existing projects and prevents unexpected issues, while still allowing users to benefit from quadratic ramps if they explicitly choose so. For these reasons, I kindly ask you to reconsider making trapezoid the default again. This would significantly reduce the risk of unexpected behaviour in future projects while still preserving the advantages of the quadratic ramp type for those who actively select it. Of course, the final decision is entirely at your discretion. Best Regards, imdatatas
Last updated: 2025-09-26
Post by ph0010421 on How to create a stopwatch?
CODESYS Forge
talk
(Post)
Do you need an 'hours-run' counter? And 1 second resolution is ok? I think you're over-thinking it. (The task time needs to be < 1second) Have a look at the LAD... Then, the time in seconds can be made into hh:mm:ss with this FUNction Declarations: FUNCTION funSecondsToStringTime: string VAR_INPUT InSeconds: UDINT; END_VAR VAR AsString: STRING; Minutes: UDINT; Hours: UDINT; Seconds: UDINT; MinutesAsString: STRING(2); HoursAsString: STRING(2); SecondsAsString: STRING(2); END_VAR and the code: Hours := InSeconds / 60 / 60; //Derive hours Minutes := (InSeconds - (Hours * 60 * 60)) / 60; //Derive minutes Seconds := InSeconds - ((Hours * 60 * 60) + (Minutes * 60));//Derive seconds HoursAsString := UDINT_TO_STRING(Hours); MinutesAsString := UDINT_TO_STRING(Minutes); SecondsAsString := UDINT_TO_STRING(Seconds); IF LEN(HoursAsString) = 1 THEN HoursAsString := CONCAT('0',HoursAsString); END_IF; IF LEN(MinutesAsString) = 1 THEN MinutesAsString := CONCAT('0',MinutesAsString); END_IF; IF LEN(SecondsAsString) = 1 THEN SecondsAsString := CONCAT('0',SecondsAsString); END_IF; AsString := CONCAT(HoursAsString, ':'); //assemble string AsString := CONCAT(AsString,MinutesAsString); AsString := CONCAT(AsString,':'); AsString := CONCAT(AsString, SecondsAsString); funSecondsToStringTime := AsString;
Last updated: 2023-12-08
Post by wildcard on Modbus Client Request Not Processed
CODESYS Forge
talk
(Post)
Hi, does anyone has a solution for this issue. I've the same problem. I've implemented a very simple client based on the Modbus Examples and connected the soft PLC to a Modbus Simulator. PROGRAM ModbusClient VAR initDone : BOOL := FALSE; errorID : ModbusFB.Error; client : ModbusFB.ClientTCP; timeout : UDINT := 500000; replyTimeout : UDINT := 200000; aUINT : ARRAY [0..8] OF UINT; clientRequestReadHoldingRegisters : ModbusFB.ClientRequestReadHoldingRegisters; clientRequestsCnt : UINT := 0; clientRequestsProcessCnt : UINT := 0; ipAddress : ARRAY[0..3] OF BYTE := [10,54,0,72]; END_VAR IF NOT initDone THEN initDone := TRUE; client(aIPaddr:=ipAddress, udiLogOptions:=ModbusFB.LoggingOptions.All); client(xConnect:=TRUE, ); clientRequestReadHoldingRegisters(rClient:=client, udiTimeOut:=timeout, uiUnitId:=1, uiStartItem:=0, uiQuantity:=4, pData:=ADR(aUINT[0]), udiReplyTimeout:=replyTimeout); clientRequestReadHoldingRegisters.xExecute := TRUE; clientRequestsCnt := 0; END_IF clientRequestReadHoldingRegisters(rClient:=client, udiTimeOut:=timeout, uiUnitId:=1, uiStartItem:=0, uiQuantity:=4, pData:=ADR(aUINT[0]), udiReplyTimeout:=replyTimeout, xExecute := TRUE); IF clientRequestReadHoldingRegisters.xError THEN clientRequestsCnt := clientRequestsCnt +1 ; errorID := clientRequestReadHoldingRegisters.eErrorID; END_IF clientRequestReadHoldingRegisters(rClient:=client, udiTimeOut:=timeout, uiUnitId:=1, uiStartItem:=0, uiQuantity:=4, pData:=ADR(aUINT[0]), udiReplyTimeout:=replyTimeout, xExecute := NOT clientRequestReadHoldingRegisters.xExecute); When the system is running I do get the following on the logs: 2024-05-13T10:18:07.443Z: Cmp=MODBUS lib, Class=1, Error=0, Info=0, pszInfo= Client.RequestProcessed ClientRequest,16#0164ADC561A0 unitId=1 fc=ReadHoldingRegisters id=2070 state=Error 2024-05-13T10:18:07.443Z: Cmp=MODBUS lib, Class=1, Error=0, Info=0, pszInfo= ClientRequest,16#0164ADC561A0 unitId=1 fc=ReadHoldingRegisters id=2070 change state Error -> None timestamp=63843421226 2024-05-13T10:18:08.444Z: Cmp=MODBUS lib, Class=1, Error=0, Info=0, pszInfo= ClientRequest,16#0164ADC561A0 unitId=1 fc=ReadHoldingRegisters id=2071 change state None -> Init timestamp=63844421420 2024-05-13T10:18:09.444Z: Cmp=MODBUS lib, Class=1, Error=0, Info=0, pszInfo= ClientRequest,16#0164ADC561A0 unitId=1 fc=ReadHoldingRegisters id=2071 change state Init -> Error timestamp=63845421675 But the errorID is jumping between OK and RequestNotProcessed. Any help is very appreciated which gives me a hint what I'm doing wrong. Thanks
Last updated: 2024-05-13
Post by davidbo on How to allow a user to handle certificates without access to sourcecode?
CODESYS Forge
talk
(Post)
With CODESYS V3.5 it is possible for a user to do the following things among many others. 1) Handling certificates especially move a certificate to the trusted folder. 2) Change password and create new users for OPC UA access However it requires access to the whole projects and its source code. Something you might not want to hand over to an end user for a stand alone product. Is there a way out of this problem?
Last updated: 2023-11-06
Post by voffi on Converting UINT into bytes and converting 2Bytes into UINT
CODESYS Forge
talk
(Post)
There are some ways. One is to use SHR and SHL and it depends on your byte order in the data array. For Motorola byte order: PROGRAM PLC_PRG VAR u : UINT; byte_array_in : ARRAY [1..8] OF BYTE := [16#11, 16#12, 16#13, 16#14, 16#15, 16#16, 16#17]; byte_array_out : ARRAY [1..8] OF BYTE; END_VAR u := SHL(TO_UINT(byte_array_in[2]), 8) + TO_UINT(byte_array_in[1]); byte_array_out[1] := TO_BYTE(u); byte_array_out[2] := TO_BYTE(SHR(u, 8)); If it's Intel byte order just change 1 and 2 in the array indexes.
Last updated: 2023-12-07
Post by nikgind on Codesys Communication Manger - Required information model version exists in the model repository but is not found
CODESYS Forge
talk
(Post)
Hi, yes i did solve it. You have to change the namespace 0 model in the UaModeler. Open the modeler --> Settings --> Edit Settings --> scroll down to the last option "External Model Support" --> Check "Allow replacing built-in..." Now create a new project in the UaModeler. If you have to choose your base models, you can see the option "Find another Opc.Ua.NodeSet2". I have attached the .xml i am using.
Last updated: 2024-06-28
Post by taqamert on Codesys 2.3 & Peak PCAN
CODESYS Forge
talk
(Post)
Despite working on it for days, I haven't achieved any results. I followed the necessary steps one by one as mentioned in the file you sent, but there hasn't been the slightest change. I couldn't find the step you mentioned "Set the 'Can Board Type' to PCAN USB" in the Word document. There is no such setting anywhere I looked. Is there a more detailed explanation available, or can you explain it in more detail? What am I missing?
Last updated: 2024-07-16
Post by kislov on Change modbus server parameters from program
CODESYS Forge
talk
(Post)
Use in IEC-code: Modbus_Serial_Device.UpdateComPortSettings(...) https://content.helpme-codesys.com/en/libs/IoDrvModbusSerialSlave/Current/pou-ModbusSerialDeviceDiag/UpdateComPortSettings.html Take note: "Only possible if server is disabled (see xEnable Input)" So: Modbus_Serial_Device.xEnable := FALSE; Modbus_Serial_Device.UpdateComPortSettings(...) Modbus_Serial_Device.xEnable := TRUE; Please note that after PLC reboot the values from the GUI (from your screenshot) will be applied again. So you need to save values from HMI in RETAIN and restore them after start of application.
Last updated: 2024-07-17
Post by mikek10 on Error IoDrvEthernetIP: Connection Failure. (16#1) How to solve
CODESYS Forge
talk
(Post)
Make sure the number of bytes matches the values in the Ethernet/IP>Assembly Information section of the Wagos web management page (expand by clicking on the +). The EDS file will probably have defaulted to assemblies 101 and 104. If you want a different assembly there is an article that tells you how to modify but seems to be unavailable at the moment. An alternative is to modify the .eds file to change the default assemblies.
Last updated: 2024-07-22
Post by egau on Mutate Hash table value
CODESYS Forge
talk
(Post)
Hi, using the ElementCollections Library, why isn't it possible to mutate a value found within a HashTable? From what I understand, the only way to change a value would be to use the RemoveByKey(), followed by AddKeyValuePair(). My goal is to use a Data Structure that works like a Dictionary in Python. The HashTable seems to come close to this, except that the values themselves seem to be immutable... In python, we can mutate a dict easily (see attached picture).
Last updated: 2024-08-29
Post by hbuitrago on CmpIecTask-program loaded exception
CODESYS Forge
talk
(Post)
I'm facing an error that show on the codesys and the PLC that dont let either the PLC run or access it using the remote software, Error: program loaded exception Log: exception position:IP=0x0xfffffffe (no IEC context could be retrieved) component: CmpIecTask exception [accessviolation] ocurred: APP=[application], Task=[Task] POU changed, that inhibits an online change, Plase let me know if there is a solution for this issue, Best regards,
Last updated: 2024-09-06
Post by jwhaley on C0007 Errors
CODESYS Forge
talk
(Post)
I ended up figuring it out It wasn't in my code. It kept taking me to 2 of my visualizations but it wasn't going to anything specific. Figured out it was some arrows that I had made to buttons for a mouse click to go to the other visualizations. I removed the text in the assign box but didn't remove the action "change shown Visualization from the list. If I deleted the images all together, the error went away. That's how I thought to go look at that.
Last updated: 2024-10-10
Post by xabier on Problem Update new version Master ethercat
CODESYS Forge
talk
(Post)
Hi, I have a project in Codesys...and i need update a new version of amster ehtercat and i have a problem. The origianl version with create of project was 3.5.13.10 I can change version to Master Ethercat 3.5.13.10 to 3.5.16.70 but i canΒ΄t update the last version 4.4.0.0 (I attached the screen "Version Master OK-NO OK"). In the moment update to the last version appear a lot of error("Version Master NO OK") Can anyone help me please?
Last updated: 2024-10-25
Post by jeroenaero on CodeSys Raspberry pi I2C driver not found
CODESYS Forge
talk
(Post)
I succeed to change the device to PI_SL but still the same problem of the I2C device switching between running and not running. the only difference with your project is that yo use I2C_master device version 4.7.0 and i 4.7.13, for GPIO i also use the 4.7.13 version and you the 4.7.0. Can you send me the older version of the Raspberry PI pheripals library, because i cannot choose lower version then 4.7.10 for the GPIO and I2C_master device
Last updated: 2024-11-11
Post by durallymax on Access Variable Visu Dialog
CODESYS Forge
talk
(Post)
Is there a way to access the variable in the called dialog? Example: Text Field element with PLC_PRG.myVar as Text variable. OnMouseClick configured to write variable with keypad pop-up. OnValueChanged configured to Execute ST RND(PLC_PRG.myVar,2); Rather than change myVar with each copy of this Text Field, is there a way to access whatever the configured text variable is? Generally try to stay away from ST in visu, but was curious regardless.
Last updated: 2024-11-14
Post by dogulas on OPC UA C# client connecting to OPC UA CODESYS server
CODESYS Forge
talk
(Post)
Ok, for the sake of completeness in case anyone else has this problem. I can tell you that what finally worked for me was to change the line: // create an ExtensionObject to wrap the value to be written ExtensionObject extensionObject = new ExtensionObject( new ExpandedNodeId("GVL_StructA", 5), structAData ); to: // create an ExtensionObject to wrap the value to be written ExtensionObject extensionObject = new ExtensionObject( new ExpandedNodeId("GVL_StructA|defaultbinary", 5), structAData ); I'm sure there are many other problems that could cause this very generic error, but this was my problem.
Last updated: 2024-12-30