Post by imdatatas on Unrecoverable SoftMotion state after switch to PreOp CODESYS Forge talk (Post)
Dear @alimans, Additionally, As far as I know since starting from Softmotion V4.18.0.0 automatic restart behaviour for an axis has been changed for this issue. See below explanation from release notes. "With CODESYS SoftMotion 4.18.0.0, the behavior of SoftMotion axes after a loss of communication to the servo drive has changed. Now, an automatic reinitialization is performed as soon as the communication is established again. Before, an explicit call to SMC3_ReinitDrive had to be performed. An example for a loss of communication is that the cable to one of the drives is unplugged." Regards, imdatatas
Last updated: 2025-10-23

Post by darwin03 on Mismatch between coordinate monitor and actual motion using SMC_GroupJog2, MC_MoveLinearAbsolute (6DOF) CODESYS Forge talk (Post)
Dear Georg, Thank you for your explanation about the axis scaling. I checked the scaling of Joint6 and corrected it so that one technical unit equals one angular degree. However, I am now facing another issue. When I move all axes to zero position and then try to use SMC_GroupJog2 and MC_MoveLinearAbsolute, I receive the error SMC_CP_CONFIGS_DIFFER I already tried moving each joint manually to different positions before executing the motion command, but the error still appears. Could you please explain: What exactly causes SMC_CP_CONFIGS_DIFFER Thank you very much for your support. Best regards, darwin03
Last updated: 2026-05-04

Post by gseidel on Limit Axis CNC Jerk using SMC_Polynomial_AbsMaxLocs CODESYS Forge talk (Post)
Dear josepmariarams, this (internal) function has been removed with SoftMotion 4.17.0.0. We do not have public functions to compute the extrema of a polynomial. On which polynomials exactly did you call SMC_Polynomial_AbsMaxLocs? (Maybe if I understand better how you limit the jerk I can come up with an alternative.) There is no functionality to limit the jerk of individual axes in the CNC. With SMC_LimitDynamics, you can limit the velocity and acceleration of cartesian (X/Y/Z) and additional (P/Q/U/V/W/A/B/C) axes, but not the jerk. And with a quadratic ramp type you can limit the jerk on the path. Best regards, Georg
Last updated: 2026-06-10

Post by imdatatas on The default ramp type selection in SoftMotion V4.18.0.0 is Quadratic CODESYS Forge talk (Post)
Dear @gseidel, Thank you for your clarification. I fully agree that the quadratic ramp type may have certain technical advantages. However, the main problem is backward compatibility and consistency across projects. In many automation projects, application developers rely on the fact that creating a new axis object will behave exactly the same way as in previous versions. With SoftMotion V4.18.0.0 and later, if an application developer adds an axis and overlooks the changed default, the motion function blocks behave differently than expected. In particular, since the Jerk value in SM3_Basic function blocks is ineffective in trapezoid ramp type, users are accustomed to leaving this parameter empty in their projects. In many existing projects, this variable has not even been assigned. When the default is changed to quadratic, the Jerk parameter suddenly becomes relevant, which can cause errors or unexpected behaviour in the field. From a user perspective, a default setting should always be the “safe” and “expected” option, while alternative options (like quadratic) can be selected manually if desired. Keeping the default as trapezoid ensures compatibility with existing projects and prevents unexpected issues, while still allowing users to benefit from quadratic ramps if they explicitly choose so. For these reasons, I kindly ask you to reconsider making trapezoid the default again. This would significantly reduce the risk of unexpected behaviour in future projects while still preserving the advantages of the quadratic ramp type for those who actively select it. Of course, the final decision is entirely at your discretion. Best Regards, imdatatas
Last updated: 2025-09-26

Post by ph0010421 on How to create a stopwatch? CODESYS Forge talk (Post)
Do you need an 'hours-run' counter? And 1 second resolution is ok? I think you're over-thinking it. (The task time needs to be < 1second) Have a look at the LAD... Then, the time in seconds can be made into hh:mm:ss with this FUNction Declarations: FUNCTION funSecondsToStringTime: string VAR_INPUT InSeconds: UDINT; END_VAR VAR AsString: STRING; Minutes: UDINT; Hours: UDINT; Seconds: UDINT; MinutesAsString: STRING(2); HoursAsString: STRING(2); SecondsAsString: STRING(2); END_VAR and the code: Hours := InSeconds / 60 / 60; //Derive hours Minutes := (InSeconds - (Hours * 60 * 60)) / 60; //Derive minutes Seconds := InSeconds - ((Hours * 60 * 60) + (Minutes * 60));//Derive seconds HoursAsString := UDINT_TO_STRING(Hours); MinutesAsString := UDINT_TO_STRING(Minutes); SecondsAsString := UDINT_TO_STRING(Seconds); IF LEN(HoursAsString) = 1 THEN HoursAsString := CONCAT('0',HoursAsString); END_IF; IF LEN(MinutesAsString) = 1 THEN MinutesAsString := CONCAT('0',MinutesAsString); END_IF; IF LEN(SecondsAsString) = 1 THEN SecondsAsString := CONCAT('0',SecondsAsString); END_IF; AsString := CONCAT(HoursAsString, ':'); //assemble string AsString := CONCAT(AsString,MinutesAsString); AsString := CONCAT(AsString,':'); AsString := CONCAT(AsString, SecondsAsString); funSecondsToStringTime := AsString;
Last updated: 2023-12-08

Post by wildcard on Modbus Client Request Not Processed CODESYS Forge talk (Post)
Hi, does anyone has a solution for this issue. I've the same problem. I've implemented a very simple client based on the Modbus Examples and connected the soft PLC to a Modbus Simulator. PROGRAM ModbusClient VAR initDone : BOOL := FALSE; errorID : ModbusFB.Error; client : ModbusFB.ClientTCP; timeout : UDINT := 500000; replyTimeout : UDINT := 200000; aUINT : ARRAY [0..8] OF UINT; clientRequestReadHoldingRegisters : ModbusFB.ClientRequestReadHoldingRegisters; clientRequestsCnt : UINT := 0; clientRequestsProcessCnt : UINT := 0; ipAddress : ARRAY[0..3] OF BYTE := [10,54,0,72]; END_VAR IF NOT initDone THEN initDone := TRUE; client(aIPaddr:=ipAddress, udiLogOptions:=ModbusFB.LoggingOptions.All); client(xConnect:=TRUE, ); clientRequestReadHoldingRegisters(rClient:=client, udiTimeOut:=timeout, uiUnitId:=1, uiStartItem:=0, uiQuantity:=4, pData:=ADR(aUINT[0]), udiReplyTimeout:=replyTimeout); clientRequestReadHoldingRegisters.xExecute := TRUE; clientRequestsCnt := 0; END_IF clientRequestReadHoldingRegisters(rClient:=client, udiTimeOut:=timeout, uiUnitId:=1, uiStartItem:=0, uiQuantity:=4, pData:=ADR(aUINT[0]), udiReplyTimeout:=replyTimeout, xExecute := TRUE); IF clientRequestReadHoldingRegisters.xError THEN clientRequestsCnt := clientRequestsCnt +1 ; errorID := clientRequestReadHoldingRegisters.eErrorID; END_IF clientRequestReadHoldingRegisters(rClient:=client, udiTimeOut:=timeout, uiUnitId:=1, uiStartItem:=0, uiQuantity:=4, pData:=ADR(aUINT[0]), udiReplyTimeout:=replyTimeout, xExecute := NOT clientRequestReadHoldingRegisters.xExecute); When the system is running I do get the following on the logs: 2024-05-13T10:18:07.443Z: Cmp=MODBUS lib, Class=1, Error=0, Info=0, pszInfo= Client.RequestProcessed ClientRequest,16#0164ADC561A0 unitId=1 fc=ReadHoldingRegisters id=2070 state=Error 2024-05-13T10:18:07.443Z: Cmp=MODBUS lib, Class=1, Error=0, Info=0, pszInfo= ClientRequest,16#0164ADC561A0 unitId=1 fc=ReadHoldingRegisters id=2070 change state Error -> None timestamp=63843421226 2024-05-13T10:18:08.444Z: Cmp=MODBUS lib, Class=1, Error=0, Info=0, pszInfo= ClientRequest,16#0164ADC561A0 unitId=1 fc=ReadHoldingRegisters id=2071 change state None -> Init timestamp=63844421420 2024-05-13T10:18:09.444Z: Cmp=MODBUS lib, Class=1, Error=0, Info=0, pszInfo= ClientRequest,16#0164ADC561A0 unitId=1 fc=ReadHoldingRegisters id=2071 change state Init -> Error timestamp=63845421675 But the errorID is jumping between OK and RequestNotProcessed. Any help is very appreciated which gives me a hint what I'm doing wrong. Thanks
Last updated: 2024-05-13

Post by davidbo on How to allow a user to handle certificates without access to sourcecode? CODESYS Forge talk (Post)
With CODESYS V3.5 it is possible for a user to do the following things among many others. 1) Handling certificates especially move a certificate to the trusted folder. 2) Change password and create new users for OPC UA access However it requires access to the whole projects and its source code. Something you might not want to hand over to an end user for a stand alone product. Is there a way out of this problem?
Last updated: 2023-11-06

Post by voffi on Converting UINT into bytes and converting 2Bytes into UINT CODESYS Forge talk (Post)
There are some ways. One is to use SHR and SHL and it depends on your byte order in the data array. For Motorola byte order: PROGRAM PLC_PRG VAR u : UINT; byte_array_in : ARRAY [1..8] OF BYTE := [16#11, 16#12, 16#13, 16#14, 16#15, 16#16, 16#17]; byte_array_out : ARRAY [1..8] OF BYTE; END_VAR u := SHL(TO_UINT(byte_array_in[2]), 8) + TO_UINT(byte_array_in[1]); byte_array_out[1] := TO_BYTE(u); byte_array_out[2] := TO_BYTE(SHR(u, 8)); If it's Intel byte order just change 1 and 2 in the array indexes.
Last updated: 2023-12-07

Post by nikgind on Codesys Communication Manger - Required information model version exists in the model repository but is not found CODESYS Forge talk (Post)
Hi, yes i did solve it. You have to change the namespace 0 model in the UaModeler. Open the modeler --> Settings --> Edit Settings --> scroll down to the last option "External Model Support" --> Check "Allow replacing built-in..." Now create a new project in the UaModeler. If you have to choose your base models, you can see the option "Find another Opc.Ua.NodeSet2". I have attached the .xml i am using.
Last updated: 2024-06-28

Post by taqamert on Codesys 2.3 & Peak PCAN CODESYS Forge talk (Post)
Despite working on it for days, I haven't achieved any results. I followed the necessary steps one by one as mentioned in the file you sent, but there hasn't been the slightest change. I couldn't find the step you mentioned "Set the 'Can Board Type' to PCAN USB" in the Word document. There is no such setting anywhere I looked. Is there a more detailed explanation available, or can you explain it in more detail? What am I missing?
Last updated: 2024-07-16

Post by kislov on Change modbus server parameters from program CODESYS Forge talk (Post)
Use in IEC-code: Modbus_Serial_Device.UpdateComPortSettings(...) https://content.helpme-codesys.com/en/libs/IoDrvModbusSerialSlave/Current/pou-ModbusSerialDeviceDiag/UpdateComPortSettings.html Take note: "Only possible if server is disabled (see xEnable Input)" So: Modbus_Serial_Device.xEnable := FALSE; Modbus_Serial_Device.UpdateComPortSettings(...) Modbus_Serial_Device.xEnable := TRUE; Please note that after PLC reboot the values from the GUI (from your screenshot) will be applied again. So you need to save values from HMI in RETAIN and restore them after start of application.
Last updated: 2024-07-17

Post by mikek10 on Error IoDrvEthernetIP: Connection Failure. (16#1) How to solve CODESYS Forge talk (Post)
Make sure the number of bytes matches the values in the Ethernet/IP>Assembly Information section of the Wagos web management page (expand by clicking on the +). The EDS file will probably have defaulted to assemblies 101 and 104. If you want a different assembly there is an article that tells you how to modify but seems to be unavailable at the moment. An alternative is to modify the .eds file to change the default assemblies.
Last updated: 2024-07-22

Post by egau on Mutate Hash table value CODESYS Forge talk (Post)
Hi, using the ElementCollections Library, why isn't it possible to mutate a value found within a HashTable? From what I understand, the only way to change a value would be to use the RemoveByKey(), followed by AddKeyValuePair(). My goal is to use a Data Structure that works like a Dictionary in Python. The HashTable seems to come close to this, except that the values themselves seem to be immutable... In python, we can mutate a dict easily (see attached picture).
Last updated: 2024-08-29

Post by hbuitrago on CmpIecTask-program loaded exception CODESYS Forge talk (Post)
I'm facing an error that show on the codesys and the PLC that dont let either the PLC run or access it using the remote software, Error: program loaded exception Log: exception position:IP=0x0xfffffffe (no IEC context could be retrieved) component: CmpIecTask exception [accessviolation] ocurred: APP=[application], Task=[Task] POU changed, that inhibits an online change, Plase let me know if there is a solution for this issue, Best regards,
Last updated: 2024-09-06

Post by jwhaley on C0007 Errors CODESYS Forge talk (Post)
I ended up figuring it out It wasn't in my code. It kept taking me to 2 of my visualizations but it wasn't going to anything specific. Figured out it was some arrows that I had made to buttons for a mouse click to go to the other visualizations. I removed the text in the assign box but didn't remove the action "change shown Visualization from the list. If I deleted the images all together, the error went away. That's how I thought to go look at that.
Last updated: 2024-10-10

Post by xabier on Problem Update new version Master ethercat CODESYS Forge talk (Post)
Hi, I have a project in Codesys...and i need update a new version of amster ehtercat and i have a problem. The origianl version with create of project was 3.5.13.10 I can change version to Master Ethercat 3.5.13.10 to 3.5.16.70 but i can´t update the last version 4.4.0.0 (I attached the screen "Version Master OK-NO OK"). In the moment update to the last version appear a lot of error("Version Master NO OK") Can anyone help me please?
Last updated: 2024-10-25

Post by jeroenaero on CodeSys Raspberry pi I2C driver not found CODESYS Forge talk (Post)
I succeed to change the device to PI_SL but still the same problem of the I2C device switching between running and not running. the only difference with your project is that yo use I2C_master device version 4.7.0 and i 4.7.13, for GPIO i also use the 4.7.13 version and you the 4.7.0. Can you send me the older version of the Raspberry PI pheripals library, because i cannot choose lower version then 4.7.10 for the GPIO and I2C_master device
Last updated: 2024-11-11

Post by durallymax on Access Variable Visu Dialog CODESYS Forge talk (Post)
Is there a way to access the variable in the called dialog? Example: Text Field element with PLC_PRG.myVar as Text variable. OnMouseClick configured to write variable with keypad pop-up. OnValueChanged configured to Execute ST RND(PLC_PRG.myVar,2); Rather than change myVar with each copy of this Text Field, is there a way to access whatever the configured text variable is? Generally try to stay away from ST in visu, but was curious regardless.
Last updated: 2024-11-14

Post by dogulas on OPC UA C# client connecting to OPC UA CODESYS server CODESYS Forge talk (Post)
Ok, for the sake of completeness in case anyone else has this problem. I can tell you that what finally worked for me was to change the line: // create an ExtensionObject to wrap the value to be written ExtensionObject extensionObject = new ExtensionObject( new ExpandedNodeId("GVL_StructA", 5), structAData ); to: // create an ExtensionObject to wrap the value to be written ExtensionObject extensionObject = new ExtensionObject( new ExpandedNodeId("GVL_StructA|defaultbinary", 5), structAData ); I'm sure there are many other problems that could cause this very generic error, but this was my problem.
Last updated: 2024-12-30

Post by andre-luis on Device diagnosis ( EtherCAT IO card ) CODESYS Forge talk (Post)
Hi @TimvH, In the meantime, I did some experiments and could find a way to achieve similar result. I made some tests, removing the last card from the array, seeing the change on status. PROGRAM P_IOS_STATUSES VAR devStateInput : DEVICE_STATE; devStateOutput : DEVICE_STATE; devStateEncoder : DEVICE_STATE; END_VAR devStateInput := IoConfig_Globals.EL1819.GetDeviceState(); devStateOutput := IoConfig_Globals.EL2809.GetDeviceState(); devStateEncoder := IoConfig_Globals.EL5151.GetDeviceState(); GVL.bInputCardOK := ( devStateInput = DEVICE_STATE.RUNNING ); GVL.bOutputCardOK := ( devStateOutput = DEVICE_STATE.RUNNING ); GVL.bEncoderCardOK := ( devStateEncoder = DEVICE_STATE.RUNNING ); Many thanks for your quick and extensive reply.
Last updated: 2025-02-06

Post by dogulas on Removing a symbol from the IEC Symbols Editor grid CODESYS Forge talk (Post)
Right now when I make a change to one of the tags in my code, I have to completely remove the IEC Symbol Publishing object from the tree view and re-add it. Then I have to completely re-add every symbol to the grid view by dragging them over. This can be a lot. Surely, this is not the intended behavior. Can anyone tell me how this is supposed to work?
Last updated: 2025-02-11

Post by struccc on When running as a service, CodesysControl doesn't write log files to the disk (and other CmpLog related issuess) CODESYS Forge talk (Post)
Are you sure when running as service, it is not reading configuration from C:\Windows\System32\config\systemprofile\AppData\Roaming\CODESYS... ? Is the SRV user is set for the CODESYS services? 2 ways to fix it: Change the CODESYSControl.cfg in the installation directory (ProgramFiles/CODESYS...). Replace %APPDATA% with something fix. Modify the service configuration in windows service manager to run as a different user (ie bot as Local system account)
Last updated: 2025-02-28

Post by trusty-squire on Ethernet/IP Scanner Exception CODESYS Forge talk (Post)
What is the task configuration? When you are online and look at the task monitor, what does it show? (Put a screenshot here). If the processor is overloaded you'll likely need to increase the cycle interval, disable the watchdog, or change to a cyclic task instead of interval based? Also, You might want to adjust your task priorities so they don't all have the same priority. Just a few thoughts, although looking at the task monitor would help in troubleshooting.
Last updated: 2025-03-12

Post by pistola on How to change font and font color rectangle/or related object CODESYS Forge talk (Post)
Here is the help sections for visual elements rectangle. https://content.helpme-codesys.com/en/CODESYS%20Visualization/_visu_elem_rectangle.html Under "Font Variable" there is "Color" which is a Dword, you can make a variable that changes colour within your code to the color needed. Note the format for the Dword variable is: colorVariable := 16#TTRRGGBB Where: TT = Transparency 00-FF RE = Red 00-FF GG = Green 00-FF BB = Blue 00-FF https://content.helpme-codesys.com/en/CODESYS%20Visualization/_visu_animate_color.html
Last updated: 2025-03-17

Post by atone on Set DeviceID of an IO-Link Sensor at Runtime CODESYS Forge talk (Post)
I need to be able to change (set) the DeviceID of an IO-Link sensor (see DeviceID.png) at runtime. I tried with both ProfinetCommon.PN_PortConfiguration and ProfinetCommon.IOL_PortConfiguration, but I get an error for both when I try to read the port configuration (see PN_PortConfiguration.png). Does one of those FBs is the right one for my purpose? Do I possibly make a mistake when assigning the parameter IOLD_ID/IOLM_ID?
Last updated: 2025-03-19