Post by wbj0t on Global variable access by Programms and Modbus Devices (attach device to bus) CODESYS Forge talk (Post)
Hi everyone. I use Raspberry Pi 4, one core codesys SL. I have a question about global variable access via programm when I glued the same variable to MODBUS SERIAL/TCP DEVICE holding register. So, the question: what behavior of this modifying? When I set "Always update variables (in bus cycle)" and set some task as bus for the Device, then in another task I cant change this varible (can, but immediatly the old value setted again). But the same things works with MODBUS SLAVE: again "Always update..." and master attached to some task, then I change variable in another task and all works. I cant set up my variables from retains file at PrepareStart event because of this behavior with MODBUS SERIAL/TCP DEVICE. Thanks, wbj0t.
Last updated: 2024-07-18

Post by timvh on Dynamically enabling/disabling Modbus slave devices in runtime (performance issue with timeouts) CODESYS Forge talk (Post)
As far as I remember, the Reconfigure functionality doesn't work for Modbus devices. But... Each Modbus device in your device tree has a name. You can set the property "Enable" of this device to FALSE to stop communicating with it. So if one of your Modbus Slave devices name is "MbSlave1" in the device tree, then in your code you can set the Enable to FALSE to let it stop communicating: MbSlave1.Enable := FALSE; Please let us know if this worked on your controller with your application and your CODESYS version. Alternatively you could use the ModbusFB library. See: https://forge.codesys.com/prj/codesys-example/modbus/home/Home/
Last updated: 2025-08-13

Post by joanm on Programmatically change the IP addresses of the Modbus TCP slave devices CODESYS Forge talk (Post)
Hello all, I am working in a project in which there are multiple Modbus TCP slaves. I need to be able to change the IP addresses of those devices from the HMI and I was planning to use the process depicted here: https://faq.codesys.com/display/CDSFAQ/Modbus+TCP+Slave%3A+Dynamic+Setting+of+the+IP+Address I can see the port number is what is used to specify which slave device we want to modify the IP address of. This said, can I freely set arbitrary port numbers to each device? I mean, can I set the first device to be at port 502, the second one at port 503... Any drawback or restriction? Is there any other way to reference to the device without having to change the port numbers? Thank you all in advance.
Last updated: 2024-01-04

Post by fless on No source code available for profinet library CODESYS Forge talk (Post)
looks like you are running in a bug in the newest version 4.4.0 of the profinet library or the new library triggers a bug in your code. did you update your profinet device too? you could try to downgrade to an older version of the library. via library manager - placeholders, double click Profinet 4.4.0 in the library column and choose an older version.
Last updated: 2023-08-23

Post by fefefede on Error C0521 - unknow compiler CODESYS Forge talk (Post)
Hello, i'm a new user of Codesys and student of ST program for PLC. Since today for a few new projects i have two error code C0521 and i can't solve. I also just try to update device and search library but nothign resolve. How can i fix this? Thanks
Last updated: 2023-09-02

Post by egau on Hard shutdown: no code on device after power on CODESYS Forge talk (Post)
Hi, thanks for the fast response :) Yes I Have a .err file. Sorry I forgot to upload it. It is a binary file though... "Runtime goes in exception before the shutdown ?" I think it goes into exception at the same time as the power is lost...
Last updated: 2024-10-03

Post by jeroenaero on CodeSys Raspberry pi I2C driver not found CODESYS Forge talk (Post)
I don't have a multiplexer so it very weird that it connects with that multiplexer. If i do a I2C scan on the PI terminal, i only get the device addresses 0x48 and 0x51. One for the ADC and one for RTC. I will try again with your libraries
Last updated: 2024-11-12

Post by alawwirbilal on Codesys for raspberry pi 5 not working exactly CODESYS Forge talk (Post)
Hello, I have installed the runtime system on my raspberry pi 5 and when I scan for the devices it sees. But when I try to log in to the device it always ask me for a password and no matter what I give it says this is a wrong password. anyone could help?
Last updated: 2025-03-06

Post by clabaldo on Open dialog from ST previous to version 3.5.16 CODESYS Forge talk (Post)
I have found a similar topic but tried to run it in C3.5.16 and the visualization crashed. https://forge.codesys.com/forge/talk/Engineering/thread/8be0f6f14a/ My question is what is the easiest way to run a dialog from ST, as we need an external device to open the dialog so we cannot use the button on the display itself.
Last updated: 2024-03-22

Post by eschwellinger on connect IDE to plc that uses modem ppp CODESYS Forge talk (Post)
Which plc type is it? Easy connection is to install a Gateway on remote side - this is available for Windows and Linux devices Then just add a new Gateway in CODESYS (with the IP Adress of the remote device) -> then scan the plc via this new added Gateway
Last updated: 2024-05-21

Post by jnoyau on Visualisaion while in simulation CODESYS Forge talk (Post)
Hi all, Im new to Codesys 3.5, and am in the process fo making a visualisation i'd eventually export towards a Wago device. The issue I'm having currently is that when I compile and connect to the simulated program, my simulation won't launch. On the Visualisation tab, all I get is a text message (where previously there was my prepared visualisation) that says "The visualisation awaits a connection. Start the application" One thing to note: I work with Codesys 3.5 in french, so this is a rough translation. And a second: I'm not getting any errors nor warnings about the visualisation tab itself upon compiling Is there a step i'm missing after launching my simulation? Or would it be some really specific issue caused by the way I've set up my program? Thanks, J
Last updated: 2024-07-31

Post by jp23 on Unable to Connect to Modbus RTU Device CODESYS Forge talk (Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26

Post by jp23 on Unable to Connect to Modbus RTU Device CODESYS Forge talk (Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26

Post by jp23 on Unable to Connect to Modbus RTU Device CODESYS Forge talk (Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26

Post by jp23 on Unable to Connect to Modbus RTU Device CODESYS Forge talk (Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26

Post by jp23 on Unable to Connect to Modbus RTU Device CODESYS Forge talk (Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26

Post by jp23 on Unable to Connect to Modbus RTU Device CODESYS Forge talk (Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26

Post by jp23 on Unable to Connect to Modbus RTU Device CODESYS Forge talk (Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26

Post by thierry-b on CODESYS device discovery performance in large networks (/16) CODESYS Forge talk (Post)
Hello, We are using CODESYS 3.5 SP19.70 in an educational environment with several WAGO PFC200 controllers (CODESYS Runtime). Our campus network is currently configured as a /16, which creates a very large broadcast domain. We observe slow device discovery and long scan times when opening the network view. Before restructuring our architecture, we would like to know the recommended network practices for CODESYS: Recommended broadcast domain size for device discovery Possible impact of large networks (/16) on scan performance Usual recommendations (VLANs, /24 segmentation, etc.) Known limitations or points of attention in extended networks Any guidance or official recommendations would be very helpful. Thank you.
Last updated: 2026-03-29

Post by cd-tt on cannot connect ot linux runtime: device does not answer the scanrequest CODESYS Forge talk (Post)
I have the following setup: Proxmox PC with a debian 13 VM running CODESYS Control Linux SL and Edge Gateway. Installation method was through the Deploy Control SL and went rather smoothly. In my Device Tab I find the gateway and when scanning my network I also find my runtime. I want to connect and get promted that I should add a user. After setting up the user I get an error saying, that the device is not responding my scanrequest. Deploy Control SL Operation saying everythings up and running. I can confirm that from the terminal on the VM with "systemctl status codesyscontrol" and "systemctl status codesysgateway". I am running out of ideas how to fix that issue. Can anybody help? Screenshots attached.
Last updated: 2026-06-11

Post by eschwellinger on Connection to device closed CODESYS Forge talk (Post)
is there a way to check the plclog on Opus A3 by using cmd line under Linux? This log is what you need to check for the disconnection problem
Last updated: 2023-08-24

Post by chris12345 on FILE_OPERATION_DENIED CODESYS Forge talk (Post)
Hello everyone, I am using SP19 patch 2 on a Kunbus device with runtime package 4.9.0.0. I am having the same problem as mentioned above. With the FB File.open I get the FILE_OPERATION_DENIED error. I have also tried the path /var/opt/codesys/PlcLogic. Any advice? Chris
Last updated: 2023-10-17

Post by totorovic on Hard shutdown: no code on device after power on CODESYS Forge talk (Post)
Hi, Runtime goes in exception before the shutdown ? Do you have a .err file which is created ? (located in the folder of the .app and .crc)
Last updated: 2024-10-03

Post by timvh on Modbus TCP & RTU with Control for Linux SL CODESYS Forge talk (Post)
Most likely your IP address is set to 172.... because you use a VPN connection to your device. Probably best to use the other Ethernet interface for your modbus communication.
Last updated: 2024-10-24

Post by zatalian on Beckhoff EL7037 softmotion CODESYS Forge talk (Post)
Hi, Is the Beckhoff EL7037 supported by codesys with softmotion? Where can I find a device descriptor that includes the drive object for the EL7037?
Last updated: 2024-11-25