Post by salvadegianluca on SysPlcCtrl23 and C0338: The library 'cmperrors interfaces, 3.5.5.0 (system)' is supported just in 32 bit applications
CODESYS Forge
talk
(Post)
Good afternoon to everyone; I'm stuck with this error and I don't know how to get out from it... I tried several time googling for alternative systems to control the PLC applications and resets but without success. I would like to realize the possibility to reset the CPU and to start/stop the applications as it was possible with the SysPlcCtrl23, but this library is no longer supported in 64 bit systems and it seems due to the cmperrors interfaces sub library that was included in the above said one. Someone found a work around for this issue?
Last updated: 2024-06-14
Post by alez on CANopen safety , SRDO error behavior
CODESYS Forge
talk
(Post)
I have a project in which there is a Safety device in CANopen, and the PLC interfaces with it as Master. I would like to understand if it is possible to set the behavior in case one of the SRDOs that I receive from the slave is no longer received. From what I have seen, if the SRDOs are not received, the CANopen safety status becomes "Not in progress" and the mapped variables freeze at the last value detected. I want to understand if it was possible to set the variables connected to the SRDOs to take a default value (e.g. zero) in the event of a CANOpen error during reception.
Last updated: 2024-07-15
Post by mubeta on parker servo and position
CODESYS Forge
talk
(Post)
Reading between the lines of what you did not specify, it therefore seems to appear that in the programme, at the end of the movement order, there is an order to remove power and switch off the pulse modulation. if this is the case, it is obvious that the motor then remains free. If the position is to be maintained at the end of the movement, the motor current modulator, which on the PLC side is controlled via the MC_Power method, must not be interrupted. Another possibility is that in the motor drive settings, the standstill torque current is set very low or zero and without position monitoring. You have to check this via the servo motor drive.
Last updated: 2024-08-05
Post by cfam on Codesys Control for PLCnext SL, Bus not running
CODESYS Forge
talk
(Post)
Good day I would appreciate it if you can give me some advice on how to fix my "Bus Not Running Error". I am Using Codesys 3.5 SP20 and Codesys Control PLCnext SL V4.12.0.0. Codesys control was installed on the device and I can log into it but it seems that it does not pick up the PLC or the IO attached (Please see attached Image). The Bus Cycle Task of the AXL F 2152 is set to Main Task and the "Always update Variable" is Enabled on each IO Module. My Main Task interval is set to 100ms and Priority is set to 0. I have tried other options and none seem to work. Your response to this issue will be highly appreciated.
Last updated: 2024-08-12
Post by micik on Python scripting - print whole project tree
CODESYS Forge
talk
(Post)
Hello, I have found a script for printing device tree in Codesys project. This script is available as code snippet as an exmaple for using Python in Codesys. However I feel main documentation is lacking. For example, where can I find that object has "is_device" attribute? Code examples are given here: https://content.helpme-codesys.com/en/CODESYS%20Scripting/_cds_access_cds_func_in_python_scripts.html However, I have a question how to print the whole Project tree and not just devices? Of course I need to remove check: if treeobj.is_device: But simply removing this test condition will not produce what I want. I need to print PLC Logic, Application, ad other nodes in the Project tree. Where to find this documentation?
Last updated: 2024-08-12
Post by cfam on Codesys Control for PLCnext SL, Bus not running
CODESYS Forge
talk
(Post)
Good day I would appreciate it if you can give me some advice on how to fix my "Bus Not Running Error". I am Using Codesys 3.5 SP20 and Codesys Control PLCnext SL V4.12.0.0. Codesys control was installed on the device and I can log into it but it seems that it does not pick up the PLC or the IO attached (Please see attached Image). The Bus Cycle Task of the AXL F 2152 is set to Main Task and the "Always update Variable" is Enabled on each IO Module. My Main Task interval is set to 100ms and Priority is set to 0. I have tried other options and none seem to work. Your response to this issue will be highly appreciated.
Last updated: 2024-08-12
Post by expertplas on No connection to opc server from codesys opc client
CODESYS Forge
talk
(Post)
Hello, we have aproblen to connect our CODESYS OPC Client to the OPC Server. We installed the client according the CODESYS manual. We can browse the server and variables can be linked to the PLC. I created a self signed certificate for the CmpOPCUAClent as described. The server has a cerificate also. I copied the certificates to the trusted zone of server and client. But when it comes to data exchange we get an error message. "Communication error in data source OPC UA Library. Error ID : 7001 German : "Kommunikatinsfehler inder Datenquelle OPC UA -Bibiothek. Es wurde kein genauer Fehler angegeben. Fehler ID : 7001" It semms that there is no cerificate exchange. We are working with CODESYS 3.5 SP19 Patch 5. Can anyone here say something about this error or has an idea for a solution? Thanks.
Last updated: 2024-08-19
Post by jinlee on Reading Camera Feed in Codesys v3.5 webvisu web element browser
CODESYS Forge
talk
(Post)
Hi guys, I have been trying to use web browser element in the visualisation to connect with my IP camera. From the past few weeks, I have not been successful of doing it. I thought it would be very easy to just connect to the ip address, but apparantly it is not. I am using WAGO PLC PFC200 and my PC as a webvisu. or else can you guys please advice me on which kind of camera should I use as a CCTV system in my project instead of IP Camera. Ideally, I want multiple web browser elements to browse my IP Cameras in one frame. Kind regards, Jin.
Last updated: 2024-09-16
Post by jinlee on Reading Camera Feed in Codesys v3.5 webvisu web element browser
CODESYS Forge
talk
(Post)
Hi guys, I have been trying to use web browser element in the visualisation to connect with my IP camera. From the past few weeks, I have not been successful of doing it. I thought it would be very easy to just connect to the ip address, but apparantly it is not. I am using WAGO PLC PFC200 and my PC as a webvisu. or else can you guys please advice me on which kind of camera should I use as a CCTV system in my project instead of IP Camera. Ideally, I want multiple web browser elements to browse my IP Cameras in one frame. Kind regards, Jin.
Last updated: 2024-09-16
Post by jinlee on Reading Camera Feed in Codesys v3.5 webvisu web element browser
CODESYS Forge
talk
(Post)
Hi guys, I have been trying to use web browser element in the visualisation to connect with my IP camera. From the past few weeks, I have not been successful of doing it. I thought it would be very easy to just connect to the ip address, but apparantly it is not. I am using WAGO PLC PFC200 and my PC as a webvisu. or else can you guys please advice me on which kind of camera should I use as a CCTV system in my project instead of IP Camera. Ideally, I want multiple web browser elements to browse my IP Cameras in one frame. Kind regards, Jin.
Last updated: 2024-09-16
Post by opineiro on How to manage variable types larger than 64 bits - Ethernet/IP
CODESYS Forge
talk
(Post)
Hi there, I have a Keyence bar code reader connected to my plc through Ethernet/IP. The Bar code is 20 digits long (like 30100790020493036016), the scanner reads it correctly (I can verify that through the keyence software) but when it sends it through ETH/IP, it doesn't fit into a 64 bit variable and it trunks the data.(I've tried ULINT and LWord without success). When I loaded the EDS file, the read variable was defined as a byte with 128 bits length, which is quite strange for me. (see attached picture) How do I manage this variable? Thanks!
Last updated: 2024-09-23
Post by ricola on Change default node Id name on Raspberry Pi
CODESYS Forge
talk
(Post)
EDIT : https://forge.codesys.com/forge/talk/Engineering/thread/cb5a492aa0/ hyplcmotion - 2022-12-16 Found out how! Needed to connect to PFC200 via Putty, and open CodesysControl.cfg with “sudo nano /etc/CODESYSControl.cfg”. Then adding following command to the end of file, and use the name you want, save/close CODESYSControl.cfg, and reboot your PLC. [CmpOPCUAProviderIecVarAccess] CustomNodeName= PFC200 Hi! , I'm digging up this issue cause we have still this long name within current versions on CodesysControl. Is it a lock for "demo" licences or can it be changed in some way ? This DeviceSet name is too way long with spaces inside, not easy to handle with string parsing... Cheers !
Last updated: 2024-10-10
Post by bjarne-pagaard on OPC UA Server Status on Win RTE
CODESYS Forge
talk
(Post)
Hi there, An "OPC Expert" client software is connecting to a Codesys Control RTE (x64) OPC UA Server. It reads only about 25 variables every 5 minutes. The OPC UA Server seems to shut down on the Codesys runtime. Is there any way to get information about the Codesys OPC UA Server status? Restart it? There is nothing in the PLC Logs after the OPC UA Server has started. It works for a while, then it doesn't. Any ideas? Any way of getting more info out of the Codesys OPC UA Server? -Bjarne
Last updated: 2024-10-21
Post by timvh on Modbus TCP & RTU with Control for Linux SL
CODESYS Forge
talk
(Post)
It seems you have 2 network interfaces. Did you try eth1? Did you already configure the IP address for this interface in Linux? If yes, then maybe undo this. - or only set eth0 in the Nic configuration without anything else (so no IP address, because this is already set in Linux). For more information about the Nic settings, see (probably already read it?): https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_obj_deploy_control_sl_configuration.html PS, if you only want to run CODESYS Control SL, you don't necessarily need the Virtual PLC variant. You could also install and run the CODESYS Control SL Runtime in the Host operating system. This way you should also be able to access the serial port and directly access all ethernet ports. Maybe this is easier?
Last updated: 2024-10-23
Post by wistaro on How to use PLC_Open FBs with PROFINET servodrive (PROFIdrive layer)
CODESYS Forge
talk
(Post)
Hello, I would like to know if there is a PROFIdrive layer in CODESYS. I am already familliar with Codesys's SoftMotion on CANOpen/EtherCAT (to control PLC Open FBs), and I need the same kind of stuff for PROFINET-IO devices; In my configuration, I have a CIFX board from Hischer to enable IRT, the SoftPLC "Codesys Control RTE V3 x64", and a servo-drive from INFRANOR that implements PROFINET / PROFIdrive (with IRT) protocol. This drive works well with the Object Technology of Tia Portal, but some customers use Codesys. Do you have an idea how to do that? Thanks in advance. Regards, William ROMIGUIERES INFRANOR France
Last updated: 2024-10-29
Post by xabier on BUG CODESYS-NO WORK AUTOMATICALLY RESTARSLAVES
CODESYS Forge
talk
(Post)
I detect a Bug of Codesys....NO WORK AUTOMATICALLY RESTARSLAVES. I explain the secuence: I have click in my project the option AUTOMATICALLY RESTARSLAVES In the moment start my Ipc, the network ethercat start correctly I disconnect the wire of my first slave and later connect again the wire..(see the screen Bug Codesys restart slave1) NO work the restart automatic slaves...and is not possible execute of FB MC_REset beacuause appear this error (see the screen Bug Codesys restart slave2) The only way for resolver this problem is execute the FB SMC3ReinitDrive I replay the same with PLC BECKHOFF in Twincat3 and I havent this problem...In the moment connect the wire again in the slave the comunication of ehterCat restart and the slave comunication again with out problem
Last updated: 2024-11-07
Post by cdutz on Problems connecting to Codesys 4.9.0.0 runtime on my Wago PFC200
CODESYS Forge
talk
(Post)
Hi all. I am currently struggling to get my Wago PFC200 running the Codesys Runtime in version 4.9.0.0 working. I am using Codesys V3.5SP19. I updated the PFC200 to the firmware version 04.01.10(23) after having tried the latest version (04.03.03(25) from Wago and not being able to start the runtime. After reading version 23 was needed, I changed to that and at least was able to have it start the codesys runtime. I also installed the "Codesys Control for PFC200 SL 4.9.0.0" plugin for Codesys to install the Codesys runtime in version 4.9.0.0 as well as update the Gateway on the device. While I seem to be able to connect to the gateway on the PLC (the dot is green) and when doing a scan, I do now find my PFC200, which is a huge improvement to before, where with firmware version 25 it just failed to start the runtime and I never found any device when doing a scan. Unfortunately I don't seem to be able to connect to the PLC in codesys. I logged in via SSH and changed the password and I can see that this password is correct as the stuff in the Codesys PFC200 tools tab only works if I use my changed password. And I used those credentials to update the installed Runtime version, which the log claimed to have worked fine. Now whenever I try to connect to the device found in the scan, I get a authentication pop-up with empy device name, device address: 000A. As User I use "root" and as password the password that I changed it to. As a response I just get "Ungültige Benutzerauthentifizierung auf dem Gerät" (Eng. probably something like "Invalid user authentication on the device". What could I be doing wrong? Admittedly I'm a bit lost here :-/ Chris
Last updated: 2023-08-26
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by thysonfury on OPTO22 Groov Epic PR2 Modbus Comms Dropping out every 2 hours and 4 Mins
CODESYS Forge
talk
(Post)
Hi after some assistance with an error on a Groov PR2 PLC. We have a few different communications set up as shown below: One Modbus TCP Slave Connection - ( Sending / Receiving Data from a PC ) Two Modbus TCP Master Connection - ( Reading Data from a UPS Panel and Reading Data Gas Chromatograph) One Modbus RTU Slave Connection 485 - (Reading Data from a fire and gas panel) One Modbus RTU Master Connection 485 - (Sending Data to a Telemetry Unit) All Licenses have been installed as per OPTO22 suggestions of the order below: Modbus TCP Master Modbus TCP Slave Modbus RTU Master Modbus RTU Slave When I check on License manager the RTU Master license seems to disappear on installing the RTU. (What ever reason I’ve been told this is “normal”). If I use Device License Read It will successfully read all the licenses correctly. Now the issue is every 2 hours and between 4. For what ever reason the communications seems to end and lock up for about 20 seconds. During this time even if I was logged into the PLC it would kick me off and I’d have to re type the password to enter. Most of the devices can handle this however the RTU flags up a communications failure at the SCADA and is raising alarms every 2 hours and 4 mins. We’ve had multiple people go through the code to check for anything obvious. Does anyone have any ideas?
Last updated: 2024-04-15
Post by tcarlbom on Read tag values using external program
CODESYS Forge
talk
(Post)
This is my first time posting in this forum and I am new to codesys. I am a fullstack developer and I am trying to figure out how the following. What would be the best approach to create a own/custom tag browser? Either directly in codesys ide or using a separate custom program (perhaps a winforms application). 1.a. Shall I parse the .project xml file to get a list of all tags in the project? 1b. Shall I use python scripting in codesys ide to get a list of tags? Once one have selected some tags. These tags shall be exposed to a python program which will be acting as a edge computer. It’s fine to be able to import a file. 2a. I found a library called codesys plchandler which (as I understand) acts a rest api server. Is this correct? If so, can I query the api from a custom python script, ie can query what tags exist in project and or read tag values? My research so far. From earlier projects I know that using opc ua would be perfect for this but from my opinion it’s bloating the plc since it’s resource intensive. So opc ua is not an option. Codesys automation server is neat. But I don’t want to rely on some cloud services and subscription based pricing. There seem to be several interesting codesys libraries like mqtt, tcp server and NVL sender which would help me expose plc tags. But all have a common problem. One have to manually write what tags which will be used in these function blocks. I want a similar experience like “selecting” tags in the opc ua or the codesys tracing, ie a tag browser.
Last updated: 2024-06-28
Post by ofey on EtherCAT fieldbus
CODESYS Forge
talk
(Post)
Hi, everyone! I'm trying to set up a PLC controller and a connection to an EtherCAT slave device in Codesys. I want to create a flexible program that I can upload to multiple controllers with different remote IO connected (same program). On one plant i may have 5 AI-cards and 3 DO-cards, and on another I may have 4 AI-cards and 2 DO-cards. For not needing to maintain several different programs wih different devices defined in the program (one for each set up) I thought that using a remote IO would make it easier having a single program. That way I could refer to different memory addresses instead of predefined slots/channels and IO's, that would give me errors if there was a different IO on the plant than what the program expected. When I tried setting up the etherCAT master, I saw that I had to define the etherCAT slave devices with the different IO'cards for me to be able to refer to the memory addresses in a PRG. Exactly what I was trying to avoid. My setup is something like a program that can handle 16 separate pump controls. In a year maybe 6 plans get deployed, and depending on how large the project is, the number of pumps can vary between 4 and 16. And the managers dont want to have IO's for all 16 pumps on every cabinet, and I dont want to maintain 16 separate projects files in case of updates etc. I thought the best way to tackle this was having a single project that read/write data to the different pump IO's by remote IO (fieldbus ethercat) addresses. And the number of pump controls are activated by an external GUI. If pump 1-6 is activated by the GUI, then the PLC-program tries to read/write input/outputs from predefined addresses for the expected IO's. My test setup is a PFC200 WAGO controller and a EtherCAT fieldbus coupler (750-354) with some IO. I hope I didn't explain this too horrible, and if there is a more easy and elegant solution for this challenge I appreciate a feedback on this.
Last updated: 2024-04-08
Post by mgabryel on Problems with CAN 2.0 comunication on Wago PLC (Codesys 3.5)
CODESYS Forge
talk
(Post)
Hello, I am trying to program CAN Bus comunication on WAGO PLC (more precisely on WAGO Touch Monitor model TP600). I am using for this purpose library "WagoAppCanLayer2" from Wago company. My IDE for programming this device is CODESYS V3.5 SP19 Patch 2 + (64-bit). My program is written in Structured text using function blocks from previously mentioned library. Here is code of this program: 1) Variables declarations: PROGRAM PLC_PRG VAR oOpenInterface : WagoAppCanLayer2.FbCanL2Open :=( udiBaudrate := 125000 ); xInterfaceIsOpen : BOOL; sInterfaceInfo : STRING; oReceive : WagoAppCanLayer2.FbCanRx29BitFrame :=( xBufferMode := FALSE, wCanId := 16#181 ); xRecv : BOOL; sReceiveInfo : STRING; oSend : WagoAppCanLayer2.FbCanTx29BitFrame :=( dwCanId := 16#100, //was 16#201 xRtrFrame := FALSE ); xSend : BOOL; sSendInfo : STRING; oCanDiag : WagoAppCanLayer2.FbCanErrorInfo; xRst : BOOL; aSendData : ARRAY [1..8] OF BYTE; bSendLen : BYTE; TON_0 : TON; TON_1 : TON; END_VAR 2) Program body: oOpenInterface( xEnable := NOT xInterfaceIsOpen, I_Port := IoConfig_Globals.WAGO_CAN_LAYER2_DEVICE ); sInterfaceInfo := oOpenInterface.oStatus.GetDescription(); xInterfaceIsOpen S= oOpenInterface.xValid AND NOT oOpenInterface.xError; oReceive( xEnable := xInterfaceIsOpen, I_Port := IoConfig_Globals.WAGO_CAN_LAYER2_DEVICE, xRxTrigger := xRecv ); sReceiveInfo := oReceive.oStatus.GetDescription(); IF NOT xRecv THEN IF oReceive.bRxNBytes > 0 THEN oReceive.aRxBuffer[1]; oReceive.aRxBuffer[2]; oReceive.aRxBuffer[3]; oReceive.aRxBuffer[4]; oReceive.aRxBuffer[5]; oReceive.aRxBuffer[6]; oReceive.aRxBuffer[7]; oReceive.aRxBuffer[8]; END_IF xRecv := TRUE; END_IF aSendData[1] := 224; aSendData[2] := 13; aSendData[3] := 14; aSendData[4] := 15; aSendData[5] := 222; aSendData[6] := 13; aSendData[7] := 14; aSendData[8] := 15; bSendLen := 8; TON_0(IN:= NOT TON_1.Q, PT:= T#2S , Q=>xSend, ET=> ); TON_1(IN:= TON_0.Q, PT:= T#2S , Q=>, ET=> ); oSend( xEnable := xInterfaceIsOpen, I_Port := IoConfig_Globals.WAGO_CAN_LAYER2_DEVICE, aTxBuffer := aSendData, bTxNBytes := bSendLen, xTxTrigger := xSend ); sSendInfo := oSend.oStatus.GetDescription(); oCanDiag( xEnable := TRUE, I_Port := IoConfig_Globals.WAGO_CAN_LAYER2_DEVICE, xTriggerResetCounter := xRst, xValid=> , xError=> , oStatus=> , wBusState=> , wBusDiag=> , uiRxOverflowsL2=> , uiTxOverflowsL2=> , uiRxOverflows=> , uiMsgTimeouts=> , uiBusOffs=> , uiBusWarnings=> ); Program first opens comunication on CAN 2 device and then periodically try send one CAN data frame. After starting program CAN 2 interface is properly open. The xSend variable is toggling with period 2s. When program sends data an "Tx overflow" error appears. When I am watching CAN_H line on DSub 9 socket i am not able to see proper CAN frames - see screenshot attached to this message. Could somebody help me determine what is wrong with this program. Best regards
Last updated: 2024-08-02
Post by george32 on Readable IO names
CODESYS Forge
talk
(Post)
Hello Folks, I have a quite basic understanding of how PLC programming works. However I keep getting stuck on 1 problem I could not get my head around. The problem is as follow: I have a PLC with 60 IO (20 inputs, 40 outputs). Each IO is defined as a function block. Furthermore I have an external IO card connected trough a CanBus connection. This IO card has 4 analog input channels (USINT), 4 digital inputs (Bool) and 4, digital outputs (Bool) Because I have 2 different components which both has data have I made 4 arrays to store the data off every component in one variable. PLC_Input: Array [1..20] of BOOL; PLC_Output: Array [1..40] of BOOL IOCard_Input: Array [1..8] of BOOL IOCard_Output: Array [1..4] of BOOL Because the control and reading of the different in and outputs is done by a TCP connection I want to use some kind of enumeration or struct to give each index a name so that my main would be a little bit more readable instead of all the magic numbers. Also this would make my program more dynamic for the furter in case I need to changes some in the IO nummers. For example: pump is placed on the fysical terminal strip number place 54, which is the 3th output of the IO card in the program: if I am sending a message with value 54 I would like to control IOCard_Output[3]. If there is a solution or methode to get this done, I can eventually do the following in my main program: IOCard_Output[Pump]. I have tried the following: IOCard_Output[Pump - 51] with an enumration but this keeps raising an error I hope some of you could help me further with this problem. In gross lines: I want to couple all the different IO to a more readable name and this readable name should control the right Array index Thanks in advance, George
Last updated: 2024-09-26
Post by rossanoparis on After un upgrade of "CODESYS Control for Raspberry Pi MC SL" from v4.7 to v4.9 SysFileOpen function stopped working
CODESYS Forge
talk
(Post)
Hello at all. After un upgrade of "CODESYS Control for Raspberry Pi MC SL" from v4.7 to v4.9 SysFileOpen function stopped working. I'm not able to read or write files from the PLC application. Before this upgrade all worked fine. I've read this thread [ https://forge.codesys.com/forge/talk/Engineering/thread/3da9ded84e/ ] Despite I followed that indications I couldn't get my code working again. Perhaps I'm missing something or I didn't understand how to use placeholders at all. Is there a different syntax to use for "SysFileOpen" in order to use placeholders? Thanks in advance for your help. Information Compiler: CODESYS V3.5 SP19 Patch 2 Runtime: codesyscontrol 4.9.0 HW: KUNBUS RevPi Connect S Below the paths I want to access (The entire CODESYSControl_User.cfg file is attached) [SysFile] PlaceholderFilePath.1=/home/pi/hpca/bin, $hpcabin$ PlaceholderFilePath.2=/home/pi/hpca/cfg, $hpcacfg$ PlaceholderFilePath.3=/home/pi/hpca/logs, $hpcalogs$ PlaceholderFilePath.4=/home/pi/hpca/resources, $hpcares$
Last updated: 2023-08-22