Post by arundara on Variable Sync Issue In Soft Plc Redundancy
CODESYS Forge
talk
(Post)
Hello, I was trying to create a redundancy POC for our application where we read data from few modbus tcp devices. As there is a limitaion that modbus tcp device support only for single master device, we wanted to test how the variable sync happens in redundancy mode. For that i have used the redundancy sample code added a variable "b" under a condition. What i observed was while active controller is running, if passive controller is powerup, passive controller is able to sync all the data configured for redundacny. But after that the variable data which resided under a condition is not synching from active to passive controller. I have attached the image where i have highlighter the variable. Can some help me to understand how redundacny work in codesys soft plc and if there is a solution to sync variable which are under condition, please explain the same or suggestion to achieve the same. Hardware - Raspberry Pi (2 qty) Redundancy licence used - yes in both controllers. Codesys runtime - 4.9.0.0 Codesys software version - V3.5 SP19 if i have posted this question in wrong section, please do let me know in whcih section i have to post this question.
Last updated: 2023-12-01
Post by acc00 on Main Task cycle too long leading to PLC Fail
CODESYS Forge
talk
(Post)
I have 2 Wago PFC200 PLC, running with Runtime SP19 Patch 5, with the Redundant application. The PLC communicates as Modbus Master with at this moment 15 Modbus Slaves -later there will be 28 in total- (Drives, Power management units,...). These devices are connected in 2 rings (1 ring of Drives, 1 ring of Power Management units), with 2 Managed Moxa Switches being part of the ring. Each PLC is connected to one of these switches. The issue I'm encountering is that the Cycle time of the Active PLC goes very high when I'm closing the Drive ring (simulating an issue on one Cabinet supply, resulting in that one Drive shut down, which can happen on field quite often). As a result of this long cycle, the PLC fails and goes to Exception, and the Passive PLC does not take control of the system. A normal cycle is around 30ms for the Main task, and a few ms for the Ethercat task. When I monitor with Profiler, I see that in this Maximum Cycle, the main Task is only taking 13ms, so I'm not sure where the PLC is hanging for so long. Is the remaining cycle time the Redundant management/sync or something else? Thank you in advance.
Last updated: 2024-03-08
Post by paro on Modbus Client Request Not Processed
CODESYS Forge
talk
(Post)
Hi, Problem in your code is that you are not calling the ClientFb cyclic. Please look at the Example from CODESYS: https://forge.codesys.com/prj/codesys-example/modbus/home/Home/ Your code works if the client fb is called cyclic! IF NOT initDone THEN initDone := TRUE; // configure clientTcp clientTcp(aIPaddr:=Ethernet.IPAddress, uiPort:=502); // configure clientSerial clientSerial(iPort:=SysCom.SYS_COMPORT2, dwBaudRate:=SysCom.SYS_BR_115200, byDataBits:=8, eParity:=SysCom.SYS_EVENPARITY, eStopBits:=SysCom.SYS_ONESTOPBIT, eRtuAscii:=ModbusFB.RtuAscii.RTU); // configure clientRequestReadCoils_1 clientRequestReadCoils_1(rClient:=clientTcp, uiUnitId:=42, udiTimeout:=TO_UDINT(T#10MS)); // configure clientRequestWriteSingleRegister clientRequestWriteSingleRegister(rClient:=clientTcp, uiUnitId:=43, udiTimeout:=TO_UDINT(T#10MS)); // configure clientRequestReadCoils_2 clientRequestReadCoils_2(rClient:=clientTcp, uiUnitId:=44, udiTimeout:=TO_UDINT(T#10MS)); // configure clientRequestReadInputRegisters clientRequestReadInputRegisters(rClient:=clientTcp, uiUnitId:=44, udiTimeout:=TO_UDINT(T#10MS)); END_IF // call the client FB's clientTcp(); clientSerial(); // call client request FB's clientRequestReadCoils_1(rClient:=clientTcp, xExecute:=TRUE, uiStartItem:=2, uiQuantity:=3, pData:=ADR(aDataCoils_1[0])); // for more details see Example_TCP, especially ClientRequest control (xExecute, xDone, xError). IF clientRequestReadCoils_1.xDone THEN // get data from aDataCoils_1 ... END_IF clientRequestWriteSingleRegister(rClient:=clientTcp, xExecute:=TRUE, uiItem:=3, uiValue:=123); clientRequestReadCoils_2(rClient:=clientTcp, xExecute:=TRUE, uiStartItem:=2, uiQuantity:=3, pData:=ADR(aDataCoils_2[0])); clientRequestReadInputRegisters(rClient:=clientTcp, xExecute:=TRUE, uiStartItem:=16, uiQuantity:=3, pData:=ADR(aDataInputRegisters[0]));
Last updated: 2024-05-29
Post by ryusoup on JSONByteArrayWriter problem?
CODESYS Forge
talk
(Post)
Hello, I am trying to implement a FB to make JSON formatted WSTRING type message using JSON Utilities 1.9.0.0 included in the IIoT library. In my case, I want to set some objects or arrays and set values to them later. But when I wrote as the sample below, // init builder builder(pJsonData:=pJsonData, diRootObj=>diRootObj); // set the 1st key to root diKey1 := builder.SetKeyWithArray(wsKey:="key1", diParentIndex:=diRootObj, eError=>eError); // set a value to the 1st key wsValue:="value01"; builder.SetValue(Value:=wsValue, diParentIndex:=diKey1, eError=>eError); // set the 2nd key to root diKey2 := builder.SetKeyWithArray(wsKey:="key2", diParentIndex:=diRootObj, eError=>eError); // set a value to the 2nd key wsValue:="value02"; builder.SetValue(Value:=wsValue, diParentIndex:=diKey2, eError=>eError); // set a value to the 1st key again wsValue:="value03"; builder.SetValue(Value:=wsValue, diParentIndex:=diKey1, eError=>eError); // set a value to the 2nd key again wsValue:="value04"; builder.SetValue(Value:=wsValue, diParentIndex:=diKey2, eError=>eError); // write build result writer(xExecute:=TRUE, pwData:=ADR(wsResult), udiSize:=SIZEOF(wsResult), xAsyncMode:=FALSE, jsonData:=pJsonData^); the result was: { "key1": ["value01"], "key2": ["value02", "value03", "value04"] } while my expection was: { "key1": ["value01", "value03"], "key2": ["value02", "value04"] } Inspecting pJsonData^, JSONData itself seems to be ok, so I believe the issue is something caused by the writer FB. Does anyone know how to fix it? Thanks,
Last updated: 2023-10-04
Post by biiebs on Aufbau von Ablaufsteuerungen ermitteln
CODESYS Forge
talk
(Post)
Hallo Zusammen, gibt es in CODESYS bei Ablaufsteuerungen weitere Möglichkeiten außer den AS-Einstellungen z.B. die Aufbaustruktur der Ablaufsteuerung herauszufinden? Gesamtanzahl der verwendeten Aktionen / Schritte - Im besten Fall auch die einzelnen Verzweigungen? Ich würde den gesamten Aufbau der Schrittkette gerne als "View" in einer übergeordneten Software abbilden lassen, da sich die Ablaufsteuerungen, je nach Projekt im Aufbau unterscheiden bräuchte ich die Kenntniss über den Aufbau dieser Schrittketten. Oder müsste ich mir hier einen "Workaround" programmieren, der z.B. bei Init erstmal den Aufbau der Ablaufsteuerung durchläuft und mir die nötigen Informationen liefert? Natürlich wäre auch ein Weg den Aufbau des AS-Bausteins über die PLCopen XML zu exportieren, jedoch müsste dies bei Änderungen jeweils nachgezogen werden - was etwas unschön wäre, falls dies vergessen würde. Mittlerweile habe ich auch das Tool "SFC Visu Generator" gefunden, dessen Funktion im Prinzip genau das darstellt, was ich benötige - jedoch leider nur als CODESYS interne Visualisierung. Ich würde den Export des Bausteins gerne in meine übergeordnete Software implementieren. Gibt es hier die Möglichkeit das Vorgehen zu Erfahren oder den vom Baustein generierten Export bei mir zu implementieren? Hat hier jemand sowas ähnliches schonmal gelöst? Vielen Dank im Voraus Mit freundlichen Grüßen Biiebs
Last updated: 2024-07-25
Post by muhq on Profinet connection to Siemens CP343-1 Lean (IO-Device/Slave)
CODESYS Forge
talk
(Post)
Hi, I am quite new to Codesys and I try to do a Profinet connection to an Siemens PLC (315-2DP) with CP343-1 Lean Modul. I already configured the Siemens PLC, exported the GSDML. Then I added a new project in Codesys, added following moduls: - Ethernet - PN_Controller - Imported Profinet Device via GSDML importer When I start the programm everything looks fine but I always get the message "Stopped Profinet" and no data is available This is only for a small test. Therefore I start to do that on a Windows 10 with Development System. Later I will try to realize this on Raspberry. Ethernet Adapter is configured (192.168.1.1 / 24) Firewall deactivated WinPCap is installed S7-Station seems to be found ('fuadazenzitest') Can please somebody help me?
Last updated: 2023-08-26
Post by seppi on Establishing communication between a Raspberry Pi 4 and an Arduino UNO R3 using I²C.
CODESYS Forge
talk
(Post)
Hello everyone, I want to establish communication between my Arduino and my Raspberry Pi via I²C, but I have no idea how to make it work. However, it should work because there are many examples available, although none of them were programmed using Codesys, but rather using Python. My Raspberry Pi will be the master and is supposed to exchange measurement data such as speed and battery capacity with the slave (Arduino). I would be very grateful if someone could help me with my problem. Here is another link that could be helpful. However, I can't find the mentioned libraries
Last updated: 2023-12-03
Post by seppi on Raspberry 4 I²C with Arduino UNO R3
CODESYS Forge
talk
(Post)
Hallo zusammen Ich möchte meinen Arduino und meinen PI miteinander kommunizieren lassen via I²C doch ich habe keine Ahnung wie das funktionieren soll. Aber es müsste funktionieren da es viele Beispiele dazu gibt jedoch wurde keines der Beispiele mit Codesys programmiert sondern über Python. Mein PI wird der Master sein und soll mit dem Slave (Arduino) Messdaten wie Geschwindigkeit und Akkukapazität und so weiter austauschen. Wenn mir bei meinen Problem jemand weiterhelfen könnte währe ich sehr Dankbar. Hier noch ein Link der Hilfreich sein könnte. Ich finde aber die angegeben Bibliotheken nicht. https://forge.codesys.com/forum/en/773/genmed-documentation.pdf
Last updated: 2023-12-03
Post by esave on Stepper Drive with Ethercat
CODESYS Forge
talk
(Post)
Hello everybody I am new into Codesys. I have a stepper driver (EM3E-556E) from Leadshine. I want to controll the stepper driver via EtherCat to a ST programm but I dont have any function block or anything that i can use. I only have the XML-File wich I loaded. With it I implemented the drive as a Ethercat slave and now I see these variables. (See picture) I dont know how to controll the stepper drive. And the manufacturer doesnt provide support for me. Can anybody help me or atleast tell me how they would do it?
Last updated: 2024-03-14
Post by fugtwad on Automation Builder V2.5 EtherCAT CM579 Master Scan for devices - >No gateway selected
CODESYS Forge
talk
(Post)
ABB Automation Builder v2.5.0.22 Premium CodeSys 2.3.9.62 Running on Win 10 VM x64 Goal: I have an EtherCAT topology issue which normally a "Scan for devices.." on the EtherCAT master would shed some light on. Issue: Upon trying such I get a "No gateway selected" error. Question: How might I point the the "scanner" at a gateway? What is working: Gateway is running in system tray. I can go online to PLC. A scan from the "Diagnostics live" tab of the EtherCAT master gives slave status. What I have tried: Restarting gateway in system tray. Exiting system tray gateway and reloading it. Turning off firewall. Contacting ABB support multiple times. Any help appreciated.
Last updated: 2024-05-20
Post by kuegerls on SysProcessExecuteCommand2 and CANopen Device
CODESYS Forge
talk
(Post)
Hello, CODESYS Control is running on my RevPi, and my system communicates over a CANbus with a master using the ConnectCan module (Slave - CANopen Device). The communication works perfectly fine so far. However, as soon as I call a Python script with "SysProcessExecuteCommand2" that creates a CSV file and executes without errors, the master does not adopt any changes to the Transmission Process Data Objects (TPDOs). I don't quite understand what one has to do with the other, and perhaps someone can help me with this. Here is my script call: SysProcess.SysProcessExecuteCommand2(pszCommand:='python /home/pi/test.py', pszStdOut:=sCMDOutput, udiStdOutLen:= SIZEOF(sCMDOutput), pResult := ADR(eResult)); Thank you in advance! Best regards, Stefan
Last updated: 2024-06-20
Post by alez on CANopen safety , SRDO error behavior
CODESYS Forge
talk
(Post)
I have a project in which there is a Safety device in CANopen, and the PLC interfaces with it as Master. I would like to understand if it is possible to set the behavior in case one of the SRDOs that I receive from the slave is no longer received. From what I have seen, if the SRDOs are not received, the CANopen safety status becomes "Not in progress" and the mapped variables freeze at the last value detected. I want to understand if it was possible to set the variables connected to the SRDOs to take a default value (e.g. zero) in the event of a CANOpen error during reception.
Last updated: 2024-07-15
Post by siscu on Raspberry i2c master device
CODESYS Forge
talk
(Post)
I want to implement an extended I2C master for Raspberry Pi Control. I was hoping for it to be as easy as creating a library with a FB that extends i2cMaster and associating it with a device following the forge drivers documentation, but I haven't managed to make it work as the driver behaves only as an i2c slave. I'm thinking this is because the forge forum only talks about extending i2c, and the master portion is omitted since most users won't want to add a custom one. I'd like to know if I'm doing something wrong. Is it really possible to make an I2C master extension device? If so, are there public examples we can check out? Any info on this topic will be appreciated.
Last updated: 2024-10-16
Post by niallel on CamBuilder and first boundary position not zero
CODESYS Forge
talk
(Post)
Hi, I've read the CamBuilder documentation and it shows to use the left boundary of the first segment as SMCB.BoundImplicit(), so that the transition is as smooth as possible. With this it sets X and Y to 0. My first slave position is not 0 (say for example it's 100), so I would set it with SMCB.Bound(0,100). My question is that when the cam goes back to the start (Periodic := TRUE) , will it blend with the last position (360, 100) if I do this? I imagine it will, but the documentation isn't clear as the information in the Periodic Cams only says to set Smooth Transition in the cam properties - but when I'm defining it with code there isn't an option for Smooth Transition to be set. Hope this makes sense? Many thanks,
Last updated: 2024-10-23
Post by struccc on Problem Update new version Master ethercat
CODESYS Forge
talk
(Post)
Hi, I had some issues as well migrating to the new version. What I have learnt: - Have to check all the libraries in the library manager, if they are the proper versions. - Some other parts of the application, maybe an old library referenced by another one can keep the old Ethercat libraries.... Use the "Placeholders" function on the library manager - See if there is a new version available of the slave "devices". Might just have to update them ... I had problems moving from 4.7 to with 4.8, especially with the 2nd adapter for redundancy - some devices failed to initialize properly.... So I have just downgraded those libraries now. P.
Last updated: 2024-10-28
Post by solidlogicguy on Little endian to Float from Modbus RTU
CODESYS Forge
talk
(Post)
Hello, I got a device from which I require to read values from I am using a WAGO PLC 750-8212 and I am communicating through Modbus Master FUNCTION BLOCK from library WagoAppPLCModbus in Codesys 3.5 to this device. I already receive data from the device that is a CVM to monitor voltage from a fuel cell. The technical support of the company that makes these devices says that the data is sent in little endian form. And I want to convert it to a float value. The tech support sent me the next instructions of how to do it but I am new using codesys, so any advice or help I will really appreciate so much. Message from tech support: The process is complicated, better to do it with already implemented library in the language/program you use. Basically the process should be next: To convert the two Modbus registers containing parts of a 32-bit float in little-endian byte order to a floating-point number using mathematical operations, you first need to combine the two 16-bit integers (assuming reg1 is the lower word and reg2 is the higher word) and then interpret the result according to the IEEE 754 standard. Given: - Register 192 (reg1) = 4096 - Register 193 (reg2) = 14884 Step 1: Combine the two registers. Since we are dealing with little-endian byte order, reg2 is the high word, and reg1 is the low word: combined = reg2 * 2^16 + reg1 combined = 14884 * 65536 + 4096 combined = 975175680 + 4096 combined = 975179776 Step 2: Convert the combined value to binary: combined_binary = '1110101101011100000000000000000' Step 3: Split the binary into IEEE 754 components: Sign bit (1 bit): 0 Exponent (8 bits): 11101011 Mantissa (23 bits): 01011100000000000000000 Step 4: Convert the binary exponent to decimal and subtract the bias (127 for 32-bit floats): exponent = int('11101011', 2) - 127 exponent = 235 - 127 exponent = 108 Step 5: Calculate the mantissa as a fraction: The mantissa in IEEE 754 format is the fractional part after the leading 1 (which is implicit). Therefore, we need to convert the binary mantissa to decimal and add the implicit leading 1: mantissa_fractional = 1 + int('01011100000000000000000', 2) / 2^23 mantissa_fractional = 1 + 18688 / 8388608 mantissa_fractional = 1 + 0.002227783203125 mantissa_fractional ≈ 1.002227783203125 Step 6: Combine the sign, exponent, and mantissa to get the float value: float_value = (-1)^0 * mantissa_fractional * 2^exponent float_value = 1 * 1.002227783203125 * 2^108 Because the exponent is quite large, the resulting float value is a very large number.
Last updated: 2023-12-15
Post by alexgooi on Modbus writing on value change
CODESYS Forge
talk
(Post)
The way I usally tackle this is by syncing only words (then you are able to use the FB above). If you then want to write a Boolean simply type it like this. Value[1].0 := Bool1; Value[1].1 := Bool2; Value[1].2 := Bool3; Uints have the same number of bits than a INT/WORD so these ones will work as well (they are only represented diffrently). A Real will work but you will loose some infomration in the conversion. If you want to keep the information you can convert 2 words to a float with a function (for example with the IEEE-754 standard) . In this way the syncing to the server is very simple and in the Codesys Program you decide what part of the word you want to use.
Last updated: 2024-04-03
Post by paro on Modbus Client Request Not Processed
CODESYS Forge
talk
(Post)
Hi, works in my case if I increase the timeout! to_udint(t#100ms) -> 100 -> 100us.. FUNCTION_BLOCK MODBUS_master_example_ST VAR initDone : BOOL := FALSE; aIPAddress : ARRAY [0..3] OF BYTE := [127,0,0,1]; clientTcp: ModbusFB.ClientTcp; // buffer to read input registers aDataInputRegisters : ARRAY[0..9] OF UINT; // some client requests clientRequestReadInputRegisters: ModbusFB.ClientRequestReadInputRegisters; xExecute: BOOL; uistart: UINT := 100; udiTimeout1: UDINT; END_VAR IF NOT initDone THEN initDone := TRUE; // configure clientTcp clientTcp(aIPaddr:=aIPAddress, uiPort:=502, udiLogOptions := ModbusFB.LoggingOptions.All); // configure clientRequestReadInputRegisters clientRequestReadInputRegisters(rClient:=clientTcp, uiUnitId:=1, udiTimeout:=1000000); // 1sec END_IF // call the client FB's clientTcp(); clientRequestReadInputRegisters(rClient:=clientTcp,xExecute := xExecute AND NOT clientRequestReadInputRegisters.xBusy ,uiStartItem:=uistart, uiQuantity:=3, pData:=ADR(aDataInputRegisters[0]));
Last updated: 2024-05-30
Post by zer0g on Modbus Client Request Not Processed
CODESYS Forge
talk
(Post)
I'm using the code bellow which is based on the Codesys example: FUNCTION_BLOCK MODBUS_master_example_ST VAR initDone : BOOL := FALSE; aIPAddress : ARRAY [0..3] OF BYTE := [127,0,0,1]; clientTcp: ModbusFB.ClientTcp; // buffer to read input registers aDataInputRegisters : ARRAY[0..9] OF UINT; // some client requests clientRequestReadInputRegisters: ModbusFB.ClientRequestReadInputRegisters; xExecute: BOOL; END_VAR IF NOT initDone THEN initDone := TRUE; // configure clientTcp clientTcp(aIPaddr:=aIPAddress, uiPort:=502, udiLogOptions := ModbusFB.LoggingOptions.All); // configure clientRequestReadInputRegisters clientRequestReadInputRegisters(rClient:=clientTcp, uiUnitId:=1, udiTimeout:=TO_UDINT(T#1000MS)); END_IF // call the client FB's clientTcp(); clientRequestReadInputRegisters(rClient:=clientTcp,xExecute := xExecute AND NOT clientRequestReadInputRegisters.xBusy ,uiStartItem:=2, uiQuantity:=3, pData:=ADR(aDataInputRegisters[0])); As you can see the clientTCP is called cyclically with the same result.
Last updated: 2024-05-30
Post by yannickasselin on codesys VLAN tagging
CODESYS Forge
talk
(Post)
I ordered a cheap managed switch and tested it as soon as I received the switch. It works great! I even went a bit further. As you can see in the screenshot, I created 2 Codesys containers. Each one having 2 fieldbuses. The first one has EtherCAT and EtherNet/IP and the second one has EtherCAT and Modbus/TCP. All going through the same ethernet port from the PC to the switch. The switch splits it up into 4 different networks. The hardest part was to figure out how to configure the switch. @eschwellinger, thank you very much.
Last updated: 2024-09-17
Post by timvh on Modbus TCP & RTU with Control for Linux SL
CODESYS Forge
talk
(Post)
It seems you have 2 network interfaces. Did you try eth1? Did you already configure the IP address for this interface in Linux? If yes, then maybe undo this. - or only set eth0 in the Nic configuration without anything else (so no IP address, because this is already set in Linux). For more information about the Nic settings, see (probably already read it?): https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_obj_deploy_control_sl_configuration.html PS, if you only want to run CODESYS Control SL, you don't necessarily need the Virtual PLC variant. You could also install and run the CODESYS Control SL Runtime in the Host operating system. This way you should also be able to access the serial port and directly access all ethernet ports. Maybe this is easier?
Last updated: 2024-10-23
Post by ben1 on How to write multiple coils (Modbus FC15)
CODESYS Forge
talk
(Post)
If I am understanding what you are saying, then yes that would be your problem. I would create an array of bools on the client side for the transfer and try that. Or if client can't be changed then use words on server and unpack. But I am not sure if you or I are mis interpreting but it sounds a bit jumbled. I don't know what you have control of, but, if you are turning on BITS in the server, you should write to BITS in the client with a Function 15. If you are writing to WORDS in the server, you should write to WORDS in the client with a Function 16.
Last updated: 1 day ago
Post by youness on No source code available (cip object)
CODESYS Forge
talk
(Post)
Hi yotaro, hope your problem was resolved. I had the same, but with an other library title. This exception is not detected during compilation, but rather at a given position in the program (when switching to a given visualization). Although the exception is generated at this point, it does not involve the visualization in question. This error is due to one of 3 reasons: 1) A division by zero somewhere: The program is able to detect divisions by zero at compile time. But in the case of a variable, which takes a valid value at init and changes to 0 at a later stage. 2) An invalid pointer: (either because it has a value of 0, or because it points outside the memory reserved for the program) is being dereferenced. Locate any pointers or interfaces you have in the code and check them - you should also be wary of mixing inline modifications and pointers. 3) Array overflow: Generally when a processing operation is executed outside the array's definition range. Example: a write loop with n iterations is executed on an array of dimmension n-1. On the other hand, the error message may not appear. In the latter case, the error may have fatal consequences, as the overflow has induced writing to potentially forbidden memory areas. This problem can be explained by the fact that it's not always the adjacent memory areas of PLC_PRG that are overwritten, but the memory areas that are randomly allocated to the array during compilation. In this case, however, there is no entry in the log, so you need to integrate the "Implicit Check function", which checks the line of code generating the error. To integrate this functions, click on Application --> POU for implicit controls Regards,
Last updated: 2024-07-16
Post by ofey on EtherCAT fieldbus
CODESYS Forge
talk
(Post)
Hi, everyone! I'm trying to set up a PLC controller and a connection to an EtherCAT slave device in Codesys. I want to create a flexible program that I can upload to multiple controllers with different remote IO connected (same program). On one plant i may have 5 AI-cards and 3 DO-cards, and on another I may have 4 AI-cards and 2 DO-cards. For not needing to maintain several different programs wih different devices defined in the program (one for each set up) I thought that using a remote IO would make it easier having a single program. That way I could refer to different memory addresses instead of predefined slots/channels and IO's, that would give me errors if there was a different IO on the plant than what the program expected. When I tried setting up the etherCAT master, I saw that I had to define the etherCAT slave devices with the different IO'cards for me to be able to refer to the memory addresses in a PRG. Exactly what I was trying to avoid. My setup is something like a program that can handle 16 separate pump controls. In a year maybe 6 plans get deployed, and depending on how large the project is, the number of pumps can vary between 4 and 16. And the managers dont want to have IO's for all 16 pumps on every cabinet, and I dont want to maintain 16 separate projects files in case of updates etc. I thought the best way to tackle this was having a single project that read/write data to the different pump IO's by remote IO (fieldbus ethercat) addresses. And the number of pump controls are activated by an external GUI. If pump 1-6 is activated by the GUI, then the PLC-program tries to read/write input/outputs from predefined addresses for the expected IO's. My test setup is a PFC200 WAGO controller and a EtherCAT fieldbus coupler (750-354) with some IO. I hope I didn't explain this too horrible, and if there is a more easy and elegant solution for this challenge I appreciate a feedback on this.
Last updated: 2024-04-08
Post by mondinmr on Direct Pointers in IOMapping for EtherCAT with IoDrvEthercatLib.ETCSlave_Dia
CODESYS Forge
talk
(Post)
Using SDO, I can read the EtherCAT mappings and offsets from various registers like 0x1c12, 0x1c13, etc. When I obtain registers mapped in the PDOs and various offsets, I could technically access directly to the statusword, controlword, etc., if they are mapped. I have noticed that on IoDrvEthercatLib.ETCSlave_Diag I can find pointers to the input and output buffers. However, although the input buffer can be easily read by referring to what has been obtained from the SDOs, it is not possible to write to the output buffer, as it is overwritten in each cycle by the data from the IOMapping task. Is there a way, knowing an instance of IoDrvEthercatLib.ETCSlave_Diag, to obtain the pointer to the first data in the IOMapping? The offsets are identical to those of the PDOs, but obviously the data is a copy. For me, the cleanest thing would be to access the pointers on IOMapping, for DS402a devices to retrieve the key data and point them to internal references. I need to know this as, having developed our own motion library, I would like to simplify the initial setup by eliminating unnecessary and nonsensical mappings that can lead users to unnecessary errors. In the current version that we have been using for years, we have to map everything manually. I would like to pass only the slave reference to the FB_init constructors and eliminate the mapping.