Post by andrax on Mux I2C
CODESYS Forge
talk
(Post)
the TCA9548a does not work in Codesys. In Pyton this is only queried once and in Codesys cyclically. Of course you can also insert a terminating resistor in each port, then you should have no problems. I use this one: https://botland.de/8-bit-multiplexer/12723-qwiic-mux-breakout-8-kanal-modul-mit-i2c-multiplexer-tca9548a-sparkfun-bob-16784-5904422341428.html You can simply set the library to the latest version. You do not need Oscat. Do you need an example project for the BMP280?
Last updated: 2024-01-02
Post by andrax on Mux I2C
CODESYS Forge
talk
(Post)
the TCA9548a does not work in Codesys. In Pyton this is only queried once and in Codesys cyclically. Of course you can also insert a terminating resistor in each port, then you should have no problems. I use this one: https://botland.de/8-bit-multiplexer/12723-qwiic-mux-breakout-8-kanal-modul-mit-i2c-multiplexer-tca9548a-sparkfun-bob-16784-5904422341428.html You can simply set the library to the latest version. You do not need Oscat. Do you need an example project for the BMP280?
Last updated: 2024-01-02
Post by eschwellinger on Edge Gateway online, but PLC is not online
CODESYS Forge
talk
(Post)
we need some logfiles from the edge gateway /etc/Gateway.cfg [CmpLog] CmpEdgeGateway.Filter=0xFFFFFFFF Logger.0.Name=/tmp/codesysedge.log Logger.0.Filter=0x0000000F Logger.0.Enable=1 Logger.0.MaxEntries=100000 Logger.0.MaxFileSize=5000000 Logger.0.MaxFiles=1 Logger.0.Backend.0.ClassId=0x00000104 ;writes logger messages in a file Logger.0.Type=0x314 ;Set the timestamp to RTC and does the scan via Automation Server show the plc?
Last updated: 2024-01-09
Post by felipemsgarcia on Edge Gateway online, but PLC is not online
CODESYS Forge
talk
(Post)
Hi Edwin, The PLC is already in the automation server so nothing happens when I scan the network, however the PLC show offline (not connected). Please see logs below. [CmpLog] Logger.0.Name=codesysedge.log Logger.0.Filter=0x0000000F Logger.0.Enable=1 Logger.0.MaxEntries=100000 Logger.0.MaxFileSize=1000000 Logger.0.MaxFiles=1 Logger.0.Backend.0.ClassId=0x00000104 ;writes logger messages in a file Logger.0.Type=0x314 ;Set the timestamp to RTC Thank you!
Last updated: 2024-01-09
Post by warrumungi on Beckhoff EL6652-0010 with Codesys
CODESYS Forge
talk
(Post)
Hi Has anyone successfully used a Beckhoff EL6652-0010 Ethernet/IP slave terminal through an EK1101 EtherCAT coupler, or similar, and been able to set it up through Codesys? It seems there is no driver for it, and it can't be done? The only option would be to use the Ethernet/IP capability of the controller directly with one of its ethernet ports and a Codesys Ethernet/IP adapter + module and routing it through EtherCAT by tunnelling it through via an EL6614 switchport? Any advice would be appreciated. Billy.
Last updated: 2024-01-15
Post by jinlee on Multiple WebVisu
CODESYS Forge
talk
(Post)
Hi guys, I am new to the Visualization. I am having a problem. I have multiple web-panel to use webvisu. I have my software dowwloaded into the one PFC200. There are 3 screens connected to it. I noticed that if I switch page/visualisation on one of the screens, the others will change as well. Three screens are with different URLs that I set in the software. Is there any method to make them independently ? Kind regards, Jin.
Last updated: 2024-01-25
Post by wind-11 on Problem with simulation Modbus
CODESYS Forge
talk
(Post)
Hello everyone, I encountered a problem in the simulation while working. In a test project we set up a Modbus connection. We wanted to simulate this with test values. The connection also worked, but unfortunately the values are frozen and do not report any βcurrent dataβ. (Picture attached) Since these are my first points of contact with Codesys and my colleague continues to work elsewhere, I was hoping that someone here might have an idea. Kind regards and thanks in advance.
Last updated: 2024-03-22
Post by yannick on Raspberry PI 5 not working
CODESYS Forge
talk
(Post)
Hello I'm using Codesys V3.5 SP19 Patch 6 and a Raspberry PI 5 4GB Bookworm 32bit with the Runtime 4.11.0.0 SL. I can install the runtime and download the software completly but after a few seconds the connection disconnects with the message no connection to device. Please scan network again. And the object reference was not set to an object instance. See screenshot. Can somebody help me with that? Thanks
Last updated: 2024-04-28
Post by dkugler on Codesys SVN
CODESYS Forge
talk
(Post)
Don't set on SVN. The service phase has started in March 2024 and will be discontinued in 2027. We actually use SVN and have to switch to GIT in the future. As I informed, there is no way of getting a single SVN or GIT licence. I' dont understand, why Codesys forces us customers to pay for an expensive Professional Edition paket from year to year using only one part of it! If you find a way to buy a single licence, let me know.
Last updated: 2024-04-29
Post by william-blandon on RecipeManCommands.ReloadRecipes
CODESYS Forge
talk
(Post)
Hello. I'm trying to use RecipeManCommands.ReloadRecipes Method for getting recipes from files. When I call the method it does not generate any error but also not reload any recipe to the recipe definition. Actually I have 6 recipe files on the directory PlcLogic. The rest of the methods work creating recipes, saving to file, etc. Does any one have the same issue? it is something to be set on the recipe manager?
Last updated: 2024-05-16
Post by plunje on Sensor not set
CODESYS Forge
talk
(Post)
A got a larger project but this very small example makes it clear. I have a button, and after it's clicked a lamp should flip on and stays on, and when the mouse-button is released it should stay on. When I try that in the PLC_PRG it works, but when I change it to a function block (seet attched demo proj) it isn't. I'm fairly new to PLC programming but are very experienced C# engineer, but this goes above my head...
Last updated: 2024-05-26
Post by taqamert on Codesys 2.3 & Peak PCAN
CODESYS Forge
talk
(Post)
Despite working on it for days, I haven't achieved any results. I followed the necessary steps one by one as mentioned in the file you sent, but there hasn't been the slightest change. I couldn't find the step you mentioned "Set the 'Can Board Type' to PCAN USB" in the Word document. There is no such setting anywhere I looked. Is there a more detailed explanation available, or can you explain it in more detail? What am I missing?
Last updated: 2024-07-16
Post by mubeta on Some 'pathetic' errors in SoftMotion program
CODESYS Forge
talk
(Post)
Yes, this point is part of my misunderstanding. Why, after the execution ot the motion FBs is set to FALSE and exsecuted at lest one time, it must be continuosly called, even if the motion control it's take from another subsequent instruction. This is what I really don't undertand, but what in fact it's happening. For example, in case of stopping a MoveVelocity FB, then Halting the motion by the related FB, the axis at spot goes into error. If there was bad trigger management, the various instructions would NEVER work.
Last updated: 2024-07-18
Post by mikek10 on Error IoDrvEthernetIP: Connection Failure. (16#1) How to solve
CODESYS Forge
talk
(Post)
Your connection configuration should look something like the attachment. Consuming assembly O->T will be the hex of the assembly you want to reference for output data - I want 102 (DO Data Only) shown in the Wago web page 102 = 16#66. Producing assembly (T->O) is the assembly you require for input data - again shown in the Wago web page - I want 108 (DI Data Only) or 16#6C Then set the number of bytes as per the data in the Wago web page too (both 2 in my case)
Last updated: 2024-07-22
Post by stuartjr on POU Private variables
CODESYS Forge
talk
(Post)
Pretty sure I know the answer, but thought I would ask just in case. Is there a way to set variables declared in a POU to private so that they can not be accessed from other POUs. I tried using the library pragma, but that just stops the variables being displayed in the selection tree. My compiler version is 2.3.9.62 if that's relevant, and I'm using an ABB AC500 V2 PLC. Cheers
Last updated: 2024-07-31
Post by alex-at-xana on EThercat Dynamic configuration
CODESYS Forge
talk
(Post)
Ah - forgot another question as it may be related to the PLL problem: I am executing a 4ms cycle. I do not call (from what I know) the Ethercat_MAster periodically in my program. The bus cycle task is set to the Ethercat task. I would assume that the master should send 250 frames per second. Yet, the status of the master says it transmits 500 frames per second which would indicate that the master is called twice. Any ideas there?
Last updated: 2024-09-10
Post by dkugler on TargetVisu Freezing
CODESYS Forge
talk
(Post)
The only weird situation i remeber with particular or complete frozen target visu was after the rtc clock was fallen or set back to the past. It looked like after running a while the alarm history database crashed during writing entries at a date lot of years in the past. After setting the rtc clock to actual date/time and deleting the alarm db every thing worked fine. I don't know, if this is/was a problem of our PLC hardware/firmware? Maybe check date/time at your system?
Last updated: 2024-09-13
Post by winki on Modbus TCP & RTU with Control for Linux SL
CODESYS Forge
talk
(Post)
For small project, I would like to use my industrial computer as a PLC + Industrial Computer. Like that I can save the cost of one PLC. That why I am using Codesys on Linux. With the nic it is not working. I already set the IP adress with /etc/network/interfaces. Can it comes from there ? looking to "Control Linux SL" docuemntation it should work with rtu.
Last updated: 2024-10-23
Post by pmanuele on Beckhoff AS1060 and EL7041 configuration
CODESYS Forge
talk
(Post)
Hello everyone, i'm having some problems commanding AS1060 step motor with EL7041 (rev22) drive. With motor i've also the incremental encoder (05.2420.1230.0200.5009). I can correctly move the motor in "Position controller" operating mode with the internal counter. The problems start when i set the Encoder in feedback type or i change the operating mode. Does anyone have experience with these two terminals and can give me some advice of main parameters to check or change? Thanks everyone
Last updated: 2024-12-11
Post by struccc on When running as a service, CodesysControl doesn't write log files to the disk (and other CmpLog related issuess)
CODESYS Forge
talk
(Post)
Are you sure when running as service, it is not reading configuration from C:\Windows\System32\config\systemprofile\AppData\Roaming\CODESYS... ? Is the SRV user is set for the CODESYS services? 2 ways to fix it: Change the CODESYSControl.cfg in the installation directory (ProgramFiles/CODESYS...). Replace %APPDATA% with something fix. Modify the service configuration in windows service manager to run as a different user (ie bot as Local system account)
Last updated: 2025-02-28
Post by trusty-squire on Codesys for raspberry pi 5 not working exactly
CODESYS Forge
talk
(Post)
Not sure if you've resolved this yet, but the Codesys runtime user/password is different than the Linux user/password. You'll need the Linux user credentials when you log in over SSH (for example, to install the Codesys runtime). When you first log in to Codesys on the RaspPi you'll set up a Codesys user and password. If you lost those credentials, you could try uninstalling and then re-installing the Codesys runtime on the RaspPi so you can setup a new user/password.
Last updated: 2025-03-16
Post by jbu0105 on Dynamic limits invaild
CODESYS Forge
talk
(Post)
Hello, For my delta robot i wil use the MC_MoveCirvularAbslolute function. Every time that i set the execute of this function has my Axis group a error. Thats is: The dynamic limits for the movement are invalid. What can i do that this error go away? I saw a view funcitons with limit dymanics but i don't now how they work. If i use the function MC_MoveLinearAbsolute than i have no error. Does anyone know how i fix this?
Last updated: 2025-04-04
Post by jbu0105 on Dynamic limits invaild
CODESYS Forge
talk
(Post)
Hello, For my delta robot i wil use the MC_MoveCirvularAbslolute function. Every time that i set the execute of this function has my Axis group a error. Thats is: The dynamic limits for the movement are invalid. What can i do that this error go away? I saw a view funcitons with limit dymanics but i don't now how they work. If i use the function MC_MoveLinearAbsolute than i have no error. Does anyone know how i fix this?
Last updated: 2025-04-04
Post by altus22 on RemoteTargetVisu creates Unresolved Reference
CODESYS Forge
talk
(Post)
In order to set the placeholder to empty, open the Library Manager and click on Placeholders in the Library Manager ribbon. If you left click in the library column for CmpEventMgr Implementation, it will show you the available library versions for CmpEventMgr Implementation. To update the runtime, open the Project menu and select Project Environment. That window will show you the current version of CmpUserMgr Implementation and if there is a newer version available in the Recommended column.
Last updated: 2025-04-17
Post by paulg on RasPi CAA Serial example - unexpected behavior during debug
CODESYS Forge
talk
(Post)
I've trimmed down the CAA Serial Codesys example to only listen on one port but, when stepping through the Case structure in debug mode, it jumps out of the structure during a specific point in every scan (I'll point it out below after describing the setup and listing the code). I'm using a Pi 4 Model B, and I have an Arduino Nano Every plugged in via USB which is streaming the following serial message at 1 Hz: Time since opening connection: 1 s Time since opening connection: 2 s ...and so on. The Pi shows the Nano at /dev/ttyACM0 so I edited CODESYSControl_User.cfg to read: Linux.Devicefile=/dev/ttyACM The code in my PLC_PRG is (ignore some of the comments, I hadn't deleted them out from the original example): PROGRAM PLC_PRG VAR xStartTest : BOOL:= TRUE; iState : INT; xTestDone : BOOL;(* True, when the test was done succesfully *) (* Settings to communicate with the COM Port *) aCom1Params : ARRAY [1..7] OF COM.PARAMETER; como1 : COM.Open; comc1 : COM.Close; comw1 : COM.Write; comr1 : COM.Read; //sWrite : STRING := 'Test String!'; sRead : STRING(25); szRead : CAA.SIZE; xCom1OpenError : BOOL; xCom1CloseError : BOOL; xCom1WriteError : BOOL; xCom1ReadError : BOOL; END_VAR //This example shows the communication of two COM Ports with each other. //The first one writes a string of characters, which is read by the second one. //After successful execution, the two COM Ports are closed and the test is done. IF xStartTest THEN CASE iState OF 0: //The parameters are set for the COM Port aCom1Params[1].udiParameterId := COM.CAA_Parameter_Constants.udiPort; aCom1Params[1].udiValue := 1; // the correct Port should be adapted aCom1Params[2].udiParameterId := COM.CAA_Parameter_Constants.udiBaudrate; aCom1Params[2].udiValue := 115200; aCom1Params[3].udiParameterId := COM.CAA_Parameter_Constants.udiParity; aCom1Params[3].udiValue := INT_TO_UDINT(COM.PARITY.NONE); aCom1Params[4].udiParameterId := COM.CAA_Parameter_Constants.udiStopBits; aCom1Params[4].udiValue := INT_TO_UDINT(COM.STOPBIT.ONESTOPBIT); aCom1Params[5].udiParameterId := COM.CAA_Parameter_Constants.udiTimeout; aCom1Params[5].udiValue := 0; aCom1Params[6].udiParameterId := COM.CAA_Parameter_Constants.udiByteSize; aCom1Params[6].udiValue := 8; aCom1Params[7].udiParameterId := COM.CAA_Parameter_Constants.udiBinary; aCom1Params[7].udiValue := 0; //The first Port is opened with the given parameters como1(xExecute := TRUE, usiListLength:=SIZEOF(aCom1Params)/SIZEOF(COM.PARAMETER),pParameterList:= ADR(aCom1Params)); IF como1.xError THEN xCom1OpenError := TRUE; iState := 1000; END_IF //After a successful opening, the next state is reached IF como1.xDone THEN iState := 15; END_IF 15: // the reading process is started comr1(xExecute := TRUE,hCom:= como1.hCom, pBuffer:= ADR(sRead), szBuffer:= SIZEOF(sRead)); IF comr1.xError THEN xCom1ReadError := TRUE; END_IF //After completion the size of the written bytes are saved IF comr1.xDone OR comr1.xError THEN szRead := comr1.szSize; iState := 20; END_IF 20: // If everything was successful the ports are closed and the handles are released comc1(xExecute := TRUE,hCom:= como1.hCom); IF comc1.xError THEN xCom1CloseError := TRUE; END_IF IF comc1.xDone OR comc1.xError THEN iState := 25; END_IF 25: // The first port is closed and the used handle released xTestDone := TRUE; xStartTest := FALSE; iState := 0; como1(xExecute := FALSE); comw1(xExecute := FALSE); comc1(xExecute := FALSE); ELSE iState := 0; END_CASE END_IF I realize as I write this that the .udiPort should be 0 and not 1, but that shouldn't be causing the issue I'm seeing. I'm forcing xStartTest:=TRUE every scan so that I can step into each line and observe what's happening. What I see is that the port parameters are set and the port is opened with no errors, but the code jumps out of the case structure to the last line every time it reaches (and I step into) the iState:=15 line (at the end of the iState:=0 block). So every scan cycle it goes through the block for iState=0 and jumps out at the same spot. I'm a little new to PLC programming so I may be misunderstanding the flow, but shouldn't this case structure keep moving down in the same scan? If it only handles one case per scan, why doesn't the value of iState persist? Thanks! Update: I restarted the Codesys control today and I was then able to see an error for como1.eError of "WRONG_PARAMETER". I tried doing some digging and another post made me think I should add another line to CODESYSControl_User.cfg, so I now have: [SysCom] Linux.Devicefile=/dev/ttyACM portnum := COM.SysCom.SYS_COMPORT1 So now when I set .udiPort to 1, I get "NO_ERROR" but I also don't read anything from the port (i.e. szRead = 0 always). If I try setting the port to 0 (which I'm confused about, because I added a COMPORT1 line but the device shows on the Pi as ACM0), I get the "WRONG_PARAMETER" error again. Is there an easier way to troubleshoot the Pi and view what ports the Codesys runtime is actually able to see while the Pi is running?
Last updated: 2024-06-06