Post by marcolim on Slow modbus digital input response CODESYS Forge talk (Post)
[Update]. My issue's solved, I applied the resistors in Pull-down configuration on each digital input. In thus configuration never happened "floating or delaying" acquisition on SoftPLC/Arduino Board.
Last updated: 2024-04-15

Post by timvh on IoDrvModbusTCP_Diag not defined when using MODBUS CODESYS Forge talk (Post)
Most likely related to the Device Diagnostics functionality. Double click on your device (PLC), go to the tab "PLC settings". Enable the advanced option "Enable diagnosis for devices". Build your application again.
Last updated: 2024-04-15

Post by mbmik on IoDrvModbusTCP_Diag not defined when using MODBUS CODESYS Forge talk (Post)
Thanks alot for your time and help! I quickly tested the suggestion, as it makes a lot of sense. Unfortunately the erros still appear as before. The settings was already set before, and i tried turning it off.. no effect..
Last updated: 2024-04-16

Post by hyet on IoDrvModbusTCP_Diag not defined when using MODBUS CODESYS Forge talk (Post)
Currently seeing the same issue here, with a project moved from 3.5.19. Diving into it too to see if i can find the cause
Last updated: 2024-05-01

Post by guilhermeleao on How to communicate 2 pcs that are using CODESYS CODESYS Forge talk (Post)
I need to connect 2 computers on the same network that are running codesys, so that they can receive and change variable values from each other. This connection must preferably be made using Modbus.
Last updated: 2024-05-06

Post by zer0g on Modbus Client Request Not Processed CODESYS Forge talk (Post)
Hi, I have the same problem as the guys above. Any solution or hint in the right direction is appreciated. Codesys version 3.5.19.2, Lib version: 4.4.0.0. Thank you!
Last updated: 2024-05-29

Post by risele on Modbus connection via Qronox PCD3 M6893 CODESYS Forge talk (Post)
First, if you don't need to change conversion rules in runtime, take a look at "Unit conversion" module (Application -> add object -> UnitConversion). You can specify there biderectional conversion with different units, limits and so on. Second, since MODBUS don't have "real" types but only general 16-bit registers and Real is 32-bit, generally you need a byte-was conversion Real <> two Words. Note, that depending on the devices on both sides, there are two options: Real-> Word1, Word2 or Real-> Word2, Word1, where Word1 is minor register in Modbus register pair and Word2 is major. You can use simple union: TYPE u_Real : UNION rVal:REAL; wVal:ARRAY[0..1] OF WORD; dwVAL:DWORD; //same as previous, may be easier to specify the MB register END_UNION END_TYPE and convert it as following: VAR myUnion:u_Real; rValue_TO_SEND:REAL; rValue_TO_GET:REAL; END_VAR myUnion.rVal:=rValue_TO_SEND; rValue_TO_GET:=myUnion.rVal; Note, that WORD-order should be properly set in MODBUS registers, otherwise you will get strange values. This tool is helpful: https://www.scadacore.com/tools/programming-calculators/online-hex-converter/ Alternative, you can use functions as REAL_TO_DW and DW_TO_REAL from OSCAT_BASIC, for example.
Last updated: 2026-02-19

Post by esave on Softmotion Light Problem: The license is missing or invalid CODESYS Forge talk (Post)
Hello everybody I want to controll a stepper driver from Leadshine (EM3E-556E). The EtherCat slave is CiA 402 compatible. Because of this I bought the Softmotion Light Package from Codesys and implemented it in my project. I rightclicked the EtherCat slave and added the Softmotion Light axis. But now the error message shows: "The license is missing or invalid. The PLC runs in demo mode." What have i done wrong? I use Codesys 3.5.17. Is it possible that the stepper driver is not compatible with the Softmotion license? Thanks for all your help
Last updated: 2024-05-02

Post by jonasz on Device diagnosis ( EtherCAT IO card ) CODESYS Forge talk (Post)
Hi, I'll link to the topic not wanting to start a new one. In the application I am building, I wanted to use the diagnostics described in the CAA Device Diagnosis library. In principle, everything is ok, except for the elements related to ModbusTCP. Despite the fact that ModbusTCP is taken into account in the documentation, it is not recognised via the interfaces. FUNCTION_BLOCK NET_HW_DIAG VAR_INPUT END_VAR VAR_OUTPUT END_VAR VAR (* Referencja do struktury z danymi dla HMI ASTRAADA.*) Visu: REFERENCE TO VISU; (* Wskaźnik na mastera EtherCAT.*) pEtherCATMaster : POINTER TO IoDrvEtherCAT; (* Wskaźnik na slave EtherCAT.*) pEtherCATSlave : POINTER TO EtcSlave; (* Interfejs dla węzła w drzewie urządzeń.*) _itfNode: DED.INode; (* Ogólny interfejs magistrali. Zapewnia podstawowe informacje o magistrali polowej.*) _itfBus: DED.IBus; (* Interfejs urządzenia. Zapewnia rozszerzone informacje o urządzeniu (magistralowym).*) _itfDevice2: DED.IDevice2; (* Ogólny interfejs magistrali. Zapewnia podstawowe informacje o magistrali polowej.*) _itfStack: DED.IStack; (* Numer węzła w drzewie urządzeń.*) uiNodes: UINT; (* Operator jest rozszerzeniem normy IEC 61131-3. W czasie wykonywania operator wykonuje konwersję typu odwołania do interfejsu na inny typ. Operator zwraca wynik BOOL. Wartość TRUE oznacza, że CODESYS pomyślnie wykonał konwersję. *) xQueryResultBus: BOOL; xQueryResultDevice2: BOOL; xQueryResultStack: BOOL; (* Struktura danych dotyczących węzłów w drzewie urządzeń.*) NetHwDiag: NW_HW_STAT; ModbusTcpClientDeviceInfo: IoDrvModbusTCP.DED.DEVICE_INFO; ModbusTcpClientDeviceState: IoDrvModbusTCP.DED.DEVICE_STATE; ModbusTcpDeviceInfo: IoDrvModbusTCP.DED.DEVICE_INFO; ModbusTcpDeviceState: IoDrvModbusTCP.DED.DEVICE_STATE; END_VAR (* Pobranie wskaźników dla pierwszego mastera i pierwszego slave w sieci EtherCAT.*) pEtherCATMaster := g_pFirstMaster; pEtherCATSlave := pEtherCATMaster^.FirstSlave; (* Diagnostyka sieci EtherCAT.*) pEtherCATMaster := g_pFirstMaster; pEtherCATSlave := pEtherCATMaster^.FirstSlave; NetHwDiag.xConfigFinished := pEtherCATMaster^.xConfigFinished; NetHwDiag.xDistributedClockInSync := pEtherCATMaster^.xDistributedClockInSync; NetHwDiag.xError := pEtherCATMaster^.xError; NetHwDiag.xSyncInWindow := pEtherCATMaster^.xSyncInWindow; NetHwDiag.sLastMessage := pEtherCATMaster^.LastMessage; NetHwDiag.LastError := pEtherCATMaster^.LastError; (* Diagnostyka drzewa urządzeń.*) uiNodes := 0; _itfNode := DED.GetRoot(); REPEAT NetHwDiag.asDeviceName[uiNodes] := DED.GetDeviceNameString(itfNode := _itfNode); xQueryResultBus := __QUERYINTERFACE(_itfNode,_itfBus); IF xQueryResultBus THEN _itfBus.GetBusInfo(buiInfo := NetHwDiag.aBusInfo[uiNodes]); NetHwDiag.aBusState[uiNodes] := _itfBus.GetBusState(); END_IF xQueryResultDevice2 := __QUERYINTERFACE(_itfNode,_itfDevice2); IF xQueryResultDevice2 THEN _itfDevice2.GetDeviceInfo(deiInfo := NetHwDiag.aDeviceInfo[uiNodes]); NetHwDiag.aDeviceState[uiNodes] := _itfDevice2.GetDeviceState(); IF pEtherCATSlave <>0 THEN pEtherCATSlave^(); IF pEtherCATSlave^.SlaveAddr = NetHwDiag.aDeviceInfo[uiNodes].idSystem THEN NetHwDiag.aAlStatus[uiNodes] := pEtherCATSlave^.ALStatus; pEtherCATSlave := pEtherCATSlave^.NextInstance; END_IF END_IF ELSE xQueryResultStack := __QUERYINTERFACE(_itfNode,_itfStack); IF xQueryResultStack THEN _itfStack.GetDeviceInfo(deiInfo := NetHwDiag.aDeviceInfo[uiNodes]); NetHwDiag.aDeviceState[uiNodes] := _itfStack.GetDeviceState(); END_IF END_IF uiNodes := uiNodes + 1; _itfNode := DED.GetNextNode(_itfNode); UNTIL _itfNode = 0 END_REPEAT (* Diagnostyka Modbus.*) Modbus_TCP_Client.GetDeviceInfo(deiInfo := ModbusTcpClientDeviceInfo); ModbusTcpClientDeviceState := Modbus_TCP_Client.GetDeviceState(); PAC_3200T.GetDeviceInfo(deiInfo := ModbusTcpDeviceInfo); ModbusTcpDeviceState := PAC_3200T.GetDeviceState(); Of course, you can take the easy way out and refer directly to the devices, but I wanted a reusable component. Any constructive help is very welcome Best regards Jonasz
Last updated: 2025-07-15

Post by ph0010421 on TCP/IP client CODESYS Forge talk (Post)
Hello TCIS_Send needs to be longer than 4 bytes because idata is 28 bytes long. There may be other ways, but I would make a UNION with string/array of bytes. Write your STRING into the AsString part then copy the AsBytes part into TCIS_Send (Elements [3] to [30]) then 252 would be in [31] (I've assumed the idata is always the same length)
Last updated: 2023-12-19

Post by andreag0 on How to access to variable value through symbolic string name CODESYS Forge talk (Post)
Hello, anyone know how to get valiable value using a symbolic string name? For example: - send string to runtime using TCP/IP contains "GVL.TestINT" and get back the value. I need function that will translate the string to symbolic variable. Thank you. Andrea
Last updated: 2024-06-13

Post by nano on Cant login to Rpi4 but can see it in codesys communications settings. CODESYS Forge talk (Post)
which ports in detail are configured. the search of the rts works via broadcast-messages, programming with tcp-port on p2p-connection woth port-hopping, handled by runtime after siccesfully handshake. look at this entry on forge https://forge.codesys.com/forge/talk/Runtime/thread/4078a2ed28/
Last updated: 2024-06-23

Post by simotion on Variable indicating axis pending gearing or camming CODESYS Forge talk (Post)
Is there a variable indicating that a gearing or camming operation is pending? For instance MC_Gearin has beeen triggered, but starting point of master axis to start the sychronisation movement is not reached yet, so the slave axis is just waiting for this. I should be able to differ between a pending and active gearing or camming
Last updated: 2023-11-28

Post by charleskentyfz on (no subject) CODESYS Forge talk (Post)
I have created an EtherCAT slave code and fixed two slaves (IDs written in the 0xF050 object dictionary). The module IDs are 0x1 and 0x101, respectively. It can be scanned normally in TwinCAT, but when scanning in CODESYS, it reports an error. Why is this happening?text in the second pic means 'device cannot be found in repository'
Last updated: 2024-07-07

Post by mrrobot on No source code available for this object CODESYS Forge talk (Post)
Hello, I have this strange error while I am adding an axis to my slave: "No source code available for this object because it is in the compiled library 'sm3_drive_etc_ds402_cyclic' ..... I looked on google/chatgpt but i cannot find a solution for this issue Any help is welcome ! Thanks in advance Mrrobot
Last updated: 2024-07-15

Post by mrrobot on No source code available for this object CODESYS Forge talk (Post)
Hello, I have this strange error while I am adding an axis to my slave: "No source code available for this object because it is in the compiled library 'sm3_drive_etc_ds402_cyclic' ..... I looked on google/chatgpt but i cannot find a solution for this issue Any help is welcome ! Thanks in advance Mrrobot
Last updated: 2024-07-15

Post by atone on Change IO-Link Device Interface connected to a Profinet-Slave at Runtime CODESYS Forge talk (Post)
OK, I figured out that I can simply define all the sensors as 16 bytes IN/OUT, even if they are not all used. EDIT: The negative effect is that each bit is taken into account as an I/O for the license, even if not used.
Last updated: 2025-04-28

Post by lbouchard on CANOpen SIL2 error: UNSAFESTACK_NOT_OPERATIONAL CODESYS Forge talk (Post)
Hello, Working in 3.5 SP11 32 bit and using the 3S CANopenSafety Slave 3.5.11.0 library on an IFM CR711S. The 3SCSSD.CANOpenDevicesSIL2 function block keeps throwing "UNSAFESTACK_NOT_OPERATIONAL" Additionally, the Status of the device gives "There was an error accessing an I/O parameter". Any ideas on where my issues may lay? I have not found any good documentation that would explain the issue.
Last updated: 2025-05-23

Post by rmaas on Direct Pointers in IOMapping for EtherCAT with IoDrvEthercatLib.ETCSlave_Dia CODESYS Forge talk (Post)
Hi, Im not sure if this is what you mean, but i do succesfully use the IoDrvEthercatLib.ETCSlave.InputData and IoDrvEthercatLib.ETCSlave.OutputData to read from and write to beckhoff DI and DO cards. Very convenient as you can make an FB with an VAR_IN_OUT of type IoDrvEthercatLib.ETCSlave and only have to pass the slave reference... So i am not using .ETCSlave_Diag but .ETCSlave...
Last updated: 2024-02-13

Post by eschwellinger on Problem mit control runtime V3 und profinet CODESYS Forge talk (Post)
Hallo Tim, man hat halt einfach mit der Control Win - keine wirkliche harte Echzeit. Man müsste den Fehler genauer analysieren + ich denke er müsste den Slave wieder an den Busholen oder fällt ads ganze Netzwerk aus? Welche Versionen genau sind im Einsatz? Ist das halbwegs aktuell (PN 4.4.0.0?) Grüße Edwin
Last updated: 2024-04-11

Post by felipemsgarcia on Generic EtherCAT slave CODESYS Forge talk (Post)
Hello, Without much info, I would assume that this is an optional object on the EtherCAT network and it's either disconnected or the address doesn't match. I would look into the devices manual or contact the manufacturer for further assistance. And, I would have posted a new topic instead of using a non related one... Cheers!
Last updated: 2024-05-16

Post by xiaoyan on Generic EtherCAT slave CODESYS Forge talk (Post)
Hello Well i need some basic advice. My protegoD drive is shown deactivated in the device tree. i can see its variables and other i/o in online mode but the device itself is deactivated. how can i address this issue. is there any configuration error.using ethercat link to connect to protegoD by Primo MC plc
Last updated: 2024-05-16

Post by fabrp on CPU + EtherCAT redundancy CODESYS Forge talk (Post)
Hi TimvH, thanks for feedback. I also test the redundancy with Wago PFC 8212 but when I did it (firmware 28) it was not so much stable..Did you have some issue on master/slave switchover? are you using with EtherCAT remote I/O? I was looking for a most powerful hardware (PC based, x64) BR
Last updated: 2026-02-01

Post by reinier-geers on Compare applications in one project CODESYS Forge talk (Post)
HI,ive got one project with 6 applications. one master and 5 slaves. All 5 slaves should be the same. Can i compare applications in one project ? sind version 20.5 ive got problems. One slave freeze compleetly after a while. Ive got an other project freezes after a while , after a online change
Last updated: 2026-03-19

Post by mecmag on gear over gear (2 masters,1 slave) - how to do it? CODESYS Forge talk (Post)
Hello, i need to create an application that uses 2 masters, with 2 different ratios, and it outputs in one single slave. I explain better: Imagine axis A, B and C. -Axis A is the slave. -Axis B is master of A, with a specific ratio. -Axis C is master of A, with a specific ratio. the result motion from B and C should be executed by A, proportionally in position and ratios from B and C. With standard softmotion libraries (MC_...) it is not possible (i couldn't) because it is allowed only one master with its ratio. I have made a similiar application in past, using MoveOverGear in order to synch gears before engage. Instead this time, i need to do a gear over gear application, using 2 different masters. The position have to be the sum of both masters (considering their ratios). Any clue about how to do it? Or were to find some FB that can do it?
Last updated: 2024-08-16