Post by brell on Automatic xExecute NBS.TCP_write
CODESYS Forge
talk
(Post)
I've recently started experimenting with CODESYS for a project and am fairly new to it. I'm currently working with Function Block Diagrams (FBD) to set up TCP communication between a server and a client, where the client is implemented as a Python script. Once the communication is established, my connection status changes to True, which is the expected behavior. My challenge arises with the TCP write module, which requires the xEnable_write flag to toggle between True and False. If xEnable_write remains True, the module only performs a single write operation. To address this, I introduced a falling edge trigger (F_TRIG), expecting it to help in toggling xEnable_write and it does, However, I've encountered an issue where in the beginning after connxion established I need to manually set xEnable_write to True for the system to work as intended. I'm looking for a way to automate this process so that xEnable_write becomes True automatically upon establishing a connection . Initially, I tried setting xEnable_write to True from the start, but this approach didn't work well since it left the flag permanently True, preventing further toggling. I also experimented with using a TON timer, but I faced similar issues. I am seeking a solution that automatically toggles xEnable_write between True and False after a connection is established, ensuring continuous write operations without manual intervention. Any advice or guidance on how to achieve this would be greatly appreciated."
Last updated: 2024-03-05
Post by imdatatas on Read "Homed" status from EtherCAT drive
CODESYS Forge
talk
(Post)
Hello, I have experienced such situations with some servo drive devices in the past. The home completion information is reported to the upper controller by the slave drive with the states of the relevant bits in the StatusWord (for example; 6041h Bit10, Bit12 in Home mode). If the states of these bits are correct in terms of number and state but the motor does not actually perform the action; You can contact the slave drive manufacturer. There may be a problem with the device firmware. Another area you can play around with is looking at the settings in the "Advanced configuration" for Softmotion axis on the page the link to below, and trying it out and using the one that works for you. https://content.helpme-codesys.com/en/CODESYS%20SoftMotion/_sm_cmd_add_softmotion_cia402_axis.html A method I recommended worked for a user as in below message. https://forge.codesys.com/forge/talk/Engineering/thread/40bc82454d/ I hope your problem will be solved as soon as possible and by sharing the result here, you will help others to know and overcome it. Good luck. Best regards, Imdat
Last updated: 2025-01-08
Post by mubeta on Profibus DP master with EL6731 and automatic restart of slaves
CODESYS Forge
talk
(Post)
WHEREAS, I have already searched various posts and forums, where mostly there are few references and mostly geared toward integration in TwinCAT. I am looking for how to properly configure the EL6731 board as a DP master, (where I have its 3S license), with CoDeSys 3.5.19.x. I have three types of slaves, all integrated with their GSD descriptors. In the tab for the various slaves, I don't see options related to node restart on 'station return'. On the card manual, I read that for each slave I should be able to configure parameter 8000:2C: “8000:2C Restart behavior after DP fault Reserve, must be 0 BIT1 RW 0x00 (0dec)” However, in the project I see no way to configure this parameter, in any of the boards; and the arrays do not always have such an extensive size; most of the time they are only two or three words in size. The problem is that, after the hot reset of CoDeSys, the master restarts by starting all slave nodes, but if one or more get lost and go offline, there is then no automatic restart upon their return. I would need to figure out any solution, even via software, how to figure out that this one is back available and restart it.
Last updated: 2025-02-02
Post by ernesto881124 on ernesto881124
CODESYS Forge
talk
(Post)
Hello good morning everyone I would like to ask a question, is it possible to directly connect a device that only contains modbus RTU communication through an R-45 connector, directly to the PC? Or would you need an intermediate device to achieve communication? It would be of great help to me because I cannot achieve communication between the Codesys simulator plc and a Fuji Frenic mini VFD, please help me if anyone has had the same experience. Thank you so much
Last updated: 2023-09-13
Post by jeffgamsby on Accessing ModbusTCP addresses from python
CODESYS Forge
talk
(Post)
Hi, I am new to modbusTCP and I am trying to access Input registers from codesys (3.5.SP13). The offset is 16#0000 and I am trying to access Channel 1[24] %IW24 to pull analog values. I am using pyModbusTCP and I need to supply a modbus address and the number of registers to read. What does 16#0000 mean in terms of the actual offset, how do I translate this number plus the channel to access this info via python? Any help would be appreciated, thank you.
Last updated: 2023-09-20
Post by kislov on Change modbus server parameters from program
CODESYS Forge
talk
(Post)
Use in IEC-code: Modbus_Serial_Device.UpdateComPortSettings(...) https://content.helpme-codesys.com/en/libs/IoDrvModbusSerialSlave/Current/pou-ModbusSerialDeviceDiag/UpdateComPortSettings.html Take note: "Only possible if server is disabled (see xEnable Input)" So: Modbus_Serial_Device.xEnable := FALSE; Modbus_Serial_Device.UpdateComPortSettings(...) Modbus_Serial_Device.xEnable := TRUE; Please note that after PLC reboot the values from the GUI (from your screenshot) will be applied again. So you need to save values from HMI in RETAIN and restore them after start of application.
Last updated: 2024-07-17
Post by naps on Welchen I-Port benötige ich?
CODESYS Forge
talk
(Post)
Hallo, ich versuche eine 750-653(konfiguriert per iocheck) über die Wago Modbus Lib einzusetzen. Ich scheitere im moment an dem Korrekten I-Port. Ich habe es mit 75x_653 und IoConfig_Globals.75x653 versucht, jedoch bekomme ich folgenden fehler: ------ Übersetzungslauf gestartet: Applikation: Device.Application ------- Code typisieren... Code erzeugen... [FEHLER] Unbenannt7: POU_1 Device: SPS-Logik: Application: C0032: Typ 'DED.CAADiagDeviceDefault(caa device diagnosis, 3.5.20.0 (caa technical workgroup))' kann nicht in Typ 'WagoTypesCom.I_WagoSysComBase(wagotypescom, 1.6.2.3 (wago))' konvertiert werden Übersetzung abgeschlossen -- 1 Fehler, 0 Warnungen : Kein Download möglich Wie kann ich den die Karte benutzen?
Last updated: 2024-10-01
Post by garrian on How to write multiple coils (Modbus FC15)
CODESYS Forge
talk
(Post)
Thanks for your reply. I belive it is contiguous, I'm writing to adress 0 to 4. Or, do you mean something else? Well, something is happening. If I on the client set adress 1,2,3 to true, only 1 is set to true on the server side. On the client side, the data is array of word. But on the server side, the coils are array of bool. Holding register is array of word on server side. Can this be a problem? Attached screenshot of how it looks at the server side.
Last updated: 2024-11-17
Post by garrian on How to write multiple coils (Modbus FC15)
CODESYS Forge
talk
(Post)
Thanks! As far as I can see, the client can only send words. And on the server side there are an array for each of the functions: bool for coil and discrete, word for holding and input registers. I assume I can use holding register, then use bit mapping on the words instead of coils. But I really want to use the FC15/coils.
Last updated: 2024-11-17
Post by tim2508 on Werte von NodeRed an Codesys für Raspberry
CODESYS Forge
talk
(Post)
Guten Abend liebe Community, Im Rahmen meiner Technikerarbeit muss ich ein Gewächshaus mit einem RaspberryPi und Codesys erstellen. Mein Problem liegt hierbei bei den Sensoren. Ich bekomme über NodeRed alle Sensor Signale ausgelesen jedoch bekomme ich sie nicht im Codesys übertragen. Hat hier jemand evtl. eine Idee ? wenn ja am besten mit Codebeispiel. Habe generell an Modbus oder MQTT gedacht. Vielen Dank im Vorraus Tim
Last updated: 2025-02-19
Post by ivan-g on MODBUS
CODESYS Forge
talk
(Post)
Hi There, I took over a project from a colleague (in GTB) who left the company. When I took over his project, it wouldn't compile because some libraries were missing. I managed to recover quite a few libraries, but I can't find the library that contains the block functions shown in the image. Here are a few examples: Fb_RegMel_ISO Fb_DefModbus FbDecalConsSalSO Fb_Autor_FreeCool_CTA_C I'm a little stuck at the moment, so if you see a Facebook post that speaks to you, don't hesitate to get in touch! Thank you in advance for your help.
Last updated: 2025-08-05
Post by ivan-g on MODBUS
CODESYS Forge
talk
(Post)
Hi There, I took over a project from a colleague (in GTB) who left the company. When I took over his project, it wouldn't compile because some libraries were missing. I managed to recover quite a few libraries, but I can't find the library that contains the block functions shown in the image. Here are a few examples: Fb_RegMel_ISO Fb_DefModbus FbDecalConsSalSO Fb_Autor_FreeCool_CTA_C I'm a little stuck at the moment, so if you see a FB that speaks to you, don't hesitate to get in touch! Thank you in advance for your help.
Last updated: 2025-08-05
Post by camjam on BOOL variable in OPC UA and modbus simultaneously
CODESYS Forge
talk
(Post)
I have come across this. The only way i could get it to work would be to define a word that is also the same address as the Bools. eg %MX600.0 through to %MX600.15 would be individually defined in the variables and them have another variable word defined at %MW300. You still need to break out the word in what ever program you are using to read/write the OPCUA tags.
Last updated: 2025-08-18
Post by wind-11 on Simulation Modubus
CODESYS Forge
talk
(Post)
Hallo zusammen, ich bin über die Arbeit auf ein Problem in der Simulation gestoßen. In einem Test-Projekt haben wir eine Modbus Verbindung aufgebaut. Dies wollten wir mit Test-Werten simulieren. Verbindung hat auch funktioniert, jedoch sind leider die Werte eingfrohren und melden keine "laufenden Daten". (Bild im Anhang) Da es meine ersten Berührungspunkte mit Codesys sind und mein Kollege an anderer Stelle weiter arbeitet, hatte ich gehofft, dass vielleicht hier jemand eine Idee hat. MfG und schon jetzt ein Danke vorweg.
Last updated: 2024-03-22
Post by ph0010421 on General question about library versions
CODESYS Forge
talk
(Post)
Hello I can't find anything to read on the subject so I'll ask here. Up to now, when adding a (for example) Modbus Master, I've selected the version <= the RT version, so if I'm using SP13 Patch 3, I can use a library that doesn't exceed this. I've no idea if this is correct, but it's always worked. Can someone explain the 4.x.x.x libraries that have appeared; are they tied to a RT version? The controller I use is now at SP18Patch60, so should I continue to use 3.5.xxx or change? thanks
Last updated: 2024-05-29
Post by mubeta on Some 'pathetic' errors in SoftMotion program
CODESYS Forge
talk
(Post)
Hello everyone, I have a very simple program for the process, but it's driving me crazy and I can't see the problems I'm left with: Short topological description: Dual Core Berghof controller with softmotion runtime version 3.5.19.30; Two axes with servodrive on canopen bus, clocked distributed from master; Ethercat I/O node; 2 ms ethercat task, 2 ms canopen bus cycle time; I/O objects of the canopen master and canopen drives connected to the ethercat task cycle; Problem 1: Two separate programs each manage their own axis and drive, with separate state machines. A first axis moves primarily in velocity, except having to position itself absolutely at a predetermined point at the end of the job; the second axis, on the other hand, is a paper unwinder that changes, for each job cycle, from actions in absolute, relative, and cam displacement with the master axis. Well, the state machine of both axes was written in such a way as to call running the useful FB and change it on state change in this way: CASE i_stateMachine OF 0: o_Power(Enable := TRUE, bRegulatorOn := FALSE, bDriveStart := FALSE, Axis := o_PaperUnwinderAxis); o_MoveAbs(Execute := FALSE, Axis := o_PaperUnwinderAxis); o_MoveRel(Execute := FALSE, Axis := o_PaperUnwinderAxis); o_CamSelect(Execute := FALSE, Master := o_MachineAxis, Slave := o_PaperUnwinderAxis, CamTable := cam_PaperUnwinder); o_CamIn(Execute := FALSE, Master := MachineEncoder, Slave := o_PaperUnwinderAxis); o_CamOut(Execute := FALSE, Slave := o_PaperUnwinderAxis); o_SetPosition(Execute := FALSE, Axis := o_PaperUnwinderAxis); IF ... THEN i_StateMachine := 10; END_IF; 10: o_Power( Enable := TRUE, bRegulatorOn := TRUE, bDriveStart := TRUE, Axis := o_PaperUnwinderAxis ); IF o_Power.Status THEN i_StateMachine := 20; END_IF; 20: (* Avanzamento carta *) o_MoveAbs( Execute := TRUE, Position := o_Somewhere, Velocity := 25.0, Acceleration := 3666.7, Deceleration := 3666.7, Jerk := 48000.0, Direction := MC_DIRECTION.positive, Axis := o_PaperUnwinderAxis ); IF o_MoveAbs.Done THEN o_MoveAbs(Execute := FALSE, Axis := o_PaperUnwinderAxis); i_StateMachine := 30; END_IF 30: d_HomingPosition := ...; o_SetPosition( Execute := TRUE, Position := d_HomingPosition, Mode := FALSE, Axis := o_PaperUnwinderAxis ); (* ... *) IF o_SetPosition.Done = TRUE THEN o_SetPosition(Execute := FALSE, Axis := o_PaperUnwinderAxis ); o_LogServer.Append(sMessage := '...', lscClass := LOGSERVER_CLASS.ALWAYS, sdt := o_CommonsMgrData.systime.sdtLocal); i_StateMachine := 40; END_IF; 50: ... The code above is a sketchy example of what I wanted to write. But it gives me a spot problem: in some, the state change results in a drive error, which is unrecoverable except with a reinitialization via SM3_ReinitDrive(). Things are improved a little if in the program I always run the call of all softmotion blocks in this way: o_Power(Axis := o_PaperUnwinderAxis); o_Jog(Axis := o_PaperUnwinderAxis); o_Halt(Axis := o_PaperUnwinderAxis); o_MoveAbs(Axis := o_PaperUnwinderAxis); o_MoveRel(Axis := o_PaperUnwinderAxis); o_CamIn(Master := MachineEncoder, Slave := o_PaperUnwinderAxis); o_CamOut(Slave := o_PaperUnwinderAxis); If I don't execute all the calls of all the motion FBs used, when exchanging machine state often (but not always), the axis goes into error with event id THE_FB_WASNT_CALL... Done a little diagnostics it seems that the FBs return the bDone, before they are completely terminated. I tried doing the machine state exchange not with the bDone bit of the FBs, but with the 'standstill' state of the axis. It didn't seem to change anything. Problem 2: During the use SM3_ReinitDrive() I get the erro in the log: "NetID 0: SDO read error for object 16#607C..." Assuming that the device involved it's one of the two servodrive, (no others device are present in the network), I don't found any object 0x607C in the 'possible object list in/out' of the two drive, and I don't understand where this object can be listed. So any ideas and suggestions regarding these two issues will be very, very welcome. If you need the source project, I am willing to send it.
Last updated: 2024-07-17
Post by kurtk on dynamic modbus devices
CODESYS Forge
talk
(Post)
I am CODESYS neophyte getting my wheels on. My goal is to re-platform an existing PLC application written in 61131 ST I've got the majority of the code/variables in a compilable form - excluding all the IO and comms nuances I am not sure whether this the right forum An important functionality which I implemented on the other platform was totally dynamic modbus devices... Most configurations I have come across impose static MB configs in which all configured devices MUST be present and functional... I have monkeyed around with MB enough to know that herding a half dozen MB cats into a working config can be tricky. I just do them one at a time and dynamically turn them on/off in whatever combination is convenient with ID, IP, baud, parity etc being runtime tweakable. I am totally curious whether this is possible with codesys, or whether its device configuration corrals one into a static cage which requires re-building the code to support flexible variations. Best regards
Last updated: 2025-08-19
Post by kurtk on runtime dynamic modbus devices
CODESYS Forge
talk
(Post)
I am CODESYS neophyte getting my wheels on. My goal is to re-platform an existing PLC application written in 61131 ST I've got the majority of the code/variables in a compilable form - excluding all the IO and comms nuances I am not sure whether this the right forum An important functionality which I implemented on the other platform was totally dynamic modbus devices... Most configurations I have come across impose static MB configs in which all configured devices MUST be present and functional... I have monkeyed around with MB enough to know that herding a half dozen MB cats into a working config can be tricky. I just do them one at a time and dynamically turn them on/off in whatever combination is convenient with ID, IP, baud, parity etc being runtime tweakable. I am totally curious whether this is possible with codesys, or whether its device configuration corrals one into a static cage which requires re-building the code to support flexible variations. Best regards
Last updated: 2025-08-19
Post by acc00 on Main Task cycle too long leading to PLC Fail
CODESYS Forge
talk
(Post)
I have 2 Wago PFC200 PLC, running with Runtime SP19 Patch 5, with the Redundant application. The PLC communicates as Modbus Master with at this moment 15 Modbus Slaves -later there will be 28 in total- (Drives, Power management units,...). These devices are connected in 2 rings (1 ring of Drives, 1 ring of Power Management units), with 2 Managed Moxa Switches being part of the ring. Each PLC is connected to one of these switches. The issue I'm encountering is that the Cycle time of the Active PLC goes very high when I'm closing the Drive ring (simulating an issue on one Cabinet supply, resulting in that one Drive shut down, which can happen on field quite often). As a result of this long cycle, the PLC fails and goes to Exception, and the Passive PLC does not take control of the system. A normal cycle is around 30ms for the Main task, and a few ms for the Ethercat task. When I monitor with Profiler, I see that in this Maximum Cycle, the main Task is only taking 13ms, so I'm not sure where the PLC is hanging for so long. Is the remaining cycle time the Redundant management/sync or something else? Thank you in advance.
Last updated: 2024-03-08
Post by paro on Modbus Client Request Not Processed
CODESYS Forge
talk
(Post)
Hi, Problem in your code is that you are not calling the ClientFb cyclic. Please look at the Example from CODESYS: https://forge.codesys.com/prj/codesys-example/modbus/home/Home/ Your code works if the client fb is called cyclic! IF NOT initDone THEN initDone := TRUE; // configure clientTcp clientTcp(aIPaddr:=Ethernet.IPAddress, uiPort:=502); // configure clientSerial clientSerial(iPort:=SysCom.SYS_COMPORT2, dwBaudRate:=SysCom.SYS_BR_115200, byDataBits:=8, eParity:=SysCom.SYS_EVENPARITY, eStopBits:=SysCom.SYS_ONESTOPBIT, eRtuAscii:=ModbusFB.RtuAscii.RTU); // configure clientRequestReadCoils_1 clientRequestReadCoils_1(rClient:=clientTcp, uiUnitId:=42, udiTimeout:=TO_UDINT(T#10MS)); // configure clientRequestWriteSingleRegister clientRequestWriteSingleRegister(rClient:=clientTcp, uiUnitId:=43, udiTimeout:=TO_UDINT(T#10MS)); // configure clientRequestReadCoils_2 clientRequestReadCoils_2(rClient:=clientTcp, uiUnitId:=44, udiTimeout:=TO_UDINT(T#10MS)); // configure clientRequestReadInputRegisters clientRequestReadInputRegisters(rClient:=clientTcp, uiUnitId:=44, udiTimeout:=TO_UDINT(T#10MS)); END_IF // call the client FB's clientTcp(); clientSerial(); // call client request FB's clientRequestReadCoils_1(rClient:=clientTcp, xExecute:=TRUE, uiStartItem:=2, uiQuantity:=3, pData:=ADR(aDataCoils_1[0])); // for more details see Example_TCP, especially ClientRequest control (xExecute, xDone, xError). IF clientRequestReadCoils_1.xDone THEN // get data from aDataCoils_1 ... END_IF clientRequestWriteSingleRegister(rClient:=clientTcp, xExecute:=TRUE, uiItem:=3, uiValue:=123); clientRequestReadCoils_2(rClient:=clientTcp, xExecute:=TRUE, uiStartItem:=2, uiQuantity:=3, pData:=ADR(aDataCoils_2[0])); clientRequestReadInputRegisters(rClient:=clientTcp, xExecute:=TRUE, uiStartItem:=16, uiQuantity:=3, pData:=ADR(aDataInputRegisters[0]));
Last updated: 2024-05-29
Post by mikek10 on HTTP Client TCP Init Error
CODESYS Forge
talk
(Post)
Hi, I tried posting in the discussion for the HTTP Client example but perhaps that is not monitored? I have been using http client successfully for approximately 12 months, however in recent weeks I have begun to get TCP_INIT_ERROR when attempting to communicate. The only resolution seems to be power cycling and then the connection begins to work again for a time. I am not aware of any changes to code or libraries between working ok and now. Cold reset does not resolve, only power cycle. It seems the error from NBS.TCP_Client is 6002 which I think is invalid_addr However the address is the same when working and not working?
Last updated: 2024-07-04
Post by sigurdrb on Codesys and error messages, warnings exceptions etc.
CODESYS Forge
talk
(Post)
Hi, I tried some different libraries (CmpApp etc.) to find some global variables that I could read out as a variable in the codesys environment. Do any one of you know which libraries are best suited for this, and how I can read it out? My goal is to send messages, warnings etc. to the system that communicates to the PLC. Currently if something goes wrong I need to see the logfiles, or go online with the controller. I think I could save a lot of time if I could read the errors from our user interface that is connected to the PLC by TCP/IP.
Last updated: 2024-11-06
Post by matt-purcell on Which Lib to use, connect to a socket with URL instead of IP address
CODESYS Forge
talk
(Post)
Hello, I have a new project and I need to connect to a TCP socket using the URL instead of an explicit IP address, myendpoint@mydomain.com Which library is best suited for this? This is for a new enterprise project, the endpoint is a server in a datacenter running some real time application. We have big IP, it will automatically reassign the IP address to the backup server if a crash occurs so an explicit IP won't work for me. I've done this in RS logix, working now to migrate that code over to codesys. Thanks in advance!
Last updated: 2024-06-17
Post by muhq on Profinet connection to Siemens CP343-1 Lean (IO-Device/Slave)
CODESYS Forge
talk
(Post)
Hi, I am quite new to Codesys and I try to do a Profinet connection to an Siemens PLC (315-2DP) with CP343-1 Lean Modul. I already configured the Siemens PLC, exported the GSDML. Then I added a new project in Codesys, added following moduls: - Ethernet - PN_Controller - Imported Profinet Device via GSDML importer When I start the programm everything looks fine but I always get the message "Stopped Profinet" and no data is available This is only for a small test. Therefore I start to do that on a Windows 10 with Development System. Later I will try to realize this on Raspberry. Ethernet Adapter is configured (192.168.1.1 / 24) Firewall deactivated WinPCap is installed S7-Station seems to be found ('fuadazenzitest') Can please somebody help me?
Last updated: 2023-08-26
Post by seppi on Establishing communication between a Raspberry Pi 4 and an Arduino UNO R3 using I²C.
CODESYS Forge
talk
(Post)
Hello everyone, I want to establish communication between my Arduino and my Raspberry Pi via I²C, but I have no idea how to make it work. However, it should work because there are many examples available, although none of them were programmed using Codesys, but rather using Python. My Raspberry Pi will be the master and is supposed to exchange measurement data such as speed and battery capacity with the slave (Arduino). I would be very grateful if someone could help me with my problem. Here is another link that could be helpful. However, I can't find the mentioned libraries
Last updated: 2023-12-03