Post by peterned on Programatically restart Codesys OPC UA server? CODESYS Forge talk (Post)
Hi, I'm using a Festo Codesys PLC (CPX-CEC-C1-V3), which is connected to a HMI panel. Both exchange data via OPC UA. Occasionally, the HMI stops displaying data, and looks as if there is no connection. If the HMI stops, the only way to make it work again is to restart the PLC. Restarting HMI has no effect. When the PLC is restarted, HMI starts working normally again. Is it possible to restart the OPC UA server from PLC code? I hope this will make fixing the HMI possible without a PLC restart. Thanks
Last updated: 2024-07-19

Post by peterned on Array to String CODESYS Forge talk (Post)
max. string length in Codesys is 255 chars. It's not possible to cram 20,000 things in a string. If you need to send the data to another device, send the whole data[] array (as byte array, without doing anything to it) and extract the information on the other end. As each struct member has a fixed size (81 bytes, as per you declaration), this will be easy. To save some resources, consider declaring string lengths - e.g. if the max possible length for key is 10 chars, declare it key: STRING(10); and it will occupy 11 bytes instead of 81
Last updated: 2024-07-20

Post by dawidr on Best practices for querying multiple MODBUS devices CODESYS Forge talk (Post)
Hi! What are the best practices for querying multiple Modbus devices? Single PRG or maybe multiple PRG (so basically multiple thread) per each Modbus device. In my current implementation I'm using single PRG and I'm utilizing FbMbMasterMultiQuerySerial and WagoAppPlcModbus.FbDigitalTwinMbSlaveDevice in eCockpit with PFC200. I've the timer with 2 seconds delay there and it was working fine for single device. But now I have three Modbus devices and for two of them I need to run 2/3 queries to get data from all registers. I noticed that the delays for getting the data from the Modbus devices is much bigger right now.
Last updated: 2024-07-31

Post by expertplas on No connection to opc server from codesys opc client CODESYS Forge talk (Post)
Hello, we have aproblen to connect our CODESYS OPC Client to the OPC Server. We installed the client according the CODESYS manual. We can browse the server and variables can be linked to the PLC. I created a self signed certificate for the CmpOPCUAClent as described. The server has a cerificate also. I copied the certificates to the trusted zone of server and client. But when it comes to data exchange we get an error message. "Communication error in data source OPC UA Library. Error ID : 7001 German : "Kommunikatinsfehler inder Datenquelle OPC UA -Bibiothek. Es wurde kein genauer Fehler angegeben. Fehler ID : 7001" It semms that there is no cerificate exchange. We are working with CODESYS 3.5 SP19 Patch 5. Can anyone here say something about this error or has an idea for a solution? Thanks.
Last updated: 2024-08-19

Post by trent on Automation server - trends stop recording - need to manually reconnect CODESYS Forge talk (Post)
Hi All, I use the analysis page in automation server to capture historical trends from my PLC - i only sample one point per hour but it does the job (for now) One issue I have is I often log on to analysis page to find the system has stopped recording trends from my PLC. To fix this, I need to choose "state information" in the "List view" under PLC and click "Reconnect" When I do this I see my variables listed under "parameters" under "PLC Details" start updating again and the trend in Data analyzer continues to update. My Question, Why do I need to manually reconnect? Is there a way to get automation server to automatically reconnect to the PLC so I continue to capture data from the PLC? Regards, Trent
Last updated: 2024-10-22

Post by struccc on HTML5 Controls - string(>80) values CODESYS Forge talk (Post)
Dear all, does anyone have experience with HTML5 controls recently? CODESYS 3.5.20.30 / Visualization 4.6.0.0 I'd like to create a simple lightweight text editor, with proper multiline handling, cut & paste, scrolling, etc. And it seems to work fine, just have problems with strings longer than 80 bytes.... Declaring a variable sText1 : STRING(8000) and referencing it in the HTML5 Controls corresponding value property works perfectly one way: the code receive the data as a string (See log1)... (Note TypeID 1000...) Also sending back the data (seems to work (See log2) except it doesn't change the value of the bound variable. Probably the issue is with using SendSimpleValue method... Naturally, I could do a workaround, but maybe there is a more standard way to implement this... Please let me know if you have any suggestions.
Last updated: 2024-10-23

Post by mehakfatima on Need Help Configuring Energy Analyzers via Modbus TCP & RTU (RS-485) in CODESYS 3.5 CODESYS Forge talk (Post)
Hello everyone, I am currently working on reading data from energy analyzers using Modbus TCP and RTU (RS-485). In my previous software, I used the following method to add slave devices (i have attached the image) and configure registers: Add the Modbus slave device. Configure the communication parameters (baud rate, parity, etc.). Define the registers and their addresses for data retrieval. Now, I am trying to achieve the same in CODESYS 3.5, but I am not sure how to configure the Modbus master, add slave devices, and set up the registers properly. If anyone has experience with Modbus TCP/RTU setup in CODESYS 3.5, I would really appreciate your guidance! A step-by-step explanation or any references/tutorials would be extremely helpful.
Last updated: 2025-03-13

Post by sumit on Not able to see input data coming from eip adapter on codesys CODESYS Forge talk (Post)
dhumphries, I changed the datatype this time from BYTE to USINT (because that's what my adapter is sending: array of uint8_t). The text "New Help String" you saw in previous screenshots is just the description of the input/s (it can be anything). I also looked into the logs (see attached) for that ! sign next to the device, I found that connection is being timeout. I tried some suggestions from online such as increase the RPI but still got connection timeout issue, also by changing the datatype, I still don't see incoming data from the adapter, although its visible on wireshark. thanks,
Last updated: 2024-03-07

Post by garrian on How to sort JSON object in codesys CODESYS Forge talk (Post)
Hi there, I'm testing out MQTT from my Wago PLC using JSON object. I have managed to publish this {"Temperature":15.6,"Setpoint":38.0} to my broker. Now I', trying to subscribe to the same message. The result is this: '{"Temperature":15.6,"Setpoint":38.0}95}ê$10šå$04$Nå$08²Ÿå$0B` á$08@šå' First, why do I see 95}ê$10šå$04$Nå$08²Ÿå$0B` á$08@šå' at the end of the message? Second, how Can i sort out this data to use it in my program? I followed a youtube tutorial which gave me the attached result, which works. But I need some other smart way of doing this when the object gets even more data in it. Any help is very appreciated :)
Last updated: 2024-05-04

Post by uluking on CodeSys2.3 Modbus 64-Bit Double Read Problem CODESYS Forge talk (Post)
Hi everyone, I would appreciate your help with a problem I've been working on for a few days but haven't been able to resolve. I am reading data from a Siemens PAC3220 energy analyzer using Modbus with Wago-8202. However, the device's energy indices are given as doubles. Since a double variable is 64-bit, it is not possible to read it directly. I have been struggling for days, I have written many conversion functions but I have not been able to get results. I would appreciate your help. I read 4 word variables and processed them. I am converting them according to IEEE-754, but I can't seem to read the correct data. I would appreciate your help.
Last updated: 2025-10-27

Post by uluking on CodeSys2.3 Modbus 64-Bit Double Read Problem CODESYS Forge talk (Post)
Hi everyone, I would appreciate your help with a problem I've been working on for a few days but haven't been able to resolve. I am reading data from a Siemens PAC3220 energy analyzer using Modbus with Wago-8202. However, the device's energy indices are given as doubles. Since a double variable is 64-bit, it is not possible to read it directly. I have been struggling for days, I have written many conversion functions but I have not been able to get results. I would appreciate your help. I read 4 word variables and processed them. I am converting them according to IEEE-754, but I can't seem to read the correct data. I would appreciate your help.
Last updated: 2025-10-27

Post by swol on HTML 5 - Controls -> Change Content-Security-Policy settings CODESYS Forge talk (Post)
Sorry for being late to the party... so it is not possible to use the webbrowser tool to display external websites in a visu anymore? As it is not possible to simply "adjust the ContentSecurityPolicyIncludeTrustedOrigins setting in the automatically generated webvisu.cfg.json file" as stated in the docs? We need to display data read from a Raspberry Pi (part of our computer network) in our webvisu. We used to do it by entering the Pi's IP address as the URL variable in the webbrowser element but now (I don't know since when, I'm new on the job) "The page’s settings blocked the loading of a resource (frame-src) at 'IP address' because it violates the following directive: “default-src 'self' 'unsafe-inline'”. What are the options for displaying the data?
Last updated: 2025-11-11

Post by reinier-geers on wEBCLIENT Post data api CODESYS Forge talk (Post)
Ive got the webclient axample. If i put https://reversed.notion.site/Marktprijzen-API-89ce600a88ac4abe8c2ad89d3167a83e example to https://reqbin.com/post-online then i get data. If i do the same in Webclient example i get " not a valid graphql request. Why ? sUrl := 'https://graphql.frankenergie.nl/' Request_type_post Contenttype = 1 (json ) Postvalue := '{"query":{"query":"query MarketPrices {\n marketPrices(date:\"2025-12-25\") {\n electricityPrices {\n from\n till\n marketPrice\n marketPriceTax\n sourcingMarkupPrice\n energyTaxPrice\n perUnit\n }\n gasPrices {\n from\n till\n marketPrice\n marketPriceTax\n sourcingMarkupPrice\n energyTaxPrice\n perUnit\n }\n }\n}' I tranfer the postvalue from String to WSTRING
Last updated: 2025-12-25

Post by tk096 on Some 'pathetic' errors in SoftMotion program CODESYS Forge talk (Post)
Meanwhile, I would like to understand why the motion FB instances must still be called even after the Execute is set to FALSE, especially in view of the fact that the next instruction is programmed to abort the previous one, with BufferMode set to 'Aborting'. All these unnecessary FB calls are an unnecessary overhead on the CPU anyway. Is there any precise rule about when to cease calling the various instances? (It should precisely be the 'done' status that says this one has finished its work). In general: - Motion function blocks have to be called until they report 'Done', 'Error', 'CommandAborted' or a subsequent motion FB with BufferMode=Aborting is started in the current cycle. - Setting the Execute input to FALSE will not abort any ongoing motion of the motion function block. For example, one case that is often problematic is the execution of the Axis Halt instruction. When, after a MoveAbosulte instruction this returns the event as 'done' and indeed the axis is in standstill, the state machine first sets the move instruction to FALSE, and the next cycle sets the Halt request to TRUE. Some of the time everything works out fine. Occasionally, however, in this exchange, the axis goes into fault, also losing the OPERATIONAL state. I think the error SMC_FB_WASNT_CALLED_DURING_MOTION is only a follow-up (and misleading) error that results from the axis not being in operational state anymore (bus problems). Is there an error 'regulator or start not set' in the device log before the error 'motion generating FB wasn't called for at least one cycle'? Which error does the respective function block (Halt.ErrorId) report?
Last updated: 2024-07-22

Post by timvh on Get Alarm status in Codesys CODESYS Forge talk (Post)
You are right, that you can use the GetState method, but it is not that simple. You first have to get a list of (filtered) alarms from the AlarmManager. You can find an example in Forge how to do this. See https://forge.codesys.com/prj/codesys-example/alarm-manager/home/Home/ Then you can go through this list to get the state of all the (filtered) alarms. See below the code which you could use. This is all based on the example from forge. Create a program: // This example shows how to access alarms via structured text. PROGRAM PLC_PRG VAR xInit : BOOL := TRUE; udiResult : UDINT; fbAlarmFilterCriteriaAll : FB_AlarmFilterCriteriaAll; fbAlarmManagerClient : FB_AlarmManagerClient; itfAlarmManagerClient : IAlarmManagerClient := fbAlarmManagerClient; xAlarm1 : BOOL; xAlarm2 : BOOL; xWarning : BOOL; iNrOfAlarmsInAlarmList : INT; iNrOfActiveAlarmsInAlarmList : INT; paitfAlarm: POINTER TO ARRAY [0..0] OF AlarmManager.IAlarm; iAlarmIndex : INT; eAlarmState: AlarmManager.AlarmState; END_VAR IF xInit THEN xInit := FALSE; fbAlarmManagerClient.itfAlarmFilterCriteria := fbAlarmFilterCriteriaAll; // register alarm client to get updated about alarm status / changes udiResult := AlarmManager.g_AlarmHandler.RegisterClient(itfAlarmManagerClient, 0, 0); END_IF // Polling the number of alarms udiResult := AlarmManager.g_AlarmHandler.GetActiveAlarms(itfAlarmManagerClient, parritfActiveAlarms => paitfAlarm, iCountActiveAlarms => iNrOfAlarmsInAlarmList); iAlarmIndex := 0; iNrOfActiveAlarmsInAlarmList := 0; WHILE iAlarmIndex < iNrOfAlarmsInAlarmList DO eAlarmState := paitfAlarm^[iAlarmIndex].GetState(); IF eAlarmState = AlarmManager.AlarmState.Active OR eAlarmState = AlarmManager.AlarmState.ActiveAcknowledged THEN iNrOfActiveAlarmsInAlarmList := iNrOfActiveAlarmsInAlarmList + 1; END_IF iAlarmIndex := iAlarmIndex + 1; END_WHILE See below some details about the function blocks: One function block should implement the IAlarmFilterCriteria interface. This can be empty except a few methods. FUNCTION_BLOCK FB_AlarmFilterCriteriaAll IMPLEMENTS AlarmManager.IAlarmFilterCriteria Method implementation (others related to interface are empty) METHOD AreAllAlarmClassesSelected : BOOL AreAllAlarmClassesSelected := TRUE; METHOD AreAllAlarmGroupsSelected : BOOL AreAllAlarmGroupsSelected := TRUE; METHOD GetPriorityFrom : USINT GetPriorityFrom := 0; METHOD GetPriorityTo : USINT GetPriorityTo := 255; The other function block should implement IAlarmManagerClient and get a reference to the FB which implements the IAlarmFilterCriteria FUNCTION_BLOCK FB_AlarmManagerClient IMPLEMENTS AlarmManager.IAlarmManagerClient VAR_INPUT itfAlarmFilterCriteria: AlarmManager.IAlarmFilterCriteria; END_VAR Method implementation (others related to the interface are empty) METHOD GetFilterCriteria : AlarmManager.IAlarmFilterCriteria // see VAR_INPUT for filter GetFilterCriteria := itfAlarmFilterCriteria; Off course you have to add the AlarmManager to your application and add some alarms to it.
Last updated: 2025-09-02

Post by anhkdv on Data storage and Export in Codesys CODESYS Forge talk (Post)
I am doing a SCADA project on temperature and humidity monitoring system. The customer requested that we store the database through codesys without the need for intermediary software such as MySQL, MSSQL,... and be able to export reports at selected times, reports exported to csv files. , xslm,... Can anyone help me?
Last updated: 2023-10-29

Post by leon78 on Codesys 3.5 SP17 Patch 2 CheckBounds (POUs for Implicit Checks) CODESYS Forge talk (Post)
Unfortunately, it was fixed in SP19, but I need SP17 CDS-82162 Bug Compiler: Checkbounds is not working for dynamic arrays with VAR_IN_OUT as index access Fixed [[GENERAL]] Compilerversion >= 3.5.19.0 https://de.codesys.com/fileadmin/data/Images/System/Releaseinformation/Release-Notes-CODESYS-35190.html
Last updated: 2023-11-16

Post by seesle on Extracting information out of a *.library or *.compiled-library file CODESYS Forge talk (Post)
Hey there, is there a way to extract any data out of a .library or a .compiled-library file? Do you have any tools or a description of the binary or something like this to get for example the referenced libraries of a *.library file or any other stuff? Thx in advance M.
Last updated: 2023-12-04

Post by talhaali on Adding a variable from text list into ST code CODESYS Forge talk (Post)
Hi, can I use a entry of a text list as variable in structured text? for example in attach picture, if i use want to use data of first row. I am trying to write: A : STRING := TextList.Default.0; but it is not workings
Last updated: 2023-12-07

Post by talhaali on Adding a variable from text list into ST code CODESYS Forge talk (Post)
Hi, can I use a entry of a text list as variable in structured text? for example in attach picture, if i want to use data of first row. I am trying to write: A : STRING := TextList.Default.0; but it is not workings
Last updated: 2023-12-07

Post by tomast on Communication PLC with HMI - how to send DUT via NVL. CODESYS Forge talk (Post)
Hi everyone, I am working with project where i have DUT wihth struct. I would like to fill this data trough a form on HMI. I use NVL to communicate and i would like to know how is it possible to do this? Thanks for all your advice in advance.
Last updated: 2024-08-23

Post by hassaank on CODESYS V3+ WAGO PFC200+ MODBUS RTU CODESYS Forge talk (Post)
Hi everyone, I’m new to CODESYS and Wago devices, and I’m trying to set up Modbus RTU communication. I have a Wago PFC200 (8110) and a 750-653 RS485 module, and I want to read data from an energy meter using Modbus RTU. Thanks in advance for your help!
Last updated: 2025-03-17

Post by lacypaige on Engineering Dissertation Help & Assignment Assistance. CODESYS Forge talk (Post)
This thread is for discussing engineering dissertation help, including research methods, choosing a topic, writing, and data analysis. Whether you need advice on structuring your dissertation, understanding industry trends, or solving research challenges, this is the place to ask questions and share ideas. Feel free to exchange tips, discuss best practices, and get support with engineering assignments and dissertations.
Last updated: 2025-03-19

Post by kevinm on Attaching Trace variable to Frame Configuration Variable CODESYS Forge talk (Post)
Is it possible to show a variable from a Frame Configuration in a Trace on that Visualization? I want to pass the FB for an AXIS_REF_ETC_SoE_Standard to the visualization and display live axis data in the visualization. However, I cannot find a way to use a Frame Configuration variable in the Trace Configuration dialog.
Last updated: 2025-04-04

Post by timvh on update data/tim CODESYS Forge talk (Post)
Change the actual time of your PLC. How to do this sometimes depends on the PLC you use. Please contact the vendor of the PLC to get this information. Or see the following example for using CODESYS date and time functions: https://forge.codesys.com/prj/codesys-example/date-and-time/home/Home/
Last updated: 2025-08-26