Post by dengsberg on Disable Communications to 'Modbus_Server_COM_Port' from the logic
CODESYS Forge
talk
(Post)
I have a serial Modbus RTU communicating to the Slave device. But when the control system is not in Run there is no power applied to one of the Modbus Devices. Can I enable / disable the communications to that Modbus Slave in the code based on my running mode, so I don't get all the errors?
Last updated: 2024-08-29
Post by dkugler on User management
CODESYS Forge
talk
(Post)
If the PLC is equieped with a USB socket it's possible to copy the user management file via IEC code to a USB stick and restore it at the new plc. The file is located there: /PlcLogic/visu/app_visuusermgmtdb.csv I use this to reset the user management to default in case of the customer has changed passwords and lost it.
Last updated: 2024-09-04
Post by damian177 on Codesys Control for Linux SL
CODESYS Forge
talk
(Post)
Hi, For many years my application has been running on Raspberry Pi. Now I have ported the application to a PC running with Debian OS with Codesys Control for Linux SL. Most of things works. But some is wrong with serial ports. Firstly , I wonder why /etc/CODESYSControl.cfg in Debian is empty ?
Last updated: 2024-09-08
Post by bbm1995 on Camera RTSP Feed
CODESYS Forge
talk
(Post)
Can you provide some infos on what you did? What model is your camera and which protocols does it support? Is there a direct link to the feed? Does your camera prevent embedding of the feed (this was my issue.)? I had to use additional software (go2rtc) to be able to stream the feed from an ABUS TVIP48511...
Last updated: 2024-09-16
Post by boris on EtherCAT error: the device is deactivated
CODESYS Forge
talk
(Post)
Hi, I am currently working in BCS-tools (basiscally codesys) and I am trying to run the GN-9386 network adapter in the EtherCAT_master , but when I run the program the Ethercat status shows the error: ''The device is deactivated''. I don't know what to do right now. Can someone explain me how to fix this error? regards, Boris
Last updated: 2024-10-02
Post by egau on Hard shutdown: no code on device after power on
CODESYS Forge
talk
(Post)
Hi, thanks for the fast response :) Yes I Have a .err file. Sorry I forgot to upload it. It is a binary file though... "Runtime goes in exception before the shutdown ?" I think it goes into exception at the same time as the power is lost...
Last updated: 2024-10-03
Post by davidmic on What is this ST syntax?
CODESYS Forge
talk
(Post)
I found some structured text code which contained this statement: bHidden:= TRUE(*NOT _somevariable*) I haven't seen TRUE() used like a function before, and I also haven't seen the enclosing asterisks * * before. What do they do? (sorry if this is a duplicate question, I don't know what words to use to search for this syntax)
Last updated: 2024-10-11
Post by janber on REFERENCE TO in an array
CODESYS Forge
talk
(Post)
Hi all, in the online help it written, that array of reference to data type is not possible. Ok... but if I create array of struct of reference to - everything works fine - please see the screenshots: and it works this way OK. Is it intention or error in compiler 3.5.18.20 and we should avoid it? Thanks a lot, Jan.
Last updated: 2024-10-14
Post by eschwellinger on Scan Network on gateway created with Control Sl
CODESYS Forge
talk
(Post)
it seems that the device you scan, is not the same type which you have added to the project in CODESYS. Virtual Control is Arm 64 SL so please select this type in CODESYS when you generate a new Application..or right click to the device- update device - virtual Control Arm 64 SL
Last updated: 2024-10-16
Post by lbartik on MPC predictive control
CODESYS Forge
talk
(Post)
Would this work? https://www.mathworks.com/hardware-support/codesys.html I'm also interested in real-world MPC and have no idea where to start. There is an exciting Python library that is also beyond my grasp: https://www.do-mpc.com/en/latest/index.html Step 1, get PhD(s). Step 2, get job in aerospace/robotics. Step 3, return 15 years later to share this knowledge?
Last updated: 2024-10-19
Post by davidbo on Modbus: Is there a way to get the channel index from the channel name?
CODESYS Forge
talk
(Post)
When I use the FUNCTION_BLOCK ModbusChannel I have to sepcify the integer iChannelIndex It can easily go wrong if one has many channels. It would be better if one could use the name. Is that possible? Attached a snippet of the channel name and the channel index to the left.
Last updated: 2024-10-21
Post by daniel on SysFileOpen not working
CODESYS Forge
talk
(Post)
Hello, I have the same problem now with 3.5.20 Patch 3. Normally it works if I ad in CODESYSControl.cfg: [SysFile] ForceIecFilePath=0 (This told me codesys last time) I try to use the placeholders but without success. Something special is that the Files are not in C:. The Plc Configuration Path is not as usual C:\ProgrammData\CODESYS\CODESYSControlRTEV3\, it's E:\Control.
Last updated: 2024-10-23
Post by jeroenaero on CodeSys Raspberry pi I2C driver not found
CODESYS Forge
talk
(Post)
yes i took the library from another forum: https://forge.codesys.com/forge/talk/Runtime/thread/f1400b71b6/, it is made for the ads1115 but the ads1015 is almost the same device with same adresses i only changed the divide value of the analog value, because thats the only difference between the ads1115 and ads1015.
Last updated: 2024-11-07
Post by jeroenaero on CodeSys Raspberry pi I2C driver not found
CODESYS Forge
talk
(Post)
Okay i will try. I tried already the different settings. The CodeSys version i use, is CodeSys 3.5 SP20 Patch 3. The device which i use is CodeSys Control For Raspberry PI 64 SL version 4.13.0.0. The wiring should be okay because i'm using the Edatec ED-CM4IND-1432-4C(EU).
Last updated: 2024-11-07
Post by andrax on CodeSys Raspberry pi I2C driver not found
CODESYS Forge
talk
(Post)
I took a look at your project. First of all, a Raspbery Pi4 is installed. You must use the GPIOs_A_B(GPIOs B+/Pi2). The error ULINT can't be set to IDINT.... with your project as well. If I change your project to βCODESYS_Control_for_Raspberry_Pi_SLβ the error is gone.
Last updated: 2024-11-09
Post by bertcom on Converting each character to a string into ASCII
CODESYS Forge
talk
(Post)
@TimvH, Thank you, i think this way i can seperate the complete string to characters. Next part of the topic is converting the characters to an ASCII code. Is there an standerd function in Codesys for this? I alredy searched a few hours for it on the internet. no succes.
Last updated: 7 days ago
Post by yr00 on OPC UA datasource low read frequency
CODESYS Forge
talk
(Post)
Hello everyone, I am trying to test the OPC UA client feature in Codesys. My setup is the following; I have a Codesys simulation/ visualization running on Control Win V3. My OPC UA server is hosted on a Siemens 1518 PLC using PLCSim Advanced. The setup is completely virtual so there are no really PLCs. Everything is on my laptop. Writing data from the Codesys simualtion to the server is very quick. I have a PLC program running on another 1500 PLC which reads data from simulation via the server, and changes in the simulation (e.g. button pressed) appear within hundreds of miliseconds if not tens of miliseconds in my PLC program. However, when it comes to reading data from the OPC UA Server by Codesys, it taks around 1-2s. I connected a UAExpert client and it gets update very quickly so I am fairly sure the problem is with Codesys. I have tried changing the update rate in datasource -> General and Diagnosis, but it doesn't seem to have an effect. Do you guys have any suggestion on what I can do?
Last updated: 2023-08-29
Post by rcaponi on Codesys Control RTE V3. Remote Control
CODESYS Forge
talk
(Post)
Hello, I would like to have, if possible, some clarification on this function. That is, I would like to understand if it is useful for managing, fom my development PC, the RTE runtime executed on a remote control. This is what the help says: Remote PLC: Opens the Remote Configuration dialog. By enabling or disabling the Control remote PC, not local option, you determine whether a PLC is used that is on a remote or local PC. Accordingly, the menu commands Start PLC, Stop PLC, and PLC Configuration refer to the local PC or a PC reached on the network. For the remote PC, specify the Target PC address, Port number, and a Timeout value (in ms) for the connection (Remote Timeout [ms]). But does this mean that I also need to install the RTE runtime on my development PC? Is it possible to have some more information? Best regards Roberto Caponi
Last updated: 2023-09-22
Post by captaincookie on increase default string length in queue
CODESYS Forge
talk
(Post)
Hello, I'm using Codesys V3.5 SP18 Patch 4. In the ElementCollectionExample Project from Codesys, I test the SimpleQueueExample in a Control Win V3 x64 environment. I try to add a string of 95 characters length to a queue. The default length of strings is defined as 80 characters. In the initialization of a string variable, it is possible to increase the length by the definition of e.g. STRING(1000). But when I write the string defined like this to the queue, only 80 characters are written to it and the rest is missing. I think the default length is still set in the queue definition, so it is necessary to change this, isn't it? Is there any option to increase the default length of strings in the queue? Attached you can find the used project. Thanks in advance. If any information are missing or my description unclear please let me know.
Last updated: 2023-10-05
Post by timvh on VisuElems.CurrentUserGroupId is not stable
CODESYS Forge
talk
(Post)
I'm not sure what you are trying to do, but getting the CurrentUserGroupID like this will not work, because there could be multiple Visualization Clients and each can have a different user that is logged in. Also when you go online with CODESYS and open an Visualization, this is counted as a client. Probably this is the reason you see it changing. What you can to is "iterate" over all clients and then see which user is logged in on which visualization Client. For this you need to add the Visu Utils library to the project and call the FbIterateClients. See https://content.helpme-codesys.com/en/libs/Visu%20Utils/4.4.0.0/VisuUtils/VisuActionUtilities/Function-Blocks/FbIterateClients.html fbClientIteration( xExecute := x_Execute, itfClientFilter := VU.Globals.AllClients, itfIterationCallback := fbIterator, xDone => x_Done, xBusy => x_Busy, xError => x_Error, eError => e_Error); The fbIterator, in the example above, should be an instance of an FB which you have created yourself and this must implement VU.IVisualizationClientIteration. For example: FUNCTION_BLOCK FB_ITERATOR IMPLEMENTS VU.IVisualizationClientIteration Then automatically the corresponding methods will be called. In the HandleClient Method, you will get an interface to the client(s) and then you can get the current user through this interface: itfClient.UserGroupId You can also get the UserName: itfClient.UserName
Last updated: 2023-11-14
Post by riccardo on VisuElems.CurrentUserGroupId is not stable
CODESYS Forge
talk
(Post)
Goodmorning TimvH, Thanks for the reply. I don't know if your solution solve my trouble yet, I am going to see the link you sent me. In the mean time I try to explane better what I need to do. I have a turbine system that get in alarm under some condition (E.g low speed of turbine) and block the itself. When the system is stoped there is no speed turbine and the system cannot start. To give to the operetor the possibility to bypass the alarms, there is an acknoledgement alarm pushbutton. This bypass must not work for everyone but only for those client that perform the login by (User Management). Furthermore, if the user perform the (manual or automatic) logout in alarm conditions, the acknowlegment must be annulled and block the system again. To do this, I need to know if an operator is logged in the page and is working to fix the problem; otherwise the syste must autoturn off again. Now I go to study your solution, if I have explaned better and you have another idea tell me please.
Last updated: 2023-11-16
Post by ewi04 on Git with visu
CODESYS Forge
talk
(Post)
Hi, I have several problems with the git extension. Situation: I am working with Codesys v3.5 SP19 Patch 1 and Git V1.2.1.0. The remote repository is GitLab Community Edition v16.1.2. I am working on a project with one other person. Problems: 1: After each start of Codesys all of the visu pages are marked as modified. So we have to discard all changes first. Otherwise the history is not clean and the merge request becomes more complex. I tested it with a new project and only local. I made the observation, that a page is not marked as modified when it is committed a second time (after a restart of codesys). But this is necessary after every change of a page. However, since we are working in a team, it seems we are playing ping-pong and so all pages are marked as modified on each startup. 2: Each image pool causes a parent child conflict. Also in my local project. The only solution that I have found, is to ignore the issue. Does anyone have the same problems? I think it looks more like bugs. Thanks ewi04
Last updated: 2023-11-22
Post by arundara on Variable Sync Issue In Soft Plc Redundancy
CODESYS Forge
talk
(Post)
Hello, I was trying to create a redundancy POC for our application where we read data from few modbus tcp devices. As there is a limitaion that modbus tcp device support only for single master device, we wanted to test how the variable sync happens in redundancy mode. For that i have used the redundancy sample code added a variable "b" under a condition. What i observed was while active controller is running, if passive controller is powerup, passive controller is able to sync all the data configured for redundacny. But after that the variable data which resided under a condition is not synching from active to passive controller. I have attached the image where i have highlighter the variable. Can some help me to understand how redundacny work in codesys soft plc and if there is a solution to sync variable which are under condition, please explain the same or suggestion to achieve the same. Hardware - Raspberry Pi (2 qty) Redundancy licence used - yes in both controllers. Codesys runtime - 4.9.0.0 Codesys software version - V3.5 SP19 if i have posted this question in wrong section, please do let me know in whcih section i have to post this question.
Last updated: 2023-12-01
Post by open on How to create a stopwatch?
CODESYS Forge
talk
(Post)
Hi @ph0010421, I tried the program the TimeTaken is calculated when stop is triggered. I want the TimeTaken to be continuously calculated and counting when a BOOL variable is true. I tried to program this way: Declaration: PROGRAM PLC_PRG VAR bStartStop: BOOL := FALSE; // Start/Stop button bReset: BOOL := FALSE; // Reset button bRunning: BOOL := FALSE; // Flag indicating whether the stopwatch is running tStartTime: TIME; // Variable to store the start time tElapsedTime: TIME; // Variable to store the elapsed time END_VAR Implementation: // Main program logic IF bReset THEN // Reset button pressed, reset the stopwatch bRunning := FALSE; tElapsedTime := T#0s; ELSIF bStartStop THEN // Start/Stop button pressed, toggle the running state IF bRunning THEN // Stop the stopwatch bRunning := FALSE; ELSE // Start the stopwatch bRunning := TRUE; tStartTime := tElapsedTime; END_IF; END_IF // Update the elapsed time when the stopwatch is running IF bRunning THEN tElapsedTime := tElapsedTime + T#1s; // Adjust the time increment as needed END_IF However counting of the seconds is not accurate. I tried changing the main task cycle time interval to 1000ms. The counting of seconds become slower. (see attached) Please help
Last updated: 2023-12-08
Post by axilleas on SMC_Interpolator + SMC_controAxislbyPos
CODESYS Forge
talk
(Post)
dear all I am working on a very generic gantry system (virtual drives + win v3 control) reading gcode from external file. In order to stop the interpolator function from running when gaps are detected, SMC_controlAxisByPos FB has the bStopIpo output which according to the manual is connected to the Interpolator's bEmergencyStop. Lets assume that the axis are parked in position X1000 Y1000 and the initial G code movement is G00 X500 Y500. The normal behavior is to travel from the actual x1000 y1000 to G00 X500 Y500. The SMC_Interpolator always gets the X0 Y0 as the initial position, meaning that the bStopIpo is active until the axis are in X0 Y0 and the release the interpolator to set the new positions to X500 Y500. Is there a suggested method to solve this behavior? bonus question: I get a lot of bStopIpo during standard interpolation movements (not gaps). While working with virtual axis this is not a problem but when real axis are installed this will be an issue. What exactly triggers the bStopIpo output? Slow axis accelerations compare to Gcode defaults? Kind Regards