Post by struccc on Bibliothek: floatingpointutils
CODESYS Forge
talk
(Post)
The issue s the byte order typically in this case. Can be especially problematic with floating point numbers - even more tricky if transferred with a word based protocol. It is a peasant way to try out the alternatives, dword order can be a-b-c-d, b-a-d-c, c-d-a-b, d-c-b-a where a is the most significant, d is the least significant byte. So all you need is to swap the bytes in your dword, until you get the expected result. If you don't want to mess writing code for this, I'd recommend CAA_Memory library for that: MEM.ReverseBYTEsInDWORD and MEM.ReverseWORDsInDWORD functions would definitively do the trick. Otherwise, can do like this: VAR dwIn : DWORD := 16#11223344; dwOut : DWORD; rOut : REAL; pIN : POINTER TO BYTE; pOUT : POINTER TO BYTE; END_VAR pIN := ADR(dwIn); //pOUt := ADR(dwOut); pOUt := ADR(rOut); pOut[0] := pIN[3]; pOut[1] := pIN[2]; pOut[2] := pIN[1]; pOut[3] := pIN[0]; Ugly, but does the job...
Last updated: 1 hour ago
Post by john-robinson on Limiting Memory Access of an Array to Within its Bounds
CODESYS Forge
talk
(Post)
Recently we had an issue regarding some simple code to calculate a rolling average. The code indexes from zero to 199 to properly store the current input into a circular buffer which then allows us to calculate a rolling average: VAR input_5s : REAL; outs_arr : ARRAY[0..199] OF REAL; i : USINT := 0; END_VAR ___ //this code runs every five seconds, calculating a rolling average outs_arr[i] := input_5s; i := i + 1; output := OSCAT_BASIC.ARRAY_AVG(ADR(outs_arr), SIZEOF(outs_arr)); IF i >= SIZEOF(outs_arr) THEN i := 0; END_IF There is a simple bug in this code where the index will be set to 0 when it has surpassed the length of the array in bytes (800 in this case) rather than larger than the number of reals in the array (200). The solution here is simple, replacing i >= SIZEOF(outs_arr) with i >= SIZEOF(outs_arr)/SIZEOF(outs_arr[0]). In this example when the index increased to 201 and the line outs_arr[201] := input_5s was called, codesys arbitrarily wrote to the address in memory that is where outs_arr[201] would be if the array was that long. I would like to find a way to wrap the codesys array inside of a wrapper class that checks if an input is within the bounds of an array before writing to that value. I know how I would implement that for a specific array, I could create a method or class that takes an input of an array of variable length, ie. ARRAY[*] OF REAL, but I don't know how to make this for any data type. I am wondering if anyone has ever done anything similar to this, or has any better suggestions to ensure that none of the programmers on this application accidentally create code that can arbitrarily write to other locations in memory.
Last updated: 2024-03-05
Post by manuknecht on Maximum dynamic limits of MC_MoveLinearAbsolute and MC_MoveLinearRelative
CODESYS Forge
talk
(Post)
Hello all I use an axis group with two linear axes in a kinematic system. Using MC_MoveLinearAbsolute and MC_MoveLinearRelative, I am trying to realise dynamic movements (set velocity: 1 m/s, set acceleration: 30 m/s^2) with the highest possible jerk, as I want to compare this with a movement with a trapezoidal velocity profile. However, my measurements show that the axes accelerate with a maximum jerk of approx. 800 m/s^3, even if the value in the function block was set to 10,000 m/s^3. I have already increased the dynamic limits of the two axes accordingly (Velocity: 5000 u/s, Acc-/Deceleration: 250'000 u/s^2, Jerk: 100'000'000 u/s^3, where 1 u = 1 mm), but this had no effect. I have checked the input parameters of the function blocks and the VelFactor, AccFactor and JerkFactor factors are all set to the maximum (value 1). Reducing the cycle time has resulted in a higher jerk, but as we are already working with a cycle time of 1 ms, there is nothing more that can be done here. The axes themselves are still a long way from drawing the maximum current, which is why I assume that this should not be a problem either. Are there other factors or parameters that influence the dynamic limits and therefore allow faster movements? The PLC I am using is a Raspberry Pi 4 and Codesys V3.5 SP20 with all libraries up to date. Thanks in advance Manuel
Last updated: 2024-05-08
Post by youness on No source code available (cip object)
CODESYS Forge
talk
(Post)
Hi yotaro, hope your problem was resolved. I had the same, but with an other library title. This exception is not detected during compilation, but rather at a given position in the program (when switching to a given visualization). Although the exception is generated at this point, it does not involve the visualization in question. This error is due to one of 3 reasons: 1) A division by zero somewhere: The program is able to detect divisions by zero at compile time. But in the case of a variable, which takes a valid value at init and changes to 0 at a later stage. 2) An invalid pointer: (either because it has a value of 0, or because it points outside the memory reserved for the program) is being dereferenced. Locate any pointers or interfaces you have in the code and check them - you should also be wary of mixing inline modifications and pointers. 3) Array overflow: Generally when a processing operation is executed outside the array's definition range. Example: a write loop with n iterations is executed on an array of dimmension n-1. On the other hand, the error message may not appear. In the latter case, the error may have fatal consequences, as the overflow has induced writing to potentially forbidden memory areas. This problem can be explained by the fact that it's not always the adjacent memory areas of PLC_PRG that are overwritten, but the memory areas that are randomly allocated to the array during compilation. In this case, however, there is no entry in the log, so you need to integrate the "Implicit Check function", which checks the line of code generating the error. To integrate this functions, click on Application --> POU for implicit controls Regards,
Last updated: 2024-07-16
Post by ernesto881124 on ernesto881124
CODESYS Forge
talk
(Post)
Hello good morning everyone I would like to ask a question, is it possible to directly connect a device that only contains modbus RTU communication through an R-45 connector, directly to the PC? Or would you need an intermediate device to achieve communication? It would be of great help to me because I cannot achieve communication between the Codesys simulator plc and a Fuji Frenic mini VFD, please help me if anyone has had the same experience. Thank you so much
Last updated: 2023-09-13
Post by transmin01 on CANbus issue
CODESYS Forge
talk
(Post)
Update: This initial issue was when using a Linux target PLC. Since then I have created a Win10 target PC and the Codesys software reported an issue associated with the device version (see attached). I am assuming this is an incompatibility with the xml file from the manufacturer and the firmware version on the module and I am chasing this up with Beckhoff. Question is, why would this not report with a Linux target?
Last updated: 2023-09-14
Post by nico01 on Integer with comma in visualization
CODESYS Forge
talk
(Post)
Hello everyone, I created a visualization with a lot of REAL, with one or two digits after the decimal point. This causes me problems in terms of rounding and memory... is it possible to display an integer with a comma, like with PROFACE or SIEMENS? It's just an "abuse" of display, the comma is just on the visualization. This limits the memory (16 versus 64 bytes) and rounding is easier to manage... See print screen on proface software THANKS
Last updated: 2023-09-20
Post by docker on Canopen connection. Unknown node id.
CODESYS Forge
talk
(Post)
hi, i am currently trying to adapt an i/o device for a project. the node id is unknown and there is no eds file available. no data is being emitted from the device as a giveaway, the baudrate is known but useless without the node id. is there an sdo request available to determine the id? i cannot get the device to leave pre op status even with a global nmt request. please help. no hair left.
Last updated: 2023-09-25
Post by ofey on Symbol configuration / GVL
CODESYS Forge
talk
(Post)
Hi! I have som variables that I communicate to a Modbus Master. These variables are declared in a "Global Variable List" where I have assigned them memory addresses. To organize this mapping I want to make a MODBUS list where I show all the variable names together with the memory address. Is there an easy way to export this list from CODESYS? Either through script or some export function maybe?
Last updated: 2023-10-11
Post by ofey on Symbol configuration / GVL
CODESYS Forge
talk
(Post)
Hi! I have som variables that I communicate to a Modbus Master. These variables are declared in a "Global Variable List" where I have assigned them memory addresses. To organize this mapping I want to make a MODBUS list where I show all the variable names together with the memory address. Is there an easy way to export this list from CODESYS? Either through script or some export function maybe?
Last updated: 2023-10-11
Post by tehthoams on Find Function: Object reference not set to an instance of an object.
CODESYS Forge
talk
(Post)
Hey, Sorry this isn't super helpful, but i had this problem once and was able to resolve it. I can't recall how I solved it and whether it was a problem with my codesys installation or the project itself. If it is the codesys installation, make sure all your required libraries and plugins are installed and available. compare with a colleagues installation if possible. I vaguely recall saving a copy of my project and deleting things one by one until the error went away...
Last updated: 2023-10-30
Post by tehthoams on Find Function: Object reference not set to an instance of an object.
CODESYS Forge
talk
(Post)
Hey, Sorry this isn't super helpful, but i had this problem once and was able to resolve it. I can't recall how I solved it and whether it was a problem with my codesys installation or the project itself. If it is the codesys installation, make sure all your required libraries and plugins are installed and available. compare with a colleagues installation if possible. I vaguely recall saving a copy of my project and deleting things one by one until the error went away...
Last updated: 2023-10-30
Post by timvh on SafetyApp - "Invalid ERR Ack input"
CODESYS Forge
talk
(Post)
I had a similar error "Invalid ERR Ack input". What you need to do is link an variable from the "non-safe" PLC to the Group IOs of the POU in the Safety app. * Add a POU to the SafetyApp (probably already done, otherwise you don't get this error) * Right click on this POU - select properties * Go to the Group IOs tab * Link a variable to the Err.Ackn. input I don't know about the Size of zero, I didn't get this error. Were you able to fix this?
Last updated: 2023-11-16
Post by vformanek on OPCUA Datasource, can not login...
CODESYS Forge
talk
(Post)
Hello? I have a problem with datasource... I am trying to connect to a OPCUA server. I create a datasource, but I can not login into it. I need to use login credentials to login... Everything works fine in UAExpert, but in codesys I cant seem to get in properly using the login credentials... I have tried to configure the datasource initializer but seem to keep failing... Do I need to call it somewhere ? Will the find endpoints work with this configured to store my password ? !
Last updated: 2023-11-20
Post by fred on Rasperry Control Debian 12
CODESYS Forge
talk
(Post)
Hi, I have Proxmox running on a Rasperry 4 and have debian 12 ARM installed here. I wanted to install Codesys Control for Raspberry on it. According to the messages, the runtime environment and the gateway were installed successfully, but I can't find a device to downplay a program. The sudo service codesys start command fails. (see image) Does somebody has any idea? Thank you for your help! Greetings Fred
Last updated: 2023-11-22
Post by simover on TCP/IP client
CODESYS Forge
talk
(Post)
I want to send a string to a tics TCP/IP server. I got i working with the Net Base lib. for communication good with this tcis i need to by array of byte I want to include a string in the third position of the array TCIS_Send[1] :=254; //this valus is fix for evry communication TCIS_Send[2] :=80; //this valus is fix for evry communication TCIS_Send[3] := ; here I put my and my string is lik this 5806509-DRAP10#AB#3452302073 TCIS_Send[4] :=252; //this valus is fix for evry communication
Last updated: 2023-12-18
Post by sturmghost on Find visualization elements that require a lot of computing time
CODESYS Forge
talk
(Post)
I found out that the Codesys simulation mode is not good to measure performance. As soon as I upload the code onto the hardware PLC I can see that my visu-task needs around 60 ms to complete. I'm wondering if there is a possibility to find out which visualization/visualization element takes a lot of computing time? Then I would look for ways to decrease the long computing time.
Last updated: 2024-01-22
Post by wiresplus on INT_TO_WORD function not working
CODESYS Forge
talk
(Post)
Hello, I need to take an INT input, and convert it to a WORD value. VAR DRV2Speed : WORD; //IO card takes a WORD where 16000 = full 10V output (equivalent to 50Hz) PumpFillSpeed : INT; //Users enter a value between 0 and 50 END_VAR IF <conditions> THEN DRV2Speed :=INT_TO_WORD((PumpFillSpeed/50)*16000); END_IF </conditions> According to me this should work - but it stays at 0, no matter what. What am I doing wrong?
Last updated: 2024-01-26
Post by rpostwvu on Shared Memory Access Issues
CODESYS Forge
talk
(Post)
I got the shared memory example. I'm pretty sure I'm successfully created a memory space, CreateResult returns 18. szName:='CodesysDataShare'; hShm := SysSharedMemoryCreate(szName, 0, ADR(uxiSize), ADR(CreateResult)); I'm trying to access this memory with a C# application, but I get "Unable to Find Specified File". I suspect that Codesys and/or Visual Studio code alters the name I choose? Being in Windows, I cant find a way to see the mapped memory list. ~~~ using (var mmfRead = MemoryMappedFile.OpenExisting("CodesysDataShare",MemoryMappedFileRights.ReadWrite)) ~~~
Last updated: 2024-01-29
Post by josephbourgeois on Tracking out product
CODESYS Forge
talk
(Post)
Hi everyone! I synchronize the operation of the tripod and the conveyor. I have a problem with the product tracking algorithm on the conveyor (PCS_1). Sometimes I need to stop tracking a product on command without completing the operation. I do this using MC_GroupStop. But when I need to start moving in WCS again (using fb movelinearabsolute), I get a tripod kinematics error - SMC_CP_INVALID_ORIENTATION (Invalid orientation (non-orthonormal matrix or non-unit quaternion, internal error)). MC_ResetGroup does not help. What could be the problem? Has anyone encountered this?
Last updated: 2024-02-05
Post by josephbourgeois on tracking out product
CODESYS Forge
talk
(Post)
Hi everyone! I synchronize the operation of the tripod and the conveyor. I have a problem with the product tracking algorithm on the conveyor (PCS_1). Sometimes I need to stop tracking a product on command without completing the operation. I do this using MC_GroupStop. But when I need to start moving in WCS again (using fb movelinearabsolute), I get a tripod kinematics error - SMC_CP_INVALID_ORIENTATION (Invalid orientation (non-orthonormal matrix or non-unit quaternion, internal error)). MC_ResetGroup does not help. What could be the problem? Has anyone encountered this?
Last updated: 2024-02-05
Post by jinlee on Multiple WebVisu
CODESYS Forge
talk
(Post)
Hi, thank you for replying. Basically, I have a main visu with frame selection. So, under some condition the frame will switch to a specific frame. It used to be controlled by variable using "Switch frame variable". However, I realise it will change all the HMI screen at one time. So I removed the variable, and still looking for a solution to do that. Do you have any idea?
Last updated: 2024-02-06
Post by suthesan on Error when I go online on Simulation or PLC
CODESYS Forge
talk
(Post)
Hello I not sure if I made this topic under the right category. But I have a error, when I try to run a simple code on simulation or PLC. I have also tried to make a fresh project. I am testing the PLC and want to see if there is some way I can make an actuator run. Please help by looking at the picture, Iam stuckd and I don't know how to fix it.
Last updated: 2024-02-07
Post by durstloescher on Codesys Input Detector
CODESYS Forge
talk
(Post)
Good morning, I am currently working on implementing a display dimmer. I want the display to dim after X minutes. This works so far. The implementation is done via the Linux subsystem, to which a command is sent to dim the display. However, my problem is resetting the timer when input is received. I want the dimming timer to be reset with each click/touch. Unfortunately, I can't find a suitable solution for this. Are there any ways to do this? Codesys v3.5 SP19 Patch 2
Last updated: 2024-02-15
Post by kleeswi on SysFileOpen does not work after update to V3.5 SP19 Patch 5
CODESYS Forge
talk
(Post)
I use the function SysFile.SysFileOpen(sFileNamePara, SysFile.ACCESS_MODE.AM_WRITE, pErrorFileOpen); to open and write a file. Since the update from Codesys V3.5 SP17 to V3.5 SP19 Patch 5 it does not work anymore. I first had SysFile.SysFileOpen(sFileNamePara, SysFile.ACCESS_MODE.AM_APPEND_PLUS, pErrorFileOpen); in both versions. hFile_Test is a pointer to byte. It gives an exceptional error when dereferencing the hFile_Test pointer. Edit: I use Codesys on a Raspberry pi
Last updated: 2024-02-19