Post by davidbo on RPI can system operation like rm in a shell have an impact on a Task cycle time CODESYS Forge talk (Post)
3.5 18 SP2 I think the control is 4.2.0.0. I am not in the office before on Wednesday.
Last updated: 2024-09-23

Post by reinier-geers on Sel Error on an adressed output 3.5.20.5 CODESYS Forge talk (Post)
if i do : sVisu_Uitwerp := SEL( qxUitwerp_Ventiel ,'Cil_H_Uit' ,'Cil_H_In' ); then i get see picture Why ? It works normaly but not in 20.5
Last updated: 2025-03-27

Post by tk096 on Cam Editor And Cam Problem CODESYS Forge talk (Post)
Hi, in the XYVA compile format the editor is adding an additional point if the derivatives are jumping at this point. However, this should not change the path?
Last updated: 2025-06-30

Post by abjha1998 on Converting UINT into bytes and converting 2Bytes into UINT CODESYS Forge talk (Post)
Thank you for the reply. I got an error saying that MEM.PackBytesToWord(GVL.Actual_Speed_DUT_high,GVL.Actual_Speed_DUT_low) = u; is not a valid statement. Am I missing some library?
Last updated: 2023-12-08

Post by abjha1998 on Converting UINT into bytes and converting 2Bytes into UINT CODESYS Forge talk (Post)
Thank you for the reply. I got an error saying that MEM.PackBytesToWord(GVL.Actual_Speed_DUT_high,GVL.Actual_Speed_DUT_low) = u; is not a valid statement. Am I missing some library?
Last updated: 2023-12-08

Post by tvm on multiply gives negatives CODESYS Forge talk (Post)
you might have some slight inaccuracies with using a REAL. See here for an explanation: https://knowledge.ni.com/KnowledgeArticleDetails?id=kA00Z0000019ZSMSA2&l=en-US It might not matter, depends on how accurate you need it. I usually stick with integer types for something like this
Last updated: 2024-01-04

Post by julianramirez on Codesys Trend - setting Y axis minimum and maximum as variables - error CODESYS Forge talk (Post)
Hello Hannibal, I am using real vars and it works, however, if I update those vars in real time it doesnt quite change it on y axis, do you think it is because it is not an integer?
Last updated: 2026-05-21

Post by struccc on Problem Update new version Master ethercat CODESYS Forge talk (Post)
Hi, I had some issues as well migrating to the new version. What I have learnt: - Have to check all the libraries in the library manager, if they are the proper versions. - Some other parts of the application, maybe an old library referenced by another one can keep the old Ethercat libraries.... Use the "Placeholders" function on the library manager - See if there is a new version available of the slave "devices". Might just have to update them ... I had problems moving from 4.7 to with 4.8, especially with the 2nd adapter for redundancy - some devices failed to initialize properly.... So I have just downgraded those libraries now. P.
Last updated: 2024-10-28

Post by hardcoder on EtherCAT Mailbox Gateway CODESYS Forge talk (Post)
Hi all I found that in the last Ethercat master release (4.8.0.0) the Mailbox Gateway feature has been added. This would be useful for me to connect to a specific slave in my system, since its configuration software supports this type of gateway communication. Anyway I don't find usage information or examples. At the moment I tried to enable it in the ethercat master device settings and I configured with an IP address on the subnet of the ethercat adapter (i.e. ethercat nic configured with static ip 192.168.10.100 subnet 255.255.255.0, mailbox gateway configured to 192.168.10.30). I expected it would have responded to ping commands on the address but nothing happens. I am missing something?
Last updated: 2024-12-11

Post by pethun on Upgrade from codesys 3.5.19 to 3.5.20 CODESYS Forge talk (Post)
Hi We upgraded our ptoject from 3.5.19 to 3.5.20 but we get an error message in the latest version. We made our own trend function and its related to this we get error message: Trend_Menu Device: PLC Logic: Application: C0032: Cannot convert type 'RTS_SYSTIMEDATE(systimertc, 3.5.20.0 (system))' to type 'RTS_SYSTIMEDATE(systimertc, 3.5.17.0 (system))' The variables are defined as follow: start : SysTimeRtc.SYSTIMEDATE; end : SysTimeRtc.SYSTIMEDATE; The code that creates the error is the variable start and end IF xAssign THEN xAssign := FALSE; xPanEnable := FALSE; xZoomEnable := FALSE; drs.liFrom := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(start, 0 (us)); drs.liTo := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(end, 0 (us)); drs.m_itfDateRangeSelectorClient.SetCurrentRange(drs.liFrom, drs.liTo); END_IF I cant understand really what the error message means and what can be the cause of the error? It compiles fine in dthe older codesys 3.5.19. If anyone has some experience of this please help us out? We must upgrade due to the new licenses. Thanks
Last updated: 2024-04-20

Post by pethun on Upgrade from codesys 3.5.19 to 3.5.20 CODESYS Forge talk (Post)
Hi We upgraded our ptoject from 3.5.19 to 3.5.20 but we get an error message in the latest version. We made our own trend function and its related to this we get error message: Trend_Menu Device: PLC Logic: Application: C0032: Cannot convert type 'RTS_SYSTIMEDATE(systimertc, 3.5.20.0 (system))' to type 'RTS_SYSTIMEDATE(systimertc, 3.5.17.0 (system))' The variables are defined as follow: start : SysTimeRtc.SYSTIMEDATE; end : SysTimeRtc.SYSTIMEDATE; The code that creates the error is the variable start and end IF xAssign THEN xAssign := FALSE; xPanEnable := FALSE; xZoomEnable := FALSE; drs.liFrom := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(start, 0 (us)); drs.liTo := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(end, 0 (us)); drs.m_itfDateRangeSelectorClient.SetCurrentRange(drs.liFrom, drs.liTo); END_IF I cant understand really what the error message means and what can be the cause of the error? It compiles fine in dthe older codesys 3.5.19. If anyone has some experience of this please help us out? We must upgrade due to the new licenses. Thanks
Last updated: 2024-04-20

Post by williamcorlin on The future and proper use of CAA.BOLT, CAA.SEMA,.. CODESYS Forge talk (Post)
I've been moving in the same direction. For new libraries, I'm trying to minimize dependencies on APIs that look like they're being phased out unless the documentation explicitly recommends them. For synchronization primitives like CAA.BOLT and CAA.SEMA, I'd love to see an official replacement or abstraction layer that's guaranteed to remain stable across runtimes. That would make library development much cleaner than relying on platform-specific SysLib* implementations or conditional compilation everywhere. Until there's clearer guidance, my approach has been to isolate the locking mechanism behind a small wrapper interface. If CODESYS changes the recommended API in the future, only that wrapper needs to be updated instead of every library that uses it. It isn't perfect, but it's made maintenance much easier. https://forge.codesys.com/forge/talk/Engineering/thread/e6c20a740e/ https://zapgames.io/
Last updated: 2026-07-14

Post by dantheman on Connecting to SoftPLC Only Works By Turning Off Modbus Ethernet Port CODESYS Forge talk (Post)
I have an IPC with 2 ethernet ports and 1 Wi-Fi. I'm using ModbusTCP with the ethernet port named "enp2s0" connected to my remote I/O. This works fine when testing with Python and also works with CODESYS, but CODESYS is only able to scan for the Linux SoftPLC when I turn off the "enp2s0" interface. In other words, I can't get online with the IDE if I want my ModbusTCP comms to run with CODESYS. I'm using a Linux SoftPLC that has the following entry in CODESYSControl.cfg, hoping that this will allow me to connect with "enp1s0" or "wlp3s0", and leave "enp2s0" for field comms, but this seems to only make the source IP of the ModbusTCP comms to be bound to "enp2s0". That last point is the case only if I don't restart the service, but if I do restart the service after changing the config file, the source IP for the ModbusTCP comms then becomes the one for "enp1s0", which is very confusing to me: [SysSocket] Adapter.0.Name="enp2s0" Adapter.0.EnableSetIpAndMask=1 On the device list, I only have "enp2s0" given as the ethernet device that has the ModbusTCP master & slave beneath it, shown in Screenshot 1. On the IPC, I can ping the ModbusTCP client (remote I/O) from "enp2s0", and I've attached a Wireshark capture of running ModbusTCP from the CODESYS runtime as Screenshot 2, 3 & 4 (again, I can't get online when this is running, I have to turn off "enp2s0" to connect even when it's idle and I don't have an active TCP session with my Python tests). Like I explained above, the source IP is "enp1s0", even though the ethernet device on the project is "enp2s0". I was lucky to catch the red message that showed the source IP that makes sense to me (the one for "enp2s0"), but for some reason that connection was reset and I never saw that packet again. I've also tried this with Auto-reconnect both enabled & disabled, for the ModbusTCP Master device. I also have to turn off "enp1s0" and then turn it on, just so that I can have the ModbusTCP comms running from "enp2s0" (which is not intuitive in any way to me, I'd love some help understanding that phenomenon as well) in the weird manner that I've described above. I would be very appreciative if someone can help me figure out this pickle. I'd love to just connect to CODESYS through my Wi-Fi interface and leave my ethernet ports for field comms.
Last updated: 2024-08-01

Post by caspershes on Checking the device tree, not just the code: what else is worth a static check? CODESYS Forge talk (Post)
I spend most of my time reviewing other people's CODESYS projects before commissioning, and two kinds of defects keep showing up. Both compile clean. Both read fine. One is in the code. A pause timer whose own input gets cleared inside the branch the timer is supposed to gate: rampDelay(IN := run_2); IF NOT run_2 OR rampDelay.Q THEN run_1 := TRUE; run_2 := FALSE; // the timer's own input, cleared right here ELSE run_1 := FALSE; run_2 := FALSE; END_IF Next scan IN is FALSE, the timer resets, the condition is true again, and the second pump starts immediately. A 30-second ramp delay that actually lasts one task cycle. The setpoint is on the HMI, the operator turns it, and nothing changes. The other is not in the code at all. On one site the outdoor temperature read 0.0 Β°C in mild weather. The ST was correct, the variable was bound to the channel β€” but the channel's sensor type was left at "disabled", so nothing was ever digitised. Same class: a module with Disable_module = TRUE, or an analog output bound to a variable while its mode is off. Nothing in the project reports any of this, and the code review never looks there, because the configuration lives in the device tree and not in the POUs. That second class is what pushed me to parse the .export format rather than PLCopenXML alone β€” the export carries the device tree and the visualization, so "nothing ever writes this alarm variable" stops being a guess and becomes a fact you can check against the screen bindings. Three things about the format that cost me time, in case they save you some: the same device parameter can appear three times (template, internal copy, actual configuration) β€” the last occurrence is the one in effect; the enum value of a parameter is not in the parameter itself, it is one level down in BaseType/Value; a channel counts as used when a variable is bound to SensorValueN.SensorValue β€” InputStatus is a bad indicator, people deliberately bind it on spare inputs. So the question. What else would you check automatically, given both the code and the device tree? I am collecting rules from sites, not from style guides, and the configuration side feels largely unexplored. For what it is worth, the checker I use for this is free and runs offline (single exe, no install, nothing uploaded anywhere): https://github.com/caspershes/plc-lint β€” 43 rules at the moment, reads .export and PLCopenXML. Happy to add rules people here suggest.
Last updated: 2026-10-27

Post by micik on Changed Device of Rapberry Pi to MC SL instead of standard SL and cannot connect anymore CODESYS Forge talk (Post)
I have a test application and use Codesys Control for Rasp Pi SL. I made a mistake and updated device from MSL to MC SL, and now if I try to go online with archived version of the project I gett error message that IDs are different between project device and target device. Of course, I can go online if I changed device in the project from SL to MC SL, but I'm not sure that is correct. So I have two questions: 1. What is the actual difference between MC SL device and standard SL device when it comes to raspberry pi 4? 2. What change I need to do on raspberry pi4 side to change device back from MC SL to SL? Thank you!
Last updated: 2025-08-05

Post by kaotic2499 on Upgraded Raspberry 2b to Raspberry 5, Trends Broken? CODESYS Forge talk (Post)
Hello! Raspberry pi 2b just is getting a bit slow so decided to go for a Raspberry 5. Project is now upgraded to suit Pi 64 SL... so, now although everything runs perfectly... for some reason my trends will not save! its driving me nuts... ^Tried merging tasks with main program & trends ^tried re-prioritizing tasks (shifting 1 - 31 etc) ^Recreated the Trend Recording manager from scratch ^Tried swapping persisitant vars to GVL Retains then non-retains... (Project attached is as per before trial&error) Raspberry Pi 2b still runs "perfectly" though its very chuggy (Still saves the trends, note this is of an pretty much identical project minus the device compatibility) Does anyone have any advice to offer? project attached.... I feel it could be outside of Codesys itself causing the issues, but cant see/find anything on the internet to assist (or anyone else with the same problem as me...) Can attach project in another format (non archive) any assistance is much appreciated!
Last updated: 2025-10-19

Post by timvh on Dynamically enabling/disabling Modbus slave devices in runtime (performance issue with timeouts) CODESYS Forge talk (Post)
As far as I remember, the Reconfigure functionality doesn't work for Modbus devices. But... Each Modbus device in your device tree has a name. You can set the property "Enable" of this device to FALSE to stop communicating with it. So if one of your Modbus Slave devices name is "MbSlave1" in the device tree, then in your code you can set the Enable to FALSE to let it stop communicating: MbSlave1.Enable := FALSE; Please let us know if this worked on your controller with your application and your CODESYS version. Alternatively you could use the ModbusFB library. See: https://forge.codesys.com/prj/codesys-example/modbus/home/Home/
Last updated: 2025-08-13

Post by dhumphries on Codesys device configuration CODESYS Forge talk (Post)
First make sure the programming laptop and HMI are both on the same subnet. For example if the IP address of the HMI is 192.168.1.125 with a subnet mask 255.255.255.0 set your laptop IP to 192.168.1.120 with a subnet mask of 255.255.255.0. Make sure the cables are fully connected (the ethernet port on my programming laptop will click once but the cable is not fully seated.) Make sure the HMI is powered on, try pinging the device from a command prompt, if you can't ping the HMI there is a network issue that has to be resolved first.
Last updated: 2023-12-30

Post by andrax on Need help to get RS-485 signal in Cosesys . CODESYS Forge talk (Post)
You need an SPI driver for the board. If there is nothing on the net, you will have to write one yourself
Last updated: 2024-12-03

Post by eschwellinger on How to download dependencies packages for CODESYS Control for Raspberry Pi SL ? CODESYS Forge talk (Post)
with latest version? 4.16.0.0? Use the CODESYS Installer to download all required packages if you need an offline installation
Last updated: 2025-06-24

Post by alexanderraab on EtherCAT: How to change station-alias/ Slave address CODESYS Forge talk (Post)
Hello, i have the same situation to change the Station-Alias adress online by IEC-Code. Have someone an exsample for that?
Last updated: 2025-08-13

Post by gatto on Application-based license Modbus Channels CODESYS Forge talk (Post)
Hi Sandro, did you find any solution? I'm in version 3.5.20.40 and i have only one modbus channel. I don't want the problem to happen to me if I do an update one day.
Last updated: 2025-09-01

Post by matteodigani on Add library .dll to project codesys. CODESYS Forge talk (Post)
Is there a way to import an external library made with c++/CLI or python? then call the function that i have made inside the program POU ?
Last updated: 2025-10-15

Post by dkugler on Unable to load dynamic modules (Download failed: Application=Application) CODESYS Forge talk (Post)
Maybe shared memory is an opinion for you to give it a try: https://content.helpme-codesys.com/en/CODESYS%20Examples/_ex_cds_shared_memory_communication.html
Last updated: 2024-02-16