Post by romrot on MS SQL Compact cutting off Database name?
CODESYS Forge
talk
(Post)
I'm trying to use an fbMsSQL_compact function to read data from an SQL database. It works with some databases, but there is one database that I can't seem to get it to work on. It's set up the same as the other databases that I've tested with the only difference I see is that the name of the database is cut off in the status message. I'll get a message like "User: User logged out succesfully from database: 12345" But the whole name of the database is something like 1234567.
Last updated: 2025-08-21
Post by timvh on I want to show the current recipe name in the visualization screen
CODESYS Forge
talk
(Post)
Maybe the easiest solution for you is to add one STRING variable to your recipe and enter the name of the recipe in variable value. This is little bit double the work (naming the recipe and entering the value of the STRING variable), but in that case you always have the current value of the variable which you can read from the application and show in the visualization.
Last updated: 2025-09-04
Post by ofey on two different OPC clients with different privileges
CODESYS Forge
talk
(Post)
Hi! I have usually only connected one OPC client (our system) to an OPC server created in the codesys environment on a PLC. This OPC client has a lot of write privileges. A customer also want OPC access, but I want to restrict his access to only read certain values. Do you know if this is possible inside the single codesys runtime running on a controller?
Last updated: 2024-02-01
Post by esave on Softmotion Axis Controll
CODESYS Forge
talk
(Post)
Hello everybody I have two of these EtherCat CiA402 stepper driver from Leadshine: https://www.leadshine.com/product-detail/EM3E-556E.html I want to controll them. I already have implemented them in Codesys with Softmotion. I see the position, the velocity and the status word so I can read everything. See picture 1. But when I want to write something like MC_Power or MC_MoveAbsolut with the SM3_Basic library it wont work and with the MC_Reset POU it shows: "SMC_R_DRIVE_DOESNT_ANSWER". See picture 2. Can somebody help me? Thanks a lot esave
Last updated: 2024-05-24
Post by installwhat on C0077 on one machine but not another
CODESYS Forge
talk
(Post)
https://forge.codesys.com/forge/talk/Engineering/thread/92c913bf7c/ Solved by changing the ethercat master version after reading the thread linked above. I think I need to read up on why this happened. I understand that placeholders should point to a particular version for obvious reasons however what has occurred in this instance is different. The example project was released as a "project archive" but it seems to load differently based on what I've got installed in my repositories. I'm going to dig into that tomorrow but any advice is welcome.
Last updated: 2024-06-11
Post by steven-schalm on Github Actions CI/CD tasks - development topic
CODESYS Forge
talk
(Post)
hello kevinrn, I've been looking for a solution to the CI/CD issue for a long time. Briefly about me... I am 32 and software architect for Codesys V3 and fullstack dev for web (VueJS, NestJS) in a small company in Erfurt (Germany). https://www.rex-at.de/. Through my web part, we already have CI/CD running well via GitLab (YAML-based configuration file (.gitlab-ci.yml), which defines which pipelines and jobs are executed when certain events occur) with everything you know. Stages for npm packages - prepare (GitVersion, npm install or whatever) - build (vite, tsc or whatever) - testing (vitest, jest or whatever) - deploy (npm packages) And similar for monorepo's or backend services (in NestJS) as DockerImages. For Codesys we have been building an OOP framework for years (~50 libraries now), which is currently managed via SVN and a specially written Svn-Watcher (in Python) gets commits and runs and builds everything together and deploys it to an FTP server and network drive. Why do we still have SVN? Because we are unfortunately still tied to the safety integration of Codesys and can therefore only go to SP15 at most with our controller/Eckelmann. But soon there will be an update and there will be no more obstacles to using Git. Hence my questions: 1. the basic idea is to run a local Windows Runner on some machine? 2. install Codesys on the machine where the runner is running? 3. powershell & python scripts are then used to execute builds (compile, build, sign libraries) & deploys? 4. can the Github action also be used in GitLab? ChatGPT has already told me that it's not the same, but it doesn't hurt to ask. Do you have any ideas on this? Greetings :D
Last updated: 2024-08-20
Post by westcountryewe on ac_persistence not working when creating a Boot Application but works with a Direct Download to the PLC
CODESYS Forge
talk
(Post)
I am using V3.5 SP18 Patch 5. I have noticed that when I Create a Boot Application from CODESYS, and upload this to my PLC via a USB stick the AC_Persistence does not work and none of my values that are in my PersistenceChannel are retained. However, if I connect direct to my PLC and I perform a direct download of my CODESYS program, my values that are in my PersistenceChannel are retained and work as they should. This makes me wonder if there are files that are missing when a Boot Application is created. I have tried taking a backup of my configuration files after performing a direct download, which gives me the plclog.zip folder, and appears to have the ac_persistence folder present within the file structure, however when I replace the plclogic.zip with the same folder that was created when I created a Boot Application, it still does not work but I wonder whether this is because the ac_persistence folder isn't stored in the correct location for reading. The .app and .crc files are embedded within the plclogic.zip folder, which obviously when uploading need to be standalone files in the root directory of the USB, so the intention there is clearly to extract the .app and .crc files and put them into the correct location within the USB. I wonder if it could be the same for the ac_persistence folder? I have tried moving it to different locations but none have worked. Has anybody else discovered a fix for this? I know the short-term solution is to do a direct download to the PLC but there are some logistical reasons why this isn't neccesarily the best solution for us.
Last updated: 2024-02-27
Post by matthew on New Ladder Editor Issues
CODESYS Forge
talk
(Post)
Hi There, When using the new ladder editor there is no option for function blocks to Remove uncalled FB call parameters. I also see no update function block. When you double click the function block it no longer opens the function block. I also now get warnings if I insert FB call without a contact in front. Warning is: (Impl)): C0373: Expression or part of it has no effect I take it the new editor must work differently? The only reason for using new ladder editor is the ST execute/block editing is far better, If you have alot of text in the old ST execute the editor window is very small and when online it's even worse. The new ST block seems a lot better Thanks!
Last updated: 2023-10-10
Post by jmorit on CAM Table - Quadratic velocity ramp with jerk limitation
CODESYS Forge
talk
(Post)
Hello, I'm working on setup a CAM table by using the Codesys CAM Editor. My purpouse is to obtain a quadratic velocity ramp with jerk limitation motion profile, for which i define the accel/decel phases with Poly5 segment type, but the problem is that due to the fact i can "only" adjust until the acceleration, and the jerk is always setup to 0, and i cannot change the jerk values, i cannot achieve the desired results, as i need to generate jerk steps. Is there any way it can be achieved with the editor, or maybe by using PLC runtime code? Thank you in advance for your help BR, Jordi Morito
Last updated: 2023-12-02
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by jp23 on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
Hi all, I am attempting to use the Control Win V3 soft PLC to control a WAGO 750-315 remote I/O system via modbus RTU communication. I am struggling to connect to the device. I have been following this tutorial: https://www.youtube.com/watch?v=YlRfkESaNds I have setup my devices as shown in the images below. I have verified that my com port settings are correct as I am able to connect/control using modbus simulator software with these settings. I have also connected to a modbus master simulator program as instructed in the video, but the orange triangles will not go away. Additionally, I have updated my settings to 485 using the PLC shell. I have also set "always update variables" to enabled (1). Serial port, PCI-Bus, and modbus serial device status all show as "Not Running."
Last updated: 2024-08-26
Post by otbeka on CmpCrypto CryptoGenerateHash Not Outputting
CODESYS Forge
talk
(Post)
Unfortunately I noticed that, and tried: * using CryptoGeteAlgorithmByID within the function call * inputting the raw byte pointer as a testByte * instantiating the _hHash handle within the function body * using a different cryptoID or the raw DINT values from the RtsCryptoID DUT ... to no avail. The pReturn value is also set to 0, which would indicate that it is OK, right? This is odd given that the function is the same within the CryptoDemo example project here, just with a newer version. Is it possible that there is something wrong with the way my bytestring is being set up? I use the following DUTs here: TYPE MESSAGE : STRING(255); END_TYPE TYPE HASH_CODE : ARRAY[0..19] OF BYTE; END_TYPE
Last updated: 2024-09-06
Post by thn-power on How to change OPC NodeId IdentifierType
CODESYS Forge
talk
(Post)
Hi Yet another OPC UA question. When setting up a OPC server using "Communcation manager" (Symbol set and information model) in Codesys the NodeId is always given as "opaque" type. At least when browsing using UAExpert. Other standard OPC objects use numeric (or string) identifier, but for some reason my variables seems to get opaque/binary type. See attached photo. How can I change this? I can't see that this is a parameter in the CodesysControl.cfg. Can this be specified in the information model nodeset? And is it possible to specify the exact numeric or string NodeId for each instance? And on a related topic, is there a way to export the OPC server nodeId's with variable name so that it can be imported in a OPC Client? The .xml files in the project folder does not seem to contain the NodeId.
Last updated: 2024-09-20
Post by danielbeers on Automation Server + Pi Gateway + PLC w/ CAN
CODESYS Forge
talk
(Post)
Hello, I have a project using some EPEC PLC's. Some of them are programmable using Ethernet and some use CAN. We currently have a Raspberry Pi that is acting as a gateway to the Codesys Automation Server and is successfully working for the PLC's communicating over ethernet. I am trying to achieve a similar result for the PLC's that have only CAN access. I have PEAKCan drivers on the Pi, and can successfully send/receive messages. But the Gateway does not recognise the PLC when scanned from the Automation server online. Is there a library or service that exists to translate the CAN messaging, to the Edge Gateway, and be able to achieve remote access with the Automation Server? Or is this not possible without creating something custom? Cheers, Daniel
Last updated: 2024-09-22
Post by pistola on Error during Updating the Visualisation
CODESYS Forge
talk
(Post)
I've got a visualization I'm working on with some rectangles and lines. When I simulate the program I get an Error and Message in my message box, "Error during Updating the Visualisation:" and "Overflow error." Any ideas on how to fix this? I only have 70 elements total for this visualization. I am using absolute movement for a few of the elements, would this cause the issue? The visualization seemed fine before I added these movement elements, but there is only 7 that move, that doesn't seem like it should over load the system. I am currently testing using simulation so I'm not sure if that has an effect either. I tried looking in the codesys help manual and couldn't find anything referencing this.
Last updated: 2024-11-19
Post by rshabsh on Using Latch Variable in Alarm as input from text list
CODESYS Forge
talk
(Post)
I am currently utilizing Alarm Managerβs Latch Variable 1 to display additional information related to alarms. However, instead of mapping this latch variable to a fixed PLC variable, I would like to dynamically update its text content based on the selected language in the system. To achieve this, I am considering using a text list that corresponds to different languages rather than directly linking Latch Variable 1 to a PLC variable. This approach would allow the displayed alarm information to be automatically translated according to the active language setting. Could you please confirm if this method is feasible within the Alarm Manager configuration? Additionally, if there are specific steps or best practices to follow when implementing this functionality, I would appreciate any guidance you can provide. Looking forward to your insights.
Last updated: 2025-02-26
Post by pauloricardoss on Codesys Control Raspberry PI 4.10.0 - missing 'Update Raspberry PI' option
CODESYS Forge
talk
(Post)
I am having the same problem. 'Update Raspberry PI' disappeared from the 'Tools' menu. Using RaspberryPI 3B+, Codesys V3.5 Sp21 + RaspberryPI Package 4.16. I installed the package as Administrator, executed Codesys as Administrator I also tried to connect using the deploy (even with ssh and everything enabled on the RaspberryPi I received password denied). I used in the past the same equipment with Codesys V3.5 Sp18 and RaspberryPI Package 4.08, it was really easy. (I also did a brand new RaspbianOs installation to make sure that nothing affect the connection). Anyone, knows how to fix it? Thanks,
Last updated: 2025-06-13
Post by rafa on MODBUS TCP SERVER DONT AUTO-STARTUP
CODESYS Forge
talk
(Post)
Dear all, I have a project where I have two ModbusTCP communication drivers in the application. It's working normally until a power outage or the installation panel is restarted. As soon as the PLC CPU is restarted, the Ethernet port is OK, but the TCP Server displays an "UNDEFINED" error. I can't reset the error using the diagnostic confirmation or the "mbserver.xConfirmError" bit. I noticed that the error only appears in the "mbserver.byModbusError" memory and the description is "UNDEFINED." The "mbserver.xError" memory doesn't flag an error. When using the warm restart function and then START CPU, the devices return to normal operation. The following demonstration images; The main question is: How can I make devices boot automatically?
Last updated: 2025-07-15
Post by ranadheer on Implementation of IEC-104
CODESYS Forge
talk
(Post)
Hi Everyone, As we didn't have client for IEC - 104 - only server server is available , so because of that we are trying to make establish the communication between the external simulator as a Client and codesys itself as a server. We are looking for the variable behavior from CODESYS has to change according to the message triggered by the CLIENT (we are using simulator Application like Redisant). We are able to see the log data as the status of triggering the SCS from Client received to the Log data of the codesys device(attached screen shot of it) and in simulator panel we had set the details to trigger the data from Redisant to Codesys. Current Status: The project builds and runs successfully, but I need guidance on how to connect this to an external IEC-104 simulator for testing and visualization by using demo mode.
Last updated: 2025-10-14
Post by ranadheer on Implementation IEC-104
CODESYS Forge
talk
(Post)
Hi Everyone, As we didn't have client for IEC - 104 - only server server is available , so because of that we are trying to make establish the communication between the external simulator as a Client and codesys itself as a server. We are looking for the variable behavior from CODESYS has to change according to the message triggered by the CLIENT (we are using simulator Application like Redisant). We are able to see the log data as the status of triggering the SCS from Client received to the Log data of the codesys device(attached screen shot of it) and in simulator panel we had set the details to trigger the data from Redisant to Codesys. Current Status: The project builds and runs successfully, but I need guidance on how to connect this to an external IEC-104 simulator for testing and visualization by using demo mode.