Post by mozed on Signature verification faited fro the following package
CODESYS Forge
talk
(Post)
Good morning, I'm trying to open a project but codesys tells me that there are certain packages that I don't have and that I need to download them. Once the installation of the packages begins, it shows me a error that the signature of certain packages does not correspond to that coming from the accepted installation context. Do you have a solution to my problem please, it is very urgent in my work. Sincerely
Last updated: 2024-06-11
Post by adam on Get/Set I/O Address Mapping of DeviceObjects in python Script
CODESYS Forge
talk
(Post)
I want to cancel the automatic address allocation for all IO mappings. If I directly set the automatic_iec_address in class ScriptIoMapping to False, the address becomes None. So I reset manual_iec_address with itselfs value. It only work with the Input IOMapping . For output, it reports an error: "Invalid address: The channel type 'Output' requires address type '%Q'." I checked the description file ,both accessRight are total same. Does anyone know what causes this?
Last updated: 2025-11-14
Post by gseidel on MC_Phasing state explenation
CODESYS Forge
talk
(Post)
Hi kenth1973, MC_Phasing has been improved in recent versions. I would recommend to install the latest version of SoftMotion (4.20.1.0) and test whether the problem still exists, and if so, what the error identifier is. (Also check the PLC log in this case, it might contain additional information.) Setting the internal state of the FB is not recommended, it could lead to malfunction of the FB and unintended movements of the drive. Best regards, Georg
Last updated: 2025-11-28
Post by harryc on Soft Container License issue with ARM64 Linux
CODESYS Forge
talk
(Post)
hi @eschwellinger Thanks for the hint. This is what I get with "cmu -x" There is no Dongle. I think that I'm trying to install the soft container from CODESYS development system, where I have the licensed installed in the License Repository. The development system gives me the error when I try to install the Soft Container license. # cmu -x - CodeMeter Universal Support Tool. Version 8.20 of 2024-Sep-10 (Build 6539) for Linux/ARMHF 64-Bit Copyright (C) 2007-2024 by WIBU-SYSTEMS AG. All rights reserved. #
Last updated: 2025-12-10
Post by trusty-squire on SysProcessCreate2 on Linux runtime
CODESYS Forge
talk
(Post)
Hi, I'm trying to launch a continuously running python script from Codesys and monitor the script status inside the Codesys runtime (running on a Linux enviroment). For now I'm testing with the below to emulate a continuously running Python script: #test.py i = 0 while True: i += 1 I'm able to successfully run the script using SysProcessExecuteCommand2 (I can see the Python process running in the task manager). However, this "freezes" the Codesys execution of the task - it sits on that command and will not continue until the Python script ends. I've proven this works by using the task monitor to kill the process, then Codesys continues on happily through the task. What I want to do is use SysProcessCreate2 to set up the Python script as a background task and monitor the process using SysProcessGetState. This always results in the error "ERR_OPERATION_DENIED". I know that I'm able to execute commands (as above), so my config should be correct. Is SysProcessCreate2 functional on a Linux environment? Is there something in the config file I'm missing? Here's my "working" code that uses SysProcessExecuteCommand2: VAR bTest : BOOL; sCommand : STRING := '/usr/bin/python3 /var/opt/codesys/PlcLogic/Application/test.py'; refCommand : REFERENCE TO STRING REF= sCommand; sOutput : STRING; refOutput : REFERENCE TO STRING REF= sOutput; result : RTS_IEC_RESULT; END_VAR IF bTest THEN SysProcessExecuteCommand2( pszCommand:= refCommand, pszStdOut:= refOutput, udiStdOutLen:= SIZEOF(sOutput), pResult:= ADR(result) ); bTest:= FALSE; END_IF And here's the code that always results in the ERR_OPERATION_DENIED error: VAR bTest : BOOL; sApp : STRING := '/usr/bin/python3'; sCommand : STRING := '/var/opt/codesys/PlcLogic/Application/test.py'; refApp : REFERENCE TO STRING REF= sApp; refCommand : REFERENCE TO STRING REF= sCommand; hResult : SysProcess.RTS_IEC_RESULT; hHandle : SysProcess.RTS_IEC_HANDLE; END_VAR IF bTest THEN hHandle := SysProcessCreate2( pszApplication:= refApp, pszCommandLine:= refCommand, ulFlags:=SYSPROCESS_CREATEFLAG_HIDDEN, pResult:= ADR(hResult) ); bTest:= FALSE; END_IF Here's the relevant section from the config file at /etc/codesyscontrol/CODESYSControl.cfg: [SysProcess] Command=AllowAll Appreciate any support or ideas. Thanks!
Last updated: 2025-03-16
Post by egau on Hard shutdown: no code on device after power on
CODESYS Forge
talk
(Post)
Excellent merci pour ton aide!
Last updated: 2024-10-03
Post by eschwellinger on Licensing info not available.
CODESYS Forge
talk
(Post)
check on cli on your device 'cmu -x'
Last updated: 2024-03-19
Post by bernhardw on Probleme mit MC_HALT_SML und MC_STOP_SML
CODESYS Forge
talk
(Post)
Hallo … ich verwende: SoftMotionLight im Positions-Mode Ethercat-Bus Servoverstärker: Metronix BL4104-C . MC_HALT_SML funktioniert nicht zuverlässig (Achse fährt manchmal zu weit oder bis zum Softwareschalter) Ich habe festgestellt, dass intern beim Aufruf von Positions- auf Velocity-Mode umgeschaltet wird - und dann wird wahrscheinlich intern auf Drehzahl 0 abgeregelt. Kennt jemand dieses Problem? – der Wechsel der Betriebsart ja ist nicht verzögerungsfrei! MC_STOP_SML Der Baustein hat keinen Eingangsparameter "Deceleration" Die Achse stoppt und bleibt im Positions-Mode. Aber die Verzögerung ist nicht wie beschrieben: nicht "Objekt 6085h: quick_stop_deceleration" - sondern "Objekt 6084h: profile_deceleration" - aus zuvor aufgerufenem MC_MOVE_ABSOLUTE_SML Ich wäre dankbar für jeden Hinweis Gruß Bernhard
Last updated: 2024-08-05
Post by jonathan1321351 on IO-Link write parameters Ethernet/IP
CODESYS Forge
talk
(Post)
I want to read and write parameters of an IO-Link device using acyclic messages. I have a Cube67+ in Ethernet/IP, connected to an IO-Link master. In the datasheet, I can find the parameters required for the message (Service, Class, Instance, etc.). I see the function block "Set_attribute_single" in the "EthernetIP Services" library, but I'm not sure how to correctly send the index and sub-index for the IO-Link device. The class in the datasheet is 0x80 for the IO-Link Parameter Object, but it’s not present in the CPIClass enum. Is there another function block more suitable for configuring IO-Link devices? (similar to "iol_call" in PROFINET or what’s used in EtherCAT).
Last updated: 2024-09-02
Post by jonathan1321351 on IO-Link read/write parameters Ethernet/IP
CODESYS Forge
talk
(Post)
I want to read and write parameters of an IO-Link device using acyclic messages. I have a Cube67+ in Ethernet/IP, connected to an IO-Link master. In the datasheet, I can find the parameters required for the message (Service, Class, Instance, etc.). I see the function block "Set_attribute_single" in the "EthernetIP Services" library, but I'm not sure how to correctly send the index and sub-index for the IO-Link device. The class in the datasheet is 0x80 for the IO-Link Parameter Object, but it’s not present in the CPIClass enum. Is there another function block more suitable for configuring IO-Link devices? (similar to "iol_call" in PROFINET or what’s used in EtherCAT).
Last updated: 2024-09-04
Post by timvh on Modbus TCP & RTU with Control for Linux SL
CODESYS Forge
talk
(Post)
RS485 doesn't seem very logical to use in VPLC's in my opinion. I also don't know if this is supported.... But for TCP/IP, I think you still need to configure the Nic settings. See the attached png. In my case enp6s0. When changing this setting, restart the VPLC. What is really nice, is that you don't have to configure the IP address setting in Linux. By setting the Nic to a certain IP address in the CODESYS instance configuration, this is automatically done for you. I only tested this with EtherCAT, but I guess this works the same for Modbus TCP/IP.
Last updated: 2024-10-23
Post by trusty-squire on Read "Homed" status from EtherCAT drive
CODESYS Forge
talk
(Post)
@imdatatas, thanks for the info, I increased DSP402.uiHomingMinCycles to 10 and have a good feeling that will solve the issue of "false" homings. It's an intermittent issue so I'll report back once it's confirmed. @bruno-roth, also good info. According to my documentation, bit 14 is used to indicate the homed status. I did a test and the bit always stays true after it's been homed once (eg. even if I initiate a new homing procedure then hit the the e-stop mid homing), so I need to take that into consideration, but I can work with that. Thanks!
Last updated: 2025-01-09
Post by climblinne on OPC UA Method - How to wait for result?
CODESYS Forge
talk
(Post)
Hello, I am already able to run an OPC UA method in Codesys. Now my question, how can I interact with other tasks (e.g. read an SDO from EtherCAT and return it by the function)? The OPC UA method seems to be called only once (I tried to return BOOL or UINT values). Up to now I only found to do a while loop to wait for the result of the other task. Is there a better way to do it? Is this the way OPC UA functions should be used (for "not too long" function calls) or should I use another mechanism (method: Start, event: Finish, method: getResult)? Regards
Last updated: 2025-01-13
Post by trusty-squire on Strange problem with the ‘MC_SetPosition’ function
CODESYS Forge
talk
(Post)
How are the servo drives controlled? EtherCAT, step/dir pulses, other? Another thought is that - if it's step/dir pulse based control - the pulses from the PLC to the drive are getting missed/lost at high frequencies? If that's the case then there would be multiple troubleshooting steps/corrections that could be investigated. You could try to create a simplified program, with all the same parameters, that only has an MC_SetPosition FB you manually trigger and see if you are still getting the same results? When you manually control the motor directly from the servo drive software at the speeds you are calling for, does it move precisely to the target position?
Last updated: 2025-01-18
Post by ahofer on ETHERCAT EK1100 und EL8601-8411
CODESYS Forge
talk
(Post)
Liebe Forumsteilnehmer, hat jemand schon die Beckhoff-Multi-Klemme EL8601-8411 am EK1100 zusammen mit dem Raspberry Pi verwendet? Ich bin gerade am Testen und habe festgestellt - dass das mit dem Einstecken der Geräte nur teilweise funktioniert. - DI/DO und AI(U) lässt sich benutzen. - Den Zähler kann ich nicht testen, weil das Gerät nicht einsteckbar ist. Ich kann es zwar einstecken, aber dann läuft der Bus nicht. - Beim Encodereingang fehlt mir vermutlich ein geeigneter Funktionsbaustein um den zu betreiben. Gibts da evtl. irgendwo eine Bibliothek? Ich benutze CODESYS V3.5.19.70, habe die neuesten Gerätedateien (XML) von Beckhoff eingespielt und für den Raspberry Pi benutze ich die Version Codesys Control for Raspberry Pi 4.14. Für Antworten bedanke ich mich schon mal herzlich VG A. Hofer
Last updated: 2025-04-04
Post by ph0010421 on Stepper Drive with Ethercat
CODESYS Forge
talk
(Post)
Hello That's certainly CiA402. I'll attach a part of the manual for my servos, but the state diagram should be the same at yours. To be sure, get one from your manufacturer. Look at the bits in the StatusWord to see where you are in the diagram, then twiddle the bits in the ControlWord to get you to the next step. Then there are other bits in the StatusWord to tell you 'InPosition' and things like that. From the screenshot, as it mentions only 'PositionProfile' the driver will create the motion profile. So you need to put a target position in here - there should be profile velocity somewhere? Possibly, you need to write these with SDO's? At the minimum, you need to write a value to 0x6081, 0x6083 and 0x6084 (velocity, accel, decel)
Last updated: 2024-03-22
Post by lzml on Safety
CODESYS Forge
talk
(Post)
I have a problem with a project that uses EtherCAT Safety. The project is developed with CODESYS version 3.5.19.20, runtime 3.5.18.30, safety CPU EL6900 4.3.1.0, TCEL6900FBS 3.5.1.10, IODrvEL6900 4.3.1.0, IODrvEtherCAT 4.1.0.0. The safety project works correctly, but when I download the PLC project for modifications, the ESM objects are no longer aligned with the states inside the safety program. Specifically, inside the safety program, they are seen as true, while outside the safety program, the state is reported as false, but not for all ESMs, only some. I have already tried to completely redo the safety from scratch, but nothing has changed. Any solutions? Thanks
Last updated: 2024-05-24
Post by bjarne-pagaard on Communication between applications on same device/controller/runtime (Win RTE 3.5.20.20)
CODESYS Forge
talk
(Post)
Thanks for this - I have now been looking in to just having an extra (non-RTE) runtime on the same machine, as you suggest. I will probably proceed this way. Even though it still seems very odd to me, that variable exchange to a different runtime is easier than between applications on the same controller. There will be some fun with the licensing, it seems. Does anyone know if it is possible to specify which license container/specific license the runtime is going to use at runtime. Let's say I have two available licenses with different resources available, for example one license allows multicore and multiple EtherCAT channels, but not many visu tags (for the RTE). Another with less resources but a lot of visu tags (for the Visu controller). Let's say the program in one of the controllers could be fully licensed by either of the two available licenses, but picks the 'largest' first. A bit later, the larger application starts, but is left with the smaller license.. How can I make sure that the 2 runtimes select the right license at startup?
Last updated: 2024-10-01
Post by jeindhoven on Deploying to raspberry pi 5 hangs
CODESYS Forge
talk
(Post)
Hi CoDeSys support forum, hope that this is the correct place to ask this. Might be double as i am new to Codesys and dont know all terminology. I am trying to test Codesys with a virtual plc on a raspberry pi 5. Already figured that i need Tools -> Deploy Control SL, enter Communication parameters. Codesys says "Connected". Then tab "Deployment", there i select "CODESYS Control for Raspberri Pi SL" and "4.16.0.0 (all)". Click "Install" and the gui turns grey and unresponsive. The titlebar says "Untitled1.project - CODESYS (Not Responding)" as well. Restarting Codesys and checking shows no package was installed. How to deploy the runtime? Thank you in advance for your time. Edit: After some patience, an error showed up: "Error when sending ssh heartbeat: Session operation has timed out" "Error installing codesyscontrol" Any pointers to what remote command might have failed, or log of some sort, would be welcome. Software versions: Codesys version 3.5.21.10 Raspberry pi 5 (deployment machine): $ uname -a Linux raspberrypi 6.1.21-v8+ #1642 SMP PREEMPT Mon Apr 3 17:24:16 BST 2023 aarch64 GNU/Linux $ lsb_release -a No LSB modules are available. Distributor ID: Debian Description: Debian GNU/Linux 11 (bullseye) Release: 11 Codename: bullseye $ apt list --installed | grep openssh-server openssh-server/oldstable,now 1:8.4p1-5+deb11u3 arm64 Development machine: $ uname -a Linux 2B 6.1.0-35-amd64 #1 SMP PREEMPT_DYNAMIC Debian 6.1.137-1 (2025-05-07) x86_64 GNU/Linux $ lsb_release -a No LSB modules are available. Distributor ID: Debian Description: Debian GNU/Linux 12 (bookworm) Release: 12 Codename: bookworm VirtualBox Version 7.0.26 r168464 (Qt5.15.8) Virtual OS: Windows 10 Pro 64-bit (10.0, Build 19045) .NET version 4.0.30319.42000
Last updated: 2025-06-22
Content update through Data URI on Web Brower on Visualization Toolbox
CODESYS Forge
talk
(Thread)
Content update through Data URI on Web Brower on Visualization Toolbox
Last updated: 2024-07-30
Is there something on Codesys that's equivalent to Add On Instructions (AOI) in Studio 5000?
CODESYS Forge
talk
(Thread)
Is there something on Codesys that's equivalent to Add On Instructions (AOI) in Studio 5000?
Last updated: 2022-06-17
UniPi Neuron based on Raspberry Pi 3 and on board WiFi / Bluetooth
CODESYS Forge
talk
(Thread)
UniPi Neuron based on Raspberry Pi 3 and on board WiFi / Bluetooth
Last updated: 2018-02-08
Profinet Master on RPI3 with CodeSys Control - No live data on I/O
CODESYS Forge
talk
(Thread)
Profinet Master on RPI3 with CodeSys Control - No live data on I/O
Last updated: 2017-07-06
FTP client based on OSCAT, but works on 64 bit systems
CODESYS Forge
talk
(Thread)
FTP client based on OSCAT, but works on 64 bit systems
Last updated: 2023-08-14
Codesys OPC UA Server on Linux to OPC UA Server on Windows Communication
CODESYS Forge
talk
(Thread)
Codesys OPC UA Server on Linux to OPC UA Server on Windows Communication
Last updated: 2019-03-15
To search for an exact phrase, put it in quotes. Example: "getting started docs"
To exclude a word or phrase, put a dash in front of it. Example: docs -help
To search on specific fields, use these field names instead of a general text search. You can group with AND or OR.