Post by dekelec on The current baud rate could not be determined in CR0020 IFM with maintenance tool
CODESYS Forge
talk
(Post)
It could be a problem with the cable pinout on either side: 9 pin D-SUB connector (male) - PC side Pin Potential: 1 n.c. 2 RxD 3 TxD 4 n.c. 5 n.c. 6 GND 7 n.c. 8 n.c. 9 n.c. Shell Shield Check if TxD and RxD cross between pins 2 and 3 (what is the Recive signal/wire to one device it's a Transmit signal/wire for the othe device) or with COM port settings: Bits per second: 9600 Data bits: 8 Parity: None Stop bits: 1 Flow controll: None
Last updated: 2024-07-09
Post by umdee on Error when monitoring LAD programs
CODESYS Forge
talk
(Post)
I get the following error when monitoring my program (see attached screenshots): "Unhandled exception has occured in your application. If you click Continue, the application will ignore this error and attempt to continue. If you click Quit, the application will close immediately. Value cannot be null. Parameter name: source. And the details say: See the end of this message for details on invoking just-in-time (JIT) debugging instead of this dialog box. ** Exception Text ** System.ArgumentNullException: Value cannot be null. Parameter name: source at System.Linq.Enumerable.Any[TSource] (IEnumerable1 source, Func2 predicate) at _3S.CoDeSys.NWLEditor.NWLTextCell.OnPaintCellLayer(PaintEventArgs e) at _3S.CoDeSys.Controls.Controls.GfxEdControl.PaintCellCellLayer(PaintEventArgs e, GfxCell cell) at _3S.CoDeSys.Controls.Controls.GfxEdControl.PaintCellCellLayer(PaintEventArgs e, GfxCell cell) at _3S.CoDeSys.Controls.Controls.GfxEdControl.PaintCellCellLayer(PaintEventArgs e, GfxCell cell) at _3S.CoDeSys.Controls.Controls.GfxEdControl.OnPaint(PaintEventArgs e) at System.Windows.Forms.Control.PaintWithErrorHandling(PaintEventArgs e, Int16 layer) at System.Windows.Forms.Control.WmPaint(Message& m) at System.Windows.Forms.Control.WndProc(Message& m) at System.Windows.Forms.UserControl.WndProc(Message& m) at _3S.CoDeSys.Controls.Controls.GfxEdControl.WndProc(Message& m) at System.Windows.Forms.NativeWindow.Callback(IntPtr hWnd, Int32 msg, IntPtr wparam, IntPtr lparam) ** Loaded Assemblies ** (3000 lines of assemblies) ** JIT Debugging ** To enable just-in-time (JIT) debugging, the .config file for this application or computer (machine.config) must have the jitDebugging value set in the system.windows.forms section. The application must also be compiled with debugging enabled. For example: <configuration> <system.windows.forms jitdebugging="true"> </system.windows.forms></configuration> When JIT debugging is enabled, any unhandled exception will be sent to the JIT debugger registered on the computer rather than be handled by this dialog box The windows show red X's where the networks should be. Any advice on how to fix this? Additional Information PLC used: Wago 750-8212, Firmware FW26 Startup profile: CODESYS V3.5 SP19 Patch 5 OS version: Microsoft Windows NT 10.0.22631.0 .NET version: 4.0.30319.42000 Full Version info attached as .txt
Last updated: 2024-03-17
Post by martinlithlith on Mux I2C
CODESYS Forge
talk
(Post)
Hi! I´ll try to get this thread going again as i´m having simliar problems. Right now i get a red triangle on my connected devices (i´m testing with a BME280 sensor and a PCA9685 resvo driver). The TCA9548 have the green symbol beside it. On the "red" devices i get that the bus is not running. I have tried to either run it using the parent bus cycle setting or creating a new freewheeling task prio 1 but nothing helps. I have compared my settings to the settings from the example from the MUX package and i have read (i think) every thread in forge that could be of interest. EDIT: The ic2detect only shows the mux (70-70) and the servo drive (70-76) so i´ll look in to if i managed to burn the 280-sensor while soldering). Another question regarding the 280 sensor. I have a sensor GY-BM E/P 280 that should record humidity and temperatur. Could this be a problem with the library? Does anyone have an idea of what i might be doing wrong? I have some experience from Codesys but not much so this could be an easy one. All suggestions are welcome. I tried to upload the project archive but it did not work. Should i upload the export or how could i show you my horrible project? Best, Martin
Last updated: 2023-10-22
Post by mtho on JSON Utilities - JSON file written with invalid structure
CODESYS Forge
talk
(Post)
I'm using the JSON Utilities SL library to write configurations in my program to a file. I'm generating the JSON data using the builder function block and all appears to work correctly. When I write the jsondata to file, I'm finding that some of the JSON elements are not being written in the right location in the file. Rather than writing they keys under the parent object, they get written outside the root JSON object at the end of the file. If I then try to read the file back into the program, I get an invalid_structure error. I don't get any errors when populating the JSON data or when writing the file. I attached an example of the JSON writer output. The problems begin with key P200. Each P200 should go under MBR1 through MBR3. Among the rest of the keys, they are supposed to be under different parent objects. I am using default values for wsLineBreak and encoding.
Last updated: 2024-03-06
Post by mubeta on Some 'pathetic' errors in SoftMotion program
CODESYS Forge
talk
(Post)
Hello everyone, I have a very simple program for the process, but it's driving me crazy and I can't see the problems I'm left with: Short topological description: Dual Core Berghof controller with softmotion runtime version 3.5.19.30; Two axes with servodrive on canopen bus, clocked distributed from master; Ethercat I/O node; 2 ms ethercat task, 2 ms canopen bus cycle time; I/O objects of the canopen master and canopen drives connected to the ethercat task cycle; Problem 1: Two separate programs each manage their own axis and drive, with separate state machines. A first axis moves primarily in velocity, except having to position itself absolutely at a predetermined point at the end of the job; the second axis, on the other hand, is a paper unwinder that changes, for each job cycle, from actions in absolute, relative, and cam displacement with the master axis. Well, the state machine of both axes was written in such a way as to call running the useful FB and change it on state change in this way: CASE i_stateMachine OF 0: o_Power(Enable := TRUE, bRegulatorOn := FALSE, bDriveStart := FALSE, Axis := o_PaperUnwinderAxis); o_MoveAbs(Execute := FALSE, Axis := o_PaperUnwinderAxis); o_MoveRel(Execute := FALSE, Axis := o_PaperUnwinderAxis); o_CamSelect(Execute := FALSE, Master := o_MachineAxis, Slave := o_PaperUnwinderAxis, CamTable := cam_PaperUnwinder); o_CamIn(Execute := FALSE, Master := MachineEncoder, Slave := o_PaperUnwinderAxis); o_CamOut(Execute := FALSE, Slave := o_PaperUnwinderAxis); o_SetPosition(Execute := FALSE, Axis := o_PaperUnwinderAxis); IF ... THEN i_StateMachine := 10; END_IF; 10: o_Power( Enable := TRUE, bRegulatorOn := TRUE, bDriveStart := TRUE, Axis := o_PaperUnwinderAxis ); IF o_Power.Status THEN i_StateMachine := 20; END_IF; 20: (* Avanzamento carta *) o_MoveAbs( Execute := TRUE, Position := o_Somewhere, Velocity := 25.0, Acceleration := 3666.7, Deceleration := 3666.7, Jerk := 48000.0, Direction := MC_DIRECTION.positive, Axis := o_PaperUnwinderAxis ); IF o_MoveAbs.Done THEN o_MoveAbs(Execute := FALSE, Axis := o_PaperUnwinderAxis); i_StateMachine := 30; END_IF 30: d_HomingPosition := ...; o_SetPosition( Execute := TRUE, Position := d_HomingPosition, Mode := FALSE, Axis := o_PaperUnwinderAxis ); (* ... *) IF o_SetPosition.Done = TRUE THEN o_SetPosition(Execute := FALSE, Axis := o_PaperUnwinderAxis ); o_LogServer.Append(sMessage := '...', lscClass := LOGSERVER_CLASS.ALWAYS, sdt := o_CommonsMgrData.systime.sdtLocal); i_StateMachine := 40; END_IF; 50: ... The code above is a sketchy example of what I wanted to write. But it gives me a spot problem: in some, the state change results in a drive error, which is unrecoverable except with a reinitialization via SM3_ReinitDrive(). Things are improved a little if in the program I always run the call of all softmotion blocks in this way: o_Power(Axis := o_PaperUnwinderAxis); o_Jog(Axis := o_PaperUnwinderAxis); o_Halt(Axis := o_PaperUnwinderAxis); o_MoveAbs(Axis := o_PaperUnwinderAxis); o_MoveRel(Axis := o_PaperUnwinderAxis); o_CamIn(Master := MachineEncoder, Slave := o_PaperUnwinderAxis); o_CamOut(Slave := o_PaperUnwinderAxis); If I don't execute all the calls of all the motion FBs used, when exchanging machine state often (but not always), the axis goes into error with event id THE_FB_WASNT_CALL... Done a little diagnostics it seems that the FBs return the bDone, before they are completely terminated. I tried doing the machine state exchange not with the bDone bit of the FBs, but with the 'standstill' state of the axis. It didn't seem to change anything. Problem 2: During the use SM3_ReinitDrive() I get the erro in the log: "NetID 0: SDO read error for object 16#607C..." Assuming that the device involved it's one of the two servodrive, (no others device are present in the network), I don't found any object 0x607C in the 'possible object list in/out' of the two drive, and I don't understand where this object can be listed. So any ideas and suggestions regarding these two issues will be very, very welcome. If you need the source project, I am willing to send it.
Last updated: 2024-07-17
Post by damian177 on Codesys V3.5 + Pixtend v1.3 + RaspberryPi
CODESYS Forge
talk
(Post)
Hi, I use Pixtend v1.3 with my RaspberryPi with Codesys V3.5 SP15 Patch1. Actually in my project I used two packages: - CODESYS Contro for Raspberry PI 3.5.15.10 - PiXtend for CODESYS 1.3.8.0 Now I would like to extend my project about the IIot Libraries SL package, I installed them. Next I added SMS_Service_SL 1.0.0.8 version library and I have problem with compile my project because I get error: [ERROR] PiXtend_DemoProject_q: Library Manager [Device: PLC Logic: Application]: Could not open library '#CAADTUtil'. (Reason: The placeholder library 'CAADTUtil' could not be resolved.) Any have idea what can I do to properly add SMS library to my project?
Last updated: 2023-09-26
Post by dhumphries on Ethernet/IP Issue
CODESYS Forge
talk
(Post)
Make sure the O->T and T->O bytes required by the remote device match the configuration in Codesys. Most of the EDS files I've imported have not worked by default. See the attached images for the connections and assemblies tabs. Note that the connections are in Bytes and the assemblies are in bits, you have to have enough bits to equal the bytes. Either mismatch will give a red/orange triangle. Page 343 of the manual (assuming the STF10-IP is an applied motion microstep driver) has some recommended connection settings, you should be able to confirm the input and output bits somehow, some devices have a web GUI, some require a software tool.
Last updated: 2024-02-03
Post by sumit on Not able to see input data coming from eip adapter on codesys
CODESYS Forge
talk
(Post)
dhumphries, I changed the datatype this time from BYTE to USINT (because that's what my adapter is sending: array of uint8_t). The text "New Help String" you saw in previous screenshots is just the description of the input/s (it can be anything). I also looked into the logs (see attached) for that ! sign next to the device, I found that connection is being timeout. I tried some suggestions from online such as increase the RPI but still got connection timeout issue, also by changing the datatype, I still don't see incoming data from the adapter, although its visible on wireshark. thanks,
Last updated: 2024-03-07
Post by kronlundo on Licensing info not available (WAGO PFC200 + Codesys V3)
CODESYS Forge
talk
(Post)
Hi! We're using a WAGO PFC200 for several projects towards the energy sector, and recently upgraded to CODESYS V3. We have the "IEC 60870-5-104 Server" package in a test program, and it works well with the package in DEMO mode. However, when we acquired a license for the "IEC 60870-5-104 Server" package and tried to add the license on the PFC200 through the license manager, we get an error (see attached file). It seems like there is no CmContainer on the device, does anyone have an idea on how to fix this? We've also contacted WAGO on this issue a while back with no feedback yet.
Last updated: 2024-06-10
Post by jnoyau on Visualisaion while in simulation
CODESYS Forge
talk
(Post)
Hi all, Im new to Codesys 3.5, and am in the process fo making a visualisation i'd eventually export towards a Wago device. The issue I'm having currently is that when I compile and connect to the simulated program, my simulation won't launch. On the Visualisation tab, all I get is a text message (where previously there was my prepared visualisation) that says "The visualisation awaits a connection. Start the application" One thing to note: I work with Codesys 3.5 in french, so this is a rough translation. And a second: I'm not getting any errors nor warnings about the visualisation tab itself upon compiling Is there a step i'm missing after launching my simulation? Or would it be some really specific issue caused by the way I've set up my program? Thanks, J
Last updated: 2024-07-31
Post by timvh on Communication between applications on same device/controller/runtime (Win RTE 3.5.20.20)
CODESYS Forge
talk
(Post)
If you have a Windows system (RTE), then why not run the CODESYS HMI as separate controller. This could easily be moved to another PC if required. In the HMI you could also still use the Symbolic Var access as part of the Data Source Manager, although maybe OPC is the preferred way to make it more future proof. Or what about the Remote Target Visu. Then you can reduce the load of the main controller, while still only having to create one application including Visualization. This is now also supported for Linux systems. See: https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_target_visu_for_linux.html https://content.helpme-codesys.com/en/CODESYS%20Visualization/_visu_execute_remote_target_visu.html
Last updated: 2024-09-28
Post by pernockham on Linking to IO during runtime with hot swap?
CODESYS Forge
talk
(Post)
I have a project where a single PLC shall control multiple nodes (up to 10 units?) with IO connected through profinet. Ideally each node should be identical however with time I see situations were different setups/configurations will be used. Codesys PLC (GVLs) |Profinet | |--PNIO-node-1--| | | AIO, | | DIO, | | CNT etc. | |--PNIO-node-2--| | | AIO, | | DIO, | | CNT etc. Ideally I think of a configuration through yaml/xml-files (the assignment/linking of the profinet nodes towards GVL-variables in the PLC as well as scaling, channel configration etc.). Would be grateful if someone could suggest library/-ies that can handle the following: - Verify what IO is connected to a device/node. - Hot-swap/assign link for IO towards GVLs, either automatically or through a HMI.
Last updated: 2024-10-11
Post by thn-power on Updating OPC UA Core Nodeset on PLS
CODESYS Forge
talk
(Post)
Hi After much trail and error I think I found the root cause to my OPC UA problem. The problem is that I cannot manage to build and download a program with a a custom OPC UA Information model. We use a Weidmueller WL2000 PLS, but the problem also exsist on the Win V3 PLC. Our custom information model is based on the latest versions of the OPC UA Core Nodeset v 1.05.03 (2023-09-20) and UA/DI nodeset 1.04.0 (2022-11-03) Those nodesets are installed in the Codesys Information Model Repository (3.5.19.6) However, when trying to build I get the following error. [ERROR] Untitled1: Communication Manager [Device: PLC Logic: Application]: The information model http://opcfoundation.org/UA/ is required by http://bos.org/ with a minimal publication date from 15.12.2023 but the device has only a model from 15.09.2021 installed. Probably the information model from 15.09.2021 is missing in the information model repository. [ERROR] Untitled1: Communication Manager [Device: PLC Logic: Application]: The information model http://opcfoundation.org/UA/DI/ is required by http://bos.org/ with a minimal publication date from 03.11.2022 but the device has only a model from 09.03.2021 installed. Probably the information model from 09.03.2021 is missing in the information model repository. Build complete -- 2 errors, 1 warnings : No download possible I think the problem is that the UA Core nodeset is implemented in the PLC firmware (at least that in Siemens S7), and that only includes the "old" nodeset from 2021-09-21 etc. So the question is, how (or if?) can I transfer the new nodeset to the PLS? I have created separate Information models under Communication manager with the newer code nodesets (UA and DI). But it seems that the compiler does not recognize them being excising, neither in the Codesys IDE or on the PLC. Would have guessed that this is a common issue, sine many manufacturers use the latest versions of the OPC UA standard, and that it would be a solution to the problem.
Last updated: 2024-09-20
Post by george32 on CSV file and string manipulation.
CODESYS Forge
talk
(Post)
Dear folks, I think I have a rather simple question but I could not find the right answer to my question: I have made with Excel a CSV file where I would like to have some general data regarding my program variables. I have made an program what let me read the file. The string I am currently get is at follows: 'IP_Adres;192.168.45.12$R$NPort_number;2000$R$NCycle_time;43$R$NStart_Standard_IO;20$R$N' Now I want to split the string in multiple part, which I later would connect to the right variable. By Google and experimenting I have reached to the following code for the first part of the splitting proces: // Splitting the BOM of the string: Received_string := FileReadString; IF LEFT(STR:=New_string,3)= '' THEN Received_string_without_BOM :=RIGHT(STR:= Received_string,SIZE:= (LEN(STR:= Received_string))-3); END_IF //Splitting the remaining string in part for later declaration. WHILE index = 0 DO index_split_part := FIND(STR1:= Received_string_without_BOM,STR2:= '$R$N'); Part_of_String[index]:=LEFT(STR:=Received_string_without_BOM, SIZE:= index_split_part); index := index + 1; END_WHILE However in the splitting proces I could not understand what is really happening. I understand that the Find() function returns the first value the $R$N in the Received_string_without_BOM. This would mean that the index_split_part := 23 I|P| _ |A |d|r|e|s|;|1_|9 |2 |. |1 |6 |8 |. |4 |5 |. |1 |2 |$ |R |$ |N |P | 1|2| 3 |4 |5|6|7|0|9|10|11|12|13|14|15|16|17|18|19|20|21|22|23|24|25|26|27| So the next part is to read the first 23 characters of the Received_string_without_BOM with the LEFT() function. I expected that the outcome the following was: 'IP_Adres;192.168.45.12$'. However the outcome is: 'IP_Adres;192.168.45.12$R'. I do not understand where the R after the $ sign comes from, because its place is 24 so it would not be added to the part_of the_string[index]. If I hard coded value 24 for the size it gives me the following return: 'IP_Adres;192.168.45.12$R$N'. I would expect everything till the R but the code adds the $N also to the string. I hope someone could explain to my what I am seeing wrong in my point of view? With kind regards, George
Last updated: 2024-09-27
Post by sturmghost on Visualization using methods and cyclic ST-calls
CODESYS Forge
talk
(Post)
Im looking for a way to implement ST-code into the visualization element without creating a helper POU or method in my device/application tree. Like visualization properties are evaluated at each VISU_TASK cycle I want to be able to create own ST code which interacts with the visualization interface variables. To be more specific I want to have a property which executes user defined ST-code at each VISU_TASK cycle exactly like its already possible for Input Configuration on various mouse and dialog events. Also a property for initialization (so only executed once) and a timed property would be nice. With the situation right now I'll have to create a POU function which handles the ST-code and misuse a property, like the text variable, to execute this POU function at each VISU_TASK cycle. Or does it exist and I don't know it?
Last updated: 2023-10-02
Post by paulg on RasPi CAA Serial example - unexpected behavior during debug
CODESYS Forge
talk
(Post)
I've trimmed down the CAA Serial Codesys example to only listen on one port but, when stepping through the Case structure in debug mode, it jumps out of the structure during a specific point in every scan (I'll point it out below after describing the setup and listing the code). I'm using a Pi 4 Model B, and I have an Arduino Nano Every plugged in via USB which is streaming the following serial message at 1 Hz: Time since opening connection: 1 s Time since opening connection: 2 s ...and so on. The Pi shows the Nano at /dev/ttyACM0 so I edited CODESYSControl_User.cfg to read: Linux.Devicefile=/dev/ttyACM The code in my PLC_PRG is (ignore some of the comments, I hadn't deleted them out from the original example): PROGRAM PLC_PRG VAR xStartTest : BOOL:= TRUE; iState : INT; xTestDone : BOOL;(* True, when the test was done succesfully *) (* Settings to communicate with the COM Port *) aCom1Params : ARRAY [1..7] OF COM.PARAMETER; como1 : COM.Open; comc1 : COM.Close; comw1 : COM.Write; comr1 : COM.Read; //sWrite : STRING := 'Test String!'; sRead : STRING(25); szRead : CAA.SIZE; xCom1OpenError : BOOL; xCom1CloseError : BOOL; xCom1WriteError : BOOL; xCom1ReadError : BOOL; END_VAR //This example shows the communication of two COM Ports with each other. //The first one writes a string of characters, which is read by the second one. //After successful execution, the two COM Ports are closed and the test is done. IF xStartTest THEN CASE iState OF 0: //The parameters are set for the COM Port aCom1Params[1].udiParameterId := COM.CAA_Parameter_Constants.udiPort; aCom1Params[1].udiValue := 1; // the correct Port should be adapted aCom1Params[2].udiParameterId := COM.CAA_Parameter_Constants.udiBaudrate; aCom1Params[2].udiValue := 115200; aCom1Params[3].udiParameterId := COM.CAA_Parameter_Constants.udiParity; aCom1Params[3].udiValue := INT_TO_UDINT(COM.PARITY.NONE); aCom1Params[4].udiParameterId := COM.CAA_Parameter_Constants.udiStopBits; aCom1Params[4].udiValue := INT_TO_UDINT(COM.STOPBIT.ONESTOPBIT); aCom1Params[5].udiParameterId := COM.CAA_Parameter_Constants.udiTimeout; aCom1Params[5].udiValue := 0; aCom1Params[6].udiParameterId := COM.CAA_Parameter_Constants.udiByteSize; aCom1Params[6].udiValue := 8; aCom1Params[7].udiParameterId := COM.CAA_Parameter_Constants.udiBinary; aCom1Params[7].udiValue := 0; //The first Port is opened with the given parameters como1(xExecute := TRUE, usiListLength:=SIZEOF(aCom1Params)/SIZEOF(COM.PARAMETER),pParameterList:= ADR(aCom1Params)); IF como1.xError THEN xCom1OpenError := TRUE; iState := 1000; END_IF //After a successful opening, the next state is reached IF como1.xDone THEN iState := 15; END_IF 15: // the reading process is started comr1(xExecute := TRUE,hCom:= como1.hCom, pBuffer:= ADR(sRead), szBuffer:= SIZEOF(sRead)); IF comr1.xError THEN xCom1ReadError := TRUE; END_IF //After completion the size of the written bytes are saved IF comr1.xDone OR comr1.xError THEN szRead := comr1.szSize; iState := 20; END_IF 20: // If everything was successful the ports are closed and the handles are released comc1(xExecute := TRUE,hCom:= como1.hCom); IF comc1.xError THEN xCom1CloseError := TRUE; END_IF IF comc1.xDone OR comc1.xError THEN iState := 25; END_IF 25: // The first port is closed and the used handle released xTestDone := TRUE; xStartTest := FALSE; iState := 0; como1(xExecute := FALSE); comw1(xExecute := FALSE); comc1(xExecute := FALSE); ELSE iState := 0; END_CASE END_IF I realize as I write this that the .udiPort should be 0 and not 1, but that shouldn't be causing the issue I'm seeing. I'm forcing xStartTest:=TRUE every scan so that I can step into each line and observe what's happening. What I see is that the port parameters are set and the port is opened with no errors, but the code jumps out of the case structure to the last line every time it reaches (and I step into) the iState:=15 line (at the end of the iState:=0 block). So every scan cycle it goes through the block for iState=0 and jumps out at the same spot. I'm a little new to PLC programming so I may be misunderstanding the flow, but shouldn't this case structure keep moving down in the same scan? If it only handles one case per scan, why doesn't the value of iState persist? Thanks! Update: I restarted the Codesys control today and I was then able to see an error for como1.eError of "WRONG_PARAMETER". I tried doing some digging and another post made me think I should add another line to CODESYSControl_User.cfg, so I now have: [SysCom] Linux.Devicefile=/dev/ttyACM portnum := COM.SysCom.SYS_COMPORT1 So now when I set .udiPort to 1, I get "NO_ERROR" but I also don't read anything from the port (i.e. szRead = 0 always). If I try setting the port to 0 (which I'm confused about, because I added a COMPORT1 line but the device shows on the Pi as ACM0), I get the "WRONG_PARAMETER" error again. Is there an easier way to troubleshoot the Pi and view what ports the Codesys runtime is actually able to see while the Pi is running?
Last updated: 2024-06-06
Post by timvh on Is it possible to use debug functions such as Step Execution while the PLC ladder is in Running?
CODESYS Forge
talk
(Post)
Yes, it is possible to set breakpoints and use step into / step over (also in Ladder diagram). Yes, the PLC will actually stop, so be carefull with this. How a PLC works is that at the start of the execution of the Task, the Inputs are read, then the code is being executed and then the outputs are written. So if you set a breakpoint, you will not see your analog inputs changing, because the task cycle is interrupted and the inputs and outputs are not refreshed. For detailed information, see: https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_using_breakpoints.html
Last updated: 2024-01-16
Post by opineiro on How to manage variable types larger than 64 bits - Ethernet/IP
CODESYS Forge
talk
(Post)
Hi there, I have a Keyence bar code reader connected to my plc through Ethernet/IP. The Bar code is 20 digits long (like 30100790020493036016), the scanner reads it correctly (I can verify that through the keyence software) but when it sends it through ETH/IP, it doesn't fit into a 64 bit variable and it trunks the data.(I've tried ULINT and LWord without success). When I loaded the EDS file, the read variable was defined as a byte with 128 bits length, which is quite strange for me. (see attached picture) How do I manage this variable? Thanks!
Last updated: 2024-09-23
Post by timvh on Modbus TCP & RTU with Control for Linux SL
CODESYS Forge
talk
(Post)
It seems you have 2 network interfaces. Did you try eth1? Did you already configure the IP address for this interface in Linux? If yes, then maybe undo this. - or only set eth0 in the Nic configuration without anything else (so no IP address, because this is already set in Linux). For more information about the Nic settings, see (probably already read it?): https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_obj_deploy_control_sl_configuration.html PS, if you only want to run CODESYS Control SL, you don't necessarily need the Virtual PLC variant. You could also install and run the CODESYS Control SL Runtime in the Host operating system. This way you should also be able to access the serial port and directly access all ethernet ports. Maybe this is easier?
Last updated: 2024-10-23
Post by k2saki on CNC / G-Code streaming processing ( to start quickly in long G-Code File )
CODESYS Forge
talk
(Post)
Is it possible like G-Code streaming processing (like FANUC or SIEMENS DNC Function )? Or Does anyone know the tips for CODESYS Motion to start moving long Long G-Code File quickly? I have to wait long time after "Start" button to start moving, I have to wait finishing interpreting whole G-Code file, ( and I have to prepare huge buffer to store. ) Now, I'm working on my CNC Project using SMC_ReadNCFile2, and SMC_NcInterpreter to preprocess G-Code. I tried to set SMC_Interpolator.xExecute to true to Start while after SMC_NcInterpreter processed more 50-line of G-Code, but that not worked, I had to wait SMC_NcInterpreter processed all lines to start SMC_Interpolator. G-Code have about 2000 lines of XY of G01 (or more over.. ) of short segment that a CAM software has exploded from NURBS Curve.
Last updated: 2024-05-03
Post by vformanek on OPCUA Datasource, can not login...
CODESYS Forge
talk
(Post)
Hello? I have a problem with datasource... I am trying to connect to a OPCUA server. I create a datasource, but I can not login into it. I need to use login credentials to login... Everything works fine in UAExpert, but in codesys I cant seem to get in properly using the login credentials... I have tried to configure the datasource initializer but seem to keep failing... Do I need to call it somewhere ? Will the find endpoints work with this configured to store my password ? !
Last updated: 2023-11-20
Post by bagusd on gateway problem
CODESYS Forge
talk
(Post)
hello, I have a problem with the gateway not being able to connect to the plc, does anyone know why the gateway is difficult to connect to the plc? even though the lan cable has been connected to the plc and codesys gateway V3 has been restarted, thank you
Last updated: 2023-08-25
Post by davidredondo on Send file from codesys to...... ftp, cloud, etc
CODESYS Forge
talk
(Post)
Hi all, I am also looking for a solution to transfer a csv file from ifm HMI-PLC to some cloud and finally to node-red, for example. Do any of you advise me how to do it? Thanks
Last updated: 2023-11-08
Post by fransh on WAGO PFC200 FW25 unable to connect
CODESYS Forge
talk
(Post)
Hi I set up my WAGO PFC200 controller and am unable to connect to the processor. Gateway is set to local host. I can connect to the unit with the WAGO Web Based management but not with Codesys V3.5 SP18.5. Any suggestion?
Last updated: 2023-12-09
Post by hclai on Table Content with Multilanguage
CODESYS Forge
talk
(Post)
I have an data structure which intend to list in a table and let user to add the content to the table. How can we able to support for displaying different language in the content of the table? which is dynamic to the user input.
Last updated: 2024-01-10
To search for an exact phrase, put it in quotes. Example: "getting started docs"
To exclude a word or phrase, put a dash in front of it. Example: docs -help
To search on specific fields, use these field names instead of a general text search. You can group with AND
or OR
.