Post by valenting on Problem with Licenced Software Metrics
CODESYS Forge
talk
(Post)
Hi, When I try to install my codesys program with the new application-based licensing, I have an error "it exceeds the scope of the license agreement. See Device > Licensed Software Metrics" In the Licensed Software Metrics section, I see a code size < 3MB and less than 2700 variables in visualiaztions. I'm using a license "Control Basic L" with "Codesys Visualization L" option, so it should be enough with these metrics. What can I do ?
Last updated: 2024-04-22
Post by george32 on TCP Server
CODESYS Forge
talk
(Post)
Thank you for your advice Rinie, I have tried to follow this example but found one problem.When I disconnect with Hercules the system does not acknowledge the lost of its connection this could result in critical errors. Because of this error I am trying to implement the Syssocket library. With this library I am having a problem which I could not solve. I have the following code: ip_adres : STRING :='0.0.0.0'; port : WORD := 5000; iStep : INT := 1; // Socket information Socket_handler : SysSocket_Interfaces.RTS_IEC_HANDLE; Socket_handler_result : SysSocket_Interfaces.RTS_IEC_RESULT; Socket_adress : SysSocket_Interfaces.SOCKADDRESS; Addres_Convert : SysSocket_Implementation.RTS_IEC_RESULT; // Bind information Bind_handler : SysSocket_Interfaces.RTS_IEC_RESULT; // Listener Information Listener_handler : SysSocket_Interfaces.RTS_IEC_RESULT; Addres_Convert := SysSocket_Implementation.SysSockInetAddr(szIPAddress:= ip_adres,pInAddr:= ADR(Socket_adress.sin_addr)); Socket_adress.sin_family:= SysSocket_Interfaces.SOCKET_AF_INET; Socket_adress.sin_port := SysSocket_Implementation.SysSockHtons(usHost:= port); CASE iStep OF 1: // Create Socket Socket_handler :=SysSockCreate( iAddressFamily :=SysSocket_Interfaces.SOCKET_AF_INET, diType:=SysSocket_Interfaces.SOCKET_STREAM, diProtocol:=SysSocket_Interfaces.SOCKET_IPPROTO_TCP, pResult:=ADR(Socket_handler_result)); IF Socket_handler = SysSocket_Interfaces.RTS_INVALID_HANDLE THEN iStep := 1; ELSE iStep := 2; END_IF 2: Bind_handler := SysSocket_Implementation.SysSockBind( hSocket:=Socket_handler, pSockAddr :=ADR(Socket_adress), diSockAddrSize:=SIZEOF(Socket_adress) ); 3: Listener_handler := SysSocket_Implementation.SysSockListen( hSocket :=Socket_handler, diMaxConnections :=1); END_CASE When I am trying to get this working, the SysSockBind function gives a value of 16#207 which means adress already in use. I find this weird because of the IP-adress of 0.0.0.0. I think I am converting the Ip-adress in the wrong way, but the code does not give a error arround this. So therefore I cannot find the solution to this problem. I hope someone could help me with this problem. Thanks in advance George
Last updated: 2025-02-20
Post by trusty-squire on Read "Homed" status from EtherCAT drive
CODESYS Forge
talk
(Post)
@imdatatas, thanks for the info, I increased DSP402.uiHomingMinCycles to 10 and have a good feeling that will solve the issue of "false" homings. It's an intermittent issue so I'll report back once it's confirmed. @bruno-roth, also good info. According to my documentation, bit 14 is used to indicate the homed status. I did a test and the bit always stays true after it's been homed once (eg. even if I initiate a new homing procedure then hit the the e-stop mid homing), so I need to take that into consideration, but I can work with that. Thanks!
Last updated: 2025-01-09
Post by alexgooi on Update boot project default unchecked
CODESYS Forge
talk
(Post)
Dear Forum, I'm currently switching to Codesys V3.5 SP19. When I want to do an online change, I get the option to update the boot project, in other (codesys based) packages this is checked on by default. In Codesys V3.5 SP19 (and maybe older versions) this is unchecked by default. We are doing a lot of remote updates with systems that almost never power cycle. In other words when this box is forgotten the system will run fine until a blackout. Is it possible to get it checked on by default? This question was asked before, but no answers where given. https://forge.codesys.com/forge/talk/Engineering/thread/ffb4ffa298/ Thank you in advance.
Last updated: 2024-02-09
Post by rh-pk on v3.5 SP19 - Modbus TCP Devices - Channel Limit?
CODESYS Forge
talk
(Post)
Hi, i found a solution for me. I had installed a 'old' version of CoDeSys (3.5.18 P5). I tried to add channels there, which works fine. I created a new project, added an Ethernet-Port, added a Modbus-Master and then I copied the ModBus-Slave from my working project to the new project. Now I could add more channels. I add the channels 10 and 11. Then I deleted (please make a backup before :-) the original ModBus-Slave in my working project and copied the extended Slave back to my working project. Surprisingly it is now possible to add new channels. Maybe this will help you.
Last updated: 2024-02-14
Post by fless on Warning C0564 when compiling CNC project with variables program
CODESYS Forge
talk
(Post)
Update: We managed to avoid the warnings by changing the order of initialization by adding an attribute to the GVL with the variables. {attribute 'global_init_slot' := '49989'} The variables are initialized right before the regular GVLs (default GVL slot 49990). Note to Codesys: I see the problem, Codesys needs to initialize the CNC objects before the GVLs so they can be used in the GVL. But then you can't use variables from GVLs in CNC programs. Maybe you could disable the warning in your generated CNC objects? At least a note for a workaround would have been nice.
Last updated: 2024-04-02
Post by wistaro on Hardware compatibility with Linux RealTime PLC
CODESYS Forge
talk
(Post)
Hello, I am currently using Codesys Control RTE Softmotion V3 to control my servo-drives in CAN, EtherCAT and PROFINET IRT. I am using a PC with Windows 10 with the following boards: - PEAK-CAN PCIe board (for CAN and Softmotion); - Hilscher CifX with firmware 3.X and SysDrv3s driver (for PROFINET IRT); - Realteak standard NIC (for EtherCAT). I would like to switch to Linux (Debian), because this computer is old, slow, and outdated (Windows 11 is far from being compatible with this computer). Before doing this, I would like to be sure of the compatility between my 3 boards and Codesys Control Linux SL. Otherwize, I will stay on Windows 10 and use it in an isolated environnement. Thanks for your advices. Regards,
Last updated: 2026-06-15
Post by alexgooi on Network variable stops sending
CODESYS Forge
talk
(Post)
Hi Reinier, What usually works for me is settings it up in the following way: In the sender block make sure that the list identifier is unique for the whole installation (this is only relevant when you have multiple senders in 1 network). When you are linking the NVL to a file make sure that the path to this file doesn't change. In my experience the NVL stops working when you change the working directory and afterwards open the NVL in de Codesys IDE. If this doesnβt apply to you application, you could also try to change the port number, maybe there is an other process making use of port 1202. Kind regards Alex
Last updated: 2026-04-22
Post by captaincookie on increase default string length in queue
CODESYS Forge
talk
(Post)
Hello, I'm using Codesys V3.5 SP18 Patch 4. In the ElementCollectionExample Project from Codesys, I test the SimpleQueueExample in a Control Win V3 x64 environment. I try to add a string of 95 characters length to a queue. The default length of strings is defined as 80 characters. In the initialization of a string variable, it is possible to increase the length by the definition of e.g. STRING(1000). But when I write the string defined like this to the queue, only 80 characters are written to it and the rest is missing. I think the default length is still set in the queue definition, so it is necessary to change this, isn't it? Is there any option to increase the default length of strings in the queue? Attached you can find the used project. Thanks in advance. If any information are missing or my description unclear please let me know.
Last updated: 2023-10-05
Post by jvfred on CodesysHMI.exe: Start Error
CODESYS Forge
talk
(Post)
I have used Codesys HMI SL on several projects. Today I turned my PC on to start building another project and received the following error message when I tried to start my device: "CodesysHMI.exe: Start Error One of the following licenses is required: CodeMeter 101597:13 Failure reason: CmContainer Entry not found, Error 200 CodeMeterAct 5000304:13 Failure reasons: CmContainer Entry not found, Error 200" I have tried reloading HMI SL and even updated to the current version with no success. I am using HMI SL version V3.5.20.10. Any help would be greatly appreciated.
Last updated: 2024-11-01
Post by jvfred on CodesysHMI.exe: Start Error
CODESYS Forge
talk
(Post)
I have used Codesys HMI SL on several projects. Today I turned my PC on to start building another project and received the following error message when I tried to start my device: "CodesysHMI.exe: Start Error One of the following licenses is required: CodeMeter 101597:13 Failure reason: CmContainer Entry not found, Error 200 CodeMeterAct 5000304:13 Failure reasons: CmContainer Entry not found, Error 200" I have tried reloading HMI SL and even updated to the current version with no success. I am using HMI SL version V3.5.20.10. Any help would be greatly appreciated.
Last updated: 2024-11-01
Post by jshirazi on Restore license on Raspberry Pi
CODESYS Forge
talk
(Post)
Hi, I recently got a license for Raspberry Pi, after license activation I made a backup copy of "CMLicenseNew.WibuCmRaU" file to a safe place. Things got complicated and I tried to downgrade OS for some reason after that I tried several times/ways to restore my license with no luck. the specifications are as follows: Raspberry Pi 4 Model B Rev 1.1 codesyscontrol 4.10.0.0 SDK 3.5.19.30 Logs: **** ERROR: CodeMWriteLicenseFile: 'CMLicenseNew.WibuCmRaU' failed: Container not found or Server dose not support .... So if someone know a solution for this please kindly help me. Regards
Last updated: 2024-02-03
Post by phoward131 on Alarm Table Filtering
CODESYS Forge
talk
(Post)
I am having trouble getting the alarm table filtering to work. I downloaded the alarm filter latch example project and ran it on the local Codesys Control Win and the filters worked fine. I am trying to replicate it in my project and everything seems to be set up the exact same way and every time I turn on the filter, it shows no alarms. I even started a blank project and just copied in elements from the example project so that it is exactly the same and when I attempt to filter, it again shows no alarms. Could there be some project settings I need to adjust to make this work? I have attached my project with elements copied from the example project and filtering is not working.
Last updated: 2024-10-28
Post by gilad on CODESYS SoftMotion Generic DSP402 on WAGO PFC200 + Festo CMMT-AS: MC_Power stays Busy, Controlword remains 0
CODESYS Forge
talk
(Post)
Hello, I am trying to connect a Festo CMMT-AS-C4-3A-MP-S1 servo drive to a WAGO PFC200 (750-8210) using EtherCAT and CODESYS SoftMotion. Hardware PLC: WAGO PFC200 750-8210 Drive: Festo CMMT-AS-C4-3A-MP-S1 Communication: EtherCAT CODESYS version: Device description version 6.3.1.1 Drive firmware: 36.10.3 Current Status EtherCAT communication is working correctly: EtherCAT master = Running Drive detected and operational PDO input and output mapping is active Statusword, position and velocity are updating correctly Current PDO mapping: Outputs: 6040 Controlword -> %QW0 6060 Modes of operation -> %QB2 607A Target position -> %QD1 60FF Target velocity -> %QD3 Inputs: 6041 Statusword -> %IW2 6061 Modes of operation display -> %IB6 6064 Position actual value -> %ID2 606C Velocity actual value -> %ID3 SoftMotion Axis I added a SoftMotion CiA402 axis under the EtherCAT slave: Axis type: SM_Drive_GenericDSP402 Axis communication state: operational (100) No SoftMotion mapping errors anymore Problem MC_Power is executed with: Enable = TRUE bRegulatorOn = TRUE bDriveStart = TRUE but: Status = FALSE Busy = TRUE Error = FALSE ErrorID = SMC_NO_ERROR The axis remains in: SMC_AXIS_STATE.power_off DSP402 state = SWITCH_ON_DISABLED The most important observation: Statusword = 32784 (0x8010) Controlword (%QW0) remains 0 all the time SoftMotion never writes 6, 7, or 15 to the Controlword. Additional Information The axis status page reports: "The license is missing or invalid. The PLC runs in demo mode." I am not sure whether: The missing SoftMotion license prevents Controlword generation completely. The axis is still not correctly connected to the EtherCAT slave despite operational communication. There is an additional CiA402 configuration step required for the Festo CMMT-AS drive. Has anyone successfully used a Festo CMMT-AS MP drive with CODESYS SoftMotion Generic DSP402 on a WAGO PFC200? Any suggestions on what should be checked next would be greatly appreciated.
Last updated: 2026-06-24
Post by martinlithlith on Relay board / relays for raspberry pi 3 b+
CODESYS Forge
talk
(Post)
hi! im planning a project on a raspberry with Codesys. For this I'll need a number of relays to control heating and fans, all a max of 24v and about 2a. How would i know if the board / relays i buy will be working with Codesys? Does every hat work or does it need a library/driver? is there a list of drivers/libraries created? as this is a hobby project all tips on a relay board or single boards that works with codesys and not to expensive are very welcome.
Last updated: 2023-09-03
Post by matthew on New Ladder Diagram conversion does not work due to missing features
CODESYS Forge
talk
(Post)
Hi @eschwellinger, I have been trying out v1.0 of the new ladder and have a few questions. I have warnings Expression or part of it has no effect I can't get rid of them, what do they exactly mean? Using the ST_Block, is there a way when online to open the ST_Block and view the running code? Thanks!
Last updated: 2024-02-09
Set up the gateway and device by IP address and device address
CODESYS Forge
talk
(Thread)
Set up the gateway and device by IP address and device address
Last updated: 2022-05-04
Post by idir93dz on Identifier 'IoDrvGPIO' not defined
CODESYS Forge
talk
(Post)
Hello, After installing the pi runtime and creating a pi project, I get these errors: [ERROR] Untitled3: Application [Device: PLC Logic]: C0046: Identifier 'IoDrvGPIO' not defined [ERROR] Untitled3: Application [Device: PLC Logic]: C0080: Function block 'IoDrvGPIO' must be instantiated to be accessed [ERROR] Untitled3: Application [Device: PLC Logic]: C0004: 'IoDrvGPIO' is no component of 'IoDrvGPIO'
Last updated: 2024-04-10
Post by edepalos on Text list from sd card
CODESYS Forge
talk
(Post)
Hi guys, I have a textlist in my project which is working just as expected in a drop down list. I would like to move this text list to a sd card and access it from there, because I want to ease the editing of the contents of this textlist. I'm imagining a solution like the operator shuts down the plant, takes the sd card out, edits the textlist on the card with a windows machines notepad, then reinserts the card in the PLC and restarts the plant, having the new content of the textlist populating the dropdown list. I'm sorry that I'm asking you to spoonfeed me, but I did not find anything straightforward to do this... I saw in the Project>Project settings>Visualisation a relative path thingy, but I have the plant in operation and I would not like to make 100 trial and errors right now... I'm also not interested in SysLib file read commands and stuff, I would just like to access the file from the cards part, I don't want to replace its contents dynamically or such... nor I have language files or recipes... Thank You in advance! Br, Ede
Last updated: 2024-01-16
Post by plunje on Sensor not set
CODESYS Forge
talk
(Post)
A got a larger project but this very small example makes it clear. I have a button, and after it's clicked a lamp should flip on and stays on, and when the mouse-button is released it should stay on. When I try that in the PLC_PRG it works, but when I change it to a function block (seet attched demo proj) it isn't. I'm fairly new to PLC programming but are very experienced C# engineer, but this goes above my head...
Last updated: 2024-05-26
Post by atone on CAA File Handling: "Read only" error
CODESYS Forge
talk
(Post)
In case of error while opening the file to read you assume that the file doesn't exist and try to create one. But it could be that the SD card is not ready yet or simply not there. I would try to check first if the SD card is there and accessible. Otherwise with FILE.Create you could end up creating a new directory that is not mapped to the SD card. This would explain the errors even after a reboot, though it doesn't explain the READ_ONLY_CAA error I guess? I would use FILE.DirOpen and FILE.DirList to check if the SD card is there and ready.
Last updated: 2025-03-20
Post by milan-svarny on ModbusFB.ClientSerial Problem with Reply Timeout
CODESYS Forge
talk
(Post)
Hi All, I have problem with ModbusFB.ClientSerial. I'm using 4 different port for Modbus communication. After some time of running program ClientSerial stops to receive data to reply buffer and all request finish with Reply Timeout. The Device sent reply correctly,that it is visible on oscilloscope and it is possible to see that data( reply )are in the device. If the usbtty device is read over external app. then it is possible to see all data which were not taken by ModbusFB.ClientSerial. The stack does not overflow or something , program runs correctly forward and no exceptions or something. The main problem it is that when the error occur than it is not possible to reset port or something or maybe i'm doing it wrong way. please help me with this issue. Thank you for any help in advice Milan
Last updated: 2025-05-23
Post by rmaas on Direct Pointers in IOMapping for EtherCAT with IoDrvEthercatLib.ETCSlave_Dia
CODESYS Forge
talk
(Post)
The reference used is the ethercat slave name. For example in this screenshot the reference would be: EL1809_1
Last updated: 2024-02-13
Post by rossanoparis on Internal Error (ARM): Unsupported conversion! With new version v3.5 SP21
CODESYS Forge
talk
(Post)
I have updated CODESYS development tool to the version v3.5 SP21 (64bit) The previous version was v3.5.20.40 Compiling an existing application with the new evelopment tool I get the following error. kunbusiodrvrevpibridge, 1.4.1.0 (kunbus gmbh): IoDrvScanModules [IoDrvRevPiBridge](Line 51, Column 1 (Impl)): Internal Error (ARM): Unsupported conversion! This error was not reported in the previous compiler version and is now highlighted in a third-party library, which I cannot change or modify. The error is due to the following conversion: m_udiError := TO_UDINT(excCode); . The excCode variable is a system type, declared as shown below, and should be converted to a UDINT excCode : __SYSTEM.ExceptionCode; m_udiError: UDINT; . I would appreciate it if someone could provide feedback on this issue.
Last updated: 2025-04-15