Post by eschwellinger on WAGO PFC200 FW25 unable to connect CODESYS Forge talk (Post)
please double check if you have in the project the same plc type like online available. (untag the " Hide non matching device filter.."
Last updated: 2023-12-09

Post by lostcontrol on Remote Ethernet/ip Adapter communication with scanner running on codesys CODESYS Forge talk (Post)
is the bus running.? what type of values/IO is the adaptor providing? do you have a map of the data layout? are you actually looking at the right offset?
Last updated: 2023-12-16

Post by jdjennings1962 on Trouble accessing Math functions in OSCAT library CODESYS Forge talk (Post)
Thank you seoerr for your suggestion. When I implement that line, I get this error: ** [ERROR] 'OSCAT_BASIC.ARRAY_SDV' is of type FUNCTION and cannot be instantiated** Any other thoughts about instantiating these sections of the library which seem to be provided as source only?
Last updated: 2024-01-16

Post by dhumphries on Not able to see input data coming from eip adapter on codesys CODESYS Forge talk (Post)
The green icon with an ! next to the device is concerning. Is the data type correct for the input, you are using a byte input but the description says string. Is there anything useful in the status tab?
Last updated: 2024-03-06

Post by eschwellinger on How to Connect / Go Online without re-downloading the project CODESYS Forge talk (Post)
Which plc type is it: Either use Automationserver to do this or save the project archives instead of projects or use the source dowload function and reopen the application from plc. So you need to chose one of them.
Last updated: 2024-04-13

Post by kevinm on Data source and safety PLC CODESYS Forge talk (Post)
I am having the same trouble. However, if I change the Login Configuration settings to 'Type: Login using the credentials determined at runtime' then the Connection information continues as 'Connection state: Connecting' and 'Error information: OK'. There is no User Management on the source PLC.
Last updated: 2024-05-16

Post by gcodejedi on The element of type 'VisuFbElemImage' could not be updated. Reason: Index was outside the bounds of the array. CODESYS Forge talk (Post)
Hello, I am experiencing this exact same issue. Were you able to get yours resolved? If so, would you mind sharing the solution you discovered? Thanks!
Last updated: 2025-11-03

Post by eschwellinger on The element of type 'VisuFbElemImage' could not be updated. Reason: Index was outside the bounds of the array. CODESYS Forge talk (Post)
check with the CODESYS Installer er if you are on latest Visuversion. 4.9.1.0
Last updated: 2026-01-27

Post by gatto on Two licenses have to be installed forgot to enable one license CODESYS Forge talk (Post)
Hi. What type of PLC do you have? What activation method do you use? What license ticket did you purchase and want to activate? Can you describe the process you followed step by step?
Last updated: 2026-02-02

Post by liamb on Converting CANbus to Decimal from signed 2's complement CODESYS Forge talk (Post)
I need to combine two 8 bit CANbus messages to 16 bits signed int then convert to decimal Decimal from signed 2's complement. I've been using the below code to read for new messages, combine them then assign them to a variable What is the best way to do this for from signed 2's complement? fbRxMessage351(Data := RxMessage351Data); IF fbRxMessage351.NewMessage THEN ChargeVoltage := (WORD_TO_REAL((RxMessage351Data[0]) + ((RxMessage351Data[1]) * 256))) * 0.1; END_IF
Last updated: 2024-08-16

Post by docker on Webvisu client connection monitoring CODESYS Forge talk (Post)
Hi mate, With this snippet i was able to see the lastusage variable count, but it would not iterate between clients? i was only able to access the data of the target visu. it threw an error with the array of pointers stating it was not able to convert etc. also when i tried it with the while loop it created an endless loop and crashed the program. any ideas? Thankyou
Last updated: 2024-09-10

Post by sebastianrapi on Bibliothek: floatingpointutils CODESYS Forge talk (Post)
Hallo Zusammen, ich versuche die Bibliothek FloatingPointUtils.compiled-library-v3 zu benutzen. leider kommt dabei folgende Fehlermeldung: Kein Quellcode für dieses Objekt... (siehe Anhang) Wie kann ich diese Bib einbinden? Kann ich diese irgendwo herunterladen? Mein Ziel ist es ein DWORD (float) in ein REAL umzuwandeln. ICh hoffe, dass ich dies mit der Funktion HexStrToReal machen kann. So wie hier: https://gregstoll.com/~gregstoll/floattohex/ convert to float... Oder gibt es bei Codesys einen anderen Weg? Ich verwende v3.5 SP20 Patch 1 + (32Bit) Grüße Sebastian
Last updated: 2024-10-17

Post by svn123 on Can V3.5.19 and V2.3.9 be installed on same Windows10 PC without affecting each other? CODESYS Forge talk (Post)
Hi All, Seasons Greetings! I have Codesys V3.5.19 patch 5 installed on a Windows 10 PC. I have received a program which is for Codesys V2.3.9. First I tried to convert it but had many conversion errors. I am wondering if it is possible to install Codesys V2.3.9 on same PC without affecting the V2.5.19 installations. Is this possible? SVN123
Last updated: 2023-12-28

Post by wiresplus on INT_TO_WORD function not working CODESYS Forge talk (Post)
Hello, I need to take an INT input, and convert it to a WORD value. VAR DRV2Speed : WORD; //IO card takes a WORD where 16000 = full 10V output (equivalent to 50Hz) PumpFillSpeed : INT; //Users enter a value between 0 and 50 END_VAR IF <conditions> THEN DRV2Speed :=INT_TO_WORD((PumpFillSpeed/50)*16000); END_IF </conditions> According to me this should work - but it stays at 0, no matter what. What am I doing wrong?
Last updated: 2024-01-26

Post by i-campbell on Publish a JSON payload via MQTT Publish (using IIot Libraries) CODESYS Forge talk (Post)
your are sending as a WSTRING which is UTF16, but your receiver is interpriting as UTF8. Change the receiver to use UTF16, or better change your sender to convert to UTF8. You publish the entire storage space (SIZEOF) Instead of the number of bytes of actual text (StrLenA) try using utf8JsonData : STRING(2000); JSON.Stu.ConvertUTF16toUTF8( ADR(wsJsonData), ADR(utf8JsonData), SIZEOF(utf8JsonData) ); and change your publish to mqttPublish( mqttClient:=mqttClient, pbPayload:=ADR(utf8JsonData), udiPayloadSize:=To_UDINT(JSON.Stu.StrLenA(ADR(utr8JsonData))), wsTopicName:=topic, mQTTPublishProperties:=mqttPublishProperties );
Last updated: 2024-04-10

Post by shaunvdm on OSCAT Scale_r function not working in LD 4.60 works in LAD2 on 3.5.21sp3 CODESYS Forge talk (Post)
Hi We have picked up an issue OSCAT_BASIC.Scale_r function call not working in the old lad and FBD version 4.60. Gives no output on the function call. When we convert this to LAD2 it works. As can be see by the two screenshot in normal LD not working in LAD2 it works. Please confirm if this is an issue with Oscat or with LAD in 3.5.21sp3, is there an workaround. Regards Shaun
Last updated: 2025-10-23

Post by shaunvdm on OSCAT Scale_r function not working in LD 4.60 works in LAD2 on 3.5.21sp3 CODESYS Forge talk (Post)
Hi We have picked up an issue OSCAT_BASIC.Scale_r function call not working in the old lad and FBD version 4.60. Gives no output on the function call. When we convert this to LAD2 it works. As can be see by the two screenshot in normal LD not working in LAD2 it works. Please confirm if this is an issue with Oscat or with LAD in 3.5.21sp3, is there an workaround. Regards Shaun
Last updated: 2025-10-23

Post by codegunner on how to convert library from CodeSys 2.3 to CodeSys 3.x ? CODESYS Forge talk (Post)
hello, ive tried everything and keep getting error like i have opened a file in read only so cannot save no idea what is causing it, file is not read only i cannot even open a new file i make with one variable in 2.3, get same error for read only. do you have a 2.3 file you can send me tomtry and open for a test? thanks
Last updated: 2026-04-29

Post by nehaltrivedi96 on Modbus connection via Qronox PCD3 M6893 CODESYS Forge talk (Post)
Hello, I am currently scaling 4-20mA signals and the scaled output (temperature) has to be sent via modbus protocol to a tool like doctor modbus or modbus poll. I have defined my inputs as real as and the output is also real, but to send this output via modbus it has to be of word. So how will i convert real into word and then send the generated output via modbus?
Last updated: 2026-02-18

Post by garyl on Comments in arrays and assigning RST coil's to 600 outputs CODESYS Forge talk (Post)
Hello all, im working on a project that requires me to convert an old automation direct DirectSoft PLC d2-250-1. One of the problems im encountering is that all of the comments are attached to members of the different addresses. When i convert the addresses (1777 "C" registers, 777 X registers, and 20,0000 V registers) im running into difficulties keeping the inputs/outputs correct since they are missing documentation. Is there a good way to retain the comments of the indexes in the array? Secondly, initially i was declaring the "C" and "V" addresses individually and this worked to retain the comments as to which register did what, however i ran into a problem when one rung reset (or set to 0) approximately 600 C Addresses. Since each tag is separately declared this proved to be nearly impossible without a literal wall of code that attempted to crash the program. So i converted all of the registers (C,X,Y,V) into separate structs, declared them as arrays and pointed all of the original call outs in the program to the newly defined structs. However i have now lost comments and the program is very hard to follow. Thanks for any help with this issue.
Last updated: 2023-08-31

Post by hanoues on setting date and time on CPX-E CODESYS Forge talk (Post)
Hello, Can anybody here tell me how to modify the time and date on my CPX-E? I used the code I found on CODESYS online help, but it doesn't work. What am I missing? FUNCTION current_date_time : STRING VAR stUTC_Timestamp : SysTime; //utc time // ULINT#1528280694913 stLocal_TimeStamp : SysTime; //local time but is in general equal // ULINT#1528280694913 stdNow : SysTimeDate; //local time in an object to access each number (day, month...) dtNow : DATE_AND_TIME;//DT#2018-6-6-10:24:54 todNow : TIME_OF_DAY; // TOD#10:24:54.913 datNow : DATE; // D#2018-6-6 END_VAR SysTimeRtcHighResGet(stUTC_Timestamp); // ULINT#1528273494913 SysTimeRtcConvertHighResToLocal(stUTC_Timestamp, stdNow); //convert UTC ULINT to Local SysTime // stdNow.wYear = UINT#2018 // stdNow.wMonth = UINT#6 // stdNowy.wDay = UINT#6 // stdNow.wHour = UINT#10 // stdNow.wMinute = UINT#24 // stdNow.wSecond = UINT#54 // stdNow.wMilliseconds = UINT#913 // stdNow.wDayOfWeek = UINT#3 // stdNow.wYday = UINT#157 SysTimeRtcConvertDateToHighRes(stdNow, stLocal_TimeStamp); // ULINT#1528280694913 dtNow := TO_DT(stLocal_TimeStamp / 1000 ( ms )); // DT#2018-6-6-10:24:54 todNow := TO_TOD(stLocal_TimeStamp MOD TO_ULINT(T#1D)); // TOD#10:24:54.913 datNow := TO_DATE(dtNow); // D#2018-6-6 (convert to appropriate string) current_date_time := concat('$N[', TO_STRING(dtNow)); current_date_time:= concat(current_date_time,'.'); current_date_time:= concat(current_date_time, TO_STRING(stdNow.wMilliseconds)); current_date_time:= concat(current_date_time,'] - '); RETURN;
Last updated: 2024-05-21

Post by alimans on Hex string CODESYS Forge talk (Post)
Hi kdkwhite, for Word you still can use suggested code by using a union structure and crack down your Word to two byte as bellow: TYPE CrackWordToByte : UNION InWord : WORD; OutBytes : ARRAY [0..1] OF BYTE; END_UNION END_TYPE then define your variable as this type: udInput : CrackWordToByte; now assign your Word variable input to InWord and send OutBytes[x] to the mentioned method: udInput.InWord := WordVariableInput; Input := udInput.OutBytes[x]; Regarding your question about the code: actually 48 is ascii code of "0" and while 65 is the ascii code of "A" so in above code 55 + 10 would be 65.
Last updated: 2023-09-20

Post by eguerra on Error in ScriptingEngine Docs - create_pou() CODESYS Forge talk (Post)
In the ScriptingEngine documentation there seems to be an error (or missing information) in the ScriptIecLanguageObjectContainer part ( https://content.helpme-codesys.com/en/ScriptingEngine/ScriptIecLanguageObjectContainer.html#ScriptIecLanguageObjectContainer.ScriptIecLanguageObjectContainer ). The description of the function create_pou() doesn't specify the correct arguments requested, it only says create_pou(type: SpecialPouType) and a script using the documentation definition of the function will raise an error. I tried passing the function arguments similar to the ones specified for the create_dut() function and it seems to work fine: create_pou(name, PouType) , name : str UPDATE: The offline help has the correct definition IExtendedObject<IScriptObject> create_pou( string name, PouType type = PouType.FunctionBlock, Nullable<Guid> language = null, string return_type = null, string base_type = null, string interfaces = null )
Last updated: 2024-08-05

Post by otbeka on CmpCrypto CryptoGenerateHash Not Outputting CODESYS Forge talk (Post)
Unfortunately I noticed that, and tried: * using CryptoGeteAlgorithmByID within the function call * inputting the raw byte pointer as a testByte * instantiating the _hHash handle within the function body * using a different cryptoID or the raw DINT values from the RtsCryptoID DUT ... to no avail. The pReturn value is also set to 0, which would indicate that it is OK, right? This is odd given that the function is the same within the CryptoDemo example project here, just with a newer version. Is it possible that there is something wrong with the way my bytestring is being set up? I use the following DUTs here: TYPE MESSAGE : STRING(255); END_TYPE TYPE HASH_CODE : ARRAY[0..19] OF BYTE; END_TYPE
Last updated: 2024-09-06

Post by thn-power on How to change OPC NodeId IdentifierType CODESYS Forge talk (Post)
Hi Yet another OPC UA question. When setting up a OPC server using "Communcation manager" (Symbol set and information model) in Codesys the NodeId is always given as "opaque" type. At least when browsing using UAExpert. Other standard OPC objects use numeric (or string) identifier, but for some reason my variables seems to get opaque/binary type. See attached photo. How can I change this? I can't see that this is a parameter in the CodesysControl.cfg. Can this be specified in the information model nodeset? And is it possible to specify the exact numeric or string NodeId for each instance? And on a related topic, is there a way to export the OPC server nodeId's with variable name so that it can be imported in a OPC Client? The .xml files in the project folder does not seem to contain the NodeId.
Last updated: 2024-09-20