Post by s1ack on Wago PFC200 Ethernet / IoDrvEthernet Issue?
CODESYS Forge
talk
(Post)
It's suspected that the CPU loading is the Linux Kernal in the Wago PFC200 dealing with IGMP multicast traffic (@ 250 uSec) from inverters on site. The inverters use the ethernet network and IGMP to synchronize, the customer removed the switch that shipped with the system, and thus removed IGMP Snooping that was plug-and-play within the provided switch.
Last updated: 2025-01-24
Post by masmith1553 on SDO generation
CODESYS Forge
talk
(Post)
If you add any device to the CANOpen Manager it will send messages to verify the device is on the network. Do you have the Enable expert settings check box checked in the General tab? have you added any SDOs in the SDOs tab? I avoid using the CANOpen Manager and just use the CAN_Tx and CAN_Rx blocks from the library.
Last updated: 2024-01-25
Post by rcaponi on Codesys Control RTE V3. Remote Control
CODESYS Forge
talk
(Post)
Hello, I would like to have, if possible, some clarification on this function. That is, I would like to understand if it is useful for managing, fom my development PC, the RTE runtime executed on a remote control. This is what the help says: Remote PLC: Opens the Remote Configuration dialog. By enabling or disabling the Control remote PC, not local option, you determine whether a PLC is used that is on a remote or local PC. Accordingly, the menu commands Start PLC, Stop PLC, and PLC Configuration refer to the local PC or a PC reached on the network. For the remote PC, specify the Target PC address, Port number, and a Timeout value (in ms) for the connection (Remote Timeout [ms]). But does this mean that I also need to install the RTE runtime on my development PC? Is it possible to have some more information? Best regards Roberto Caponi
Last updated: 2023-09-22
Post by pouyavakili on Execute Codesys Tests with python
CODESYS Forge
talk
(Post)
Thank you for your input! What I'm ultimately trying to achieve is automated test execution as part of a CI/CD pipeline (e.g. in GitLab or Azure DevOps). For this, I need to: Open a CODESYS project via script Build the project Run the Test Manager tests from a .TestRepository.xml Collect test results (e.g., pass/fail + a report) Exit with a proper return code (for pipeline success/failure) To integrate this into automation, I’m using the CODESYS scripting engine via Python (headless), but the issue is that the get_testmanager() function isn't available on the project object — even though Test Manager is installed, licensed, and works interactively in the IDE. Are you suggesting that I should: Use the Test Manager GUI to script the logic with its internal scripting language? Or is there a way to launch the Test Manager in headless/scripted mode, while still being able to control things via Python? If there's a supported way to automate tests with the Test Manager using scripting, especially from pipelines or headless environments, I’d really appreciate any pointers or example workflows. Thanks again!
Last updated: 2025-07-24
Post by tcarlbom on Read tag values using external program
CODESYS Forge
talk
(Post)
This is my first time posting in this forum and I am new to codesys. I am a fullstack developer and I am trying to figure out how the following. What would be the best approach to create a own/custom tag browser? Either directly in codesys ide or using a separate custom program (perhaps a winforms application). 1.a. Shall I parse the .project xml file to get a list of all tags in the project? 1b. Shall I use python scripting in codesys ide to get a list of tags? Once one have selected some tags. These tags shall be exposed to a python program which will be acting as a edge computer. It’s fine to be able to import a file. 2a. I found a library called codesys plchandler which (as I understand) acts a rest api server. Is this correct? If so, can I query the api from a custom python script, ie can query what tags exist in project and or read tag values? My research so far. From earlier projects I know that using opc ua would be perfect for this but from my opinion it’s bloating the plc since it’s resource intensive. So opc ua is not an option. Codesys automation server is neat. But I don’t want to rely on some cloud services and subscription based pricing. There seem to be several interesting codesys libraries like mqtt, tcp server and NVL sender which would help me expose plc tags. But all have a common problem. One have to manually write what tags which will be used in these function blocks. I want a similar experience like “selecting” tags in the opc ua or the codesys tracing, ie a tag browser.
Last updated: 2024-06-28
Post by fontrap on cmDongle Raspberry Pi issue
CODESYS Forge
talk
(Post)
Hello mates, I'm working with CODESYS V3.5 SP20 on a Raspberry Pi and I use "Raspberry Pi MC SL" as device on the project. I've installed the Control Standard L (multicore) license on a Wibu System usb-Dongle (cmStick/4.50) that already had another license from another vendor. I follow the online activation procedure from CODESYS documentation. Raspberry Pi has already CodeMeter installed for the other license. When I plugin the dongle on Raspberry and start the Runtime from Raspberry Pi Update in CODESYS I receive the message that I'm on Demo mode because the license is missing. I double checked that the license is activated in the dongle, through the WebAdmin of CodeMeter and the second license runs properly without any issue. I have already try to change the dongle from HID to MSD device and backward but the the Runtime cannot recognize the Dongle. I have also try to stop and start the Runtime through CODESYS without success. Is there anything else I can do to fix this issue?
Last updated: 2024-04-22
Post by ahuckphin on Issues with Modbus Slave with Raspberry Pi
CODESYS Forge
talk
(Post)
codesyscontrol_user.cfg [SysCom] Linux.Devicefile.1 = /dev/ttyUSB0 portnum:=COM.SysCom.SYS_COMPORT1; **parameters are used in the python-script ** method: "rtu" port: "COM8" baudrate: 9600 stopbits: 1 bytesize: 8 parity: 'N' timeout: 1 register address for humidity: 0x000 register address for temperature: 0x001 unit ID: 1 **parameteized in the modbus-master-comport ** see attached files
Last updated: 2024-07-11
Post by programmer on 3.5 P20 hangs - no response
CODESYS Forge
talk
(Post)
hi imdatatas, thanks for your suggestion! I added the process execution to be sure. In the meantime I reïnstall Windows but it dind't help directly. Finally I deleted CodeMeter Runtime Server after Codesys installation. Because this Service was not able to start. And it works (for now) :)!
Last updated: 2025-06-25
Post by wagokurt on TargetVisu option missing in IDE
CODESYS Forge
talk
(Post)
I have installed both the Codesys Control for Linux SL 4.16.0.0 and Target Visu for Linux 4.16.0.0 packages in Codesys 3.5 SP21 Patch2. When I try to add a target visu, it is missing. I have spent hours on this and tried different machines, all behave the same way. Is this a bug?
Last updated: 2025-08-21
Post by antonz on CoDeSys v3.5: creating libraries for both 32-bit and 64-bit controllers
CODESYS Forge
talk
(Post)
Thanks Tim. I would think it somehow is relevant when creating a compiled library, but that may very well not be the case. If I understand you correctly, then the same compiled library created from my source code would work for both 32 bit as well as 64 bit controllers.
Last updated: 2025-09-01
Post by sanacfu on looking for v2.3 libraries on v3.5.19
CODESYS Forge
talk
(Post)
Hi all, I'm new to Codesys and Wago but well versed in Rockwell. I've been tasked with upgrading old Wago 750-880 PLCs that run Codesys v2.3. All I was giving is the original PLC program in v2.3 and the currently running machine. I've spec out to what I believe is a suitable upgrade, the PFC100 2ndGen, 750-8111. As I'm rewriting this code on the Codesys I can't find the same library functions blocks for ethernet settings PLC functions. Currently I'm working on code to get/set the PLC ethernet IP address and HMI IP addresses from the HMI screen. One other function I'm looking for is a warm reset function to the PLC. When googling for this stuff I see a lot of code not in ladder logic. Are these functions now not available to implement in ladder logic? Where can I get more information on finding and implementing this functions? Do I have to buy a license from Codesys to use these functions? The PLC I ordered should be arriving in 2-3 weeks.
Last updated: 2024-03-25
Post by hemuv on Dialog Open
CODESYS Forge
talk
(Post)
I'm programming an HMI for a machine. I want to log all the parameter's changes (used text field for displaying and changing) for particular User levels. Created a Numpad and want to log oldvalue and Newvalue on 'ok' Button press. To retrieve the oldvalue, i check if the dialogue opened is my Numpad, Then I retrieve the dialogue interface via GetDialogInterface(ADR(myNumpad)) --> numpadData.stVariableValue which contain my oldvalue and save it locally. Problem is sometimes i retrieve the data and sometimes not. Also observed when Numpad Dialogue is Opened, VisuDlgUtil_IsDialogOpen returns False in some cycles.Attached you will find my Project. please let me know what went wrong or if there is a better approach to collect old and New Value of a textfield. Thank you.
Last updated: 2025-03-26
Post by rohan on Child Application Alarm
CODESYS Forge
talk
(Post)
Hi All, I'm trying to develop a multi-application project that allows me to switch between applications. I currently have a parent application and several child applications, as this is the only way for them to share CAN/Ethernet communication. I've noticed that I am only able to create an Alarm Configuration for the parent application. But the children application do not seem to be displaying alarms on the Alarm Table in the visualisation for when an alarm is raised. Does anyone know of a fix, solution or a way around this? I am utilising Codesys v3.5 SP16 Patch 5 64Bit
Last updated: 2024-06-21
Post by imdatatas on Unrecoverable SoftMotion state after switch to PreOp
CODESYS Forge
talk
(Post)
Dear @alimans, Additionally, As far as I know since starting from Softmotion V4.18.0.0 automatic restart behaviour for an axis has been changed for this issue. See below explanation from release notes. "With CODESYS SoftMotion 4.18.0.0, the behavior of SoftMotion axes after a loss of communication to the servo drive has changed. Now, an automatic reinitialization is performed as soon as the communication is established again. Before, an explicit call to SMC3_ReinitDrive had to be performed. An example for a loss of communication is that the cable to one of the drives is unplugged." Regards, imdatatas
Last updated: 2025-10-23
Post by pernockham on Gateway in China - "Gateway not connected"
CODESYS Forge
talk
(Post)
I think I understand my problem. They are most probably related to configuration of the network. When I use DHCP for the unit to my router it all works. However when using static IP I have not managed to reach functioning state. Trying to replicate the situation on my desk. Having a static IP on the "debian host" and a connection to my computer which then routes traffic on to internet. I have entered settings for gateway and netmask. I can ping from my "debian plc host" to internet and also do "curl google.com" so traffic seems to find its way through and back, still "Automation server" will not find the gateway. Any hints how a manual configuration should be done? Is it possibly a "firewall" issue of my "normal router"? Thanks for any help! Per
Last updated: 2026-01-27
Post by timvh on gateway problem
CODESYS Forge
talk
(Post)
Maybe select the local gateway instead of the gateway on the remote device?
Last updated: 2023-08-31
Post by eschwellinger on Generic EtherCAT slave
CODESYS Forge
talk
(Post)
Sure, import the ESI file, scan the slave access the PDOs.
Last updated: 2024-05-14
Post by micik on Reverse bytes in an array
CODESYS Forge
talk
(Post)
Hello, I'm getting the data in Codesys that is an array of 8 bytes. From this array, I need to foram LREAL number, however, because of different endiannes I need to reverse bytes in this array and then copy to a LREAL variable. For this I'm using a loop and it works OK. I wonder if there is a built in function to do this. I have found CAA Memory library but it has functions like reverse bytes in DWORD. But it seems it doesn't have what I need. https://content.helpme-codesys.com/en/libs/CAA%20Memory/Current/CAA_Memory/Reverse-Bit-Swap-ByteWord-order/ReverseBYTEsInDWORD.html What I need is a function to reverse bytes in an 8 byte array, or something similar.
Last updated: 2024-08-22
Post by micik on Reverse bytes in an array
CODESYS Forge
talk
(Post)
Hello, I'm getting the data in Codesys that is an array of 8 bytes. From this array, I need to foram LREAL number, however, because of different endiannes I need to reverse bytes in this array and then copy to a LREAL variable. For this I'm using a loop and it works OK. I wonder if there is a built in function to do this. I have found CAA Memory library but it has functions like reverse bytes in DWORD. But it seems it doesn't have what I need. https://content.helpme-codesys.com/en/libs/CAA%20Memory/Current/CAA_Memory/Reverse-Bit-Swap-ByteWord-order/ReverseBYTEsInDWORD.html What I need is a function to reverse bytes in an 8 byte array, or something similar.
Last updated: 2024-08-22
Post by jzhvymetal77 on Special Chars in Visualizationfor QR code string
CODESYS Forge
talk
(Post)
In Visualization, is there any way to make special characters in a string display properly in a Text object? I wrote a function block to create QR codes at runtime. My code uses “$DB,” which in ASCII should render as a solid block. The code works, but to display it in Visualization I had to create multiple rectangles with visibility bound to a BOOL array. That works, but since each BOOL must be exposed as a separate variable, it consumes most of the available monitoring resources. See Attached image.
Last updated: 2025-09-29
Post by jzhvymetal77 on Special Chars in Visualizationfor QR code string
CODESYS Forge
talk
(Post)
In Visualization, is there any way to make special characters in a string display properly in a Text object? I wrote a function block to create QR codes at runtime. My code uses “$DB,” which in ASCII should render as a solid block. The code works, but to display it in Visualization I had to create multiple rectangles with visibility bound to a BOOL array. That works, but since each BOOL must be exposed as a separate variable, it consumes most of the available monitoring resources. See Attached image.
Last updated: 2025-09-29
Post by gustavocsw on MQTT memory leak problem
CODESYS Forge
talk
(Post)
Hello everyone, I'm using the IoT Library to implement the MQTT communication with my local broker server in order to publish and subscribe at specifics topics to share and consume information about my application. But, it seems that are occurring some memory leak problem in a "high" frequency (more than 10 Hz) subscribe process. I follow the same method as in IoT Lib exemples, and at first looks perfect but my PLC was rebooting frequently and when I check its memory usage that was increasing as fast as the subscribe massage was sent. I'm using a WEG PLC410 and a WEG PLC500, and this error occurred in both of them (including in CODESYS Control Win x64). The application sends to the system a message JSON with the float payload Ex. {"data" : 0.8500}, but this happens with a INT, or BOL as well. I use the follow code in my application to find the value: //FindFirstValueByKey VARs PROGRAM JSON_VELO VAR //------Setting the JSON Subscriber to Set the Relay Value jsonDataVelo : JSON.JSONData; jsonByteArrayReaderVelo : JSON.JSONByteArrayReader; xST1okVelo : BOOL; FindFirstValueByKeyVelo : JSON.FindFirstValueByKey; jsonElementVelo : JSON.JSONElement; xDoneReaderVelo : BOOL; xDoneFindVelo : BOOL; //STRING and WSTRING for Subscribe the massage sPayloadJsonVelo : STRING := 'opa'; psPayloadJsonVelo : POINTER TO BYTE := ADR(sPayloadJsonVelo); //wsPayloadJsonRelaySet : WSTRING := "opa"; wsPayloadJsonVelo : WSTRING := STRING_TO_WSTRING('opa'); pwsPayloadJsonVelo : POINTER TO WORD := ADR(wsPayloadJsonVelo); lrVelo : LREAL; xKeepAliveVelo : BOOL; xSetVelo : BOOL; RSSet : RS; LIMPAR : STRING; //Find the msg end sFindVelo : STRING := '}'; psFindVelo : POINTER TO STRING := ADR(sFindVelo); iLenVelo : INT; iSizeVelo : INT := 12; udiContMsg : UDINT; END_VAR // FindFirstValueByKey CODE // Relay Set configuration xSetVelo := MQTT_SUBSCRIBER.RSVelo.Q1; IF xSetVelo THEN xKeepAliveVelo := TRUE; END_IF IF xKeepAliveVelo THEN udiContMsg := udiContMsg + 1; iLenVelo := TO_INT(StrLenA(psPayloadJsonVelo)); iSizeVelo := iLenVelo - TO_INT(MQTT_SUBSCRIBER.udiPayloadSizeVelo); StrDeleteA(psPayloadJsonVelo,iSizeVelo,iLenVelo); wsPayloadJsonVelo := STRING_TO_WSTRING(sPayloadJsonVelo); pwsPayloadJsonVelo := ADR(wsPayloadJsonVelo); //MQTT.ConvertUTF8toUTF16(sourceStart:= ADR(sPayloadJsonVelo), targetStart:= ADR(wsPayloadJsonVelo), dwTargetBufferSize:= TAM, bStrictConversion:= 1); //Reset jsonByteArrayReader jsonByteArrayReaderVelo ( xExecute := TRUE, pwData := pwsPayloadJsonVelo, jsonData := jsonDataVelo, xDone => xDoneReaderVelo ); FindFirstValueByKeyVelo( xExecute := xDoneReaderVelo, wsKey := "data", diStartIndex:= 0, jsonData := jsonDataVelo, jsonElement => jsonElementVelo, xDone => xDoneFindVelo ); IF xDoneFindVelo THEN lrVelo := jsonElementVelo.value.lrValue; //Reset jsonByteArrayReader jsonByteArrayReaderVelo ( xExecute := FALSE, pwData := pwsPayloadJsonVelo, jsonData := jsonDataVelo, xDone => xDoneReaderVelo ); FindFirstValueByKeyVelo( xExecute := FALSE, wsKey := "data", diStartIndex:= 1, jsonData := jsonDataVelo, jsonElement => jsonElementVelo, xDone => xDoneFindVelo ); xKeepAliveVelo := FALSE; GVL.xSetVeloRead := TRUE; END_IF END_IF And this to subscribe at the topic: //SUBSCRIBE VAR: //----------------- Subscribe Velocity ----------------------- MQTTSubscribeVelo : MQTT.MQTTSubscribe;//Variable MQTTSubscriber block -X - function-X wsTopicSubscribeVelo : WSTRING(1024) := "CORE/odometry/GET/data/simp"; // Topic to publish a message sSubscribeMassageVelo : STRING; udiPayloadSizeVelo : UDINT; xSDoneVelo : BOOL; xSErrorVelo : BOOL; xReceiveVelo : BOOL; eSTypeVelo : MQTT.MQTT_ERROR; eSMQTTErrorVelo : MQTT.MQTT_ERROR; RSVelo : RS; udiCont : UDINT; //SUBSCRIBE CODE: MQTTSubscribeVelo( xEnable:= MQTT_CLIENT.xConnection_Broker AND NOT xSErrorVelo AND NOT JSON_VELO.xKeepAliveVelo, pbPayload:= JSON_VELO.psPayloadJsonVelo, udiMaxPayloadSize:= SIZEOF(JSON_VELO.sPayloadJsonVelo), udiPayloadSize => udiPayloadSizeVelo, mqttClient:= MQTT_CLIENT.ClientMQTT, wsTopicFilter:=wsTopicSubscribeVelo, xDone => xSDoneVelo, xError=> xSErrorVelo, xReceived => xReceiveVelo, eMQTTError=> eSMQTTErrorVelo ); RSVelo(SET := xReceiveVelo, RESET1 := JSON_VELO.xKeepAliveVelo);
Last updated: 2024-09-09
Post by riccardo on Codesys SP19 patch 4
CODESYS Forge
talk
(Post)
Hallo everyone, I am working on new PLC of Weidmueller that uses Codesys SP19. I made the upgrade at the Patch 4 coming from patch 0. Unce made the upgrade everything is working well in the progect except the web visu user menagent. In the new version, when I perfom the login, I cannot use the keyboard of the device; the window where to digit the user name and password opens, the buttons "OK" and "Cancel" work but the system doesn't allow to put input from the device keybord, the mouse behaves as it is an image. If I active the virtual keypad or numpad it works otherwise nothing. I am wondering if it is a bug of the new package or if I must set something else. Thanks in advance, Riccardo.
Last updated: 2023-11-27
Post by ppix on Establishing TLS Connection with MQTT Broker using MQTT Client SL Package
CODESYS Forge
talk
(Post)
I’m currently working on establishing a TLS connection with an MQTT broker using the MQTT Client SL package in CODESYS. While I’ve successfully established communication with the broker without TLS, I'm encountering issues when trying to enable TLS. In the 'MQTT Explorer' application, I can easily upload the server certificate (.crt), client certificate (.crt), and client key (.key). However, in CODESYS, I can’t find a way to upload my client key (.key file). Here's a summary of my current setup: Certificates: I have uploaded both the client and server certificates to the certificate store under the 'Trusted Certificates' folder in the security screen. TLS Context Initialization: Despite setting the _sCommonName as the name of my client certificate, a new self-signed certificate is created and placed within the device’s certificates. I then need to manually move this certificate to the trusted certificates folder. This results in three certificates in my trusted certs folder: client cert, server cert, and the newly created cert. _ciDefaultCertInfo : MQTT.NBS.CERT_INFO := (psInfo := ADR(_sCommonName), udiSize := TO_UDINT(LEN(_sCommonName))); // CN of the certificate (common name) _sCipherList : MQTT.NBS.CIPHER_LIST := STRUCT(psList := ADR('HIGH'), udiSize := 4); // Cipher string see https://www.openssl.org/docs/man1.1.1/man1/ciphers.html _tlsContext : MQTT.NBS.TLSContext := ( sUseCaseName := _sCommonName, // A certificate is stored in the certificate store with the use case name. You can choose any name. Here we use the common name. ePurpose := MQTT.NBS.PURPOSE.CLIENT_SIDE, // For client certificates set this to NBS.PURPOSE.CLIENT_SIDE sTLSVersion := '1.3', // The TLS version sCipherList := _sCipherList, // Set the cipher list sHostname := sHostname, // The hostname of the broker udiVerificationMode := 2, // 2 => Active Peer verification ciCertInfo := _ciDefaultCertInfo, // Set the cert info itfCertVerifer := 0); // 0 => No Verifier mqttClient : MQTT.MQTTClient := (xUseTLS:=TRUE, itfTLSContext := _tlsContext, itfAsyncProperty := _asyncProperty); Additional Details: In the client FB, I’ve set uiPort:= 8883, xUseTLS:= TRUE, and configured itfTLSContext as mentioned above. The certificates are encrypted with SHA256RSA. sHostname is the IP address of my broker. I’ve attached a copy of the client FB, which shows straight lines where variables are assigned and boxes where they are not. I am currently trying this on the only 2 compatible versions of COSDESYS with my controller (V3.5.15.20 and V3.5.18.40) My Question: How do I correctly set up this mTLS connection? What might I be missing? Any guidance or suggestions would be greatly appreciated, especially considering I’ve already successfully established a non-TLS connection with the same broker. Thank you in advance for your help!
Last updated: 2024-06-19
Post by janderson on Ethercat scan for devices not picking up EL7041 as a softmotion axis
CODESYS Forge
talk
(Post)
I have a beckhoff EL7041-1000 rev 21 in my ethercat bus but it wont correctly create a softmotion axis unless i manually insert the device. scan for devices gives me an el7041-1000 without an SM3 axis.
Last updated: 2023-09-02
To search for an exact phrase, put it in quotes. Example: "getting started docs"
To exclude a word or phrase, put a dash in front of it. Example: docs -help
To search on specific fields, use these field names instead of a general text search. You can group with AND or OR.