Post by dekelec on The current baud rate could not be determined in CR0020 IFM with maintenance tool
CODESYS Forge
talk
(Post)
It could be a problem with the cable pinout on either side: 9 pin D-SUB connector (male) - PC side Pin Potential: 1 n.c. 2 RxD 3 TxD 4 n.c. 5 n.c. 6 GND 7 n.c. 8 n.c. 9 n.c. Shell Shield Check if TxD and RxD cross between pins 2 and 3 (what is the Recive signal/wire to one device it's a Transmit signal/wire for the othe device) or with COM port settings: Bits per second: 9600 Data bits: 8 Parity: None Stop bits: 1 Flow controll: None
Last updated: 2024-07-09
Post by joschi2804 on Licensing info not available.
CODESYS Forge
talk
(Post)
Hi, maybe this fixes your problem. At least this was our issue back then. We tried to run the codesys runtime environment on an embedded Linux system. The problem on our side was that we changed the WORKDIR directory in the /etc/init.d/codesyscontrol script to /home/user/codesys, but we forgot to copy all files (including the hidden files) from the initial WORKDIR (I am not sure but I guess the initial WORKDIR was /var/opt/codesys) to the new one. After copying those files and restarting codemeter and codesyscontrol, we were able to upload licenses. Hope this help BR Josef
Last updated: 2024-07-10
Post by xiaolo on Raspberry Pi 5
CODESYS Forge
talk
(Post)
Does Ver. 4.12 support Raspberry Pi 5? I have three issues. The first issue is that Codesys cannot detect the RPI 5 when I want to download the runtime. When assigning the IP Address manually then I can download the runtime. The second issue is that I cannot connect to the RPI to download a program. Sometimes the window pops up and it ask for the user credentials, but it is still not connecting. The third issue is that I cannot connect to an ESP32 configured as a Modbus Slave with a Raspberry Pi 4B. I can connect to the ESP32 via a Radzio! Modbus Master Simulator. I am also missing the function Write Holding Registers in the setup of the slave. Are this known issues and when it will be solved?
Last updated: 2024-07-12
Post by alez on CANopen safety , SRDO error behavior
CODESYS Forge
talk
(Post)
I have a project in which there is a Safety device in CANopen, and the PLC interfaces with it as Master. I would like to understand if it is possible to set the behavior in case one of the SRDOs that I receive from the slave is no longer received. From what I have seen, if the SRDOs are not received, the CANopen safety status becomes "Not in progress" and the mapped variables freeze at the last value detected. I want to understand if it was possible to set the variables connected to the SRDOs to take a default value (e.g. zero) in the event of a CANOpen error during reception.
Last updated: 2024-07-15
Post by amy123 on Alarm Manager Example Alarm Client doesn't Populate
CODESYS Forge
talk
(Post)
Hello, I tried to run the example project from https://forge.codesys.com/prj/codesys-example/alarm-manager/home/Home/ However, I can not get the interface for Alarm History 12 Alarm Manager client to populate with any alarms. 'udiResult := AlarmManager.g_AlarmHandler.RegisterClient(itfAlarmManagerClient12, ADR(arritfAlarmsFromHistory12), iMaxCountAlarmsFromHistory12);' when I look at itfAlarmManagerClient12 its always empty. What is confusing is that when I simulate 2 alarms, iCountActiveAlarms 12 has a vlaue of 2, associated with itfAlarmManagerClient12 - so that appears to work. And yet, its useless as the ProcessAlarms Function can't extract anything from the empty array. I dont understand how these arrays are supposed to be populated and why its not working. Any help would be greatly appreciated!
Last updated: 2024-07-15
Post by peterned on Array to String
CODESYS Forge
talk
(Post)
max. string length in Codesys is 255 chars. It's not possible to cram 20,000 things in a string. If you need to send the data to another device, send the whole data[] array (as byte array, without doing anything to it) and extract the information on the other end. As each struct member has a fixed size (81 bytes, as per you declaration), this will be easy. To save some resources, consider declaring string lengths - e.g. if the max possible length for key is 10 chars, declare it key: STRING(10); and it will occupy 11 bytes instead of 81
Last updated: 2024-07-20
Post by hazarath on How extract JSONElement containing Array data
CODESYS Forge
talk
(Post)
I want to extract each element of an Array. Can someone help me with this. When I use JSONElementToString (part of JSON Utilities SL), I am seeing output as "ARRAY" instead of actual data. Here is the JSON content that I want to read : { "value1Unit": { "units": "M" }, "data": { "stepSize": 300.23, "points": [6,8] } } I would like to read each item of the element "points" i.e. 6 and 8. Here is the code I used, // Reading the content as JSON reader ( xExecute := execute , pwData := ADR ( converted_value ), jsonData := jsonDataStorage ); // Get the JSON Element jsonDataStorage.FindFirstValueByKey( wsKey := fidKeyVar, diStartIndex := searchElem, jsonElement => jsonElement ); JSON.JSONElementToString ( element := jsonElement , wsResult := valueWstring ); The content of the output of valueWstring is shown as "ARRAY" instead of the array items i.e. 6 and 8 Please can someone help me.
Last updated: 2024-07-30
Post by paulg on Converting hex bytes to float
CODESYS Forge
talk
(Post)
I'll be capturing a hex stream over serial into a RasPi and I'd like to convert a group of bytes into a float. I see this is available (https://content.helpme-codesys.com/en/CODESYS%20Development%20System/cdsoperatorrealto.html) but not its inverse (i.e. BYTE_TO_REAL). The packets will be 18 bytes but I'll be selecting 4 byte segments from the middle, swapping byte endianness (i.e. changing 0x51847641 to 0x41768451), and converting to float; I believe they adhere to IEEE 754. Is there a pre-built function for some or all of this, or do I need to follow (https://forge.codesys.com/forge/talk/Engineering/thread/dc5829c7ea/)? Thanks!
Last updated: 2024-08-02
Post by abrarsk on SysCom Library Usage
CODESYS Forge
talk
(Post)
Hello all, I am facing issues with using SysCom library. With SysCom23 library things were simple but since we are migrating to 64bit systems, I am writing a Porting program. With SysCom23, opening the comport was as simple as providing the ComPort no. which returns the Handle as a DWORD. dwHandle:=SysComOpen(Port); But the new library is a bit different. It is asking for 2 input parameters to open the Com Port - Port Number and POINTER to RTS_IEC_RESULT IF hCom = 0 THEN hCom := SysComOpen(ComSettings.sPort, ADR(pResult)); How should I use the RTS_IEC_Result? I can find RTS_IEC-REUSLT under SysType2Interfaces of SysCom library. Also, can someone give me a general understanding of this RTS_IEC_REULT and RTS_IEC_HANDLE, etc.?
Last updated: 2024-08-05
Post by eguerra on Error in ScriptingEngine Docs - create_pou()
CODESYS Forge
talk
(Post)
In the ScriptingEngine documentation there seems to be an error (or missing information) in the ScriptIecLanguageObjectContainer part ( https://content.helpme-codesys.com/en/ScriptingEngine/ScriptIecLanguageObjectContainer.html#ScriptIecLanguageObjectContainer.ScriptIecLanguageObjectContainer ). The description of the function create_pou() doesn't specify the correct arguments requested, it only says create_pou(type: SpecialPouType) and a script using the documentation definition of the function will raise an error. I tried passing the function arguments similar to the ones specified for the create_dut() function and it seems to work fine: create_pou(name, PouType) , name : str UPDATE: The offline help has the correct definition IExtendedObject<IScriptObject> create_pou( string name, PouType type = PouType.FunctionBlock, Nullable<Guid> language = null, string return_type = null, string base_type = null, string interfaces = null )
Last updated: 2024-08-05
Post by sangeetnenwani on Test Driver Availability in CODESYS 64-bit and Test Manager 5.1.0.0
CODESYS Forge
talk
(Post)
I’m operating with CODESYS in a 64-bit configuration and the Test Manager at version 5.1.0.0, where I’m attempting to use project scripts from an earlier version. These scripts call for certain test drivers that are not present in my installation. It’s unclear whether the absence is due to the 64-bit system, an update in the test drivers, or if I need to enable or install additional elements. For instance, the loadproject(Codesys.Base) command is missing, but loadproject(testmanager.project) is available. The FileIO command for CODESYS isn’t accessible, yet the testmanager’s driver for it exists, as does the execuptscript command.
Last updated: 2024-08-06
Post by sangeetnenwani on Test Driver Availability in CODESYS 64-bit and Test Manager 5.1.0.0
CODESYS Forge
talk
(Post)
I’m operating with CODESYS in a 64-bit configuration and the Test Manager at version 5.1.0.0, where I’m attempting to use project scripts from an earlier version. These scripts call for certain test drivers that are not present in my installation. It’s unclear whether the absence is due to the 64-bit system, an update in the test drivers, or if I need to enable or install additional elements. For instance, the loadproject(Codesys.Base) command is missing, but loadproject(testmanager.project) is available. The FileIO command for CODESYS isn’t accessible, yet the testmanager’s driver for it exists, as does the execuptscript command.
Last updated: 2024-08-06
Post by alimans on OPC-UA Server, Symbol Set: Raise an error: Object reference not set to an instance of an object.
CODESYS Forge
talk
(Post)
Hi everyone, I just created a very simple library without any code and, added it to my very simple project. after adding this library, I get an error when I try to open "Symbol Set" in "OPC UA Server" in "Communication Manager". Here is the code of my POU in the library: FUNCTION_BLOCK POU VAR eCommand : (CMD_NONE:=0, CMD_RESET:=-1) INT := CMD_NONE; END_VAR Attached is the error that I get. I also noticed that by removing the enumeration variable above (eCommand), I can open the "Symbol Set" again. Anybody has any idea why this error is raised and how could I use enumeration variables without error in "OPC UA Symbol Set"?
Last updated: 2024-08-08
Post by expertplas on No connection to opc server from codesys opc client
CODESYS Forge
talk
(Post)
Hello, we have aproblen to connect our CODESYS OPC Client to the OPC Server. We installed the client according the CODESYS manual. We can browse the server and variables can be linked to the PLC. I created a self signed certificate for the CmpOPCUAClent as described. The server has a cerificate also. I copied the certificates to the trusted zone of server and client. But when it comes to data exchange we get an error message. "Communication error in data source OPC UA Library. Error ID : 7001 German : "Kommunikatinsfehler inder Datenquelle OPC UA -Bibiothek. Es wurde kein genauer Fehler angegeben. Fehler ID : 7001" It semms that there is no cerificate exchange. We are working with CODESYS 3.5 SP19 Patch 5. Can anyone here say something about this error or has an idea for a solution? Thanks.
Last updated: 2024-08-19
Post by abner on Open specific Version of Codesys Control Win V3 x64
CODESYS Forge
talk
(Post)
Hi, I have installed different versions of Codesys, 3.5.7 - 3.5.8 - 3.5.16 - 3.5.19. When I create a project in Codesys 3.5.16 and I try to open an instance of Codesys Control Win V3 x64 it always open version 3.5.19, so appear a message windows about versions of devices are different. I have tried to open it from the installation folder and always open the last version 3.5.19 C:\Program Files\CODESYS 3.5.16.0\GatewayPLC C:\Program Files\CODESYS 3.5.19.70\GatewayPLC Does somebody know how to open an specific version of Codesys Control Win V3?
Last updated: 2024-08-21
Post by gilbertamine on Comparing Arrays of structure
CODESYS Forge
talk
(Post)
Hi Everybody, I'm looking for a simple way of comparing two array of a structure. My structure is define like this : TYPE Positions_T : STRUCT PosX: DINT; PosY: DINT; PosZ: DINT; END_STRUCT END_TYPE I have multiples Var : ARRAY [0..220] OF Positions_T, that I need to compare quickly. I don't really want to do a Loop that goes by every 220 points and compare each one of them so I was wondering if there is another way. I came accross the MEM.Compare function, but it require to know the size in Bytes of the memory, and I don't know how to do that... Has anybody an idea on how to do the comparing easily ? Thanks in advance
Last updated: 2024-08-22
Post by hfelek on TargetVisu for Linux Package on runtime 4.12.0.0 install error due to Qt dependencies.
CODESYS Forge
talk
(Post)
Hi, I am trying to make my runtime support TargetViso on 4.12.0.0 runtime. First when I tried to install package I got error due to missing libraries that are generated through qt-base. After compiling and installing related qt lib when I tried to install the package, I didnt get lib dependencies error but I got another error: [ERROR] The installed QT Version does not meet the minimum required version 6.4.2. Please install version 6.4.2 or higher and try again. When I check Qt version I get the following response QMake version 3.1 Using Qt version 6.5.0 in /usr/local/qt6/lib. I tried with Qt version 6.9.0 but that didn't help. Any idea on what coudl be the reason. When I looked for codesys related processes the related libraries were included within environment.
Last updated: 2024-08-27
Post by jonathan1321351 on IO-Link write parameters Ethernet/IP
CODESYS Forge
talk
(Post)
I want to read and write parameters of an IO-Link device using acyclic messages. I have a Cube67+ in Ethernet/IP, connected to an IO-Link master. In the datasheet, I can find the parameters required for the message (Service, Class, Instance, etc.). I see the function block "Set_attribute_single" in the "EthernetIP Services" library, but I'm not sure how to correctly send the index and sub-index for the IO-Link device. The class in the datasheet is 0x80 for the IO-Link Parameter Object, but it’s not present in the CPIClass enum. Is there another function block more suitable for configuring IO-Link devices? (similar to "iol_call" in PROFINET or what’s used in EtherCAT).
Last updated: 2024-09-02
Post by jonathan1321351 on IO-Link read/write parameters Ethernet/IP
CODESYS Forge
talk
(Post)
I want to read and write parameters of an IO-Link device using acyclic messages. I have a Cube67+ in Ethernet/IP, connected to an IO-Link master. In the datasheet, I can find the parameters required for the message (Service, Class, Instance, etc.). I see the function block "Set_attribute_single" in the "EthernetIP Services" library, but I'm not sure how to correctly send the index and sub-index for the IO-Link device. The class in the datasheet is 0x80 for the IO-Link Parameter Object, but it’s not present in the CPIClass enum. Is there another function block more suitable for configuring IO-Link devices? (similar to "iol_call" in PROFINET or what’s used in EtherCAT).
Last updated: 2024-09-04
Post by khaledkhalil on Question about the hairaichy of UaExpert
CODESYS Forge
talk
(Post)
Hello, I am Examining this Example from Codesys Tutorial about OPC-UA server here https://www.youtube.com/watch?v=aJhzN3Uk-Do&list=PLWtD08CpmZcSV26aWh1axCAef5c5HxX-3&index=1&t=1167s. Now i am running to problem, when i create instances and i want them to appear directly under the object directory, However, it always appear with me under Objects >> Device set >> Device Name in CODESYS. I need to know how i can change the directory of my instances 'inst_3' and so on. So they can be under objects directly. I tried to modify the settings, but couldn't find any leads till now. Thanks in advance for helping
Last updated: 2024-09-12
Post by opineiro on How to manage variable types larger than 64 bits - Ethernet/IP
CODESYS Forge
talk
(Post)
Hi there, I have a Keyence bar code reader connected to my plc through Ethernet/IP. The Bar code is 20 digits long (like 30100790020493036016), the scanner reads it correctly (I can verify that through the keyence software) but when it sends it through ETH/IP, it doesn't fit into a 64 bit variable and it trunks the data.(I've tried ULINT and LWord without success). When I loaded the EDS file, the read variable was defined as a byte with 128 bits length, which is quite strange for me. (see attached picture) How do I manage this variable? Thanks!
Last updated: 2024-09-23
Post by jacobwago on v3.5 SP19 - Modbus TCP Devices - Channel Limit?
CODESYS Forge
talk
(Post)
Hello, I have experienced the same issue as described above but for the Modbus Serial configurator. Looking for a solution. In v3.5 SP19 Patch 7 the Modbus Serial Master Slave configurator has a "virtual" limit of 10 channels. In v3.5 SP18 Patch 5 this virtual limit does not exist. I can successfully copy back and forth from 18 to 19 with out any build error. However, this is not a good solution for our customers. What is even more confusing is that the IoDrvModbus library is the same version (4.3.0.0) for both SP18 and SP19. Please help in providing a fix to the virtual channel limit of 10 in SP19. Thanks,
Last updated: 2024-09-29
Post by andrebrandt on FB string and naming
CODESYS Forge
talk
(Post)
Hi Tim. Not quite correct. What i'd like, is when you place the FB in prog, i choose a block NTC10k, and name this RT401. What i'm trying to do, is to get the name RT401 automaticly into the FB, so i can put this into the string i pass in a struct. So in var in POU, i saw this a place i could do this, RT401: NTC10k(Tag:='RT401'), but i can't get this to work. I shurly must have had something like this in FB: FUNCTION_BLOCK NTC10k String TAG But it's here where I'm stuck...
Last updated: 2024-09-30
Post by robinluckey on IDE window handling bugs, windows diasppear, multi monitor setups
CODESYS Forge
talk
(Post)
Codesys Windows (Main window as well as pop-ups) often appear outside of the viewable are in Windows when using multiple Monitors. This is exacerbated (happens more very often), when working on a notebook with different Monitor setups at different locations (which kind of is standard nowadays). The windows (not even the main Window) can not be recovered using standard short cuts like WIN + Arrow keys, alt + tab etc. The only way we found to recover the windows is by changing the Monitor positions in thew Windows Display Settings and than changing them back EVERY TIME a pop us is displayed. This makes using Codesys close to unbearable. All my colleagues face the same problem and do not have this problem with any other IDE. Please help.
Last updated: 2024-10-11
Post by siscu on Raspberry i2c master device
CODESYS Forge
talk
(Post)
I want to implement an extended I2C master for Raspberry Pi Control. I was hoping for it to be as easy as creating a library with a FB that extends i2cMaster and associating it with a device following the forge drivers documentation, but I haven't managed to make it work as the driver behaves only as an i2c slave. I'm thinking this is because the forge forum only talks about extending i2c, and the master portion is omitted since most users won't want to add a custom one. I'd like to know if I'm doing something wrong. Is it really possible to make an I2C master extension device? If so, are there public examples we can check out? Any info on this topic will be appreciated.
Last updated: 2024-10-16