Post by garmusd on Raspberry Pi 5 GPIO not working.
CODESYS Forge
talk
(Post)
Hi, Codesyscontrol 4.13.0.0 Raspberry Pi5 64bit with latest updates. Cant get working GPIO - no output and no input. SPI/I2C not tested. GPIOs B+/Pi2, Input/Output is set in the parameters, assigned variables int the Mapping. Absolutely no reaction. Do I need to configure anything else to make it work? Thanks!
Last updated: 2024-09-26
Post by phoward131 on Alarm filtering latch variables
CODESYS Forge
talk
(Post)
I am having the exact same issue and was wondering if you ever found the problem? The sample program does exactly what it's supposed to with filtering but when I implement it the exact same way in my program, the alarm list just goes blank when I attempt to apply a filter.
Last updated: 2024-10-28
Post by phoward131 on Alarm filtering latch variables
CODESYS Forge
talk
(Post)
I actually just found the solution maybe. If anyone else is running into this, go to your Project Settings > Visualization > Advanced (check 'Visible' to see advanced settings) > UNCHECK 'Activate property handling in all element properties.' I am not sure what else unchecking this might affect but it seems to allow the alarm table to be filtered as expected.
Last updated: 2024-10-28
Post by sturmghost on Initialization of visualization variables and cyclic code execution
CODESYS Forge
talk
(Post)
I'm looking for a smart and short way to implement initialization of visualization variables depending on the visualization input. For an easy example consider a rectangle which rests at XPos := 0 when the input state is false and at XPos := 50 when the input state is true. My visualization variables look like this: VAR_IN_OUT State : BOOL; END_VAR VAR XPos : INT; END_VAR I put this rectangle via a visualization frame element into another visualization and link a frame reference variable with the state to it. If the variable is true, the rectangle should rest at XPos := 50 and false at XPos := 0 at visualization init but how should I assign the 50 or 0 to the internal visualization variable XPos? I would need some init-methode for the visualization but I dont want a global init-method for such tasks. I want to do it inside of the visualization element but I can't see any solution for this? It would be good to be able to define ST-code within the visualization element which runs cyclic at each VISU_TASK task-cycle then I could just check the input state and change the XPos accordingly. Does someone have a solution?
Last updated: 2023-10-01
Post by sean-barton on Function block method default arguments
CODESYS Forge
talk
(Post)
I have default arguments specified for function block methods but when calling a method, an error is produced requiring me to supply all the arguments despite there being default values. According to the online documentation, under section "Calling a Method" and subsection "argument passing" of the following link: https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_obj_method.html "Passing an argument for an input ... can be omitted ... for which a default or initial value was specified in the declaration..." I have found this to be the case for all Codesys IDEs I've used, 3.5.11, 3.5.16, 3.5.17, 3.5.19. Am I missing something?
Last updated: 2023-12-21
Post by jdjennings1962 on Trouble accessing Math functions in OSCAT library
CODESYS Forge
talk
(Post)
Hi all, I am trying to utilize the ARRAY_SDV standard deviation function, part of the Math group in the OSCAT library downloaded from the CODESYS store. My Codesys version is 3.5.19.10. When I add the OSCAT to my Library, it shows a subset of the library (Standard) as fully installed and signed (see pic). However, the Math functions are not in this Standard group. The Math functions I need can be viewed as source code in the full OSCAT_BASIC, though this the symbol next to this library suggests it is source only and not fully installed. When I try to declare an instance of the ARRAY_SDV function in a program, it is not known. I have tried reinstalling and Building . . . Any help would be greatly appreciated. Jeff
Last updated: 2024-01-06
Post by alexgooi on FB_INIT in library
CODESYS Forge
talk
(Post)
Dear Forum, I currently have a challenge. I have a library with some communication classes. These communication classes need to be linked to an interface like this: Devices_and_controllers.Comm_Frame.Modbus_GVL_Link.KNX_TCP[Interface_Index] := THIS^; This is executed via a FB_Init() method. When I try to do this in a program this works fine. But when I declare the FB_Init() in the library the FB_Init() method is being called but the link is not made (interface still has the value 0000000000). The Objects and interfaces are defined in the library (GVL), so Iβm assuming the data should be there. When I call the FB_Init method explicitly in the program it also works fine. Whys is this not working when it is all defined in the library? And is it even possible to create a structure like this in Codesys? Kind regards Alex
Last updated: 2024-05-22
Post by installwhat on C0077 on one machine but not another
CODESYS Forge
talk
(Post)
I have a version of codesys 3.5.16 on my local machine and a vm. The local machine has loads of codesys versions and libraries installed etc. I can open the FPosCR_Example_Project_SP16_patch1 project on my vm without any errors. On the local machine I get the error C0077: unknown type IoDrvEthercatLib.ETC_CO_SdoWrite. I can, on the local machine, declare a var of type IoDrvEthercatLib.ETC_CO_SdoWrite and include it in the code without adding an extra error. The problem only seems to affect the library. This is seems more an issue with my codesys set up rather than something with festo. I would like to know the possible causes. I understand most of the library manager features but it's not clear how to find the cause. Thanks
Last updated: 2024-06-11
Post by sukrit on What licenses are required for runtime on raspberry pi cm4
CODESYS Forge
talk
(Post)
We have developed a project for 2 servo motors using raspberry pi computemodule 4 on ethercat master. we are using web visualization for display different screens. project is running well in demo. we want to implement it in production envoirment. being new still wondering which licences i need. Can We get this information in codesys devlopment software. code size is approx 5 mb, 1 instance of etharcat master and aproox 100 variables in visaualization.
Last updated: 2023-10-17
Post by tvm on multiply gives negatives
CODESYS Forge
talk
(Post)
It's probably because you have an INT in the input to the MUL function, which will then try to output an INT as well. INT variables can only handle values of -32768 to 32767. Your value of 523000 won't fit in an INT, so it turns into an invalid number. Use a DINT. This is usually better for working with time values anyway, because time values are all 32 bit. Or if you can't, use INT_TO_DINT(gvlp.detectie_nalooptijd_s) in the input to the MUL function.
Last updated: 2024-01-04
Post by matt-s on HMI Pushbutton/Move Instruction
CODESYS Forge
talk
(Post)
I have not gotten to the bottom of this yet no. I have double check that the variables are correct linked. When online with the program I can see the button and rung going true for the move instruction, yet it does not change. Forcing the bit in the program does change the value in Groov View. I am kind of at a loss here, especially since the other POU(For the pumps) does the same thing fine.
Last updated: 2024-02-02
Post by dominggus on Recipe Manager - RecipeManCommands, load & write wrong values, Bug?
CODESYS Forge
talk
(Post)
I still have the same problem even when updating to CODESYS Recipes 4.3.0.0. My scenario: I'm trying to save/load an array of structs using the Visu: - Execute Command > "SaveRecipeAs" works properly - Execute Command > "LoadWriteRecipe" works not entirely: the structs of array[6] and array[7] should have been empty but were duplicates of array[4] and array[5]... the struct contains 26 variables and the array's length is 30.. Maybe there is a upper limit on recipe variable count?
Last updated: 2024-03-02
Post by ewi04 on Recipe Manager - RecipeManCommands, load & write wrong values, Bug?
CODESYS Forge
talk
(Post)
It's good that you've found a workaround. But it's bad that you need one. The array length auf my struct is 16. My struct also contains other arrays of structs. It contains a total of 1716 variables. I have tested saving and loading extensively under version 4.3.0.0. It looks good. I couldnβt find any problems. Maybe it helps to reinstall the update (see previous post). Otherwise you could try my test project (first post). This should work with version 4.3.0.0.
Last updated: 2024-03-04
Post by stuartjr on Disabling forcing of specific variables
CODESYS Forge
talk
(Post)
Is there a way that I can create a variable in a GVL that I can control with logic but a user can not put a force on this variable. I have looked at the access rights but this seems to only limit editing the GVL or POU. This variable will only be assigned a value in one POU but it will be used throughout many other POUs.
Last updated: 2024-03-15
Post by stuartjr on Disabling forcing of specific variables
CODESYS Forge
talk
(Post)
OK.. so maybe I miss understood for how the forcing order works. It seems that the force list is applied at the beginning of every task call (I'm assuming this based on what I am seeing). If I force my variable FALSE and then write it TRUE in a task, then it stays TRUE for that task, but then in the next task it will go back to FALSE.
Last updated: 2024-03-15
Post by valenting on Problem with Licenced Software Metrics
CODESYS Forge
talk
(Post)
Hi, When I try to install my codesys program with the new application-based licensing, I have an error "it exceeds the scope of the license agreement. See Device > Licensed Software Metrics" In the Licensed Software Metrics section, I see a code size < 3MB and less than 2700 variables in visualiaztions. I'm using a license "Control Basic L" with "Codesys Visualization L" option, so it should be enough with these metrics. What can I do ?
Last updated: 2024-04-22
Post by alez on CANOpen SDO to write VISIBLE STRING
CODESYS Forge
talk
(Post)
Hello, I am experiencing difficulties in configuring a CANopen device by sending SDOs. In particular I am attempting to write an Object Dictionary that has VISIBLE STRING as the Data Type. When I try to configure the sending of an SDO from Codesys to configure this parameter I am not allowed to enter a string value. In my particular case I am trying to change the Manufacturer Device Name ( Index 0x1008 ). Could it be that Codesys doesn't manage these types of variables?
Last updated: 2024-04-29
Post by mubeta on STRUCT AT %MW1000
CODESYS Forge
talk
(Post)
This is normal and correct since in CoDeSys static addressing of variables uses the IEC method. A LONG tag has the size of 8 bytes, so %ML0 coincides with %MB0 ... %MB7; %ML1000 with %MB8000 ... %MB8007. (Similar reason for word and other formats). Also the reason the compiler won't let you map the structure to a %MW depends on the fact that the individual base elements are manipulated to 64 bits regardless of the smaller size. That said, it makes me strange that you cannot write a parser without making use of static memory allocation.
Last updated: 2024-08-13
Post by timvh on Unable to Connect to Modbus RTU Device
CODESYS Forge
talk
(Post)
If your Control Win is the Modbus "Master" then your configuration should be something like: Modbus_COM (Serial port) - Modbus Master (this is the Control Win SoftPLC actively setting up the communication) - Modbus Slave (this is then your WAGO 750-315) You need to add channels to the Modbus Slave configuration to inform the master which variables to read/write from the Wago module. The way you configured it now, the Control Win is also a slave. PS, don't forget to put the PLC (Control Win) in Run.
Last updated: 2024-09-03
Post by balazska2 on Position values with integer variables
CODESYS Forge
talk
(Post)
Hello guys! https://content.helpme-codesys.com/en/CODESYS%20Visualization/_visu_elem_label.html My question: Could I give an integer variable to the Position records (in the Element list => Position => width / height)? If yes, how? I defined a TEST integer variable with 300 value. I tried to add this variable to the width record (.TEST or only TEST), but if I saved, the value jumps back to 0. Thanks for your help! :)
Last updated: 2024-10-03
Post by varshag on Trying to pull Logged In user details and certain other variable values and in turn log to a database
CODESYS Forge
talk
(Post)
Hello All, I am new to Codesys and am trying to create a simple project which would let me log to a 6 column database table. I can use a push button on Visualization to initiate the logging. Column 1:Timestamp Column 2:Full name or Initials of Logged in operator Column 3,4,5,6: Certain variables Any help is highly appreciated. Thank you.
Last updated: 2024-11-07
Post by alex00 on DCS / Central Engineering with Codesys support
CODESYS Forge
talk
(Post)
Hello together I'm currently investing in possibilities to have a central engineering software / system for Codesys based controllers. Something like a DCS / SCADA depending on where you see the functionality. We plan to use more or less vanilla codesys. The tool should support the following: - Connect to multiple PLC's in a project to see its variables and debug it. - Central Engineering capabilities (for example shared libraries in a project). - Download the new code / binaries to the plc. - Maybe have functionality to combine visualization elements and logic together. - See the live status variables on all the systems (crosscommunication). I see that codesys theoretically supports engineering of multiple PLC's, but I couldnt find to much functionality for a DCS type of operation, but that could be lack of knowledge. Any tips from you? Is Codesys good enough for this and maybe there are some manufacturers which build around it? Or are there good tools on the market with Codesys support (and the engineering is separate, but download to codesys possible). The use case is distributed energy installations like Heating pumps, Photovoltaics, etc. All these installations should have a PLC with codesys installed and run in one larger network, the PLC's are connected via VPN. Thanks for your inputs Greetings
Last updated: 2024-02-19
Post by alex00 on DCS / Central Engineering for Codesys
CODESYS Forge
talk
(Post)
Hello together I'm currently investing in possibilities to have a central engineering software / system for Codesys based controllers. Something like a DCS / SCADA depending on where you see the functionality. We plan to use more or less vanilla codesys. The tool should support the following: - Connect to multiple PLC's in a project to see its variables and debug it. - Central Engineering capabilities (for example shared libraries in a project). - Download the new code / binaries to the plc. - Maybe have functionality to combine visualization elements and logic together. - See the live status variables on all the systems (crosscommunication). I see that codesys theoretically supports engineering of multiple PLC's, but I couldnt find to much functionality for a DCS type of operation, but that could be lack of knowledge. Any tips from you? Is Codesys good enough for this and maybe there are some manufacturers which build around it? Or are there good tools on the market with Codesys support (and the engineering is separate, but download to codesys possible). The use case is distributed energy installations like Heating pumps, Photovoltaics, etc. All these installations should have a PLC with codesys installed and run in one larger network, the PLC's are connected via VPN. Thanks for your inputs Greetings
Last updated: 2024-02-19
Post by wbj0t on mobus tcp slave device. read/write holdings with 2 variables.
CODESYS Forge
talk
(Post)
Hi there. I have an issue to read and set time for the controller. In the issue many registers described as writable by 6/16 functions, and, in this time, also(!) readable! For example: I have time registers: min, hour, day, mon, year. By specifications it is possible check time (so I need always update these varibles in loop) and set time by writing these same registers, BUT how to set, if they will immediatle updated by current time after writing? So, I need to separate one address at two variables. I have seen option mark: Overlay of the process image by the holding and input register. I understand this so: When I READ by function 3, I will get variable that connected with the same INPUT address and when I WRITE by 6/16 this will change second variable that connected with HOLDING address. BUT, this mark doesnt work, when I write 6/16 and try to get by function 3, I will get written value instead INPUT variable. So, what to do?
Last updated: 2024-03-20
Post by bjarne-pagaard on Communication between applications on same device/controller/runtime (Win RTE 3.5.20.20)
CODESYS Forge
talk
(Post)
Hi, I would like to divide a project into multiple applications - as a minimum: one handling visualization and Alarm Manager, one handling I/O and plant control logic. But how to exchange variables between the applications? What have you done to get such a solution? In versions 3.5.19 and earlier, you can have Child applications, where the children can access a GVL in the Parent application. Children apps is no longer possible in 3.5.20 - but you can have 'sibling' apps - Several apps directly under PLC Logic, that is. But how do they best communicate? The Communication Manager / Data Sources Manager is sort of possible via OPC UA, but it seems like overkill and with some limitations - for example no ARRAY OF STRUCT possible this way. If you have separate devices in your project, you can exchange data via 'CODESYS ApplicationV3', but not other applications in the same device (see attachment Datasources.png). You can do it via 'Select the project type'->'Other Project' and select the same project file, but this leads to crashing the Development system when working with the variables afterwards. It would be great to hear your thoughts / experiences on this topic - Bjarne
Last updated: 2024-09-27