Post by leafy on Use third party actuator with IO-Link Master (IFM)
CODESYS Forge
talk
(Post)
Hey there! I am currently doing a little automation project for uni. I am trying to integrate a control-valve-system (Buerkert AirLINE Field) in my IO-Link environment. With IFM sensors, I used their pre-built function blocks, but with this third-party device, i need to write my own function block. Thankfully, IFM provides a generic sensor-fb so I can write my own FB with "extends" and "super". So far, so good. I found the IODD and some other documentation and I thought I get how it works, but somehow can't really get it to work at all. From my understanding, i need to write data into the PDO-Array. But i get confused with the indices and subindices of IO-Link. I'll append the IODD and some screenshots of my project. There is an AOI for LogicXDesigner, but I can't use that in Codesys. I hope someone has integrated a IOL-device in Codesys before and can help me with this. Cheers leafy
Last updated: 2024-04-16
Post by jrsantab on Remote connection to ifm PLC & HMI
CODESYS Forge
talk
(Post)
We have finally solved the problem. The version of the Gateway in the computer that worked (3.5.11.0) and the one that didn't (3.5.17.30) was different. We have three different Codesys 3.5 versions installed because we work with different controllers. I believe that, depending on the sequence you follow to install the versions you get a different Gateway version. To solve the problem you first have to disable the "obsolete" services. Open services, serach for (in our case) CODESYS Gateway V3 Version 3.5.11.0 CODESYS ServiceControl Version 3.5.11.0 I stopped the services and changed to Manual Start. Then you have to create the new services. In our case, from a Command Prompt session (cmd): SC CREATE "Codesys GatewayService Rigual" binpath="C:\Program Files\CODESYS 3.5.17.30\GatewayPLC\GatewayService.exe" and then SC CREATE "CODESYS ServiceControl Version 3.5.17.30" binpath="C:\Program Files\CODESYS 3.5.17.30\GatewayPLC\CODESYSControlService.exe" remember also to set them as Automatic Start!
Last updated: 2024-04-22
Post by sigurdrb on send appliaction files to wago plc (codesys 3.5) via ssh
CODESYS Forge
talk
(Post)
Hi, I was hoping I could send the two files "application.app" and "application.crc" directly to the directory "/home/codesys/PlcLogic/Application" instead of logging into the device with codesys, downloading the program to the controller and then do the "create boot application", so it will reboot with the correct program running. I think i also need to edit the file "eRUNTIME.cfg" located in the "/home/codesys/ folder, because when I create the boot application from the codesys IDE, these lines are added to the file: [CmpApp] Application.1 = Application [SysFileMap] /home/codesys/PlcLogic/Application/Application.app=0x212520, 0x2DBC747E, 2DBC747E.app I think the "eRUNTIME.cfg" file is the same as CODESYSControl.cfg I also dont know the purpose of the hexadecimal numbers etc. that is generated. When I tried to replicate what codesys was doing, I placed the same files in the same folder as when codesys generated the boot file. And also added the lines in the eRUNTIME.cfg file: [CmpApp] Application.1 = Application [SysFileMap] /home/codesys/PlcLogic/Application/Application.app The controller did not boot up with any program, so my method did not work at all. I guess these lines tells the controller to run an application and where to find it? Could any of you help me with the best way to get the compiled program to the controller without using codesys or wago-software?
Last updated: 2024-05-28
Post by jkessler on IoDrvModbusTCP_Diag not defined when using MODBUS
CODESYS Forge
talk
(Post)
Hi, Same for me ! Works in Codesys 3.5.19 but not in 3.5.20. I'm currenly using with a WAGO PLC200 [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'IoDrvModbusTCP_Diag' non dĂ©fini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit ĂȘtre instanciĂ© pour permettre lâaccĂšs [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'IoDrvModbusTCP_Diag' nâest pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlave_Diag' non dĂ©fini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit ĂȘtre instanciĂ© pour permettre lâaccĂšs [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlave_Diag' nâest pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlaveUnit_Diag' non dĂ©fini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit ĂȘtre instanciĂ© pour permettre lâaccĂšs [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlaveUnit_Diag' nâest pas un composant de 'IoDrvModbusTCP' Thanks in advance
Last updated: 2024-05-29
Post by jkessler on IoDrvModbusTCP_Diag not defined when using MODBUS
CODESYS Forge
talk
(Post)
Hi, Same for me ! Works in Codesys 3.5.19 but not in 3.5.20. I'm currenly using with a WAGO PLC200 [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'IoDrvModbusTCP_Diag' non dĂ©fini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit ĂȘtre instanciĂ© pour permettre lâaccĂšs [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'IoDrvModbusTCP_Diag' nâest pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlave_Diag' non dĂ©fini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit ĂȘtre instanciĂ© pour permettre lâaccĂšs [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlave_Diag' nâest pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlaveUnit_Diag' non dĂ©fini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit ĂȘtre instanciĂ© pour permettre lâaccĂšs [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlaveUnit_Diag' nâest pas un composant de 'IoDrvModbusTCP' Thanks in advance
Last updated: 2024-05-29
Post by jkessler on IoDrvModbusTCP_Diag not defined when using MODBUS
CODESYS Forge
talk
(Post)
Hi, Same for me ! Works in Codesys 3.5.19 but not in 3.5.20. I'm currenly using with a WAGO PLC200 [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'IoDrvModbusTCP_Diag' non dĂ©fini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit ĂȘtre instanciĂ© pour permettre lâaccĂšs [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'IoDrvModbusTCP_Diag' nâest pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlave_Diag' non dĂ©fini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit ĂȘtre instanciĂ© pour permettre lâaccĂšs [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlave_Diag' nâest pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlaveUnit_Diag' non dĂ©fini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit ĂȘtre instanciĂ© pour permettre lâaccĂšs [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlaveUnit_Diag' nâest pas un composant de 'IoDrvModbusTCP' Thanks in advance
Last updated: 2024-05-29
Post by jkessler on IoDrvModbusTCP_Diag not defined when using MODBUS
CODESYS Forge
talk
(Post)
Hi, Same for me ! Works in Codesys 3.5.19 but not in 3.5.20. I'm currenly using with a WAGO PLC200 [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'IoDrvModbusTCP_Diag' non dĂ©fini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit ĂȘtre instanciĂ© pour permettre lâaccĂšs [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'IoDrvModbusTCP_Diag' nâest pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlave_Diag' non dĂ©fini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit ĂȘtre instanciĂ© pour permettre lâaccĂšs [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlave_Diag' nâest pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlaveUnit_Diag' non dĂ©fini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit ĂȘtre instanciĂ© pour permettre lâaccĂšs [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlaveUnit_Diag' nâest pas un composant de 'IoDrvModbusTCP' Thanks in advance
Last updated: 2024-05-29
Post by jkessler on IoDrvModbusTCP_Diag not defined when using MODBUS
CODESYS Forge
talk
(Post)
Hi, Same for me ! Works in Codesys 3.5.19 but not in 3.5.20. I'm currenly using with a WAGO PLC200 [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'IoDrvModbusTCP_Diag' non dĂ©fini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit ĂȘtre instanciĂ© pour permettre lâaccĂšs [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'IoDrvModbusTCP_Diag' nâest pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlave_Diag' non dĂ©fini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit ĂȘtre instanciĂ© pour permettre lâaccĂšs [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlave_Diag' nâest pas un composant de 'IoDrvModbusTCP' [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0046: Identificateur 'ModbusTCPSlaveUnit_Diag' non dĂ©fini [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0080: Le bloc fonctionnel 'IoDrvModbusTCP' doit ĂȘtre instanciĂ© pour permettre lâaccĂšs [ERREUR] EmPlcProgram: Application [Device: Logique API]: C0004: 'ModbusTCPSlaveUnit_Diag' nâest pas un composant de 'IoDrvModbusTCP' Thanks in advance
Last updated: 2024-05-29
Post by fajean on CODESYS control on RPi starts, shortly runs, then exits
CODESYS Forge
talk
(Post)
I have a Raspberry Pi 4 we have been using for years to run CODESYS for development purposes. I recently have had to re-install the OS (Raspberry OS lite). The only change to the default configuration is not creating the "pi" user during install. I (apparently successfully) installed the 4.10.0.0 control on the Raspberry Pi. We have licences on a dongle. I am able to start the control. systemctl status shows it as running for a little while (exactly, precisely 30 seconds as per my tests, every time), then it becomes exited. I can restart the control, and the same thing happens again. Every time. In the brief moments it is running, I can log in to the PLC. Working fast and restarting the control many times, I have been able to configure users. I have been able to download my application. I have been able to run the application, and stop on a breakpoint. I have been able to connect with the licence manager and confirm the dongle is detected and licences are listed as OK. I see nothing wrong until the service just exits. I have found nothing in the logs. It is like the runtime just terminates with no error code or message after exactly 30 seconds. Any help would be appreciated.
Last updated: 2024-06-13
Post by climblinne on Calling OPC UA Methods from UaExpert
CODESYS Forge
talk
(Post)
Hello, I hope someone could help me. I installed the newest Codesys 3.5 SP 20 Patch 1. When loading the demo files from @i-campbell I can upgrade them to the latest version and everthing works on the OPC-UA client side as expected (object "a" is visible, I can use the "ExampleMethod"). Now I * remove the "Information Model", * delete the "OPC_UA_Symbols Objects", * Add "Information Model" again * add "TestRootObjectType" again and "Generate IEC declarations" * and search for mapped instances (to get instance "a" again) Very good still working as expected. Now I delete the OPC_UA_Symbols and add it again referring to the "objecttest" from 16.9.2020. Also I redo the steps from above. The result is now, that I can't see the "a" object in the "Root/Objects" folder. Why ist this and how can I make it running? I think, it could may be a different version of the UA configuration file. I tried to build my own model definition files and got the same problem (but I am really not an expert). When someone has a actual model, which is also running in the actual Codesys I would be very grateful. Or even better, how to make the correct model in e.g. UA Modeler SW (I followed the description https://documentation.unified-automation.com/uamodeler/1.6.0/html/howprojnet_sec.html).
Last updated: 2024-07-01
Post by biiebs on Aufbau von Ablaufsteuerungen ermitteln
CODESYS Forge
talk
(Post)
Hallo Zusammen, gibt es in CODESYS bei Ablaufsteuerungen weitere Möglichkeiten auĂer den AS-Einstellungen z.B. die Aufbaustruktur der Ablaufsteuerung herauszufinden? Gesamtanzahl der verwendeten Aktionen / Schritte - Im besten Fall auch die einzelnen Verzweigungen? Ich wĂŒrde den gesamten Aufbau der Schrittkette gerne als "View" in einer ĂŒbergeordneten Software abbilden lassen, da sich die Ablaufsteuerungen, je nach Projekt im Aufbau unterscheiden brĂ€uchte ich die Kenntniss ĂŒber den Aufbau dieser Schrittketten. Oder mĂŒsste ich mir hier einen "Workaround" programmieren, der z.B. bei Init erstmal den Aufbau der Ablaufsteuerung durchlĂ€uft und mir die nötigen Informationen liefert? NatĂŒrlich wĂ€re auch ein Weg den Aufbau des AS-Bausteins ĂŒber die PLCopen XML zu exportieren, jedoch mĂŒsste dies bei Ănderungen jeweils nachgezogen werden - was etwas unschön wĂ€re, falls dies vergessen wĂŒrde. Mittlerweile habe ich auch das Tool "SFC Visu Generator" gefunden, dessen Funktion im Prinzip genau das darstellt, was ich benötige - jedoch leider nur als CODESYS interne Visualisierung. Ich wĂŒrde den Export des Bausteins gerne in meine ĂŒbergeordnete Software implementieren. Gibt es hier die Möglichkeit das Vorgehen zu Erfahren oder den vom Baustein generierten Export bei mir zu implementieren? Hat hier jemand sowas Ă€hnliches schonmal gelöst? Vielen Dank im Voraus Mit freundlichen GrĂŒĂen Biiebs
Last updated: 2024-07-25
Post by trusty-squire on CNC - How to manipulate SMC_GeoInfo objects
CODESYS Forge
talk
(Post)
I have an application using CNC GCode interpolation, but I need to modify the GCode provided to the PLC based on certain parameters. I am currently attempting to modify the SMC_GeoInfo objects in the SMC_OutQueue using the code below. Note that all the other code is pretty standard and works fine, but when I add the below it errors. PROGRAM TEST VAR fbReadCncFile : SMC_ReadNCFile2; fbCncInterpreter : SMC_NCInterpreter; arrCncInterpreter : ARRAY[1..99] OF SMC_GeoInfo; pGeoInfo: POINTER TO SMC_GeoInfo; giGeoInfo: SMC_GeoInfo; // ... END_VAR // ... Some code here in order to read CNC file using SMC_ReadNCFile2 and provide to SMC_NCInterpreter pGeoInfo := SMC_GetObj(poq:=ADR(fbCncInterpreter.poqDataOut), n:=1); IF pGeoInfo <> 0 THEN giGeoInfo := pGeoInfo^; // Do some manipulation here, then update the queue at the same position MC_SetObj(poq:=ADR(fbCncInterpreter.poqDataOut) , n:=0 , pgi:=ADR(giGeoInfo) ); END_IF It throws an error when I get to the line giGeoInfo := pGeoInfo^; Error: EXCEPTION [AccessViolation] occured: App=[Sim.Device.Application], Task=[PathTask] How do I use SMC_GetObj and access the data? It creates a pointer with the value as shown in the photo, but all the dereferenced values say dereference of invalid pointer.
Last updated: 2024-07-26
Post by grant32 on RAMP_REAL FB is retaining my output value when i try to re use the FB
CODESYS Forge
talk
(Post)
Hello, I'm relatively new to PLC programming. I am trying to creat a ramp down function, I have an example here of what I am using. I can get the function to work, the issue is that the OUT (variable3) value is being held by the FB so after I use it once it no longer works. In this example i set variable3 to 100 and the rest is as seen, over the course of a minute it ramped down to 10 (as desired). But when I deenergize TEST_START, set variable3 back to 100, and then re-energize TEST_START it immediately jumps back to the previously held value 10. The reset on this block just pauses the function and holds the last OUT. In my case I will need the function to start OUT at a set value, ramp down to the IN (variable2) value, and then accept a new OUT value to ramp down next time the block is energized. Hopefully this made sense, if anyone has any advice that would be awesome!
Last updated: 2024-07-29
Post by kleeswi on Visualization scaling problem with B&R T30 panel
CODESYS Forge
talk
(Post)
The probelm arises for the B&R T30 panel after updating Codesys from 3.5.17 to 3.5.19 patch 5. We have to use 3.5.19 for other reasons so we cannot downgrade the version. The scaling problem only exists for the B&R 6PPT30.0702.20F025 panel, the B&R T50 panel and a esa lumia panel work. When we choose a fixed resolution it looks also good, however we also want to support the esa lumia panel with a different resolution. The images show the anisotropic and isotropic option. In the anisotropic option it scales the hight correctly but not the width and in the isotropic option is scales both hight and width false, it also does not start in the top left corner. Does someone have any suggestion why it does not work anymore with the new codesys version and are there workarounds? I added all versions with visualization packages as an image, visuElems is 4.4.0.0.
Last updated: 2024-07-29
Post by mubeta on parker servo and position
CODESYS Forge
talk
(Post)
In general, drives have parameter sets to adjust behaviour in such cases: position recovery, adaptation with resistant torque, out-of-position window failure, etc. (Much depends on the type of configuration set for the axis: positioner, speed controller, torque controller, etc.). I have used that type of drive very little, in only two cases and a long time ago. To tell you what is normal is impossible. I know by reputation they are very simple objects, without too many pretensions and adjustments possible. Try running traces by monitoring actual position, motor current, torque and following error. These are the most sensible curves to understand what is going on. Maybe by fine tuning the motor tuning, the current controller or the speed controller you will get something closer to what you want. For example, from DS, the motor has a standstill torque of 3 Nm. Observe with traces whether this is effective: motor current trend. And afterwards, when you have your own accurate picture of the situation, you can also hear from the product's local support to see if you can steal a few more things from it performance-wise.
Last updated: 2024-08-05
Post by egau on Hard shutdown: no code on device after power on
CODESYS Forge
talk
(Post)
Hi, We have a machine running Codesys on a Windows IPC (CODESYS Control Win v3 - x64). When we hard shutdown the machine, the code on the PLC sometimes becomes "corrupted" after a power on (When trying to login to the PLC, we get the message "The application 'Application' does not exist on device."). I've noticed these errors in the logs, but I'm not sure what to make of them. We are not using any RETAIN variables in our code, although I'm not sure about referenced librairies. (we are using the persistence manager). I'm pretty sure that not doing a graceful shutdown is the root cause of this. This being said, what is the proper way of doing a graceful shutdown? Is putting the Codesys application in "stop" sufficient? I know how to implement this, so if it works then it would be a quick fix. However, I think we need to add a UPS, which would detect power loss and inform the PLC that it needs to initiate its shutdown, and then the PLC would shutdown gracefully. Any help with this will be greatly appreciated :)
Last updated: 2024-10-03
Post by egau on Hard shutdown: no code on device after power on
CODESYS Forge
talk
(Post)
This explanation aligns with the issues weâre experiencing with our machines. The scenario I described is happening with one of them (letâs call it Machine A). This machine is identical to another one (Machine B), except for some custom code that facilitates communication with an external Beckhoff PLC for MES integration in the production line. Machine B has been powered on and off daily for at least three months and has never had this problem. Given that, I highly doubt the MES custom code is the cause of the code corruption. This being said, your explanation does seem plausible. However, if faulty EtherCAT cables were the issue, why wouldn't the error occur during normal operation? Why would bad cables only cause problems during a hard shutdown? One last question: When you encountered this behavior, did you see a similar error in your logs? i.e, an "AccessViolation" exception in the EtherCAT Task?
Last updated: 2024-10-03
Post by etienneneu on loading delay with the option "check client animations and overlay of native elements"
CODESYS Forge
talk
(Post)
Hey NicolaG_89, thanks for the tip. But I have seen in the developer tools of the Webclient that a multiple fetching of the image and script data occurs when changing frames (HTTP code 304 NOT Modified), although these are already in the clients cache, which leads to unnecessary loading of resources from the web server. This behavior can also be found if the option âSupport client animations and overlay of native elementsâ is deactivated, but this does not lead to such long delays. I had already tested loading all Visu elements so that everything was fetched once before they could be used. But that didn't help either. To prevent this behavior (permanent fetching), I have used a different way of switching the Visu elements in the VisuDemo Project, which also uses HTML5 control elements. I implemented this with the visibility of entire Visu elements. As a result, it only has to be fetched once and does not have to be fetched again when reloading. But I am still unsure about this implementation if the scope of the visualization becomes larger, as the Codesys visualization documentation advises against using many invisible elements. Best regards Etienne
Last updated: 13 hours ago
Post by solidlogicguy on Little endian to Float from Modbus RTU
CODESYS Forge
talk
(Post)
Hello, I got a device from which I require to read values from I am using a WAGO PLC 750-8212 and I am communicating through Modbus Master FUNCTION BLOCK from library WagoAppPLCModbus in Codesys 3.5 to this device. I already receive data from the device that is a CVM to monitor voltage from a fuel cell. The technical support of the company that makes these devices says that the data is sent in little endian form. And I want to convert it to a float value. The tech support sent me the next instructions of how to do it but I am new using codesys, so any advice or help I will really appreciate so much. Message from tech support: The process is complicated, better to do it with already implemented library in the language/program you use. Basically the process should be next: To convert the two Modbus registers containing parts of a 32-bit float in little-endian byte order to a floating-point number using mathematical operations, you first need to combine the two 16-bit integers (assuming reg1 is the lower word and reg2 is the higher word) and then interpret the result according to the IEEE 754 standard. Given: - Register 192 (reg1) = 4096 - Register 193 (reg2) = 14884 Step 1: Combine the two registers. Since we are dealing with little-endian byte order, reg2 is the high word, and reg1 is the low word: combined = reg2 * 2^16 + reg1 combined = 14884 * 65536 + 4096 combined = 975175680 + 4096 combined = 975179776 Step 2: Convert the combined value to binary: combined_binary = '1110101101011100000000000000000' Step 3: Split the binary into IEEE 754 components: Sign bit (1 bit): 0 Exponent (8 bits): 11101011 Mantissa (23 bits): 01011100000000000000000 Step 4: Convert the binary exponent to decimal and subtract the bias (127 for 32-bit floats): exponent = int('11101011', 2) - 127 exponent = 235 - 127 exponent = 108 Step 5: Calculate the mantissa as a fraction: The mantissa in IEEE 754 format is the fractional part after the leading 1 (which is implicit). Therefore, we need to convert the binary mantissa to decimal and add the implicit leading 1: mantissa_fractional = 1 + int('01011100000000000000000', 2) / 2^23 mantissa_fractional = 1 + 18688 / 8388608 mantissa_fractional = 1 + 0.002227783203125 mantissa_fractional â 1.002227783203125 Step 6: Combine the sign, exponent, and mantissa to get the float value: float_value = (-1)^0 * mantissa_fractional * 2^exponent float_value = 1 * 1.002227783203125 * 2^108 Because the exponent is quite large, the resulting float value is a very large number.
Last updated: 2023-12-15
Post by spiessli on Raspberry Pi 4 with Legacy Drivers and Codesys 3.5.19 Patch 4
CODESYS Forge
talk
(Post)
Thanks for the suggestion, I have tried it eagerly: I have updated all packages to latest version with Codesys Installer and installed newest runtime and gateway on Raspberry Pi. Unfortunately, the error is still there. As soon as I add the SM_Drive_Servo to the device tree, I get the error below when generating the code. Reverting SM3_Basic to version 4.14 makes the error disappear. ------ Ăbersetzungslauf gestartet: Applikation: Device.Application ------- Code typisieren... Code erzeugen... [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0032: Typ 'Unbekannter Typ: 'ConfigGetParameterValueLREAL(pParam, 0)'' kann nicht in Typ 'LREAL' konvertiert werden [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0046: Bezeichner 'ConfigGetParameterValueLREAL' nicht definiert [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0035: Programmname, Funktion oder Funktionsbausteinstanz an Stelle von 'ConfigGetParameterValueLREAL' erwartet [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0032: Typ 'Unbekannter Typ: 'ConfigGetParameterValueLREAL(pParam, 0)'' kann nicht in Typ 'LREAL' konvertiert werden [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0046: Bezeichner 'ConfigGetParameterValueLREAL' nicht definiert [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0035: Programmname, Funktion oder Funktionsbausteinstanz an Stelle von 'ConfigGetParameterValueLREAL' erwartet [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0032: Typ 'Unbekannter Typ: 'ConfigGetParameterValueLREAL(pParam, 0)'' kann nicht in Typ 'LREAL' konvertiert werden [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0046: Bezeichner 'ConfigGetParameterValueLREAL' nicht definiert [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0035: Programmname, Funktion oder Funktionsbausteinstanz an Stelle von 'ConfigGetParameterValueLREAL' erwartet [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0032: Typ 'Unbekannter Typ: 'ConfigGetParameterValueLREAL(pParam, 0)'' kann nicht in Typ 'LREAL' konvertiert werden [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0046: Bezeichner 'ConfigGetParameterValueLREAL' nicht definiert [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0035: Programmname, Funktion oder Funktionsbausteinstanz an Stelle von 'ConfigGetParameterValueLREAL' erwartet [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0032: Typ 'Unbekannter Typ: 'ConfigGetParameterValueLREAL(pParam, 0)'' kann nicht in Typ 'LREAL' konvertiert werden [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0046: Bezeichner 'ConfigGetParameterValueLREAL' nicht definiert [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0035: Programmname, Funktion oder Funktionsbausteinstanz an Stelle von 'ConfigGetParameterValueLREAL' erwartet Ăbersetzung abgeschlossen -- 15 Fehler, 0 Warnungen : Kein Download möglich
Last updated: 2023-12-20
Post by ara32 on CODESYS 4 Linux:
CODESYS Forge
talk
(Post)
Hello! I managed to correctly launch CODESYS Developer Studio 3.5.17, almost all functionality works. The only issue remaining is that when connecting to a device and obtaining its public key, the NCryptEncrypt function is called, which is not fully implemented in the DLL source code, resulting in the connection not being established. Currently, the code of this function in the Wine repository looks like this: SECURITY_STATUS WINAPI NCryptEncrypt(NCRYPT_KEY_HANDLE key, BYTE *input, DWORD insize, void *padding, BYTE *output, DWORD outsize, DWORD *result, DWORD flags) { struct object *key_object = (struct object *)key; TRACE("(%#Ix, %p, %lu, %p, %p, %lu, %p, %#lx)\n", key, input, insize, padding, output, outsize, result, flags); if (flags & ~(NCRYPT_NO_PADDING_FLAG | NCRYPT_PAD_OAEP_FLAG | NCRYPT_PAD_PKCS1_FLAG | NCRYPT_SILENT_FLAG)) { FIXME("Flags %lx not supported\n", flags); return NTE_BAD_FLAGS; } if (flags & NCRYPT_NO_PADDING_FLAG || flags & NCRYPT_PAD_OAEP_FLAG) { FIXME("No padding and oaep padding not supported\n"); return NTE_NOT_SUPPORTED; } if (key_object->type != KEY) return NTE_INVALID_HANDLE; return map_ntstatus(BCryptEncrypt(key_object->key.bcrypt_key, input, insize, padding, NULL, 0, output, outsize, result, flags)); } The program crashes due to the NCRYPT_PAD_OAEP_FLAG flag. I'm not proficient in C++, but I attempted to add handling myself, and here's the result: SECURITY_STATUS WINAPI NCryptEncrypt(NCRYPT_KEY_HANDLE key, BYTE *input, DWORD insize, void *padding, BYTE *output, DWORD outsize, DWORD *result, DWORD flags) { struct object *key_object = (struct object *)key; TRACE("(%#Ix, %p, %lu, %p, %p, %lu, %p, %#lx)\n", key, input, insize, padding, output, outsize, result, flags); if (flags & ~(NCRYPT_NO_PADDING_FLAG | NCRYPT_PAD_OAEP_FLAG | NCRYPT_PAD_PKCS1_FLAG | NCRYPT_SILENT_FLAG)) { FIXME("Flags %lx not supported\n", flags); return NTE_BAD_FLAGS; } if (flags & NCRYPT_NO_PADDING_FLAG) { FIXME("No padding not supported\n"); return NTE_NOT_SUPPORTED; } BCRYPT_OAEP_PADDING_INFO oaepInfo = { 0 }; oaepInfo.pszAlgId = BCRYPT_SHA1_ALGORITHM; NTSTATUS status = BCryptEncrypt(key_object->key.bcrypt_key, input, insize, &oaepInfo, NULL, 0, output, outsize, result, flags); if (key_object->type != KEY) return NTE_INVALID_HANDLE; return map_ntstatus(BCryptEncrypt(key_object->key.bcrypt_key, input, insize, padding, NULL, 0, output, outsize, result, flags)); } Now, when calling the connection, it crashes with the error "bcrypt:BCryptEncrypt flags 0x4 not implemented." Can anyone help with enhancing this functionality or at least point me in the right direction?
Last updated: 2024-03-22
Post by ofey on EtherCAT fieldbus
CODESYS Forge
talk
(Post)
Hi, everyone! I'm trying to set up a PLC controller and a connection to an EtherCAT slave device in Codesys. I want to create a flexible program that I can upload to multiple controllers with different remote IO connected (same program). On one plant i may have 5 AI-cards and 3 DO-cards, and on another I may have 4 AI-cards and 2 DO-cards. For not needing to maintain several different programs wih different devices defined in the program (one for each set up) I thought that using a remote IO would make it easier having a single program. That way I could refer to different memory addresses instead of predefined slots/channels and IO's, that would give me errors if there was a different IO on the plant than what the program expected. When I tried setting up the etherCAT master, I saw that I had to define the etherCAT slave devices with the different IO'cards for me to be able to refer to the memory addresses in a PRG. Exactly what I was trying to avoid. My setup is something like a program that can handle 16 separate pump controls. In a year maybe 6 plans get deployed, and depending on how large the project is, the number of pumps can vary between 4 and 16. And the managers dont want to have IO's for all 16 pumps on every cabinet, and I dont want to maintain 16 separate projects files in case of updates etc. I thought the best way to tackle this was having a single project that read/write data to the different pump IO's by remote IO (fieldbus ethercat) addresses. And the number of pump controls are activated by an external GUI. If pump 1-6 is activated by the GUI, then the PLC-program tries to read/write input/outputs from predefined addresses for the expected IO's. My test setup is a PFC200 WAGO controller and a EtherCAT fieldbus coupler (750-354) with some IO. I hope I didn't explain this too horrible, and if there is a more easy and elegant solution for this challenge I appreciate a feedback on this.
Last updated: 2024-04-08
Post by herbasso88 on WebVisu flickering
CODESYS Forge
talk
(Post)
Good morning, I'm new on Codesys Forge, so I'm not sure if this is the right place to talk about my problem. When I open my WebVisu pages with Microsoft Edge, or Chrome, the background and also some rectangles blinking without reason!!! The application is developed with Codesys 3.5.17.10 and run on Codesys HMI, same version (3.5.17.10). After several experiments I discover that the problem happens when I made dynamic the "End of area" property of a meter object, but I can't understand why this blinking problem happens. Also, the problem is only at the WebVisu page, the "normal" VISU pages (the ones opened when Codesys HMI start) work always perfectly. Another strange thing is that the problem happens only if on the same page, where there is the meter object, there is also a trend object!?!? Codesys HMI is running on a Virtual Machine (VMware Workstation 15 player, v.15.5.6) running Windows 10 Pro N 64-bit. The blinking problem happen also if I convert the project to Codesys 3.5.20.0. This version of Codesys and Codesys HMI are installed on a Virtual Machine running Windows Server 2019 Standard 64-bit. In attachment the archive of my project. The attached project has only one page, if "Enable Counter" is not pressed the "End of area" variable of the meter is not updated in the software, and everything work well, normal VISU and WebVisu; if "Enable Counter" is pressed, the "End of area" variable of the meter is updated in the software, and the WebVisu page start blinking. I tried also to enable the "Support client animations and overlay..." property at VisualizationManager, this seems stop the blinking problem, but that property also destroy my WebPage, moving almost all the graphical object, that also seem not working anymore. I really need help to understand what I'm doing wrong, I have to develop a bigger project and I have to understand if trend objects and animated meters cannot stay in the same page. In the final project the WebVisu will be very important because the customer will use this way to access the application to monitor the process. Regards
Last updated: 2024-05-06
Post by dantheman on Connecting to SoftPLC Only Works By Turning Off Modbus Ethernet Port
CODESYS Forge
talk
(Post)
I have an IPC with 2 ethernet ports and 1 Wi-Fi. I'm using ModbusTCP with the ethernet port named "enp2s0" connected to my remote I/O. This works fine when testing with Python and also works with CODESYS, but CODESYS is only able to scan for the Linux SoftPLC when I turn off the "enp2s0" interface. In other words, I can't get online with the IDE if I want my ModbusTCP comms to run with CODESYS. I'm using a Linux SoftPLC that has the following entry in CODESYSControl.cfg, hoping that this will allow me to connect with "enp1s0" or "wlp3s0", and leave "enp2s0" for field comms, but this seems to only make the source IP of the ModbusTCP comms to be bound to "enp2s0". That last point is the case only if I don't restart the service, but if I do restart the service after changing the config file, the source IP for the ModbusTCP comms then becomes the one for "enp1s0", which is very confusing to me: [SysSocket] Adapter.0.Name="enp2s0" Adapter.0.EnableSetIpAndMask=1 On the device list, I only have "enp2s0" given as the ethernet device that has the ModbusTCP master & slave beneath it, shown in Screenshot 1. On the IPC, I can ping the ModbusTCP client (remote I/O) from "enp2s0", and I've attached a Wireshark capture of running ModbusTCP from the CODESYS runtime as Screenshot 2, 3 & 4 (again, I can't get online when this is running, I have to turn off "enp2s0" to connect even when it's idle and I don't have an active TCP session with my Python tests). Like I explained above, the source IP is "enp1s0", even though the ethernet device on the project is "enp2s0". I was lucky to catch the red message that showed the source IP that makes sense to me (the one for "enp2s0"), but for some reason that connection was reset and I never saw that packet again. I've also tried this with Auto-reconnect both enabled & disabled, for the ModbusTCP Master device. I also have to turn off "enp1s0" and then turn it on, just so that I can have the ModbusTCP comms running from "enp2s0" (which is not intuitive in any way to me, I'd love some help understanding that phenomenon as well) in the weird manner that I've described above. I would be very appreciative if someone can help me figure out this pickle. I'd love to just connect to CODESYS through my Wi-Fi interface and leave my ethernet ports for field comms.
Last updated: 2024-08-01
Post by alex-at-xana on EThercat Dynamic configuration
CODESYS Forge
talk
(Post)
Hi Everyone, For a fast monitoring system I am using Ethercat oversampling and timestamping inputs. As the customers has a lot of different configurations out in the field, we went for a dynamic Ethercat configuration. Already got the whole detection chain working but now I am stuck since two days in debugging the configuration. Here are my quesitons: I extended the dynamic config example for the EL3632 16#0E303052: //EL3632 pSlave^.SetDCSettings(TRUE,TRUE,80,80,TRUE,4000,0,0); pSlave^.AddSyncManager(16#1000,128,16#26,TRUE,3); pSlave^.AddSyncManager(16#1080,128,16#22,TRUE,2); pSlave^.AddSyncManager(16#1100,0,16#4,TRUE,1); pSlave^.AddSyncManager(16#1110,214,16#20,TRUE,0); pSlave^.AddFMMU(0,214,0,7,16#1110,0,1,1); pSlave^.AddFMMU(0,1,0,0,16#80D,0,1,1); xKnown := TRUE; This leads to a PLL Error for these devices. I double and triple checked the configuraton, but cannot find the issue. There seems to be one difference: the config dialog creates a startup parameter: 16#10F3:16#05, Name: Command_0, Value:0. Bitlen: 16, Stop on fault: false, jumpt at fault: false: next line: 0 a) I do not find information on how to set this in my code. Can you help me there? b) Without trying to set the value, I get a PLL error for these devices in the master log. Is the config wrong? c) Do I need to set the Master to Autoconfigure or Manual? I used autoconfigure for my tests. The stack creates input data addresses for the slaves input data range (pSlaves[i].InputData) which are different from those created when I use the Engineering tools dialogs to configure Ethercat. Specifically, the addresses seem to be aligned at 16 byte boundaries when they are created using the engineering tool, but may appear at uneven addresses when I use the script in dynamic config. I did not try to access ULINT at uneven addresses yet, but I am suspecting this may be a problem. Do I need to manually align the addresses ? Any help is appreciated...
Last updated: 2024-09-10