Post by taqamert on CANopen PDO Issue with Pressure Sensor in Codesys
CODESYS Forge
talk
(Post)
Hello everyone, I am using an IFM CR0303 model PLC, which has a tilt sensor and a pressure sensor connected via CANopen. Both sensors are from the same brand (ATEK). I can read data from the tilt sensor without any issues, but I am unable to read data from the pressure sensor. I have added the EDS file in the PLC configuration and adjusted the node-ID settings. When I check with the PCAN-View application, I can see that the selected PDOs are coming through, but the data is not reaching the Codesys side. What could be the issue, and what can I try to resolve it? Can anyone help me?
Last updated: 2024-10-22
Post by struccc on Problem Update new version Master ethercat
CODESYS Forge
talk
(Post)
Hi, I had some issues as well migrating to the new version. What I have learnt: - Have to check all the libraries in the library manager, if they are the proper versions. - Some other parts of the application, maybe an old library referenced by another one can keep the old Ethercat libraries.... Use the "Placeholders" function on the library manager - See if there is a new version available of the slave "devices". Might just have to update them ... I had problems moving from 4.7 to with 4.8, especially with the 2nd adapter for redundancy - some devices failed to initialize properly.... So I have just downgraded those libraries now. P.
Last updated: 2024-10-28
Post by gatto on Undertanding Application Based Licenses
CODESYS Forge
talk
(Post)
Hi, i think you are right. Did you press the key shopping cart? Codesys tells you the license. What I don't appreciate is that i need an additional license for communication. The system reports opc ua but this cheats you. This is communication that also concerns the tag symbols that codesys eth v3 exchanges with an operator panel. Attached is a screenshot of my case where you can see that communication opc ua is cheating you. 512 tags included in the program license are few. So, I had to buy 2 licenses. one for the program and one for communication. I don't like this policy.
Last updated: 2024-11-11
Post by micik on Using Codesys example problems
CODESYS Forge
talk
(Post)
Hello to all, I'm totally new to Codesys, but I do have some PLC programming experience, mosty with Siemens TIA and STEP7. I have just installed Codesys 3.5. sp19 and I have downloaded example with Ethernet Rockwell 1734AENT. The example can be found here: https://forge.codesys.com/prj/codesys-example/rockwell-1734-c/home/Home/ After opening, I had to manually update devices (Device, Ethernet, IP Scanner, EthernetIP adapter). However, when trying to build the project, I get the following errors: [WARNING] CODESYS_EtherNetIP_Rockwell1734AENT: Library Manager [Device: PLC Logic: Application]: C0100: Library System_VisuElemXYChart has not been added to the Library Manager, or no valid license could be found [WARNING] CODESYS_EtherNetIP_Rockwell1734AENT: Library Manager [Device: PLC Logic: Application]: C0100: Library system_visuinputs has not been added to the Library Manager, or no valid license could be found [ERROR] iodrvethernetip, 4.4.1.0 (3s - smart software solutions gmbh): ServiceCycle [IoDrvEtherNetIP]: C0040: Function 'ProcessUpdateConfigurationQueue' requires exactly '1' inputs [ERROR] iodrvethernetip, 4.4.1.0 (3s - smart software solutions gmbh): IoDrvStartBusCycle [IoDrvEtherNetIP]: C0040: Function 'GenerateRandomUINT' requires exactly '2' inputs [ERROR] iodrvethernetip, 4.4.1.0 (3s - smart software solutions gmbh): Cyclic [GenericServiceUnConnected]: C0040: Function 'GenerateRandomUINT' requires exactly '2' inputs [ERROR] cip object, 4.4.1.0 (3s - smart software solutions gmbh): ForwardOpenService [ConnectionManager]: C0040: Function 'GetAssemblies' requires exactly '3' inputs [ERROR] iodrvethernetipadapter, 4.4.0.0 (3s - smart software solutions gmbh): ServiceCycle [IoDrvEtherNetIPAdapter]: C0040: Function 'GenerateRandomUINT' requires exactly '2' inputs [ERROR] iodrvethernetip, 4.4.1.0 (3s - smart software solutions gmbh): SetupStructuredIOMapping [RemoteAdapter]: C0040: Function 'MallocData' requires exactly '1' inputs [ERROR] iodrvethernetip, 4.4.1.0 (3s - smart software solutions gmbh): SetupStructuredIOMapping [RemoteAdapter]: C0040: Function 'MallocData' requires exactly '1' inputs Compile complete -- 7 errors, 13 warnings Build complete -- 7 errors, 13 warnings : no download possible! What could be the reason for this errors and how to rectify them? Thank you!
Last updated: 2024-02-01
Post by thommy54 on Raspi-Cam: CameraStream.project nicht zum Laufen zu bringen
CODESYS Forge
talk
(Post)
Hallo, Ich bringe das CameraStream.project nicht zum Laufen. Ich sehe die Ursache darin, das das Beispielprogramm sehr sparsam mit Programm-Kommentaren umgeht (von der Hilfe gar nicht zu reden). Ich habe beide Varianten bei der zu ändernden Zielvariable getestet: //copy video.htm to the webserver; //the location of the webserver depends on the used Apache version as mentioned in online help hDirHtmlTest:=SysDirOpen( szDir:='/var/www', pDirInfo:= ADR(dirInfo), diMaxDirEntry:=iMaxDirEntry, szDirEntry:=szDirEntry, pResult:=ADR(iDirHtmlError)); IF (iDirHtmlError = 0) THEN SysDirClose(hDir:=hDirHtmlTest); SysFileCopy('/var/www/video.htm', '$$PlcLogic$$/Application/video.htm', ADR(dwCopySize)); ELSE .... als auch hDirHtmlTest:=SysDirOpen( szDir:='/var/www/html', pDirInfo:= ADR(dirInfo), diMaxDirEntry:=iMaxDirEntry, szDirEntry:=szDirEntry, pResult:=ADR(iDirHtmlError)); IF (iDirHtmlError = 0) THEN SysDirClose(hDir:=hDirHtmlTest); SysFileCopy('/var/www/html/video.htm', '$$PlcLogic$$/Application/video.htm', ADR(dwCopySize)); ELSE .... Die Url-Streams habe ich gelassen wie sie vorgegeben waren: urlStream := CONCAT('http://', CONCAT(sIPAddress, '/video.htm')); urlPicture := CONCAT('http://', CONCAT(sIPAddress, '/cam_pic.php')); In der Webvisu im Browser komme ich maximal dahin wie im Screeshot Video_Visu_1 zu sehen. Also scheint der Link zu video.htm zu klappen. Das der zu cam_pic.php nicht klappt, wundert mich nicht, denn es existiert nicht und wird auch nicht evtl. am rechten Ort angelegt. Ich bin mir vollkommen im Unklaren: muss da was auf dem Raspberry Pi im Hintergrund laufen , z.B. raspivid . Welcher Programmteil bedient die Cam ? Ich erkenne auch nicht, wo ein einzelnes picture entstehen soll. Wäre dankbar, wenn ich hier etwas Hilfe bekommen könnte. Evtl. gibt es Probleme mit der von mir verwendeten Codesys-Version 3.5.20.1 ? Ich benutze einen Raspberry 4 Rev.1.2. Grüße Thomas
Last updated: 2024-07-04
Post by paulpotat on cm4 runtime problem
CODESYS Forge
talk
(Post)
Hello, I have exactly the same issue, with the following configuration : Hardware version >>> cat /proc/cpuinfo processor : 0 model name : ARMv7 Processor rev 3 (v7l) BogoMIPS : 108.00 Features : half thumb fastmult vfp edsp neon vfpv3 tls vfpv4 idiva idivt vfpd32 lpae evtstrm crc32 CPU implementer : 0x41 CPU architecture: 7 CPU variant : 0x0 CPU part : 0xd08 CPU revision : 3 processor : 1 model name : ARMv7 Processor rev 3 (v7l) BogoMIPS : 108.00 Features : half thumb fastmult vfp edsp neon vfpv3 tls vfpv4 idiva idivt vfpd32 lpae evtstrm crc32 CPU implementer : 0x41 CPU architecture: 7 CPU variant : 0x0 CPU part : 0xd08 CPU revision : 3 processor : 2 model name : ARMv7 Processor rev 3 (v7l) BogoMIPS : 108.00 Features : half thumb fastmult vfp edsp neon vfpv3 tls vfpv4 idiva idivt vfpd32 lpae evtstrm crc32 CPU implementer : 0x41 CPU architecture: 7 CPU variant : 0x0 CPU part : 0xd08 CPU revision : 3 processor : 3 model name : ARMv7 Processor rev 3 (v7l) BogoMIPS : 108.00 Features : half thumb fastmult vfp edsp neon vfpv3 tls vfpv4 idiva idivt vfpd32 lpae evtstrm crc32 CPU implementer : 0x41 CPU architecture: 7 CPU variant : 0x0 CPU part : 0xd08 CPU revision : 3 Hardware : BCM2711 Revision : a03141 Serial : 10000000d5be5b5f Model : Raspberry Pi Compute Module 4 Rev 1.1 Kernel version >>> uname -a Linux raspberrypi 6.1.21-v7l+ #1642 SMP Mon Apr 3 17:22:30 BST 2023 armv7l GNU/Linux OS Version >>> cat /etc/os-release PRETTY_NAME="Raspbian GNU/Linux 11 (bullseye)" NAME="Raspbian GNU/Linux" VERSION_ID="11" VERSION="11 (bullseye)" VERSION_CODENAME=bullseye ID=raspbian ID_LIKE=debian HOME_URL="http://www.raspbian.org/" SUPPORT_URL="http://www.raspbian.org/RaspbianForums" BUG_REPORT_URL="http://www.raspbian.org/RaspbianBugs" /boot/config.txt I added the following line : arm_64bit=0 CodeSys runtime version 4.10 Were you able to solve the issue @michelebianchi ? Any help with this would be appreciated... BR
Last updated: 2024-08-28
Post by herbasso88 on WebVisu flickering
CODESYS Forge
talk
(Post)
Good morning, I'm new on Codesys Forge, so I'm not sure if this is the right place to talk about my problem. When I open my WebVisu pages with Microsoft Edge, or Chrome, the background and also some rectangles blinking without reason!!! The application is developed with Codesys 3.5.17.10 and run on Codesys HMI, same version (3.5.17.10). After several experiments I discover that the problem happens when I made dynamic the "End of area" property of a meter object, but I can't understand why this blinking problem happens. Also, the problem is only at the WebVisu page, the "normal" VISU pages (the ones opened when Codesys HMI start) work always perfectly. Another strange thing is that the problem happens only if on the same page, where there is the meter object, there is also a trend object!?!? Codesys HMI is running on a Virtual Machine (VMware Workstation 15 player, v.15.5.6) running Windows 10 Pro N 64-bit. The blinking problem happen also if I convert the project to Codesys 3.5.20.0. This version of Codesys and Codesys HMI are installed on a Virtual Machine running Windows Server 2019 Standard 64-bit. In attachment the archive of my project. The attached project has only one page, if "Enable Counter" is not pressed the "End of area" variable of the meter is not updated in the software, and everything work well, normal VISU and WebVisu; if "Enable Counter" is pressed, the "End of area" variable of the meter is updated in the software, and the WebVisu page start blinking. I tried also to enable the "Support client animations and overlay..." property at VisualizationManager, this seems stop the blinking problem, but that property also destroy my WebPage, moving almost all the graphical object, that also seem not working anymore. I really need help to understand what I'm doing wrong, I have to develop a bigger project and I have to understand if trend objects and animated meters cannot stay in the same page. In the final project the WebVisu will be very important because the customer will use this way to access the application to monitor the process. Regards
Last updated: 2024-05-06
Post by thn-power on Updating OPC UA Core Nodeset on PLS
CODESYS Forge
talk
(Post)
Hi After much trail and error I think I found the root cause to my OPC UA problem. The problem is that I cannot manage to build and download a program with a a custom OPC UA Information model. We use a Weidmueller WL2000 PLS, but the problem also exsist on the Win V3 PLC. Our custom information model is based on the latest versions of the OPC UA Core Nodeset v 1.05.03 (2023-09-20) and UA/DI nodeset 1.04.0 (2022-11-03) Those nodesets are installed in the Codesys Information Model Repository (3.5.19.6) However, when trying to build I get the following error. [ERROR] Untitled1: Communication Manager [Device: PLC Logic: Application]: The information model http://opcfoundation.org/UA/ is required by http://bos.org/ with a minimal publication date from 15.12.2023 but the device has only a model from 15.09.2021 installed. Probably the information model from 15.09.2021 is missing in the information model repository. [ERROR] Untitled1: Communication Manager [Device: PLC Logic: Application]: The information model http://opcfoundation.org/UA/DI/ is required by http://bos.org/ with a minimal publication date from 03.11.2022 but the device has only a model from 09.03.2021 installed. Probably the information model from 09.03.2021 is missing in the information model repository. Build complete -- 2 errors, 1 warnings : No download possible I think the problem is that the UA Core nodeset is implemented in the PLC firmware (at least that in Siemens S7), and that only includes the "old" nodeset from 2021-09-21 etc. So the question is, how (or if?) can I transfer the new nodeset to the PLS? I have created separate Information models under Communication manager with the newer code nodesets (UA and DI). But it seems that the compiler does not recognize them being excising, neither in the Codesys IDE or on the PLC. Would have guessed that this is a common issue, sine many manufacturers use the latest versions of the OPC UA standard, and that it would be a solution to the problem.
Last updated: 2024-09-20
Post by rossanoparis on After un upgrade of "CODESYS Control for Raspberry Pi MC SL" from v4.7 to v4.9 SysFileOpen function stopped working
CODESYS Forge
talk
(Post)
Hello at all. After un upgrade of "CODESYS Control for Raspberry Pi MC SL" from v4.7 to v4.9 SysFileOpen function stopped working. I'm not able to read or write files from the PLC application. Before this upgrade all worked fine. I've read this thread [ https://forge.codesys.com/forge/talk/Engineering/thread/3da9ded84e/ ] Despite I followed that indications I couldn't get my code working again. Perhaps I'm missing something or I didn't understand how to use placeholders at all. Is there a different syntax to use for "SysFileOpen" in order to use placeholders? Thanks in advance for your help. Information Compiler: CODESYS V3.5 SP19 Patch 2 Runtime: codesyscontrol 4.9.0 HW: KUNBUS RevPi Connect S Below the paths I want to access (The entire CODESYSControl_User.cfg file is attached) [SysFile] PlaceholderFilePath.1=/home/pi/hpca/bin, $hpcabin$ PlaceholderFilePath.2=/home/pi/hpca/cfg, $hpcacfg$ PlaceholderFilePath.3=/home/pi/hpca/logs, $hpcalogs$ PlaceholderFilePath.4=/home/pi/hpca/resources, $hpcares$
Last updated: 2023-08-22
Post by timvh on Detect "Cancel" Press in FileOpenSave Dialog
CODESYS Forge
talk
(Post)
Maybe there is a better way, but a long time ago I created a test application that worked like this: With a button I opened the dialog and I added a "Input configuration - OnDialogClosed" "Execute ST-Code" action to this same button which called the following Function when the dialog was closed: F_OnFileDialogClosed(pClientData); Below this Function which handled the result: // This function is called from the visualization when the dialog is closed. FUNCTION F_OnFileDialogClosed : BOOL VAR_INPUT pClientData : POINTER TO VisuElems.VisuStructClientData; END_VAR VAR dialogMan : VisuElems.IDialogManager; FileOpenCloseDialog : VisuElems.IVisualisationDialog; result : VisuElems.Visu_DialogResult; _sFileName : STRING(255); END_VAR // the DialogManager is provided via the implicitly available VisuManager dialogMan := VisuElems.g_VisuManager.GetDialogManager(); IF dialogMan <> 0 AND pClientData <> 0 THEN FileOpenCloseDialog := dialogMan.GetDialog('VisuDialogs.FileOpenSave'); // gets the FileOpenSave dialog IF FileOpenCloseDialog <> 0 THEN result := FileOpenCloseDialog.GetResult(); // gets the result (OK, Cancel) of the dialog IF result = VisuElems.Visu_DialogResult.OK THEN // Original code gvlFile.FileListProvider(); _sFileName := CONCAT(gvlFile.FileListProvider._stDirectory, gvlFile.FileListProvider.stFile); // do something with this file name... END_IF END_IF END_IF
Last updated: 2023-09-19
Post by damian177 on Codesys and SMS in RPi
CODESYS Forge
talk
(Post)
I tried initialize my GSM modem by write simple application in C, and GSM modem works, below used AT commands: AtChat: T : "AT" AtChat: F : "OK" AtChat: T : "AT+CMEE=1" AtChat: F : "OK" AtChat: T : "AT+CMGF=0" AtChat: F : "OK" AtChat: T : "AT+CGMI" AtChat: F : "WH_Ltd" AtChat: F : "WH_GM35" AtChat: F : "Revision: RDA BV5" AtChat: F : "OK" AtChat: T : "AT+CGMM" AtChat: F : "WH_GM35" AtChat: F : "OK" AtChat: T : "AT+CGMR" AtChat: F : "Revision: GM35-D_B5_R05_A01_D170914" AtChat: F : "OK" AtChat: T : "AT+CGSN" AtChat: F : "868221045990218" AtChat: F : "OK" AtChat: T : "AT+CNMI=2,1,0,1,0" AtChat: F : "OK" AtChat: T : "AT+CLIP=1" AtChat: F : "OK" AtChat: T : "AT+COPS?" AtChat: F : "+COPS: 0,2,\"26002\"" AtChat: F : "OK" operator name: "26002" AtChat: T : "AT+CREG?" AtChat: F : "+CREG: 1,1" AtChat: F : "OK" at+creg Modem is initialized I do not understand why Codesys SMS library send AT+CPIN? command ?
Last updated: 2023-09-29
Post by sturmghost on Visualization using methods and cyclic ST-calls
CODESYS Forge
talk
(Post)
Im looking for a way to implement ST-code into the visualization element without creating a helper POU or method in my device/application tree. Like visualization properties are evaluated at each VISU_TASK cycle I want to be able to create own ST code which interacts with the visualization interface variables. To be more specific I want to have a property which executes user defined ST-code at each VISU_TASK cycle exactly like its already possible for Input Configuration on various mouse and dialog events. Also a property for initialization (so only executed once) and a timed property would be nice. With the situation right now I'll have to create a POU function which handles the ST-code and misuse a property, like the text variable, to execute this POU function at each VISU_TASK cycle. Or does it exist and I don't know it?
Last updated: 2023-10-02
Post by arundara on Variable Sync Issue In Soft Plc Redundancy
CODESYS Forge
talk
(Post)
Hello, I was trying to create a redundancy POC for our application where we read data from few modbus tcp devices. As there is a limitaion that modbus tcp device support only for single master device, we wanted to test how the variable sync happens in redundancy mode. For that i have used the redundancy sample code added a variable "b" under a condition. What i observed was while active controller is running, if passive controller is powerup, passive controller is able to sync all the data configured for redundacny. But after that the variable data which resided under a condition is not synching from active to passive controller. I have attached the image where i have highlighter the variable. Can some help me to understand how redundacny work in codesys soft plc and if there is a solution to sync variable which are under condition, please explain the same or suggestion to achieve the same. Hardware - Raspberry Pi (2 qty) Redundancy licence used - yes in both controllers. Codesys runtime - 4.9.0.0 Codesys software version - V3.5 SP19 if i have posted this question in wrong section, please do let me know in whcih section i have to post this question.
Last updated: 2023-12-01
Post by acc00 on Main Task cycle too long leading to PLC Fail
CODESYS Forge
talk
(Post)
I have 2 Wago PFC200 PLC, running with Runtime SP19 Patch 5, with the Redundant application. The PLC communicates as Modbus Master with at this moment 15 Modbus Slaves -later there will be 28 in total- (Drives, Power management units,...). These devices are connected in 2 rings (1 ring of Drives, 1 ring of Power Management units), with 2 Managed Moxa Switches being part of the ring. Each PLC is connected to one of these switches. The issue I'm encountering is that the Cycle time of the Active PLC goes very high when I'm closing the Drive ring (simulating an issue on one Cabinet supply, resulting in that one Drive shut down, which can happen on field quite often). As a result of this long cycle, the PLC fails and goes to Exception, and the Passive PLC does not take control of the system. A normal cycle is around 30ms for the Main task, and a few ms for the Ethercat task. When I monitor with Profiler, I see that in this Maximum Cycle, the main Task is only taking 13ms, so I'm not sure where the PLC is hanging for so long. Is the remaining cycle time the Redundant management/sync or something else? Thank you in advance.
Last updated: 2024-03-08
Post by anlebr on Codesys Communication Manger - Required information model version exists in the model repository but is not found
CODESYS Forge
talk
(Post)
Hi I am trying use the Codesys Communication Manager to set up an Opc ua server with a custom information model. As a start I am using the Boiler model available on Opc foundations github page. I am testing with a Wago CC100 and using Codesys V3.5 SP19 Patch 6. I get the following error: Communication Manager [Device: PLC Logic: Application]: The information model http://opcfoundation.org/UA/ is required by http://opcfoundation.org/UA/Boiler/ with a minimal publication date from 15/12/2023 but the device has only a model from 15/09/2021 installed. Probably the information model from 15/09/2021 is missing in the information model repository. The error message does not make sense to me. Should it not be “Probably the information model from 15/12/2023 is missing in the information model repository”? Anyway, both versions are available in the repository. How can I solve this?
Last updated: 2024-03-13
Post by francescoc on Custom log CmpLog
CODESYS Forge
talk
(Post)
Hi, I am trying to create a log in my application. Since I cannot find any documentation regarding modifying the codesys configuration file to be able to log in ms, i tried to create a new log via CmpLog.LogCreate. Below is the part of the code where I create the logger and write a test string. In the log tab of codesys I actually see the new log that was created, but it is empty, and in the folder I cannot find any files. I can't find any detailed documentation. Can you guys give me support? Are there any examples? Thank you IF NOT FirstCycle THEN LogName:= 'LOGS/TestLog'; LogOptions.bEnable:= 1; LogOptions.iMaxEntries:= 5000; LogOptions.iMaxFiles:= 100; LogOptions.iMaxFileSize:= 5000; LogOptions.szName:= LogName; LogOptions.uiType:= CmpLog.LogTypes.LT_TIMESTAMP_RTC_HIGHRES; LogOptions.uiFilter:= CmpLog.LogClass.LOG_ALL; LogHandle:= CmpLog.LogCreate(pOptions := ADR(LogOptions), pResult:= ADR(Result)); LogHandle:= CmpLog.LogOpen(pszName:= LogName, pResult:= Result); Component_Manager.CMAddComponent2('TestLogNEW', 16#00000001, ADR(udiCmpIdNEW), 0); CmpLog.LogAdd2(LogHandle, udiCmpIdNEW, CmpLog.LogClass.LOG_INFO, 1, 1, 'Logger started...'); END_IF IF TestWrite THEN TestWrite:= FALSE; CmpLog.LogAdd2(LogHandle, udiCmpIdNEW, CmpLog.LogClass.LOG_INFO, 1, 1, 'Write test'); END_IF
Last updated: 2024-03-16
Post by squiggleypuff on RemoteTargetVisu creates Unresolved Reference
CODESYS Forge
talk
(Post)
I have a project with a Festo CPX-E-CEC-C1-PN PLC (Run-time version 3.5.12.50) that I have been developing on just fine using Codesys V3.5 SP19 Patch 5 (64bit). I am at the stage where I wanted to use the Festo HMI screen, and have added a RemoteTargetVisu object to my application. After adding this object, I am no longer able to log in to the PLC as I get an Unresolved Reference warning for 'USERMGRUSERGETPROPERTY' towards the end of the download process. I was able to find this post (https://forge.codesys.com/forge/talk/Visualization/thread/fc686a6cb2/) where the two possible solutions are to "set the placeholder to emtpy" or update the runtime. Problem is, I don't know how to do either of these things, as I'm still very green in Codesys land. I'd be happy to update the Festo PLC runtime, as that seems like the better option, but have not had any luck in finding a tutorial for this online. If anyone could point me in the right direction I'd appreciate it.
Last updated: 2024-03-19
Post by rjwkerkhof on IIot Libraries SL --> Web Socket Client SL Pong issue
CODESYS Forge
talk
(Post)
Dear all, I am developing a Web Socket Client in Codesys 3.5 using the Web Socket Client SL library to retrieve data from a third party. Connecting and reading works fine however after 40 seconds the connection gets interrupted by the server due to keepalive ping timeout. After discussion with third party it seems that the Web Socket Client SL library replys to the Ping request of the Web Socket server BUT does not add the "Application data" = 4 bytes in the body of the Pingframe to the Pongframe. Therefor the server does not recognize the Pongframe send by the Web Socket Client SL library and automatically disconnects. Is this a known issue with the libary or am I doing something wrong? Is there a workaround to add the 4 bytes manually to the Pongframe before replying it to the server? Thanks in advance, Roy
Last updated: 2024-04-09
Post by joshskellig on Publish a JSON payload via MQTT Publish (using IIot Libraries)
CODESYS Forge
talk
(Post)
I am trying to figure out how to get a JSON payload to properly publish to my MQTT Broker. I am able to generate JSON using the examples from Codesys, but when I send that payload via MQTT there are characters that are extra or not recognized by my MQTT client. Any idea what could be causing it? PROGRAM PLC_PRG VAR hostname: STRING := 'localhost'; port: UINT := 1883; topic: WSTRING(1024) := "testing/"; payload: BYTE; factory : JSON.JSONDataFactory; eDataFactoryError : FBF.ERROR; pJsonData : POINTER TO JSON.JSONData := factory.Create(eError => eDataFactoryError); fb_JBuilder : JSON.JSONBuilder; wsValue : WSTRING := "Value1"; diRootIndex, diObject1Index : DINT; iValue : INT := 1234; jsonArrayWriter : JSON.JSONByteArrayWriter; wsJsonData : WSTRING(1000); xFirst : BOOL := TRUE; mqttClient: MQTT.MQTTClient; mqttPublish: MQTT.MQTTPublish; mqttPublishProperties: MQTT.MQTTPublishProperties := (bPayloadFormatIndicator := 1, wsContentType := "application/json"); END_VAR // Json Functionality IF xFirst THEN fb_JBuilder(pJsonData := pJsonData, diRootObj => diRootIndex); fb_JBuilder.SetKeyWithValue("Key1", wsValue, diParentIndex := diRootIndex); diObject1Index := fb_JBuilder.SetKeyWithObject("Key2", diParentIndex := diRootIndex); fb_JBuilder.SetKeyWithValue("Key3", iValue, diParentIndex := diObject1Index); xFirst := FALSE; END_IF jsonArrayWriter(pwData := ADR(wsJsonData), udiSize := SIZEOF(wsJsonData), jsonData := pJsonData^, xAsyncMode := FALSE); MSU.StrTrimW(pString:= ADR(wsJsonData)); // MQTT Functionality mqttClient( sHostname:=hostname, uiPort:=port, eMQTTVersion:=MQTT.MQTT_VERSION.V5 ); mqttPublish( mqttClient:=mqttClient, pbPayload:=ADR(wsJsonData), udiPayloadSize:=SIZEOF(wsJsonData), wsTopicName:=topic, mQTTPublishProperties:=mqttPublishProperties );
Last updated: 2024-04-10
Post by tim-roelant on Problem mit control runtime V3 und profinet
CODESYS Forge
talk
(Post)
Hallo Edwin, meinst du das der control-win nicht wie SPS verwendet werden kann? Das program ist klein, und realtime brauch ich gar nicht, Es gibt im bus einem Turck inselstation mit 16 ein und ausgange, und ein MTS linearencoder, womit wir teile messen und abschneiden. Die cycluszeit reist auch nicht aus. Processorleisung bleibt unter 20%. Es geht mir darum das der profinet master in fehler geht, und nicht mehr seine telnehmer erkannen kann. Es kan passieren nach 10 minuten, aber auch nach 5 tage. Nur ein kaltstart bringt die bus wieder am laufen. (kein reconnect mochlich, auch die bus scannen functioniert nicht mehr) Wann ich aber ein ipscan durchfure mit Angryip auf der rechner sind alle telnehmer da. Ich habe noch eine andere application mit die gleiche anwendung, aber wo ein raspberry pi die SPS rolle spielt, und das functioniert einwandfrei. Soll ich fielleicht das OS von Rechenr nach linux umrusten? Der operator ist im moment sehr unzufrieden mit die "upgrade" von maschine... :-( lg Tim
Last updated: 2024-04-11
Post by tim-roelant on Problem mit control runtime V3 und profinet
CODESYS Forge
talk
(Post)
Hallo Edwin, meinst du das der control-win nicht wie SPS verwendet werden kann? Das program ist klein, und realtime brauch ich gar nicht, Es gibt im bus einem Turck inselstation mit 16 ein und ausgange, und ein MTS linearencoder, womit wir teile messen und abschneiden. Die cycluszeit reist auch nicht aus. Processorleisung bleibt unter 20%. Es geht mir darum das der profinet master in fehler geht, und nicht mehr seine telnehmer erkannen kann. Es kan passieren nach 10 minuten, aber auch nach 5 tage. Nur ein kaltstart bringt die bus wieder am laufen. (kein reconnect mochlich, auch die bus scannen functioniert nicht mehr) Wann ich aber ein ipscan durchfure mit Angryip auf der rechner sind alle telnehmer da. Ich habe noch eine andere application mit die gleiche anwendung, aber wo ein raspberry pi die SPS rolle spielt, und das functioniert einwandfrei. Soll ich fielleicht das OS von Rechenr nach linux umrusten? Der operator ist im moment sehr unzufrieden mit die "upgrade" von maschine... :-( lg Tim
Last updated: 2024-04-11
Post by jose-coro on Trouble installing codesys 64 3.5.19.0
CODESYS Forge
talk
(Post)
I tried to intalling codesys 64 3.5.19.0, during the installation process I get the following messages: "One or more problems have appeared with the current version profile. please consult with the supplier to solve the problem. -The plugin '{ee08241a-dd43-445a-b0a1-de9f717d92e0}(exactly 3.5.19.0)' is required for the current version profile but is not installed. The plug-in '{c7880c90-68c0-4cf8-a726-f0ee72b11f86}(exactly 3.5.19.0)' is required for the current version profile but is not installed. The add-on '{973a3934-1ec6-4770-83a4-59677803015a}(exactly 3.5.19.0)' is required for the current version profile but is not installed. It is recommended to terminate the application." Then the following message appears: "This package could not be installed: CODESYS Compatibility Package 3.5.17.20”. After that the instalation continue and the folling message appears: "It is possible that packages from this path could not be installed: C:\Users...\Appdata\Local\Temp{EFE2F~1}\Packages"
Last updated: 2024-04-23
Post by jose-coro on Trouble installing codesys 64 3.5.19.0
CODESYS Forge
talk
(Post)
I tried to intalling codesys 64 3.5.19.0, during the installation process I get the following messages: "One or more problems have appeared with the current version profile. please consult with the supplier to solve the problem. -The plugin '{ee08241a-dd43-445a-b0a1-de9f717d92e0}(exactly 3.5.19.0)' is required for the current version profile but is not installed. The plug-in '{c7880c90-68c0-4cf8-a726-f0ee72b11f86}(exactly 3.5.19.0)' is required for the current version profile but is not installed. The add-on '{973a3934-1ec6-4770-83a4-59677803015a}(exactly 3.5.19.0)' is required for the current version profile but is not installed. It is recommended to terminate the application." Then the following message appears: "This package could not be installed: CODESYS Compatibility Package 3.5.17.20”. After that the instalation continue and the folling message appears: "It is possible that packages from this path could not be installed: C:\Users...\Appdata\Local\Temp{EFE2F~1}\Packages"
Last updated: 2024-04-23
Post by timvh on License problem gateway
CODESYS Forge
talk
(Post)
What we are trying to explain is that, yes CODESYS creates the software, but Epis decides how they implement it on their hardware, which runtime version they use and they decide which functionality they support. So it is always a combination of the two. What CODESYS provides is a runtime with options for e.g. visualization or softmotion. Epis could add this softmotion license as default to their controller, but if they don't then CODESYS provides another option with a single license in a "Wibu CodeMeter" container. Eventhough the feature exists, Epis has to add this "CodeMeter" software on their controller to be able to access the licenses in the container. We don't know if they did this. Then finally it depends on what type of runtime is on this controller and which license Epis is using. So if they have an OEM license (not an application based license), then most likely you will need the Softmotion license (not a number of axis). See https://store.codesys.com/en/codesys-softmotion-sl-bundle.html. But to be sure if this is supported by the Epis controller, you must ask Epis.
Last updated: 2024-04-30
Post by rabaggett on CODESYS control for Raspberry Pi 64 SL errors
CODESYS Forge
talk
(Post)
Hi, I am trying to create a project using a raspberry pi, I have added the modules for the Pi and MCP3008. I have encountered som errors that I don't know how to track down. 1. The GPIOs give preprocessor errors, but I read that this does not prevent compiling. This seems to be true. I can build the empty project with no errors. 2. After adding a SPI master and MCP3008, the preprocessor errors double, but seem similar and the project again builds with no errors. 3. I add a DUT and GVL, with a function, and I get the following errors. They remain even if I delete these things. ------ Build started: Application: Device.Application ------- Typify code... [ERROR] crr: C0032: Cannot convert type 'Unknown type: 'ADR(GVL_Io_17160064_c083_41f8_9e53_208be7537753_HPS_7.Io_17160064_c083_41f8_9e53_208be7537753_HPS_7)'' to type 'POINTER TO IoConfigParameter' [ERROR] crr: C0077: Unknown type: 'GVL_Io_17160064_c083_41f8_9e53_208be7537753_HPS_7.Io_17160064_c083_41f8_9e53_208be7537753_HPS_7' [ERROR] crr: C0046: Identifier 'GVL_Io_17160064_c083_41f8_9e53_208be7537753_HPS_7' not defined Compile complete -- 3 errors, 0 warnings I attach the project. What am I doing wrong? Thanks!
Last updated: 2024-05-02