Post by jens on Modbus tcp - channel
CODESYS Forge
talk
(Post)
Help wanted This is the first time i'm doing a Modbus Tcp project. I have some VLT with a extension module MCA-122. i'm currently unable to write to the VLT slave, but i can read from status word parameter=1603 and address := 16029 where the address is calculated from parameter is ((id x 10)-1). in the manual the functions that are supported are 3 hex, 6 hex, 10 hex, b hex and 11 hex. read holdin registers, write single register, write multiple registers, get comm. event counter, report slave id. i'm only using the Modbus Slave Channel is this wrong when trying to write to the vlt ?
Last updated: 2024-06-13
Post by timvh on Modbus TCP & RTU with Control for Linux SL
CODESYS Forge
talk
(Post)
RS485 doesn't seem very logical to use in VPLC's in my opinion. I also don't know if this is supported.... But for TCP/IP, I think you still need to configure the Nic settings. See the attached png. In my case enp6s0. When changing this setting, restart the VPLC. What is really nice, is that you don't have to configure the IP address setting in Linux. By setting the Nic to a certain IP address in the CODESYS instance configuration, this is automatically done for you. I only tested this with EtherCAT, but I guess this works the same for Modbus TCP/IP.
Last updated: 2024-10-23
Post by timvh on Modbus TCP & RTU with Control for Linux SL
CODESYS Forge
talk
(Post)
It seems you have 2 network interfaces. Did you try eth1? Did you already configure the IP address for this interface in Linux? If yes, then maybe undo this. - or only set eth0 in the Nic configuration without anything else (so no IP address, because this is already set in Linux). For more information about the Nic settings, see (probably already read it?): https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_obj_deploy_control_sl_configuration.html PS, if you only want to run CODESYS Control SL, you don't necessarily need the Virtual PLC variant. You could also install and run the CODESYS Control SL Runtime in the Host operating system. This way you should also be able to access the serial port and directly access all ethernet ports. Maybe this is easier?
Last updated: 2024-10-23
Post by felipemsgarcia on Generic EtherCAT slave
CODESYS Forge
talk
(Post)
Hello, Without much info, I would assume that this is an optional object on the EtherCAT network and it's either disconnected or the address doesn't match. I would look into the devices manual or contact the manufacturer for further assistance. And, I would have posted a new topic instead of using a non related one... Cheers!
Last updated: 2024-05-16
Post by xiaoyan on Generic EtherCAT slave
CODESYS Forge
talk
(Post)
Hello Well i need some basic advice. My protegoD drive is shown deactivated in the device tree. i can see its variables and other i/o in online mode but the device itself is deactivated. how can i address this issue. is there any configuration error.using ethercat link to connect to protegoD by Primo MC plc
Last updated: 2024-05-16
Post by rjonker on codesys mqtt publish serialization
CODESYS Forge
talk
(Post)
pbPayload is a pointer, which it expects to point at a STRING. If you point it at an address holding a different data type, it will just assume those bytes are part of a string and likely trundle along memory until it finds a null byte (0x00) that would normally signify the end of a string PublishMessage := BOOL_TO_STRING(boolVariable);
Last updated: 2024-06-05
Post by rschwager on GVL to SHMem
CODESYS Forge
talk
(Post)
Hallo! Have some any idea to transfer whole GVL to Shared Memory? I also shared REATIN memory to shraed meory for making a Retain Backup System without USP in Linux on a FRAM. For an other Application we want to shared the whole GVL off obne part (e.g. GVL_Test). How cvan I get easy the Size and the Address for meory copy?
Last updated: 2024-07-09
Post by davidf on Error trying to activate the demo Git licence
CODESYS Forge
talk
(Post)
The CodeMeter Control Center log shows the following: 2024-10-11 21:02:13: Entry (6000437:8747) not found - Event WB0200 (ENTRY NOT FOUND), Request IP-Address local(IPV4) (SID 0xc079 / 0x00) with StationShare Mode 2024-10-11 21:02:13: API Error 200 (ENTRY NOT FOUND) occurred!
Last updated: 2024-10-11
Post by r-niedermayer on Issue with WebVisu on Raspberry PI
CODESYS Forge
talk
(Post)
Regarding to your application: When clicking in the web visualization, the boolean variable will be tapped for both buttons. The LED in the web visualization lights up as long as the variable is true The used variables should come from the GVL, ad/or thePLC_Prg. We see no difference or problem in both projects: You have created a visuelement Push button a a tapper, that is supposed to control the variable in this way as expected. This is also reflected (switching Bool from false to true) in the program code, as well as in the (GVL declared) variables. Wherever the misunderstanding comes from: no, this is not memory or license related. Our best guess: it is probably more of an applicative/conceptual implementation.
Last updated: 2024-04-11
Post by ac-spr on Runtime variable that indicates a user is online to the code
CODESYS Forge
talk
(Post)
Looking to access a variable at runtime that indicates a user is online to the code. essentially want to use this value to feedback to the user on the HMI. we use turck and bosch rexroth devices if this information helps. I was hoping there was a variable at the application level, or a library that could be used but I was unable to find anything. I know there's a pop up when you try to login/ go online to the code when a user is already logged in, so the system does provide an indication that it knows already online, but has no access to a value from what I can see. Any help is appreciated
Last updated: 2024-04-22
Post by ucconversions on displaying all incoming CAN bus messages
CODESYS Forge
talk
(Post)
Hello Im using CAN API Im receiving CAN messages with no problem. below is my code. METHOD ProcessMessage VAR_IN_OUT ( Incoming message ) Message : CAN.RxMESSAGE; END_VAR VAR i: USINT; END_VAR recvCANid := Message.udiCanID; IF recvCANid = 16#18FF8247 THEN UserVarGlobal.g_countMsg_RPMset := UserVarGlobal.g_countMsg_RPMset + 1; FOR i := 0 TO 7 DO myDataFF82[i] := Message.abyData[i]; END_FOR END_IF but in this way I can only display CAN messages which I know its ID. I want to display all incoming CAN messages for example first incoming CAN message - I assign it into a variable Message1. second incoming CAN message - I assign it into a variable Message2. third incoming CAN message - I assign it into a variable Message3. Can you give me guidance? Thank you BR
Last updated: 2024-07-18
Post by alexgooi on Modbus writing on value change
CODESYS Forge
talk
(Post)
Hi Duvan, You could make this in 1 single object (FB), Indeed don't use a function for this beacuse you need some memory to keep the old value. For i := 0 TO 200 BY 1 DO //Check if the value has been changed IF Old_Value[i] <> Value[i] THEN //Set the trigger to TRUE Trigger[i] := TRUE; Old_Value[i] := Value[i]; END_IF END_FOR If you define the Value array as an In_Out and the Trigger as an In_Out you arn't claiming any aditional memory to your system. You ofcourse then need to add some code arround it that does something with the trigger and writes it back to FALSE again. If you want more flexability you also could use pointers instead of using the IN_OUT FOR i := 0 TO 200 BY 1 DO address := address_Input + i * SIZEOF(*Put type here); IF Address^ <> Old_Value[i] THEN Trigger[i] := TRUE; Old_Value[i] := Address^; END_IF END_FOR
Last updated: 2024-04-02
Post by macros8 on Alarm Management - latched variable represented as Text list
CODESYS Forge
talk
(Post)
Hi all, in Alarm management you can latch some variable to show value within the alarm msg. It´s very useful sometime. But I´m wondering whether there is any possibility to represent that value as Text list. It´s quite common in other HMI tools and this is very useful in case of using some ErrorID for detail specification of error. Unfortunately I could not find any way how to do it but I believe that exists :) Thanks a lot. M.
Last updated: 2023-09-06
Post by ggarcia94 on IMAGE DISPLAY ACCORDING TO INPUT VARIABLE
CODESYS Forge
talk
(Post)
Reopening this thread as I need to make a few images visible depending on the value of a variable. However, in the properties of the image I do not have the option to make the image visible (see attached image). I´m using Codesys V3.5 SP19. However, when I use V3.5 SP17 I have the option to make the images visible. Can someone help me achieve this with V3.5 SP19? EDIT: Fixed. Just had to uncheck Support client animations in the Visualization manger settings
Last updated: 2023-09-12
Post by timvh on SafetyApp - "Invalid ERR Ack input"
CODESYS Forge
talk
(Post)
I had a similar error "Invalid ERR Ack input". What you need to do is link an variable from the "non-safe" PLC to the Group IOs of the POU in the Safety app. * Add a POU to the SafetyApp (probably already done, otherwise you don't get this error) * Right click on this POU - select properties * Go to the Group IOs tab * Link a variable to the Err.Ackn. input I don't know about the Size of zero, I didn't get this error. Were you able to fix this?
Last updated: 2023-11-16
Post by simotion on Inheritance of axis
CODESYS Forge
talk
(Post)
I have developped a function block 'Axis' the inherits from 'AXIS_REF_SM3' -> FUNCTION_BLOCK Axis EXTENDS AXIS_REF_SM3 In my global variable list I define a variable MasterDrive of type Axis and assign Axis1. Axis1 is a virtual drive (AXIS_REF_VIRTUAL_SM3). This type should inherit from AXIS_REF_VIRTUAL. VAR_GLOBAL MasterDrive : Axis := Axis1; However I get the error 'Cannot convert type'. What is the way to obtain what I want : function block inheriting AXIS_REF_SM3 and initialising this function block with a Softmotion virtual or real axis?
Last updated: 2023-12-07
Post by timvh on JSON
CODESYS Forge
talk
(Post)
I don't know the details of jsonArrayWriter, but the common behaviour for an xExecute input is that the FB starts on the trigger that it gets TRUE. In your case xExecute is never FALSE, so it is never triggered again to start the jsonArrayWriter. So change the condition from TRUE to a variable which you set to TRUE with the "xFirst". Then when the jsonArrayWriter is done (xDone), or has an error (xError), then set this variable to FALSE.
Last updated: 2024-05-01
Post by automa on Defining local variables that can be independent with several users.
CODESYS Forge
talk
(Post)
Hi, I am looking for a way to define a local variable that will be multi user independent. This is so several user can connect at the same time select frames independent of each other.
Last updated: 2023-09-04
Post by sturmghost on Specify Input Configuration "OnDialogClosed" Action to only react to certain Dialogs
CODESYS Forge
talk
(Post)
You could work around this problem by implementing some sort of "state machine". Each dialog sets a boolean variable when they are closed so you know which dialog was closed. Then you can react to this accordingly.
Last updated: 2023-10-01
Post by gorditron on Modbus Slave RTU in der Applikation abschalten
CODESYS Forge
talk
(Post)
Hallo, gibt es eine Möglichkeit die Modbus Slaves (ModbusSlaveComPort) innerhalb der Applikation über ein Variable zu aktivieren oder zu deaktivieren? Bilder als Datei Danke!
Last updated: 2023-11-09
Post by imdatatas on Axis variable indicating modulo of finite setting
CODESYS Forge
talk
(Post)
You could try with "iMovementType" member of AXIS_REF_SM3 struct. https://content.helpme-codesys.com/en/libs/SM3_Basic/Current/SM3_Basic/DriveInterface/AXIS_REF/AXIS_REF_SM3.html https://content.helpme-codesys.com/en/libs/SM3_Basic/Current/SM3_Basic/DataTypes/DriveInterface/SMC_AXIS_TYPE.html
Last updated: 2023-11-25
Post by nathant on Saving variable values on power cycle (RevPi Connect)
CODESYS Forge
talk
(Post)
Hello, this seems to be a known issue, but persistent/retain variables don't seem to work properly on RevPi devices. Is there a workaround to this? All I need is for a few configuration variables to be remembered through power cycle.
Last updated: 2023-12-03
Post by snhatton on Visu - changing auto-logout time
CODESYS Forge
talk
(Post)
You could try using the VUM_UserGroup struct from the VisuUserManagement library. I haven't tried this, but there is a variable for tAutoLogout to set the logout time.
Last updated: 2023-12-11
Post by ton on How to create a stopwatch?
CODESYS Forge
talk
(Post)
Hi, i guess you want to make a hour counter. You need to store the measured value. Try to use a retain variable, but need a graceful shutdown, or save it your self. see https://forge.codesys.com/forge/talk/Runtime/thread/278e325579/ Succes.
Last updated: 2023-12-12
Post by lostcontrol on Bool turning on in case stament in wrong state?
CODESYS Forge
talk
(Post)
i would be looking at what the case variable is doing then.. sounds like there might be a logic race going on