Post by yannickasselin on codesys VLAN tagging
CODESYS Forge
talk
(Post)
Hi, I am looking for exactly the same thing. I would think that using a layer 2/3 managed switch should work but I am not convinced. I would like to test it in order to see if it would be possible to run many Codesys Docker instances on a server and run only 1 ethernet cable from the server to a managed switch closer to the machines beeing controlled instead of having to run multiple long ethernet cables. I was going to buy a managed switch in order to test it but I want to first make sure it is possible and I want to figure out exactly what kind of switch I would need. Is this even possible? I think this is a feature that would be very useful paired with "Codesys Virtual Control SL". Thank you
Last updated: 2024-09-07
Post by timvh on Clarifications regarding the appropriate runtime system to use
CODESYS Forge
talk
(Post)
If you are not using any specific Raspberry Pi functionality, then probably the "universal" Control Linux ARM SL is the approriate runtime to run on the Pi. For the license it doesn't matter which runtime version you choose, because this is not hardware based anymore, but application based. Best is to use the latest version of CODESYS. To determine which license you need, double click on your device, go to the tab License metrics.... Generate the code for your application and see which license you need based on the metrics of your application.
Last updated: 2024-09-24
Post by pernockham on Linking to IO during runtime with hot swap?
CODESYS Forge
talk
(Post)
I have a project where a single PLC shall control multiple nodes (up to 10 units?) with IO connected through profinet. Ideally each node should be identical however with time I see situations were different setups/configurations will be used. Codesys PLC (GVLs) |Profinet | |--PNIO-node-1--| | | AIO, | | DIO, | | CNT etc. | |--PNIO-node-2--| | | AIO, | | DIO, | | CNT etc. Ideally I think of a configuration through yaml/xml-files (the assignment/linking of the profinet nodes towards GVL-variables in the PLC as well as scaling, channel configration etc.). Would be grateful if someone could suggest library/-ies that can handle the following: - Verify what IO is connected to a device/node. - Hot-swap/assign link for IO towards GVLs, either automatically or through a HMI.
Last updated: 2024-10-11
Post by siscu on Raspberry i2c master device
CODESYS Forge
talk
(Post)
I want to implement an extended I2C master for Raspberry Pi Control. I was hoping for it to be as easy as creating a library with a FB that extends i2cMaster and associating it with a device following the forge drivers documentation, but I haven't managed to make it work as the driver behaves only as an i2c slave. I'm thinking this is because the forge forum only talks about extending i2c, and the master portion is omitted since most users won't want to add a custom one. I'd like to know if I'm doing something wrong. Is it really possible to make an I2C master extension device? If so, are there public examples we can check out? Any info on this topic will be appreciated.
Last updated: 2024-10-16
Post by bjarne-pagaard on OPC UA Server Status on Win RTE
CODESYS Forge
talk
(Post)
Hi there, An "OPC Expert" client software is connecting to a Codesys Control RTE (x64) OPC UA Server. It reads only about 25 variables every 5 minutes. The OPC UA Server seems to shut down on the Codesys runtime. Is there any way to get information about the Codesys OPC UA Server status? Restart it? There is nothing in the PLC Logs after the OPC UA Server has started. It works for a while, then it doesn't. Any ideas? Any way of getting more info out of the Codesys OPC UA Server? -Bjarne
Last updated: 2024-10-21
Post by timvh on Modbus TCP & RTU with Control for Linux SL
CODESYS Forge
talk
(Post)
RS485 doesn't seem very logical to use in VPLC's in my opinion. I also don't know if this is supported.... But for TCP/IP, I think you still need to configure the Nic settings. See the attached png. In my case enp6s0. When changing this setting, restart the VPLC. What is really nice, is that you don't have to configure the IP address setting in Linux. By setting the Nic to a certain IP address in the CODESYS instance configuration, this is automatically done for you. I only tested this with EtherCAT, but I guess this works the same for Modbus TCP/IP.
Last updated: 2024-10-23
Post by gediminas on Datasource OPC UA client system failure
CODESYS Forge
talk
(Post)
I am using CODESYS v3.5 SP20 Patch 3 / Control for BeagleboneBlack SL v4.13 and after some time the OPC UA Server crashes. However, Runtime still works without any issues. The events leading up to the OPC server crash are the most suspicious: 1) Mutex deadlock detected - owner thread died, and 2) Runtime received SIGABRT. And it seems very similar with this topic except used versions - issues should be fixed with previous SP's. I can't seem to find any information about these events. Need some pointers in the right direction on how I can fix this problem.
Last updated: 2024-10-25
Post by phoward131 on Alarm Table Filtering
CODESYS Forge
talk
(Post)
I am having trouble getting the alarm table filtering to work. I downloaded the alarm filter latch example project and ran it on the local Codesys Control Win and the filters worked fine. I am trying to replicate it in my project and everything seems to be set up the exact same way and every time I turn on the filter, it shows no alarms. I even started a blank project and just copied in elements from the example project so that it is exactly the same and when I attempt to filter, it again shows no alarms. Could there be some project settings I need to adjust to make this work? I have attached my project with elements copied from the example project and filtering is not working.
Last updated: 2024-10-28
Post by martinlithlith on Device User Logon and No device is responding.. Pi4b codesys 3.5 SP19 2 + (64-bit)
CODESYS Forge
talk
(Post)
Hi! Im slowly starting to loose it and i need som help! After a few night of reading up and testing i´m still stuck as a rock and you guys and girls are my last resort for this project. Basic facts; Win 11 Codesys 3.5 SP19 2 + (64-bit) Raspberry pi 4 model b 2 gb Raspian release 11 aarch64 What keeps me up late at night; Username and Password when trying to connect to device and device only beeing connectable for a few seconds. Some of the things I have tried; Username and passord; Credientials from the raspberry Administrator Administrator admin admin Admin Admin administrator administrator Usernames and passwords that I sometimes use (this was a longshot i know, but i was running out of ideas and energy). :) Epand filesystem, activating i2c, spi, 1-wire I can start the gateway and start the runtime. I cant install the edgearm64, arm64 runtime package eventhough I guess i should, i get code [ERROR] Error output: dpkg: error processing archive /tmp/codesysedge_edgearm64_4.8.0.0_arm64.deb (--install): [ERROR] Error output: package architecture (arm64) does not match system (armhf) [ERROR] Error output: Errors were encountered while processing: [ERROR] Error output: /tmp/codesysedge_edgearm64_4.8.0.0_arm64.deb code as a respons. I have tried to Reset Origin Device - no change. I have tried to remove the /etc/CODESYSControl_User.cfg [CmpUserMgr] but i could not find it and i was not sure if i should add it instead but i did not want to mess somthing up. I have tried to create a second gateway with the specific ip if the pi, that did not help. Could it be that i´m currently connected to the pi through WIFI? I can ping the pi and I can connect and control it through VNC. When i scan to select gateway target (scan edge gateway) i find 17-21 devices but can find the pi throug the mac adress. I started of trying to use the "CODESYS Control for Raspberry Pi SL" (I have a license sience earlier) as i read somewhere that this could be used on a Pi4 as well but now i´m trying with the MC SL, no changes, same problem. Right now - gateway version 4.8.0.0 (edgearmHF, armhf), Runtime Package 4.5.0.0 (raspberry, armhf). Any sugestions are very welcome! As mentioned above, theese are some of the things that i have tried/done - but i have been going at this for a while. Best, Martin
Last updated: 2023-09-10
Post by mondinmr on Frustration-Fueled Feedback on Project File Management and Git Integration
CODESYS Forge
talk
(Post)
Good day, I’m writing this message out of frustration regarding the current way project files are saved as encrypted XML and single-file format in CODESYS. I find this approach to be quite tedious for several reasons: Limited Access to Structured Text: Not being able to access Structured Text (ST) externally makes it impossible to work with alternative editors like VSCode. Tools like VSCode are incredibly responsive and feature advanced systems such as GitHub Copilot, which would be a real game-changer when working with ST IEC. While CODESYS works well for small code snippets or debugging, when the codebase grows, switching to VSCode to boost productivity becomes essential, and copy-pasting between environments is a cumbersome workaround. Poor Integration with Git: This file format also makes it very difficult to integrate effectively with Git. I have tested the internal demo, but for advanced merges, it is unusable. Without properly formatted plain text, it’s impossible to leverage the vast ecosystem of external tools around Git that allow smooth merges in heterogeneous teams. File Corruption on Network Drives: I often work from multiple locations with shared network drives. When the development environment saves a file and something goes wrong midway (which can occasionally happen when using VPNs and network drives), the entire project becomes irrecoverable. There’s no way to cancel the save process, and the development environment freezes. This has happened to me at least four times over the past two weeks, and one of those incidents cost me an entire day of work. All of this is particularly disappointing because I truly believe that the libraries, runtime, and overall work done by CODESYS are exceptional. I find it fantastic that there is a platform allowing development of PLCs and control systems using OOP, which is a huge advantage in modern control engineering. I apologize for the rant, but this issue has been extremely frustrating. Best regards.
Last updated: 2024-10-15
Post by yr00 on OPC UA datasource low read frequency
CODESYS Forge
talk
(Post)
Hello everyone, I am trying to test the OPC UA client feature in Codesys. My setup is the following; I have a Codesys simulation/ visualization running on Control Win V3. My OPC UA server is hosted on a Siemens 1518 PLC using PLCSim Advanced. The setup is completely virtual so there are no really PLCs. Everything is on my laptop. Writing data from the Codesys simualtion to the server is very quick. I have a PLC program running on another 1500 PLC which reads data from simulation via the server, and changes in the simulation (e.g. button pressed) appear within hundreds of miliseconds if not tens of miliseconds in my PLC program. However, when it comes to reading data from the OPC UA Server by Codesys, it taks around 1-2s. I connected a UAExpert client and it gets update very quickly so I am fairly sure the problem is with Codesys. I have tried changing the update rate in datasource -> General and Diagnosis, but it doesn't seem to have an effect. Do you guys have any suggestion on what I can do?
Last updated: 2023-08-29
Post by captaincookie on increase default string length in queue
CODESYS Forge
talk
(Post)
Hello, I'm using Codesys V3.5 SP18 Patch 4. In the ElementCollectionExample Project from Codesys, I test the SimpleQueueExample in a Control Win V3 x64 environment. I try to add a string of 95 characters length to a queue. The default length of strings is defined as 80 characters. In the initialization of a string variable, it is possible to increase the length by the definition of e.g. STRING(1000). But when I write the string defined like this to the queue, only 80 characters are written to it and the rest is missing. I think the default length is still set in the queue definition, so it is necessary to change this, isn't it? Is there any option to increase the default length of strings in the queue? Attached you can find the used project. Thanks in advance. If any information are missing or my description unclear please let me know.
Last updated: 2023-10-05
Post by annd on Migration von "CODESYS Control for PFC200 SL" zu WAGO FW26 "CODESYS V3.5.19.2"
CODESYS Forge
talk
(Post)
Hallo, da Wago nun von eCockpit zum offenen "CODESYS Development System V3" wechselt, möchte ich meinen bestehenden 750-8212 von der PFC200 SL auf die Wago Firmware umstellen. Welche Schritte sind dabei notwendig? Den Controller würde ich auf die aktuelle FW 26 updaten und die 3.5.19.2 von Wago mit den Descriptions verwenden. Reicht es im Codesys Projektbaum mit "Gerät aktualisieren" auf den Wago Controller zu wechseln? Es wird dann statt dem "Pfc200Bus"ein leerer K-Bus und ein leerer Com-Port angezeigt. Müssen die einzelnen Module dann darunter neu angelegt und alle E/A Variablen manuell neu eingetragen werden? Das exportieren und danach wieder importieren funktioniert nicht, weil die Namen bzw. Adressen unterschiedlich sind. Ist das so richtig? Kann der Block "Modbus_COM_Port - Modbus_Master_COM_Port - Modbus_Slave" so bleiben wie bisher oder muss das auch unter dem neuen COM-Port neu angelegt werden? Für ein paar Hinweise wäre ich dankbar. Schöne Grüße, annD
Last updated: 2023-11-17
Post by annd on Migration von "CODESYS Control for PFC200 SL" zu WAGO FW26 "CODESYS V3.5.19.2"
CODESYS Forge
talk
(Post)
Ich hab's hinbekommen: Nach dem Controller Update hab ich ein neues Projekt gemacht und nur den PFC200(8212) eingefügt (es erscheint dann ein leerer Kbus und eine serielle Schnittstelle COM1). Dann hab ich mich am Controller eingeloggt und den Kbus (Rechtsklick: Geräte suchen) mit allen Modulen automatisch ergänzen lassen. Bei den leeren Modulen hab ich dann das E/A-Abbild in csv exportiert. Dasselbe hab ich bei meinem alten "PFC200 SL" Projekt gemacht. Und dann in Excel alle Variablennamen in die leeren csv kopiert und danach wieder im neuen Projekt importiert. Dann hab ich noch alle Programmblöcke, Tasks, Visualisierungen und auch Modbus TCP Master u. Slave und auch Modbus COM Port Master und Slave in das neue Projekt kopiert. Weiters hab ich alle notwendigen Bibliotheken im Bibliotheksverwalter eingefügt. Dann noch ein paar kleine Fehler korrigiert (ich musst einen anderen Block zum Lesen der Uhrzeit nehmen) bis ich das neue Projekt fehlerfrei übersetzen konnte. Dann konnte ich es auf den Wago Controller übertragen und direkt starten. Es sieht so aus, dass alles läuft. Gruß annD
Last updated: 2023-11-18
Post by mavitia on Application based license problem - Modbus TCP
CODESYS Forge
talk
(Post)
I am running ubuntu on a raspberry pi, and installed an application based license Control Basic M on it, it runs a demo program fine, does not timeout etc. however, when I add a modbus TCP device, I start getting errors: <Entry severity="error" component="CmpApp" user="nobody" timestamp="12/18/2023 3:49:42 PM" infoId="24">Online change denied. Application Application is in exception state!</Entry> <Entry severity="error" component="CmpApp" user="nobody" timestamp="12/18/2023 3:49:42 PM" infoId="68">Download failed: Application=Application</Entry> <Entry severity="exception" component="CmpApp" user="nobody" timestamp="12/18/2023 3:49:41 PM" infoId="0">Application app=Application has invalid license metrics!</Entry> the modbus tcp slave runs, and the counter ticks up, however, when I call the variables on the %IX0.0 in my program, and try to upload the changes, I am getting the error messages which stop the program as far as I understand, the application based, M includes 2 fieldbus instances, but on the other side is fairly new, anything obvious I am missing out here?
Last updated: 2023-12-18
Post by forest on SM Drive license error
CODESYS Forge
talk
(Post)
Hi, when it comes about license, I used INVTmatic Studio, which uses Codesys, for programming INVT plc. I bought Codesys Modbus license, it was not expensive, and then realised that INVT didn't have License Manager option (greyed out in program) which is needed for using of Codesys License. I contacted support from INVT, but developers told me that option is still not available. So depending on environment for programming Codesys, you can or not use Modbus license. Good thing about this version of Modbus TCP it works both direction. I could send commands and receive feedbacks from drive. But communication stops after 30 mins. So I used simple version of ethernet modbus which is somewhere in INVT or Condesys library (I can check tomorrow) which works only one way. I could send cmd to drive, and control it, but didn't have any feedback, like some readings back in PLC. which is bad, but at least I could start it and it didn't fail after 30 mins.
Last updated: 2024-01-10
Post by axilleas on SMC_Interpolator + SMC_controAxislbyPos
CODESYS Forge
talk
(Post)
dear all I am working on a very generic gantry system (virtual drives + win v3 control) reading gcode from external file. In order to stop the interpolator function from running when gaps are detected, SMC_controlAxisByPos FB has the bStopIpo output which according to the manual is connected to the Interpolator's bEmergencyStop. Lets assume that the axis are parked in position X1000 Y1000 and the initial G code movement is G00 X500 Y500. The normal behavior is to travel from the actual x1000 y1000 to G00 X500 Y500. The SMC_Interpolator always gets the X0 Y0 as the initial position, meaning that the bStopIpo is active until the axis are in X0 Y0 and the release the interpolator to set the new positions to X500 Y500. Is there a suggested method to solve this behavior? bonus question: I get a lot of bStopIpo during standard interpolation movements (not gaps). While working with virtual axis this is not a problem but when real axis are installed this will be an issue. What exactly triggers the bStopIpo output? Slow axis accelerations compare to Gcode defaults? Kind Regards
Last updated: 2024-02-05
Post by fredsta on Unable to load dynamic modules (Download failed: Application=Application)
CODESYS Forge
talk
(Post)
Hey there, I am currently trying to find a good solution for the communication between CODESYS Control on Raspberry Pi and "the rest of the world", i. e. the things apart from CODESYS on my linux. My first approach was to use the c-integration. So I created a lib, defined extern fbs, compiled the code on my Pi using the SDK and put the .so into my lib project. When I try to log into the Pi and load the program, I get the error message which you can see in the attached picture. "Die dynamischen Module der C-Integration konnten nicht auf das Laufzeitsystem geladen werden" is german and means roughly "the modules from the c-integration could not be loaded onto the runtime system." Is this normal? Am I doing something wrong? I will have a look at the unix domain socket thing next, as I am still in the process of finding the best solution for the communication.
Last updated: 2024-02-15
Post by timl on BacNet "Unaufgelöste Referenz"
CODESYS Forge
talk
(Post)
Hallo, ich habe Probleme beim nachbauen des BacNet2 Tutorials "Erste Schritte" aus der CODESYS Online Help. https://content.helpme-codesys.com/de/CODESYS%20BACnet/_bacnet_first_steps.html Das Anlegen des BacNet2 Servers und der danach folgenden BacNet Datenpunkte erfolgt ohne Probleme. Der Code lässt sich mit F11 auch Fehlerfrei generieren. Beim Download auf die SPS tritt dann der Fehler auf dem Bild auf. Anbei auch ein Bild des Logs nach dem Download. CODESYS BACnet 2.0.0.0 ist über den Installer runtergeladen. Device: CODESYS Control Win V3 x64 Version 3.5.19.40 CODESYS 3.5.19.40 Im Bibliotheksverwalter ist BACnet2 2.0.0.0 aufgeführt Die Konfigurationsdatei habe ich mit folgenden anpassungen abgespeichert: [ComponentManager] Component.1=CmpTargetVisuStub Component.2=CmpWebServer Component.3=CmpWebServerHandlerV3 Component.4=SysCpuMultiCore Component.5=SysReadWriteLock Component.6=SysCpuBreakpoints Component.7=SysPipeWindows ;Component.8=CmpHilscherCIFX ;Component.9=CmpPCANBasicDrv ;Component.10=CmpCANFoxDrv ;Component.11=CmpIxxatCANDrv ;Component.12=CmpBlkDrvCanServer ;Component.13=CmpBACnet Component.14=CmpBACnet2 [CmpBACnet2] ;configuration file of the BACnet stack IniFile=$PlcLogic$/bacstac2.ini ;task priority of the BACstack process task, default: TASKPRIO_NORMAL_END (159) TaskPrio=128 ;name of the named pipe for the communication with the BACstack AppName=/tmp/BACnetServer Habe ich etwas vergessen?
Last updated: 2024-02-16
Post by acc00 on Main Task cycle too long leading to PLC Fail
CODESYS Forge
talk
(Post)
I have 2 Wago PFC200 PLC, running with Runtime SP19 Patch 5, with the Redundant application. The PLC communicates as Modbus Master with at this moment 15 Modbus Slaves -later there will be 28 in total- (Drives, Power management units,...). These devices are connected in 2 rings (1 ring of Drives, 1 ring of Power Management units), with 2 Managed Moxa Switches being part of the ring. Each PLC is connected to one of these switches. The issue I'm encountering is that the Cycle time of the Active PLC goes very high when I'm closing the Drive ring (simulating an issue on one Cabinet supply, resulting in that one Drive shut down, which can happen on field quite often). As a result of this long cycle, the PLC fails and goes to Exception, and the Passive PLC does not take control of the system. A normal cycle is around 30ms for the Main task, and a few ms for the Ethercat task. When I monitor with Profiler, I see that in this Maximum Cycle, the main Task is only taking 13ms, so I'm not sure where the PLC is hanging for so long. Is the remaining cycle time the Redundant management/sync or something else? Thank you in advance.
Last updated: 2024-03-08
Post by markushunter on Different behavior between the "Start" button in the IDE and the Cmp function "AppStartApplication()"
CODESYS Forge
talk
(Post)
In our application with CODESYS V3.5 SP19 Patch 5 and the Soft-PLC Name: CODESYS Control Win V3 x64 Typ: 4096 ID: 0000 0004 Version: 3.5.19.50 the application behaves differently when we start the application via Cmp.AppStartApplication(pApp) than when we press the "Start" button in online mode in the IDE. Unfortunately, it looks like the AppStartApplication() function, which is called in the "StopDone" system event, is not able to restart the fieldbus driver correctly, in our case the EtherNet_IP_Scanner: Name: EtherNet/IP Scanner Hersteller: 3S - Smart Software Solutions GmbH Kategorien: EtherNet/IP Scanner Typ: 100 ID: 0000 100B Version: 4.5.1.0 Bestellnummer: 1 And one EtherNet/IP adapter Name: FANUC Robot R30iB Plus Hersteller: FANUC Robotics America Kategorien: EtherNet/IP Remote Adapter Typ: 101 ID: 356_12_4_3 Version: Major Revision=16#3, Minor Revision = 16#1 Beschreibung: EtherNet/IP Target imported from EDS File: fanucrobot0301_r30ibp.eds Device: FANUC Robot R30iB Plus Version Konfiguration 3.5.6.0 The application was cold reset in both cases via CmpApp.AppReset(pApp := pApp, usResetOption := CmpApp.RTS_RESET_COLD. Does anyone know the difference between the functions or services executed by the "START" button in online mode and Cmp.AppStartApplication()? Thanks and best regards, markushunter
Last updated: 2024-03-20
Post by markushunter on Different behavior between the "Start" button in the IDE and the Cmp function "AppStartApplication()"
CODESYS Forge
talk
(Post)
In our application with CODESYS V3.5 SP19 Patch 5 and the Soft-PLC Name: CODESYS Control Win V3 x64 Typ: 4096 ID: 0000 0004 Version: 3.5.19.50 the application behaves differently when we start the application via CmpApp.AppStartApplication(pApp) than when we press the "Start" button in online mode in the IDE. Unfortunately, it looks like the AppStartApplication() function, which is called in the "StopDone" system event, is not able to restart the fieldbus driver correctly, in our case the EtherNet_IP_Scanner: Name: EtherNet/IP Scanner Hersteller: 3S - Smart Software Solutions GmbH Kategorien: EtherNet/IP Scanner Typ: 100 ID: 0000 100B Version: 4.5.1.0 Bestellnummer: 1 And one EtherNet/IP adapter Name: FANUC Robot R30iB Plus Hersteller: FANUC Robotics America Kategorien: EtherNet/IP Remote Adapter Typ: 101 ID: 356_12_4_3 Version: Major Revision=16#3, Minor Revision = 16#1 Beschreibung: EtherNet/IP Target imported from EDS File: fanucrobot0301_r30ibp.eds Device: FANUC Robot R30iB Plus Version Konfiguration 3.5.6.0 The application was cold reset in both cases via CmpApp.AppReset(pApp := pApp, usResetOption := CmpApp.RTS_RESET_COLD. Does anyone know the difference between the functions or services executed by the "START" button in online mode and Cmp.AppStartApplication()? Thanks and best regards, markushunter
Last updated: 2024-03-20
Post by markushunter on Different behavior between the "Start" button in the IDE and the Cmp function "AppStartApplication()"
CODESYS Forge
talk
(Post)
In our application with CODESYS V3.5 SP19 Patch 5 and the Soft-PLC Name: CODESYS Control Win V3 x64 Typ: 4096 ID: 0000 0004 Version: 3.5.19.50 the application behaves differently when we start the application via Cmp.AppStartApplication(pApp) than when we press the "Start" button in online mode in the IDE. Unfortunately, it looks like the AppStartApplication() function, which is called in the "StopDone" system event, is not able to restart the fieldbus driver correctly, in our case the EtherNet_IP_Scanner: Name: EtherNet/IP Scanner Hersteller: 3S - Smart Software Solutions GmbH Kategorien: EtherNet/IP Scanner Typ: 100 ID: 0000 100B Version: 4.5.1.0 Bestellnummer: 1 And one EtherNet/IP adapter Name: FANUC Robot R30iB Plus Hersteller: FANUC Robotics America Kategorien: EtherNet/IP Remote Adapter Typ: 101 ID: 356_12_4_3 Version: Major Revision=16#3, Minor Revision = 16#1 Beschreibung: EtherNet/IP Target imported from EDS File: fanucrobot0301_r30ibp.eds Device: FANUC Robot R30iB Plus Version Konfiguration 3.5.6.0 The application was cold reset in both cases via CmpApp.AppReset(pApp := pApp, usResetOption := CmpApp.RTS_RESET_COLD. Does anyone know the difference between the functions or services executed by the "START" button in online mode and Cmp.AppStartApplication()? Thanks and best regards, markushunter
Last updated: 2024-03-20
Post by rmaas on Fieldbus has lost synchronicity
CODESYS Forge
talk
(Post)
Hi, On a gantry system with 2 axis i am getting the following error: SMC_DI_FIELDBUS_LOST_SYNCRONICITY This happens random, sometimes it happens every 5 minutes and sometimes no error for 2 hours... The Setup: - Using codesys 3.5 SP20 with all latest libs... - Kontron AL Pi-Tron CM4 with Preempt realtime patch (Raspberry Pi 4) - Codesys runtime 4.11.0.0 (single core) - CODESYS Control for Raspberry Pi SL licensed - Softmotion + CNC + Robotics licensed - 2x Leadshine EL8-EC400 servo drives - Axis group for a 2-axis T-Gantry Ethercat network wiring: Ethercat master softmotion -> Beckhoff EK1100 -> Servo drive #1 -> Servo drive #2 Ethercat Cycle time = 4ms Max Jitter = 140~150 What i have tried so far: - changed the sync offset from 20% to 30% - changed ethercat task priority from 1 to 0 Running tasks: - Ethercat tast: Prio = 0, Interval = 4ms - Main task: Prio = 1, Interval = 8ms - Visu task: Prio = 31, Interval = 100ms - Softmotion planning task: Prio = 15, Freewheeling - 3 other default tasks that were created by AC_Persist Motion fb's are called in the ethercat task... Does anyone have an idea how to fix this? Any help is greatly appreciated!
Last updated: 2024-04-11
Post by salvadegianluca on How to use TON inside an FB that is instanced within a Visu page
CODESYS Forge
talk
(Post)
Hi everyone; I'm building a project in which the drag of the mouse over some controls (or the click event) changes the background color of the control items; this change of color is made with an FB that assignes a color code to the background with MUX command based on the value of an enumerator, this part is perfectly working but, when I'm using a touchpanel instead of a web visu (controlled by a mouse) I get into some issues as it seems that the touch operations are not triggering the MouseEnter and MouseLeave properties as it's done with the mouse.... For this reason I'm trying to add a TON to my FB and, if the enum that changes color remains at the same state for more then 3s I'm automatically resetting it to it's "0" so the item gets back the not selected color. Anyhow it looks like the TON function from library is not working in these FB that are instanced in the various visualizations, as instead they do if I create some instances within the POUS. Anyone has ideas of how to make them work?
Last updated: 2024-04-15