Post by dhumphries on No source code available CODESYS Forge talk (Post)
Try using an Ethernet/IP scanner instead of an adapter, I'm guessing the 2 devices you're trying to communicate with are adapters, you have to have a scanner somewhere and Codesys should be a scanner. I don't know why you're getting the error, you should be able to use your Ethernet port as an EthernetIP adapter (although I've never had a reason to try,) but it's probably not what you wanted to do, unless you're connecting to another PLC that is a scanner. Good luck configuring the devices you're trying to connect to, it will be a lot easier if you have an .EDS file instead of starting with a generic module, even with an .EDS it can be tricky getting the communication working.
Last updated: 2024-02-03

Post by alexgooi on Is it possible in the log to see previous shutdown CODESYS Forge talk (Post)
Hi DavidBo, In general Codesys is used to control equipment and an exception is the worst thing that can happen in your installation. If you cannot prevent the exception from triggering, you could implement a Try catch statement, with this solution your controller keeps on running and you are able to handle the exception. __TRY //This statement will trigger an exception Result := 4/0; __CATCH(exc) //Handle the exception HandleException(exc, strExceptionText => strExceptionText); // From the Codesys help file //Create a log file //-------------------------------------------------------- __ENDTRY What you also could do is implement implicit checks, these functions cover most of the exceptions (like dividing by zero) See picture But in general avoid a complete controller shutdown!
Last updated: 2024-02-09

Post by jtebokkel on Access to the path *** is denied CODESYS Forge talk (Post)
I am also having this issue. It was working fine for the first 2ish months and is now throwing this error. I can just try and go online again a second time and it works. I'm wondering if there is an environmental variable or something that isn't set that is causing it to use an empty path as a temp directory. The empty path will be the location the app is running from which is that path C:\Program Files\CODESYS 3.5.19.50\CODESYS\Common. The permissions don't allow a normal user to write to that directory which causes the error. It also only seems to happen when there are changes or the build has been cleaned.
Last updated: 2024-02-14

Post by valenting on Runtime not working on raspberry pi Bullseye CODESYS Forge talk (Post)
Hello I have a problem with Codesys on Raspberry pi with Bullseye The device is not recognized as a Raspberry pi, as I get this error : ooops... this runtime was built for RASPBERRYPI. Hardware version or firmware version not supported! (-18, 0x00000BB8, 0xFFFFFFFB) I'm running Codesys on a compute module 4S with Raspbian GNU/Linux 11 (bullseye), my kernel version is Linux 5.10.90-v7l+ Codesys version is the latest, released last week (4.11.0.0, CODESYS Control V3.5.19.61 for ARM-32Bit - build Feb 22 2024) I know it works on the same device if I use Raspbian 10 (Buster) with Linux 5.4.81-v7l+ kernel, but for some other reasons I have to use Bullseye. What can I do ?
Last updated: 2024-03-01

Post by sachem on Problem retain values Weidmuller UC20-WL2000 CODESYS Forge talk (Post)
Good afternoon. I am working with a weidmuller uc20-wl2000 controller, using a codesys license. We made a ladder code to control a process, and it works well, but we want some variables to remain stored even when the controller is turned off. We tried to use retain variables, but at the time of loading the program, when we went offline from the controller, the program was deleted, it did not remain in the controller, and in the same way if we turned off the controller. In addition to this, when we tried to program it again, the program would not stay loaded and began to present errors with the opc-ua communication. What could be causing this problem? How can we maintain the values of the variables without damaging the program or affecting the controller? thank you
Last updated: 2024-04-10

Post by jrsantab on Remote connection to ifm PLC & HMI CODESYS Forge talk (Post)
Hello, We are trying to access remotely a PLC (ifm 711S) and a HMI (ifm CR1077). Both are connected to a Teltonika RUT200 router. We establish the connection with OpenVPN Connect and can ping both controllers. We have a laptop that, most of the time, will allow Codesys connection to the controllers, but we have several other computers that are unable to connect, although all of them can ping successfully. We cannot find any difference in the configuration or software installed from one PC to another. If we connect to the router by WIFI, instead of VPN, all the computers work fine. We know that scanning the network will not work over a remote connection, so we input the controller IP directly. Has anyone had a simlar problem and can offer any hint on what to check to meke the connection run?
Last updated: 2024-04-11

Post by jrsantab on Remote connection to ifm PLC & HMI CODESYS Forge talk (Post)
Hello, We are trying to access remotely a PLC (ifm 711S) and a HMI (ifm CR1077). Both are connected to a Teltonika RUT200 router. We establish the connection with OpenVPN Connect and can ping both controllers. We have a laptop that, most of the time, will allow Codesys connection to the controllers, but we have several other computers that are unable to connect, although all of them can ping successfully. We cannot find any difference in the configuration or software installed from one PC to another. If we connect to the router by WIFI, instead of VPN, all the computers work fine. We know that scanning the network will not work over a remote connection, so we input the controller IP directly. Has anyone had a similar problem and can offer any hint on what to check to make the connection run?
Last updated: 2024-04-11

Post by esave on OPC UA Server with on Codesys + OPC UA Client on Labview CODESYS Forge talk (Post)
Hello everyone I want a communication between my PLC as an OPC UA Server and Labview on my PC as the OPC UA Client. I have an Festo CPX-E-CEC-C1-PN PLC and I have the OPC UA Toolkit from Labview. I created some Variables for testing (see picture 1) on Codesys. I tried to use this Labview block diagram (see picture 2) but I cant connect the PLC to it. What do I have to type in the Server Endpoint URL and what in the Node ID? Is this a good way for communication with a PLC to a PC? If not is there another way?
Last updated: 2024-04-12

Post by mbmik on IoDrvModbusTCP_Diag not defined when using MODBUS CODESYS Forge talk (Post)
Hi Im trying to setup a Weidmüller WL2000 to run with MODBUS, to get some data from a server. Codesys V3.5 SP20. The issue is, that whenever i attach an ethernet port and add MODBUS Master und also a Slave, codesys will compile the project, but there always seem to be some remaining errors, which or only visible, when setting the messages window to "Pre-Compiled". I tried a lot of stuff to get rid of these errors, but cant find to seem the reason. New installation of codesys, cleaned project, setup completely empty new project, manually adding libs. Nothing helps. Any help is apreciated. Maybe we are doing something wrong.. Example Project is available, if somebodey wants to take a look. Greetings and thanks alot
Last updated: 2024-04-15

Post by ac-spr on Runtime variable that indicates a user is online to the code CODESYS Forge talk (Post)
Looking to access a variable at runtime that indicates a user is online to the code. essentially want to use this value to feedback to the user on the HMI. we use turck and bosch rexroth devices if this information helps. I was hoping there was a variable at the application level, or a library that could be used but I was unable to find anything. I know there's a pop up when you try to login/ go online to the code when a user is already logged in, so the system does provide an indication that it knows already online, but has no access to a value from what I can see. Any help is appreciated
Last updated: 2024-04-22

Post by reinier-geers on License problem gateway CODESYS Forge talk (Post)
Epis doesnt want Softmotion. I thought it was about the price. If it was possible it would be working already and i dont need an extra licence. Thats the problem of codesys. The software is running but hangs on its license. Epis made it posible to see the stick. I can see the license. Softmotion is there from 3.5.14.Xx Like is said And Motion control is alrady posible 15 year ago. And i only need a Sync of 2 drives. I want a good solution not a refund. Dont point to the manufacturer. The software is made by 3s not by epis .
Last updated: 2024-04-29

Post by amy123 on Any guides on using Codesys containers in Docker? CODESYS Forge talk (Post)
I had an issue aswell, I was trying to use docker and got stuck on the specific line ' Downloading https://download.microsoft.com/download/9/5/A/95A9616B-7A37-4AF6-BC36-D6EA96C8DAAE/dotNetFx40_Full_x86_x64.exe' within install2.sh - which is actually from the https://raw.githubusercontent.com/Winetricks/winetricks/master/src/winetricks, winetricks_selfupdate(). Would love to know if anyone has a known solution. Only other thing I can think is to download winetricks +.net, update the winetricks to point to the downloaded .net? Granted Im not too savy with Docker so I have been struggling on figuring that part out- would love any suggestions!
Last updated: 2024-05-19

Post by fpawlak on KNX SL on stock PFC200 firmware CODESYS Forge talk (Post)
Hi All. Is it possible to use CODESYS KNX SL on stock Wago firmware (Codesys version, not e!Cockpit). I have Wago 750-8212 with firmware 0.4.04.03(26). When I tried to run 'KNX SL' or even 'Device Reader', I have got [FATAL ERROR] Unresolved reference: 'CODEMGETCONTENTBYFIRMCODE3' [FATAL ERROR] Unresolved reference: 'CODEMGETCONTENTBYFIRMCODE2' [FATAL ERROR] Unresolved reference: 'CODEMGETCONTENTBYFIRMCODE2' What probbalby means that there is no running CodeMeter component on PLC. I have checked /etc/codesys3.d/CODESYSControl.cfg [CmpWebServer] WebServerPortNr=58080 [CmpSecureChannel] CertificateHash=86ccf31839a098ee32067179e26600f1bd6b36f8 [CmpUserMgr] AsymmetricAuthKey=a9d38381e75bbf1bbfc8749e97f536f68238a2ce So the question is if I can somehow add Codemeter to stock firmware? Or should I switched to CODDESYS Control for PFC200 SL or application-base runtime licence?
Last updated: 2024-05-23

Post by spice on WebVisu Recipe Save/Load CODESYS Forge talk (Post)
I'm currently reworking the controls on a cnc press brake and wanted to load various recipes as programs to run. I'm using a 2d array of REALs to store the X and Y coordinates as well as some other program parameters in a recipe. I'd like to store all of the recipes on a computer used as the HMI that way the text files can be edited and uploaded offline. I'm using Automation Directs P2CDS-622 Can this be done through webvisu? If not would a license for Codesys HMI SL on the computer allow me to accomplish this? I've attached the Project File Thanks, Spice
Last updated: 2024-05-31

Post by ragarcia on How to change login visualization for other visualization after user logged in CODESYS Forge talk (Post)
Hello everyone, I have a web visualization on Codesys and to be able to use the web visualization first an user and a password is requested. After the user logged in, I want to automatically change the visualization to the 'Home' visualization but I am not sure how to do this. In the login visualization I basically have a button with the input configuration to execute the action 'Login' after a click. Once the user is logged in, the visualization is still stuck in the login page and I want to automatically change to Home visualization if the user was succesfully logged in. How can I know the number of web visualization clients connected to my PLC? Thanks in advance
Last updated: 2024-06-04

Post by matt-purcell on Which Lib to use, connect to a socket with URL instead of IP address CODESYS Forge talk (Post)
Hello, I have a new project and I need to connect to a TCP socket using the URL instead of an explicit IP address, myendpoint@mydomain.com Which library is best suited for this? This is for a new enterprise project, the endpoint is a server in a datacenter running some real time application. We have big IP, it will automatically reassign the IP address to the backup server if a crash occurs so an explicit IP won't work for me. I've done this in RS logix, working now to migrate that code over to codesys. Thanks in advance!
Last updated: 2024-06-17

Post by hwopereis on How to use Application Trigger in Modbus TCP Server CODESYS Forge talk (Post)
Hi, I'm currently reading and writing several registers with a Modbus TCP server as a subdevice of a Modbus TCP Client. If I read and write cyclically, there are no issues. The problem is this: I see there is also the option to write by "Application", which I would like to use. However, I don't know With the Modbus RTU client, I see there is a trigger variable, xTrigger, to trigger the writing tasks. However, I can't find any such trigger for the Modbus TCP Client. Does anybody know how to implement the trigger behavior for the Modbus TCP client? In particular, I struggle to find the exact "trigger" variable. I'm running Modbus Client version 4.4.0.0 Thanks in advance!
Last updated: 2024-07-01

Post by dekelec on The current baud rate could not be determined in CR0020 IFM with maintenance tool CODESYS Forge talk (Post)
It could be a problem with the cable pinout on either side: 9 pin D-SUB connector (male) - PC side Pin Potential: 1 n.c. 2 RxD 3 TxD 4 n.c. 5 n.c. 6 GND 7 n.c. 8 n.c. 9 n.c. Shell Shield Check if TxD and RxD cross between pins 2 and 3 (what is the Recive signal/wire to one device it's a Transmit signal/wire for the othe device) or with COM port settings: Bits per second: 9600 Data bits: 8 Parity: None Stop bits: 1 Flow controll: None
Last updated: 2024-07-09

Post by hyys12 on How to use/create SOTU in LD program CODESYS Forge talk (Post)
I am trying to make a LD program for an existing installation with a motor. Here an inductive sensor is used to give an input, as a check to verify the conveyor is actually running. Here the plan was to use a TOF timer which gets constantly reset when the sensor input gets detected. The problem is, that if the conveyor is stuck, and the sensor sends a continous signal, the timer will never do what it is supposed to do. Therefor I need some help on how I can convert the input to a pulse, with the help of something like a SOTU. I just cannot find this in codesys anywhere.
Last updated: 2024-07-11

Post by pazderai on CanOpen write issue CODESYS Forge talk (Post)
Thank you for an answer. Unfortunatelly, it doesn't work. The slave needs command byte as follows 0x22. It means expedited transfer where s-bit is not set, therefore data length is not specified. If I use segmented mode by CiA405.SDO_WRITE_DATA it produce command byte as follows 0x21 which is unfortunately supported by the slave and it returns with error 0x05040001 - SDO Abort Code -Client/server command specifier not valid or unknown. I can use CAN API low level to overcome this problem where it is possible to set 0x22 as a command byte, but than I can use user interface to set the communication probably, because I thing that machine expert uses library CiA405.SDO_WRITE for setting the slave. Or am I wrong?
Last updated: 2024-07-16

Post by toffeebonbon on EL7041-0052 - does it run with EL7041 SoftMotion? CODESYS Forge talk (Post)
I let this project rest for a while and picked it up last week. I have been in contact with the support from beckhoff and got the information that the terminals were identical (communication wise). As the Log of the Axis (not the drive's log) shows the error when trying to write into the register 0x8012 and set the value for an encoder to a value that is the default - at least according to the manual - I was wondering if it is possible to "not write that value" to skip that part? Or am I misunderstanding the way the library communicates with the drive?
Last updated: 2024-07-24

Post by mubeta on Reset problem with CMZ SD/SVM drive CODESYS Forge talk (Post)
In a recent project with SoftMotion 4.15.0.0, where I integrated two SD drives from CMZ (from catalogue EDS and not imported), on CANopen bus, I found that the SoftMotion MC_Reset function does not reset the drive faults. Even if the drive is in fault, either on the device or on the drive at the CoDeSys level, the function does not reset, instead reporting the error code: no error to reset. Finally, I had to connect the reset bit of the ControlWord directly to a tag in my program. Something I never had to do on other drives: Lexium, etc. all reset simply with MC_Reset.
Last updated: 2024-07-24

Post by sangeetnenwani on Test Driver Availability in CODESYS 64-bit and Test Manager 5.1.0.0 CODESYS Forge talk (Post)
I’m operating with CODESYS in a 64-bit configuration and the Test Manager at version 5.1.0.0, where I’m attempting to use project scripts from an earlier version. These scripts call for certain test drivers that are not present in my installation. It’s unclear whether the absence is due to the 64-bit system, an update in the test drivers, or if I need to enable or install additional elements. For instance, the loadproject(Codesys.Base) command is missing, but loadproject(testmanager.project) is available. The FileIO command for CODESYS isn’t accessible, yet the testmanager’s driver for it exists, as does the execuptscript command.
Last updated: 2024-08-06

Post by sangeetnenwani on Test Driver Availability in CODESYS 64-bit and Test Manager 5.1.0.0 CODESYS Forge talk (Post)
I’m operating with CODESYS in a 64-bit configuration and the Test Manager at version 5.1.0.0, where I’m attempting to use project scripts from an earlier version. These scripts call for certain test drivers that are not present in my installation. It’s unclear whether the absence is due to the 64-bit system, an update in the test drivers, or if I need to enable or install additional elements. For instance, the loadproject(Codesys.Base) command is missing, but loadproject(testmanager.project) is available. The FileIO command for CODESYS isn’t accessible, yet the testmanager’s driver for it exists, as does the execuptscript command.
Last updated: 2024-08-06

Post by trusty-squire on parker servo and position CODESYS Forge talk (Post)
@gepert, When you say "I do not turn off power", are you saying you don't power off the drive, or you don't turn of the MC_POWER function block? I read your statement as you don't kill actual electrical power. MC_POWER should stay enabled. @Gustavo, not related to problem at all, but when you say 1.6 Nm is only enough torque to unscrew a loose bottle cap, I think that's a bit low. A quick mental math I use is 1 Nm is almost the same force as 1kG applied to a 10cm wrench. So 1.6kG applied to a 10cm wrench is still not a huge force, but more than enough to be felt if trying to turn the shaft by hand.