Post by docker on Webvisu client connection monitoring
CODESYS Forge
talk
(Post)
Hi mate, With this snippet i was able to see the lastusage variable count, but it would not iterate between clients? i was only able to access the data of the target visu. it threw an error with the array of pointers stating it was not able to convert etc. also when i tried it with the while loop it created an endless loop and crashed the program. any ideas? Thankyou
Last updated: 2024-09-10
Post by spilin on All devices lost for all installed version
CODESYS Forge
talk
(Post)
hello. After installing the latest version of codesys (3.5.20) from codesys installer, I had a problem. All my devices disappeared. Both PLCs and IO modules and network devices disappeared from my list. I browsed through the Windows files and I can find them in the programdata/codesys/devices folder. The files remain there, but they are not available within codesys (same error in all installed versions) which in this case are 3.5.16 and 3.5.19. Does anyone know how I can reimport or resynchronize my devices folder again? Thanks
Last updated: 2024-09-11
Post by thn-power on Updating OPC UA Core Nodeset on PLS
CODESYS Forge
talk
(Post)
Hi After much trail and error I think I found the root cause to my OPC UA problem. The problem is that I cannot manage to build and download a program with a a custom OPC UA Information model. We use a Weidmueller WL2000 PLS, but the problem also exsist on the Win V3 PLC. Our custom information model is based on the latest versions of the OPC UA Core Nodeset v 1.05.03 (2023-09-20) and UA/DI nodeset 1.04.0 (2022-11-03) Those nodesets are installed in the Codesys Information Model Repository (3.5.19.6) However, when trying to build I get the following error. [ERROR] Untitled1: Communication Manager [Device: PLC Logic: Application]: The information model http://opcfoundation.org/UA/ is required by http://bos.org/ with a minimal publication date from 15.12.2023 but the device has only a model from 15.09.2021 installed. Probably the information model from 15.09.2021 is missing in the information model repository. [ERROR] Untitled1: Communication Manager [Device: PLC Logic: Application]: The information model http://opcfoundation.org/UA/DI/ is required by http://bos.org/ with a minimal publication date from 03.11.2022 but the device has only a model from 09.03.2021 installed. Probably the information model from 09.03.2021 is missing in the information model repository. Build complete -- 2 errors, 1 warnings : No download possible I think the problem is that the UA Core nodeset is implemented in the PLC firmware (at least that in Siemens S7), and that only includes the "old" nodeset from 2021-09-21 etc. So the question is, how (or if?) can I transfer the new nodeset to the PLS? I have created separate Information models under Communication manager with the newer code nodesets (UA and DI). But it seems that the compiler does not recognize them being excising, neither in the Codesys IDE or on the PLC. Would have guessed that this is a common issue, sine many manufacturers use the latest versions of the OPC UA standard, and that it would be a solution to the problem.
Last updated: 2024-09-20
Post by paulpotat on Can't open license manager with raspberry CM4
CODESYS Forge
talk
(Post)
Hello, I have a problem when opening the license manager for my raspberry pi (CM4 model) with runtime 4.13.0.0. I select "Device" --> "Soft Container" and click on my device in the scan window but I get this error message : Licensing info not available. There is no dongle attached to this device. I can't install licenses anymore, and I don't understand why is CodeSys looking for a dongle when I specified I wanted to use a Soft Container. Can somebody help me please ? Best regards
Last updated: 2024-10-04
Post by jwhaley on C0007 Errors
CODESYS Forge
talk
(Post)
I ended up figuring it out It wasn't in my code. It kept taking me to 2 of my visualizations but it wasn't going to anything specific. Figured out it was some arrows that I had made to buttons for a mouse click to go to the other visualizations. I removed the text in the assign box but didn't remove the action "change shown Visualization from the list. If I deleted the images all together, the error went away. That's how I thought to go look at that.
Last updated: 2024-10-10
Post by xabier on Problem Update new version Master ethercat
CODESYS Forge
talk
(Post)
Hi, I have a project in Codesys...and i need update a new version of amster ehtercat and i have a problem. The origianl version with create of project was 3.5.13.10 I can change version to Master Ethercat 3.5.13.10 to 3.5.16.70 but i can´t update the last version 4.4.0.0 (I attached the screen "Version Master OK-NO OK"). In the moment update to the last version appear a lot of error("Version Master NO OK") Can anyone help me please?
Last updated: 2024-10-25
Post by ben1 on How to write multiple coils (Modbus FC15)
CODESYS Forge
talk
(Post)
When you say it does not work, does nothing happen or do you get an error? I have not used this function in codesys but from my past experience with Modbus I believe the coils need to be contiguous, which may be why yours is failing? Have you tried using Write Registers (16) to do the job? Or is their data in-between you do not want to edit in the transaction?
Last updated: 3 hours ago
Post by toffeebonbon on EL7041-0052 - does it run with EL7041 SoftMotion?
CODESYS Forge
talk
(Post)
Good morning everyone. In my setup I am trying to use a couple of EL7041-0052 (the EL7041 variant without terminals for an encoder) to run stepper motors without feedback. When using the softmotion drivers for the EL7041 (Rev22 and Rev24, even selecting external feedback type doesn't work) the device log shows warnings for the corresponding hardware: "SDO write error 0x1 -> 0x8012:0x08 eError 0x1 AbortCode 0x6090011". 0x8012:0x08 is the register for the Feedback Type. My best guess was setting the the register value in the start parameters to zero, but the result is the same. What else can I try to get the hardware to work? I have screenshots attatched showing the running fieldbus and the log messages. EDIT: One clarification: the "device log" that shows the error is the PLC, not the ethercat terminal. The log of the terminal itself shows neither errors nor warnings. BR Robert
Last updated: 2023-11-29
Post by ragarcia on Error while using UpdateConfiguredIPSettings to change IP address
CODESYS Forge
talk
(Post)
Hello everyone, I am trying to change dynamically by code the IP address of a Weidmuller controller. So I am basically using IoDrvEthernet library to use UpdateConfiguredIPSettings function but I am getting constantly the 'INVALID_STATE' error. Even though I am following a procedure it should work: * First I added on the config file of codesys the following: [SysSocket] Adapter.0.Name="eth0" Adapter.0.EnableSetIpAndMask=1 Adapter.1.Name="eth1" Adapter.1.EnableSetIpAndMask=1 * Secondly I am first disabling the ethernet interface by using Ethernet_0.Enable = FALSE and then executing DED.Reconfigure. After that, I run the Ethernet_1.updateConfiguredIPSettings Code: Ethernet_1.Enable:= EnableDisable; Reconfigure(xExecute:= TRUE, itfNode:= Ethernet_1, xError=> ErrorReconfigure, eError=> ErrorCodeReconfigure); IF Reconfigure.xDone THEN ErrorCodeIP:= Ethernet_1.UpdateConfiguredIPSettings(IPAddress:= newIP, SubnetMask:= newMask, Gateway:= newGW); END_IF IF Reconfigure.xDone OR Reconfigure.xError THEN Reconfigure(xExecute:= FALSE); END_IF Ethernet_1.Enable:= TRUE; Reconfigure(xExecute:= TRUE, itfNode:= Ethernet_1); IF Reconfigure.xDone OR Reconfigure.xError THEN Reconfigure(xExecute:= FALSE); END_IF Can someone help me? Thank you. All I am trying is to find a way to change dynamically with code, the IP addresses of my controller (2 ethernet ports).
Last updated: 2023-12-11
Post by chalk on No source code available
CODESYS Forge
talk
(Post)
Hello, This is my first time using Codesys, I am trying to add EtherNetIP communication to a Raspberry PI. I’ve added the EtherNetIP Adapter configured the network setting and added some modules to the pi but when I download the project it generates the following error: “There is no source code available for the object because it is in the compiled library ‘cip object, 4.5.1.0 (3s – smart software solution gmbh)’. Do you want to browse for the original library in order to display the source code? There are 2 errors in the log which are: SOURCEPOSITION App=[Application] area=3, offset=332760 EXCEPTION [Application] occurred: App=[Application], Task=[ENIPAdapterServiceTask] I can’t for the life of me work out how to get around this. I can’t find the source code anywhere or any information regarding this error. I’m using Codesys V3.5 SP19 Patch 3, the version of the Ethernet adapter is 4.5.1.0 and the version of the modules is 4.1.0.0. Any help on this will be greatly appreciated. Thanks
Last updated: 2024-02-02
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by anlebr on Codesys Communication Manger - Required information model version exists in the model repository but is not found
CODESYS Forge
talk
(Post)
Hi I am trying use the Codesys Communication Manager to set up an Opc ua server with a custom information model. As a start I am using the Boiler model available on Opc foundations github page. I am testing with a Wago CC100 and using Codesys V3.5 SP19 Patch 6. I get the following error: Communication Manager [Device: PLC Logic: Application]: The information model http://opcfoundation.org/UA/ is required by http://opcfoundation.org/UA/Boiler/ with a minimal publication date from 15/12/2023 but the device has only a model from 15/09/2021 installed. Probably the information model from 15/09/2021 is missing in the information model repository. The error message does not make sense to me. Should it not be “Probably the information model from 15/12/2023 is missing in the information model repository”? Anyway, both versions are available in the repository. How can I solve this?
Last updated: 2024-03-13
Post by rmaas on Fieldbus has lost synchronicity
CODESYS Forge
talk
(Post)
Hi, On a gantry system with 2 axis i am getting the following error: SMC_DI_FIELDBUS_LOST_SYNCRONICITY This happens random, sometimes it happens every 5 minutes and sometimes no error for 2 hours... The Setup: - Using codesys 3.5 SP20 with all latest libs... - Kontron AL Pi-Tron CM4 with Preempt realtime patch (Raspberry Pi 4) - Codesys runtime 4.11.0.0 (single core) - CODESYS Control for Raspberry Pi SL licensed - Softmotion + CNC + Robotics licensed - 2x Leadshine EL8-EC400 servo drives - Axis group for a 2-axis T-Gantry Ethercat network wiring: Ethercat master softmotion -> Beckhoff EK1100 -> Servo drive #1 -> Servo drive #2 Ethercat Cycle time = 4ms Max Jitter = 140~150 What i have tried so far: - changed the sync offset from 20% to 30% - changed ethercat task priority from 1 to 0 Running tasks: - Ethercat tast: Prio = 0, Interval = 4ms - Main task: Prio = 1, Interval = 8ms - Visu task: Prio = 31, Interval = 100ms - Softmotion planning task: Prio = 15, Freewheeling - 3 other default tasks that were created by AC_Persist Motion fb's are called in the ethercat task... Does anyone have an idea how to fix this? Any help is greatly appreciated!
Last updated: 2024-04-11
Post by ahuckphin on Issues with Modbus Slave with Raspberry Pi
CODESYS Forge
talk
(Post)
I have a DFRobot RS485 temperature & humidity sensor (SEN0438) connected to my Raspberry Pi via a USB to RS485 adapter. I am able to connect and read the sensor data when running a python code locally. However in Codesys, I encounter this error "A bus error has occurred." and "There was no response in time". Could this be because of Modbus Server Channel and Modbus Server Init configuration on my part? Admittedly I am new to Codesys. To get to this stage, I: 1. added some lines to CODESYSControl_User.cfg 2. added "Modbus_COM" in Codesys and set "Serial Port Configuration" under "General" 3. added "Modbus_Master_COM_Port" in Codesys and checked transmission mode is set to "RTU" 4. added "Modbus_Slave_COM_Port" in Codesys and checked server address is set to 1 (also set 1 in my sensor) 5. added 1 channel and 1 init for "Modbus_Slave_COM_Port" under "Modbus Server Channel" and "Modbus Server Init"
Last updated: 2024-07-10
Post by trusty-squire on CNC - How to manipulate SMC_GeoInfo objects
CODESYS Forge
talk
(Post)
I have an application using CNC GCode interpolation, but I need to modify the GCode provided to the PLC based on certain parameters. I am currently attempting to modify the SMC_GeoInfo objects in the SMC_OutQueue using the code below. Note that all the other code is pretty standard and works fine, but when I add the below it errors. PROGRAM TEST VAR fbReadCncFile : SMC_ReadNCFile2; fbCncInterpreter : SMC_NCInterpreter; arrCncInterpreter : ARRAY[1..99] OF SMC_GeoInfo; pGeoInfo: POINTER TO SMC_GeoInfo; giGeoInfo: SMC_GeoInfo; // ... END_VAR // ... Some code here in order to read CNC file using SMC_ReadNCFile2 and provide to SMC_NCInterpreter pGeoInfo := SMC_GetObj(poq:=ADR(fbCncInterpreter.poqDataOut), n:=1); IF pGeoInfo <> 0 THEN giGeoInfo := pGeoInfo^; // Do some manipulation here, then update the queue at the same position MC_SetObj(poq:=ADR(fbCncInterpreter.poqDataOut) , n:=0 , pgi:=ADR(giGeoInfo) ); END_IF It throws an error when I get to the line giGeoInfo := pGeoInfo^; Error: EXCEPTION [AccessViolation] occured: App=[Sim.Device.Application], Task=[PathTask] How do I use SMC_GetObj and access the data? It creates a pointer with the value as shown in the photo, but all the dereferenced values say dereference of invalid pointer.
Last updated: 2024-07-26
Post by ricola on ERROR: CodeMAccess2: Used CmRuntime 2.61.2705.500 is too old
CODESYS Forge
talk
(Post)
hi there , can someone tell me how to deal with this error , please? I use the Linux ARM64SL (4.11) on a bullseye distro and when I want to update or install some package, I have the following reply : pi@NanoPi-R5C:~$ sudo apt upgrade Reading package lists... Done Building dependency tree... Done Reading state information... Done You might want to run 'apt --fix-broken install' to correct these. The following packages have unmet dependencies: ** codesyscontrol : Depends: codemeter but it is not installable or codemeter-lite but it is not installable** E: Unmet dependencies. Try 'apt --fix-broken install' with no packages (or specify a solution). and if I try apt --fix-broken install as suggested, I have a proposal to uninstall codesyscontrol ... :-D so I tried to search if there is some Codesys repo: nothing, then I tried to see if ther was something inside Codesys dev (V3.5.20) and I only found that by reading/requesting my device, i spoted that codemeter was too old . I don't see how to deal with this issue. is there a codemeter.deb somewhere ? thanks in advance for any help.
Last updated: 2024-09-17
Post by egau on Hard shutdown: no code on device after power on
CODESYS Forge
talk
(Post)
This explanation aligns with the issues we’re experiencing with our machines. The scenario I described is happening with one of them (let’s call it Machine A). This machine is identical to another one (Machine B), except for some custom code that facilitates communication with an external Beckhoff PLC for MES integration in the production line. Machine B has been powered on and off daily for at least three months and has never had this problem. Given that, I highly doubt the MES custom code is the cause of the code corruption. This being said, your explanation does seem plausible. However, if faulty EtherCAT cables were the issue, why wouldn't the error occur during normal operation? Why would bad cables only cause problems during a hard shutdown? One last question: When you encountered this behavior, did you see a similar error in your logs? i.e, an "AccessViolation" exception in the EtherCAT Task?
Last updated: 2024-10-03
Post by spiessli on Raspberry Pi 4 with Legacy Drivers and Codesys 3.5.19 Patch 4
CODESYS Forge
talk
(Post)
Thanks for the suggestion, I have tried it eagerly: I have updated all packages to latest version with Codesys Installer and installed newest runtime and gateway on Raspberry Pi. Unfortunately, the error is still there. As soon as I add the SM_Drive_Servo to the device tree, I get the error below when generating the code. Reverting SM3_Basic to version 4.14 makes the error disappear. ------ Übersetzungslauf gestartet: Applikation: Device.Application ------- Code typisieren... Code erzeugen... [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0032: Typ 'Unbekannter Typ: 'ConfigGetParameterValueLREAL(pParam, 0)'' kann nicht in Typ 'LREAL' konvertiert werden [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0046: Bezeichner 'ConfigGetParameterValueLREAL' nicht definiert [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0035: Programmname, Funktion oder Funktionsbausteinstanz an Stelle von 'ConfigGetParameterValueLREAL' erwartet [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0032: Typ 'Unbekannter Typ: 'ConfigGetParameterValueLREAL(pParam, 0)'' kann nicht in Typ 'LREAL' konvertiert werden [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0046: Bezeichner 'ConfigGetParameterValueLREAL' nicht definiert [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0035: Programmname, Funktion oder Funktionsbausteinstanz an Stelle von 'ConfigGetParameterValueLREAL' erwartet [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0032: Typ 'Unbekannter Typ: 'ConfigGetParameterValueLREAL(pParam, 0)'' kann nicht in Typ 'LREAL' konvertiert werden [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0046: Bezeichner 'ConfigGetParameterValueLREAL' nicht definiert [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0035: Programmname, Funktion oder Funktionsbausteinstanz an Stelle von 'ConfigGetParameterValueLREAL' erwartet [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0032: Typ 'Unbekannter Typ: 'ConfigGetParameterValueLREAL(pParam, 0)'' kann nicht in Typ 'LREAL' konvertiert werden [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0046: Bezeichner 'ConfigGetParameterValueLREAL' nicht definiert [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0035: Programmname, Funktion oder Funktionsbausteinstanz an Stelle von 'ConfigGetParameterValueLREAL' erwartet [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0032: Typ 'Unbekannter Typ: 'ConfigGetParameterValueLREAL(pParam, 0)'' kann nicht in Typ 'LREAL' konvertiert werden [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0046: Bezeichner 'ConfigGetParameterValueLREAL' nicht definiert [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0035: Programmname, Funktion oder Funktionsbausteinstanz an Stelle von 'ConfigGetParameterValueLREAL' erwartet Übersetzung abgeschlossen -- 15 Fehler, 0 Warnungen : Kein Download möglich
Last updated: 2023-12-20
Post by mozed on Connection to device closed
CODESYS Forge
talk
(Post)
Hello I am using an OpusA3 with version 3.5 SP17 Patch 3 as part of a project. I had no real problem before I encountered a problem that blocked me. The detection of the OpusA3 from Codesys is done correctly. The gateway is well configured and if I ping the gateway or the OpusA3 I receive the response correctly. The problem is that when I try to connect, the Opus screen freezes and a few moments later Codesys displays an error message ("connection to device closed"). I tried to change PC, to update the runtime, to change OpusA3 but the problem remains the same. I'm a little lost knowing that before it worked without problem. I went back to a previous version of the project (where it worked correctly) but the message still appears. Do you have any clues to solve the problem? Sincerely,
Last updated: 2023-08-23
Post by tvm on Web Client (HMI) Disconnects from Webvisu (Weidmuller u-OS)
CODESYS Forge
talk
(Post)
ok, that's different than our issue then. We're using Schneider Electric M262 PLCs, and we've had it where certain web browsers cause the web server to only allow https connections, but it's not recoverable with a refresh. It usually requires a power cycle or even a full firmware flash. Your issue might have more to do with the timing. I don't know if it helps you, but we normally run our visu task at 200mS, with an update rate of 200mS. Seems to work. I went through this: https://faq.codesys.com/pages/viewpage.action?pageId=112525371 but it really seems like trial and error.
Last updated: 2023-09-06
Post by derpaul on PFC200 Update to 4.9.0.0 - No Connection
CODESYS Forge
talk
(Post)
Hallo Today I decided to perform an Update on my PFC200 but after the Update the Device was not reachable anymore. I tried reseting to factory reset. Software reset and so on, but nothing helps... In my Router I can see it, I cann SSH into the PFC200 but it is not reachable. Then I try to go back to 4.8.0.0 But now I get this error: [INFORMATION] Befehl SSH auf root@192.168.1.17 ausführen: Laufzeitsystem stoppen [FEHLER] Fehlerausgabe: /etc/init.d/codesyscontrol: line 34: /opt/codesys/scripts/init-functions: No such file or directory [INFORMATION] Standardausgabe: /etc/init.d/codesyscontrol: line 34: /opt/codesys/scripts/init-functions: No such file or directory Please help, I can't get this thing working... Regards
Last updated: 2023-09-27
Post by derpaul on PFC200 Update to 4.9.0.0 - No Connection
CODESYS Forge
talk
(Post)
Hallo Today I decided to perform an Update on my PFC200 but after the Update the Device was not reachable anymore. I tried reseting to factory reset. Software reset and so on, but nothing helps... In my Router I can see it, I cann SSH into the PFC200 but it is not reachable. Then I try to go back to 4.8.0.0 But now I get this error: [INFORMATION] Befehl SSH auf root@192.168.1.17 ausführen: Laufzeitsystem stoppen [FEHLER] Fehlerausgabe: /etc/init.d/codesyscontrol: line 34: /opt/codesys/scripts/init-functions: No such file or directory [INFORMATION] Standardausgabe: /etc/init.d/codesyscontrol: line 34: /opt/codesys/scripts/init-functions: No such file or directory Please help, I can't get this thing working... Regards
Last updated: 2023-09-27