Post by chalk on No source code available
CODESYS Forge
talk
(Post)
Hello, This is my first time using Codesys, I am trying to add EtherNetIP communication to a Raspberry PI. I’ve added the EtherNetIP Adapter configured the network setting and added some modules to the pi but when I download the project it generates the following error: “There is no source code available for the object because it is in the compiled library ‘cip object, 4.5.1.0 (3s – smart software solution gmbh)’. Do you want to browse for the original library in order to display the source code? There are 2 errors in the log which are: SOURCEPOSITION App=[Application] area=3, offset=332760 EXCEPTION [Application] occurred: App=[Application], Task=[ENIPAdapterServiceTask] I can’t for the life of me work out how to get around this. I can’t find the source code anywhere or any information regarding this error. I’m using Codesys V3.5 SP19 Patch 3, the version of the Ethernet adapter is 4.5.1.0 and the version of the modules is 4.1.0.0. Any help on this will be greatly appreciated. Thanks
Last updated: 2024-02-02
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by tim-roelant on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
I have set up a brandnew Beckhoff panel pc with a codesys control runtime V3. I configured it together with 2 profinet field devices: a 16in/16out IO module from Turck and an MTS linear encoder. The machine works fine untill all of a sudden the communication breaks and the profinet participants become unreachable. At that point I can still ping the device, but the profinet master does not find them anymore: When i do a scan they are not found. When i do a cold restart, the profinet master becomes active again and the devices are found again. In the log i get Ethercat packet receive error: sysethernet. I am a little confused, there is no ethercat device in the device tree. I already set the send clock and the reduction ratio to higher values, but without result. Can codesys be configured, so that the communication re-establishes without doing the cold reset? This is very annoying and is causing a lot of prodution losses. regards Tim
Last updated: 2024-02-27
Post by anlebr on Codesys Communication Manger - Required information model version exists in the model repository but is not found
CODESYS Forge
talk
(Post)
Hi I am trying use the Codesys Communication Manager to set up an Opc ua server with a custom information model. As a start I am using the Boiler model available on Opc foundations github page. I am testing with a Wago CC100 and using Codesys V3.5 SP19 Patch 6. I get the following error: Communication Manager [Device: PLC Logic: Application]: The information model http://opcfoundation.org/UA/ is required by http://opcfoundation.org/UA/Boiler/ with a minimal publication date from 15/12/2023 but the device has only a model from 15/09/2021 installed. Probably the information model from 15/09/2021 is missing in the information model repository. The error message does not make sense to me. Should it not be “Probably the information model from 15/12/2023 is missing in the information model repository”? Anyway, both versions are available in the repository. How can I solve this?
Last updated: 2024-03-13
Post by rmaas on Fieldbus has lost synchronicity
CODESYS Forge
talk
(Post)
Hi, On a gantry system with 2 axis i am getting the following error: SMC_DI_FIELDBUS_LOST_SYNCRONICITY This happens random, sometimes it happens every 5 minutes and sometimes no error for 2 hours... The Setup: - Using codesys 3.5 SP20 with all latest libs... - Kontron AL Pi-Tron CM4 with Preempt realtime patch (Raspberry Pi 4) - Codesys runtime 4.11.0.0 (single core) - CODESYS Control for Raspberry Pi SL licensed - Softmotion + CNC + Robotics licensed - 2x Leadshine EL8-EC400 servo drives - Axis group for a 2-axis T-Gantry Ethercat network wiring: Ethercat master softmotion -> Beckhoff EK1100 -> Servo drive #1 -> Servo drive #2 Ethercat Cycle time = 4ms Max Jitter = 140~150 What i have tried so far: - changed the sync offset from 20% to 30% - changed ethercat task priority from 1 to 0 Running tasks: - Ethercat tast: Prio = 0, Interval = 4ms - Main task: Prio = 1, Interval = 8ms - Visu task: Prio = 31, Interval = 100ms - Softmotion planning task: Prio = 15, Freewheeling - 3 other default tasks that were created by AC_Persist Motion fb's are called in the ethercat task... Does anyone have an idea how to fix this? Any help is greatly appreciated!
Last updated: 2024-04-11
Post by ahuckphin on Issues with Modbus Slave with Raspberry Pi
CODESYS Forge
talk
(Post)
I have a DFRobot RS485 temperature & humidity sensor (SEN0438) connected to my Raspberry Pi via a USB to RS485 adapter. I am able to connect and read the sensor data when running a python code locally. However in Codesys, I encounter this error "A bus error has occurred." and "There was no response in time". Could this be because of Modbus Server Channel and Modbus Server Init configuration on my part? Admittedly I am new to Codesys. To get to this stage, I: 1. added some lines to CODESYSControl_User.cfg 2. added "Modbus_COM" in Codesys and set "Serial Port Configuration" under "General" 3. added "Modbus_Master_COM_Port" in Codesys and checked transmission mode is set to "RTU" 4. added "Modbus_Slave_COM_Port" in Codesys and checked server address is set to 1 (also set 1 in my sensor) 5. added 1 channel and 1 init for "Modbus_Slave_COM_Port" under "Modbus Server Channel" and "Modbus Server Init"
Last updated: 2024-07-10
Post by trusty-squire on CNC - How to manipulate SMC_GeoInfo objects
CODESYS Forge
talk
(Post)
I have an application using CNC GCode interpolation, but I need to modify the GCode provided to the PLC based on certain parameters. I am currently attempting to modify the SMC_GeoInfo objects in the SMC_OutQueue using the code below. Note that all the other code is pretty standard and works fine, but when I add the below it errors. PROGRAM TEST VAR fbReadCncFile : SMC_ReadNCFile2; fbCncInterpreter : SMC_NCInterpreter; arrCncInterpreter : ARRAY[1..99] OF SMC_GeoInfo; pGeoInfo: POINTER TO SMC_GeoInfo; giGeoInfo: SMC_GeoInfo; // ... END_VAR // ... Some code here in order to read CNC file using SMC_ReadNCFile2 and provide to SMC_NCInterpreter pGeoInfo := SMC_GetObj(poq:=ADR(fbCncInterpreter.poqDataOut), n:=1); IF pGeoInfo <> 0 THEN giGeoInfo := pGeoInfo^; // Do some manipulation here, then update the queue at the same position MC_SetObj(poq:=ADR(fbCncInterpreter.poqDataOut) , n:=0 , pgi:=ADR(giGeoInfo) ); END_IF It throws an error when I get to the line giGeoInfo := pGeoInfo^; Error: EXCEPTION [AccessViolation] occured: App=[Sim.Device.Application], Task=[PathTask] How do I use SMC_GetObj and access the data? It creates a pointer with the value as shown in the photo, but all the dereferenced values say dereference of invalid pointer.
Last updated: 2024-07-26
Post by ricola on ERROR: CodeMAccess2: Used CmRuntime 2.61.2705.500 is too old
CODESYS Forge
talk
(Post)
hi there , can someone tell me how to deal with this error , please? I use the Linux ARM64SL (4.11) on a bullseye distro and when I want to update or install some package, I have the following reply : pi@NanoPi-R5C:~$ sudo apt upgrade Reading package lists... Done Building dependency tree... Done Reading state information... Done You might want to run 'apt --fix-broken install' to correct these. The following packages have unmet dependencies: ** codesyscontrol : Depends: codemeter but it is not installable or codemeter-lite but it is not installable** E: Unmet dependencies. Try 'apt --fix-broken install' with no packages (or specify a solution). and if I try apt --fix-broken install as suggested, I have a proposal to uninstall codesyscontrol ... :-D so I tried to search if there is some Codesys repo: nothing, then I tried to see if ther was something inside Codesys dev (V3.5.20) and I only found that by reading/requesting my device, i spoted that codemeter was too old . I don't see how to deal with this issue. is there a codemeter.deb somewhere ? thanks in advance for any help.
Last updated: 2024-09-17
Post by egau on Hard shutdown: no code on device after power on
CODESYS Forge
talk
(Post)
This explanation aligns with the issues we’re experiencing with our machines. The scenario I described is happening with one of them (let’s call it Machine A). This machine is identical to another one (Machine B), except for some custom code that facilitates communication with an external Beckhoff PLC for MES integration in the production line. Machine B has been powered on and off daily for at least three months and has never had this problem. Given that, I highly doubt the MES custom code is the cause of the code corruption. This being said, your explanation does seem plausible. However, if faulty EtherCAT cables were the issue, why wouldn't the error occur during normal operation? Why would bad cables only cause problems during a hard shutdown? One last question: When you encountered this behavior, did you see a similar error in your logs? i.e, an "AccessViolation" exception in the EtherCAT Task?
Last updated: 2024-10-03
Post by spiessli on Raspberry Pi 4 with Legacy Drivers and Codesys 3.5.19 Patch 4
CODESYS Forge
talk
(Post)
Thanks for the suggestion, I have tried it eagerly: I have updated all packages to latest version with Codesys Installer and installed newest runtime and gateway on Raspberry Pi. Unfortunately, the error is still there. As soon as I add the SM_Drive_Servo to the device tree, I get the error below when generating the code. Reverting SM3_Basic to version 4.14 makes the error disappear. ------ Übersetzungslauf gestartet: Applikation: Device.Application ------- Code typisieren... Code erzeugen... [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0032: Typ 'Unbekannter Typ: 'ConfigGetParameterValueLREAL(pParam, 0)'' kann nicht in Typ 'LREAL' konvertiert werden [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0046: Bezeichner 'ConfigGetParameterValueLREAL' nicht definiert [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0035: Programmname, Funktion oder Funktionsbausteinstanz an Stelle von 'ConfigGetParameterValueLREAL' erwartet [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0032: Typ 'Unbekannter Typ: 'ConfigGetParameterValueLREAL(pParam, 0)'' kann nicht in Typ 'LREAL' konvertiert werden [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0046: Bezeichner 'ConfigGetParameterValueLREAL' nicht definiert [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0035: Programmname, Funktion oder Funktionsbausteinstanz an Stelle von 'ConfigGetParameterValueLREAL' erwartet [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0032: Typ 'Unbekannter Typ: 'ConfigGetParameterValueLREAL(pParam, 0)'' kann nicht in Typ 'LREAL' konvertiert werden [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0046: Bezeichner 'ConfigGetParameterValueLREAL' nicht definiert [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0035: Programmname, Funktion oder Funktionsbausteinstanz an Stelle von 'ConfigGetParameterValueLREAL' erwartet [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0032: Typ 'Unbekannter Typ: 'ConfigGetParameterValueLREAL(pParam, 0)'' kann nicht in Typ 'LREAL' konvertiert werden [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0046: Bezeichner 'ConfigGetParameterValueLREAL' nicht definiert [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0035: Programmname, Funktion oder Funktionsbausteinstanz an Stelle von 'ConfigGetParameterValueLREAL' erwartet [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0032: Typ 'Unbekannter Typ: 'ConfigGetParameterValueLREAL(pParam, 0)'' kann nicht in Typ 'LREAL' konvertiert werden [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0046: Bezeichner 'ConfigGetParameterValueLREAL' nicht definiert [FEHLER] sm3_drive_servo, 4.10.0.0 (codesys): GetStandardConfigParams [AXIS_REF_SERVO]: C0035: Programmname, Funktion oder Funktionsbausteinstanz an Stelle von 'ConfigGetParameterValueLREAL' erwartet Übersetzung abgeschlossen -- 15 Fehler, 0 Warnungen : Kein Download möglich
Last updated: 2023-12-20
Post by mozed on Connection to device closed
CODESYS Forge
talk
(Post)
Hello I am using an OpusA3 with version 3.5 SP17 Patch 3 as part of a project. I had no real problem before I encountered a problem that blocked me. The detection of the OpusA3 from Codesys is done correctly. The gateway is well configured and if I ping the gateway or the OpusA3 I receive the response correctly. The problem is that when I try to connect, the Opus screen freezes and a few moments later Codesys displays an error message ("connection to device closed"). I tried to change PC, to update the runtime, to change OpusA3 but the problem remains the same. I'm a little lost knowing that before it worked without problem. I went back to a previous version of the project (where it worked correctly) but the message still appears. Do you have any clues to solve the problem? Sincerely,
Last updated: 2023-08-23
Post by tvm on Web Client (HMI) Disconnects from Webvisu (Weidmuller u-OS)
CODESYS Forge
talk
(Post)
ok, that's different than our issue then. We're using Schneider Electric M262 PLCs, and we've had it where certain web browsers cause the web server to only allow https connections, but it's not recoverable with a refresh. It usually requires a power cycle or even a full firmware flash. Your issue might have more to do with the timing. I don't know if it helps you, but we normally run our visu task at 200mS, with an update rate of 200mS. Seems to work. I went through this: https://faq.codesys.com/pages/viewpage.action?pageId=112525371 but it really seems like trial and error.
Last updated: 2023-09-06
Post by derpaul on PFC200 Update to 4.9.0.0 - No Connection
CODESYS Forge
talk
(Post)
Hallo Today I decided to perform an Update on my PFC200 but after the Update the Device was not reachable anymore. I tried reseting to factory reset. Software reset and so on, but nothing helps... In my Router I can see it, I cann SSH into the PFC200 but it is not reachable. Then I try to go back to 4.8.0.0 But now I get this error: [INFORMATION] Befehl SSH auf root@192.168.1.17 ausführen: Laufzeitsystem stoppen [FEHLER] Fehlerausgabe: /etc/init.d/codesyscontrol: line 34: /opt/codesys/scripts/init-functions: No such file or directory [INFORMATION] Standardausgabe: /etc/init.d/codesyscontrol: line 34: /opt/codesys/scripts/init-functions: No such file or directory Please help, I can't get this thing working... Regards
Last updated: 2023-09-27
Post by derpaul on PFC200 Update to 4.9.0.0 - No Connection
CODESYS Forge
talk
(Post)
Hallo Today I decided to perform an Update on my PFC200 but after the Update the Device was not reachable anymore. I tried reseting to factory reset. Software reset and so on, but nothing helps... In my Router I can see it, I cann SSH into the PFC200 but it is not reachable. Then I try to go back to 4.8.0.0 But now I get this error: [INFORMATION] Befehl SSH auf root@192.168.1.17 ausführen: Laufzeitsystem stoppen [FEHLER] Fehlerausgabe: /etc/init.d/codesyscontrol: line 34: /opt/codesys/scripts/init-functions: No such file or directory [INFORMATION] Standardausgabe: /etc/init.d/codesyscontrol: line 34: /opt/codesys/scripts/init-functions: No such file or directory Please help, I can't get this thing working... Regards
Last updated: 2023-09-27
Post by ofey on Modbus TCP communication
CODESYS Forge
talk
(Post)
Hi! I tried setting up the PLC I'm working with (Beijer GN-9373) to connect to a modbus master running on a laptop. I have an ethernet connection (via USB-C to ethernet) between the laptop and the controller. I have tried following tutorial on how to set this up. I have added an ethernet device with the IP-address of the PLC. Further I added a ModbusTCP_Slave_Device with default settings. I get the error "Failed to open TCP Port: 1" when I try to go online with the PLC. Earlier I tested the exact same set up with the soft PLC from codesys. I can then read/write values correctly with the Modbus master i have running on the laptop. Hope anybody can help me with this, thanks in advance!
Last updated: 2023-10-06
Post by ewi04 on Recipe Manager - RecipeManCommands, load & write wrong values, Bug?
CODESYS Forge
talk
(Post)
Hallo, I have a strange problem with the recipe manager. ISSUE: When using RecipeManCommands not all values are loaded correctly. Saving a recipe with CreateRecipe(), ReadAndSaveRecipe() or ReadAndSaveRecipeAs() works without any problems. BUT: LoadRecipe(), WriteRecipe() or LoadFromAndWriteRecipe() do not load the data correctly. It is Interesting that we have a different error pattern with LoadRecipe() than with WriteRecipe() or LoadFromAndWriteRecipe(). LoadRecipe() does not load all data and WriteRecipe() or LoadFromAndWriteRecipe() overwrites some data or assigns it incorrectly. And it is also strange that LoadRecipe() writes the values to the PLC. Normally it doesn’t do it. It makes no difference whether the memory type is textual or binary. I have an object consisting of STRUCTs which is inserted in the recipe definition. Environment: Codesys V3.5 SP19 Patch 4 (64Bit), Recipe Management 4.2.0.0 *Add a project (reduced to the problem)
Last updated: 2023-11-15
Post by sean-barton on Function block method default arguments
CODESYS Forge
talk
(Post)
I have default arguments specified for function block methods but when calling a method, an error is produced requiring me to supply all the arguments despite there being default values. According to the online documentation, under section "Calling a Method" and subsection "argument passing" of the following link: https://content.helpme-codesys.com/en/CODESYS%20Development%20System/_cds_obj_method.html "Passing an argument for an input ... can be omitted ... for which a default or initial value was specified in the declaration..." I have found this to be the case for all Codesys IDEs I've used, 3.5.11, 3.5.16, 3.5.17, 3.5.19. Am I missing something?
Last updated: 2023-12-21
Post by davidbo on Does the new license policy means I have to upgrade everything?
CODESYS Forge
talk
(Post)
We have several old project written with 3.5.17 and 3.5.18 and also some older Until now when a customer ordered a product from us. We just installed (we have a tested image) and added a license Now the license policy has changed and we have to buy a License Control Basic S or M However it only works with CODESYS Development System Version 3.5.19.10 or higher Does that mean we have to upgrade all our old products? That is not a simple task as a previous post has explained with weird error messages from CODESYS V3.5. Next we have to do rigorous testing of our applications afterwards. It is very expensive
Last updated: 2024-01-11
Post by idalu on Profinet PN_Controller Issue, Network Adapter
CODESYS Forge
talk
(Post)
i have a problem with Profinet on my project. I'm using Codesys RTE 3.5.19.50. When i download program to controller the ethernet is ok, PN_Controller is ok but every device i'm trying to connect is red with error "DCP no RealStationName". When i'm trying to Scan for Devices on PN_Controller there are no devices found. I have installed Codesys driver CmpEt1000Drv to my network adapter (i'm sure it is right intel pro 1000 model). I have noticed that when i installed codesys driver i'm no longer able to ping this network adapter (i can ping it when intel driver is installed). On my previous projects with runetimes i can ping it even with codesys driver installed. I have also tried to do downgrade of everything to version 3.5.19.20 and it not helped.
Last updated: 2024-01-17
Post by fdmartello on Unable to compare projects containing alarm manager 4.5.0.0
CODESYS Forge
talk
(Post)
Hello. In Codesys version 3.5.19.50 when comparing two projects that have an "Alarm Configuration" obj from the Alarm Manager library vers. 4.5.0.0 the attached error pops up. This originally happened with two projects that I converted from vers. 3.5.17.30 so, thinking it was some conversion issue, I created two clean projects directly in 3.5.19.50 using the Standard Project template and only added the Alarm Configuration objects in them. The result is the same and the only way I found that allowed me to compare them is by deleting the incriminated object in one of the two projects. Has anyone else encountered this issue? Best regards
Last updated: 2024-01-19
Post by matthew on New Ladder Diagram conversion does not work due to missing features
CODESYS Forge
talk
(Post)
Hi It looks like in the new ladder there is no way to remove unused FB call parameters or update the function block? It's quite often where you have a function block with multiple uses and not all the parameters are required. Need the ability to leave an input/output blank without getting an compile error Expression expected instead of '' Also double clicking on the FB no longer opens the underlying FB code and view what it was doing online. Dragging and dropping a variable does not work, only using the selection works. Will these be available in the V1.0 release or just best to stick to the old ladder until it's available? Thanks
Last updated: 2024-01-28
Post by smeitink on Timeout Error in Modbus Communication with WAGO PFC200 and iEM2050 Meter using 750-652 Module
CODESYS Forge
talk
(Post)
Hi all, I'm looking for help with an issue I've come across while trying to facilitate Modbus communication between a WAGO PFC200 PLC using a 750-652 communication module and an iEM2050 Series Single Phase Energy Meter. I believe to have everything wired and setup correcty, but I keep running into a "Error time out" message, and by now I don't really know what else to try. My setup is as follows: A PFC200 Wago PLC, which has 2 750-652 Serial Interfaces extension modules connected to its field bus. I'm using one of these to talk to a Schneider iEM2050 - kWh-meter over modbus. I have connected terminal 23 (A) of the iEM2050 to connector 6 (A) on the 750-652. I have connected terminal 24 (B) of the iEM2050 to connector 2 (B) of the 750-652. I'm using 200mm of twisted together wires to connected them both, and I have placed a 120 ohm resistor between A and B at both ends. I've attached relevant pinout images to this post. I then wrote a simple program that configures the Mobus port, as per the datasheet of the iEM2050. You can find an image of the relavent page attached to this post too. This is my program: PROGRAM PLC_PRG VAR Master: FbMbMasterSerial; xIsConnected: BOOL; xError: BOOL; iIndex: INT := 1; xTrigger: BOOL; utQuery : typMbQuery := ( bUnitId := 1, // The Modbus unit or slave address bFunctionCode := 4, // Function code for reading input registers uiReadAddress := 1829, // adress for the Power on off counter uiReadQuantity := 1 // Quantity of registers to read ); iStep: INT; oStatusModbus: WagoSysErrorBase.FbResult; utResponseModbus: typMbResponse; xConnect: BOOL := FALSE; delayTimer: TON; END_VAR Master( xConnect:= xConnect, I_Port:= _750_652_24_1, udiBaudrate:= 9600, usiDataBits:= 8, eParity:= WagoTypesCom.eTTYParity.Even, eStopBits:= WagoTypesCom.eTTYStopBits.One, eHandshake:= WagoTypesCom.eTTYHandshake.None, ePhysical:= WagoTypesCom.eTTYPhysicalLayer.RS485_HalfDuplex, xIsConnected=> xIsConnected, xError=> xError, oStatus=> oStatusModbus, eFrameType:= WagoAppPlcModbus.eMbFrameType.RTU, tTimeOut:= T#5S, utQuery:= utQuery, xTrigger:= xTrigger, utResponse:= utResponseModbus); delayTimer(IN := TRUE, PT := T#3S); // Use the Q output of the timer to set xConnect after the delay IF delayTimer.Q THEN xConnect := TRUE; END_IF CASE iStep OF 0: //Wacht totdat de master de poort geopend heeft IF xIsConnected THEN iStep := 1; END_IF 1: //Stuur request naar de slave xTrigger := TRUE; iStep := 2; 2: //Wacht totdat de master klaar is met het afhandelen van de request IF NOT xTrigger THEN iStep := 3; END_IF END_CASE The TON delay before opening the port is due to a an error I encountered when opening it straight away. This seems to be a bug, as described here. However, the TON solved that particular issue. I tried reading multiple registers, but like I said, I still always end up with the "Error time out". What else can I test or try at this point?
Last updated: 2024-02-24
Post by timvh on Profinet fault with codesys control V3 - Receive packet error
CODESYS Forge
talk
(Post)
Are you using the Control Win SL (installed together with the development environment of CODESYS)? If yes, you might want to consider using the CODESYS RTE instead. This has real-time capabilities (running on separate core(s)). But to be able to use this, you have to install the CODESYS Ethernet driver for your network interface to be able to let the RTE access the network port also in realtime. See: https://store.codesys.com/en/codesys-control-rte-sl-bundle.html https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_windows_rts_v3.html PS, I haven't tested this myself yet, but you could try to use the SetCommunicationState method of the Profinet controller to see if you can reset and start the bus communication: result := PN_Controller.SetCommunicationState(eRequestedState := DED.DEVICE_TRANSITION_STATE.START); PS, if you are located in the Netherlands or Belgium, we could also provide the license(s) for you.
Last updated: 2024-02-28