Search talk: port

 
<< < 1 .. 4 5 6 7 > >> (Page 6 of 7)

Post by konradkmiller on Variable assignments CODESYS Forge talk (Post)
I have a snippet of code that I was given as a reference in ST. ** ModbusMasterRTU( xConnect:= TRUE, IPort:= IoConfigGlobals.COM1, // IoConfigGlobals.RS232485Interface, // COM1=Front Port / Serial module = Name of module in Devices structure I/O list udiBaudrate:= 19200, usiDataBits:= 8 , eParity:= WagoTypesCom.eTTYParity.None , eStopBits:= WagoTypesCom.eTTYStopBits.One , eHandshake:= WagoTypesCom.eTTYHandshake.None , ePhysical:= WagoTypesCom.eTTYPhysicalLayer.RS485HalfDuplex, xIsConnected=> xIsConnected , xError=> , oStatus=> , eFrameType:= WagoAppPlcModbus.eMbFrameType.RTU , tTimeOut:= T#1S, utQuery:= utQuery , xTrigger:= SEND, utResponse:= utResponse)** What is the meaning of => in this context?
Last updated: 2024-07-20

Post by timvh on Unable to Connect to Modbus RTU Device CODESYS Forge talk (Post)
If your Control Win is the Modbus "Master" then your configuration should be something like: Modbus_COM (Serial port) - Modbus Master (this is the Control Win SoftPLC actively setting up the communication) - Modbus Slave (this is then your WAGO 750-315) You need to add channels to the Modbus Slave configuration to inform the master which variables to read/write from the Wago module. The way you configured it now, the Control Win is also a slave. PS, don't forget to put the PLC (Control Win) in Run.
Last updated: 2024-09-03

Post by annd on Migration von "CODESYS Control for PFC200 SL" zu WAGO FW26 "CODESYS V3.5.19.2" CODESYS Forge talk (Post)
Hallo, da Wago nun von eCockpit zum offenen "CODESYS Development System V3" wechselt, möchte ich meinen bestehenden 750-8212 von der PFC200 SL auf die Wago Firmware umstellen. Welche Schritte sind dabei notwendig? Den Controller würde ich auf die aktuelle FW 26 updaten und die 3.5.19.2 von Wago mit den Descriptions verwenden. Reicht es im Codesys Projektbaum mit "Gerät aktualisieren" auf den Wago Controller zu wechseln? Es wird dann statt dem "Pfc200Bus"ein leerer K-Bus und ein leerer Com-Port angezeigt. Müssen die einzelnen Module dann darunter neu angelegt und alle E/A Variablen manuell neu eingetragen werden? Das exportieren und danach wieder importieren funktioniert nicht, weil die Namen bzw. Adressen unterschiedlich sind. Ist das so richtig? Kann der Block "Modbus_COM_Port - Modbus_Master_COM_Port - Modbus_Slave" so bleiben wie bisher oder muss das auch unter dem neuen COM-Port neu angelegt werden? Für ein paar Hinweise wäre ich dankbar. Schöne Grüße, annD
Last updated: 2023-11-17

Post by thewizard8 on Raspberry PI4 Serial Port CODESYS Forge talk (Post)
Hi Dear All, I'm using my raspberry PI4 as a CoDeSyS PLC (Build from scratch with custom electronics). I was able to implement all fieldbuses with the exception of Modbus Serial. I'm using the internal Port (GPIO) and I configured it in /etc/Codesyscontrol_user.cfg the following away: [SysCom] Linux.Devicefile.1=/dev/ttyUSB0 Linux.Devicefile.2=/dev/ttyS0 I'm using COM2 on Master configuration. I'm using a interface board from TTL/RS485 (bidirectional board), and it's works perfectly with other devices but not in CoDeSyS. I'm able to send data with python script and read it on my pc using putty, but when I use a modbus slave simulator to interface with codesys I always get red icons on master and slave. (Please find image attached). I'm pretty shure that this might be a bad parameter on my CoDeSyS runtime configurstion file. Can someone help me? I'm stuck and this is for my master degree certification.
Last updated: 2024-03-18

Post by joshskellig on Publish a JSON payload via MQTT Publish (using IIot Libraries) CODESYS Forge talk (Post)
I am trying to figure out how to get a JSON payload to properly publish to my MQTT Broker. I am able to generate JSON using the examples from Codesys, but when I send that payload via MQTT there are characters that are extra or not recognized by my MQTT client. Any idea what could be causing it? PROGRAM PLC_PRG VAR hostname: STRING := 'localhost'; port: UINT := 1883; topic: WSTRING(1024) := "testing/"; payload: BYTE; factory : JSON.JSONDataFactory; eDataFactoryError : FBF.ERROR; pJsonData : POINTER TO JSON.JSONData := factory.Create(eError => eDataFactoryError); fb_JBuilder : JSON.JSONBuilder; wsValue : WSTRING := "Value1"; diRootIndex, diObject1Index : DINT; iValue : INT := 1234; jsonArrayWriter : JSON.JSONByteArrayWriter; wsJsonData : WSTRING(1000); xFirst : BOOL := TRUE; mqttClient: MQTT.MQTTClient; mqttPublish: MQTT.MQTTPublish; mqttPublishProperties: MQTT.MQTTPublishProperties := (bPayloadFormatIndicator := 1, wsContentType := "application/json"); END_VAR // Json Functionality IF xFirst THEN fb_JBuilder(pJsonData := pJsonData, diRootObj => diRootIndex); fb_JBuilder.SetKeyWithValue("Key1", wsValue, diParentIndex := diRootIndex); diObject1Index := fb_JBuilder.SetKeyWithObject("Key2", diParentIndex := diRootIndex); fb_JBuilder.SetKeyWithValue("Key3", iValue, diParentIndex := diObject1Index); xFirst := FALSE; END_IF jsonArrayWriter(pwData := ADR(wsJsonData), udiSize := SIZEOF(wsJsonData), jsonData := pJsonData^, xAsyncMode := FALSE); MSU.StrTrimW(pString:= ADR(wsJsonData)); // MQTT Functionality mqttClient( sHostname:=hostname, uiPort:=port, eMQTTVersion:=MQTT.MQTT_VERSION.V5 ); mqttPublish( mqttClient:=mqttClient, pbPayload:=ADR(wsJsonData), udiPayloadSize:=SIZEOF(wsJsonData), wsTopicName:=topic, mQTTPublishProperties:=mqttPublishProperties );
Last updated: 2024-04-10

Post by simone on Cannot connect to webvisu on localhost CODESYS Forge talk (Post)
As I wrote before on the title, I have difficulties to connect to see webvisu from localhost. The story: while waiting for the plc+hmi to arrive, I'm preparing the software, mainly the visual parts trough the control Win3 x64 (same version as the ide 3.5.20.10). The problem is that I can't see the webvisu with the installed webbrowser. I don't know if this is a problem, but I changed the port to 9001 (randomly "free") because 80, 8000, 8080, 8088, 3000 are all occupied by other projects (all on the Apache server). Is there something wrong with the config file? This is the url: localhost:9001/webvisu_app.htm and here the config file part "CmpWebServer". [CmpWebServer] ;The handling of startup/shutdown of the webserver: ;0->automatically start, shutdown only on shutdown of the runtime;1->automatically start, could be shutdown on demand ;2(default)->start/shutdown on demand;3->start on demand, shutdown only on shutdown of the runtime StartupType=0 ;The TCP port the webserver listens on WebServerPortNr=9001 LocalAddress=localhost ;LocalAdapterName=LAN-Connection LocalAdapterName=EthernetPCPLC ;LocalAdapterNameUnicode=L\00A\00N\00-\00C\00o\00n\00n\00e\00c\00t\00i\00o\00n\00 LocalAdapterNameUnicode=E\00t\00h\00e\00r\00n\00e\00t\00P\00C\00P\00L\00C\00 Thanks for all the help!
Last updated: 2024-07-11

Post by bbm1995 on Camera RTSP Feed CODESYS Forge talk (Post)
Hi dgrard, I had the same issue for a long time, but on a WAGO webvisu. Now I'm glad that I can share my solution. I don't know if you are trying to use the webvisu or the target visu, but this works on webvisu: Get "go2rtc" and set it up according to the documentation. I'm running the Windows binary. Here's my example of the go2rtc.yaml config file (contains working example streams): api: listen: ":1984" # default ":1984", HTTP API port ("" - disabled) origin: "*" # default "", allow CORS requests (only * supported) static_dir: "www" # default "", folder for static files (custom web interface) tls_listen: ":443" # default "", enable HTTPS server tls_cert: "./SSL/fullchain.pem" tls_key: "./SSL/privatekey.pem" streams: # Streams with multiple links will fall back on the next link. ABUS TVIP48511: - rtsp://<username>:<password>@<hostname>:<port>/ch1/main - rtsp://<username>:<password>@<hostname>:<port>/ch1/sub # Diagnostic connections Kirchhoff Institute for Physics - Germany: http://pendelcam.kip.uni-heidelberg.de/mjpg/video.mjpg Blanton Bottling, Kentucky - USA: http://camera.buffalotrace.com/mjpg/video.mjpg Tokyo - Japan: http://61.211.241.239/nphMotionJpeg?Resolution=320x240&Quality=Standard Tampere Hacklab - Finland: http://tamperehacklab.tunk.org:38001/nphMotionJpeg?Resolution=640x480&Quality=Clarity Soltorget Pajala - Sweden: http://195.196.36.242/mjpg/video.mjpg Kaiskuru Skistadion - Norway: http://77.222.181.11:8080/mjpg/video.mjpg webrtc: listen: ":8555" #ice_servers: # - urls: [ "stun:localhost:3478" ] # username: "" # credential: "" Access the webinterface of go2rtc and get the link of your stream. Use the link as for your browser frame in the visualization. Depending on your device, you need to be able to access the file /etc/lighttpd/lighttpd.conf or /etc/lighttpd/webvisu.conf and change the contents similar to this one, otherwise you'll get CORS and CSP errors in the browser and you won't be able to view the stream on the webvisu: # Webvisu specific settings $SERVER["socket"] =~ port_webvisu_used_any { url.redirect += ( "^/webvisu/?$" => "/webvisu/webvisu.htm" ) $HTTP["url"] =~ "^/webvisu/?" { var.response_header_policy_webvisu = ( # CSP for WebVisu, allowing inline sources. "Content-Security-Policy" => "default-src 'self' 'unsafe-inline'; media-src *; frame-src *", # CORS for WebVisu, allowing any origin to access. "Access-Control-Allow-Origin" => "*", # Tell older browsers that this page can only be displayed if all ancestor # frames are same origin to the page itself. "X-Frame-Options" => "SAMEORIGIN" ) # Response header policy for WebVisu setenv.set-response-header = var.response_header_policy_webvisu setenv.set-response-header += var.response_header_policy_common }
Last updated: 2023-11-14

Post by rossanoparis on How to configure CODESYSControl_User.cfg in order to use a specific network card for OPCUA Server CODESYS Forge talk (Post)
Hello at all I'd like to know how to configure CODESYSControl_User.cfg in order to use a specific network card for OPCUA Server. In the past, I tried to ask in "Forge" about this topic, but I could find neither help nor document informations about it. Reading the file "codesyscontrol.log" I see these logs OPC UA Server Started: Hostname: NTLRPICTRL01, Port: 4840 URL: opc.tcp://NTLRPICTRL01:4840 Loopbackadapter activated. **All available networkadapters are used.** Multithreading activated. 3 workers used. My controller, which is a Linux PC, has got two network cards eth0 and eth1 I whant to use the card with name "eth0" as a server for OPCUA and keep the "eth1" free for other stuffs. Is it possible ? Best regards Rossano
Last updated: 2023-08-25

Post by ofey on Modbus TCP communication CODESYS Forge talk (Post)
Hi! I tried setting up the PLC I'm working with (Beijer GN-9373) to connect to a modbus master running on a laptop. I have an ethernet connection (via USB-C to ethernet) between the laptop and the controller. I have tried following tutorial on how to set this up. I have added an ethernet device with the IP-address of the PLC. Further I added a ModbusTCP_Slave_Device with default settings. I get the error "Failed to open TCP Port: 1" when I try to go online with the PLC. Earlier I tested the exact same set up with the soft PLC from codesys. I can then read/write values correctly with the Modbus master i have running on the laptop. Hope anybody can help me with this, thanks in advance!
Last updated: 2023-10-06

Post by mark on IO link on IFM AL133x only single digital input on a channel CODESYS Forge talk (Post)
I have a problem with the CODESYS IO-Link SL software. When I insert a IO link master AL1332 and plug a discrete digital input to a channel it reads only 1 of the 2 available inputs on that channel. Is there anyone who sorted out if the second input is also usable? When we configure the module without the CODESYS IO-Link SL software then the second input on the channel can be used. At the moment we use some channels on a module as IO-link port, and some as discrete IO. It would be very nice if we can use both inputs on a channel with the use of CODESYS IO-Link SL.
Last updated: 2023-12-18

Post by dhumphries on Codesys device configuration CODESYS Forge talk (Post)
First make sure the programming laptop and HMI are both on the same subnet. For example if the IP address of the HMI is 192.168.1.125 with a subnet mask 255.255.255.0 set your laptop IP to 192.168.1.120 with a subnet mask of 255.255.255.0. Make sure the cables are fully connected (the ethernet port on my programming laptop will click once but the cable is not fully seated.) Make sure the HMI is powered on, try pinging the device from a command prompt, if you can't ping the HMI there is a network issue that has to be resolved first.
Last updated: 2023-12-30

Post by dhumphries on No source code available CODESYS Forge talk (Post)
Try using an Ethernet/IP scanner instead of an adapter, I'm guessing the 2 devices you're trying to communicate with are adapters, you have to have a scanner somewhere and Codesys should be a scanner. I don't know why you're getting the error, you should be able to use your Ethernet port as an EthernetIP adapter (although I've never had a reason to try,) but it's probably not what you wanted to do, unless you're connecting to another PLC that is a scanner. Good luck configuring the devices you're trying to connect to, it will be a lot easier if you have an .EDS file instead of starting with a generic module, even with an .EDS it can be tricky getting the communication working.
Last updated: 2024-02-03

Post by arundara on OPC UA Server Stops after 5 consecutive disconnections of ethernet port CODESYS Forge talk (Post)
Hello Every one, During testing of OPC UA communication between UA Expert software and the CODESYS SoftPLC on a Linux environment, an observation was made. When the Ethernet cable was disconnected and reconnected with 2-minute intervals, on the 5th attempt, the OPC UA connection failed to establish in UA Expert software. At this juncture, restarting the CODESYS SoftPLC enabled the reestablishment of OPC UA communication. The same result was obtained when testing on a Raspberry Pi SoftPLC. What is the reason behind this phenomenon? and whether there are settings to stop this behavior? Please help. Thanks & Regards.
Last updated: 2024-02-13

Post by rh-pk on v3.5 SP19 - Modbus TCP Devices - Channel Limit? CODESYS Forge talk (Post)
Hi, i found a solution for me. I had installed a 'old' version of CoDeSys (3.5.18 P5). I tried to add channels there, which works fine. I created a new project, added an Ethernet-Port, added a Modbus-Master and then I copied the ModBus-Slave from my working project to the new project. Now I could add more channels. I add the channels 10 and 11. Then I deleted (please make a backup before :-) the original ModBus-Slave in my working project and copied the extended Slave back to my working project. Surprisingly it is now possible to add new channels. Maybe this will help you.
Last updated: 2024-02-14

Post by timvh on Profinet fault with codesys control V3 - Receive packet error CODESYS Forge talk (Post)
Are you using the Control Win SL (installed together with the development environment of CODESYS)? If yes, you might want to consider using the CODESYS RTE instead. This has real-time capabilities (running on separate core(s)). But to be able to use this, you have to install the CODESYS Ethernet driver for your network interface to be able to let the RTE access the network port also in realtime. See: https://store.codesys.com/en/codesys-control-rte-sl-bundle.html https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_windows_rts_v3.html PS, I haven't tested this myself yet, but you could try to use the SetCommunicationState method of the Profinet controller to see if you can reset and start the bus communication: result := PN_Controller.SetCommunicationState(eRequestedState := DED.DEVICE_TRANSITION_STATE.START); PS, if you are located in the Netherlands or Belgium, we could also provide the license(s) for you.
Last updated: 2024-02-28

Post by timvh on Profinet fault with codesys control V3 - Receive packet error CODESYS Forge talk (Post)
Are you using the Control Win SL (installed together with the development environment of CODESYS)? If yes, you might want to consider using the CODESYS RTE instead. This has real-time capabilities (running on separate core(s)). But to be able to use this, you have to install the CODESYS Ethernet driver for your network interface to be able to let the RTE access the network port also in realtime. See: https://store.codesys.com/en/codesys-control-rte-sl-bundle.html https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_windows_rts_v3.html PS, I haven't tested this myself yet, but you could try to use the SetCommunicationState method of the Profinet controller to see if you can reset and start the bus communication: result := PN_Controller.SetCommunicationState(eRequestedState := DED.DEVICE_TRANSITION_STATE.START); PS, if you are located in the Netherlands or Belgium, we could also provide the license(s) for you.
Last updated: 2024-02-28

Post by mbmik on IoDrvModbusTCP_Diag not defined when using MODBUS CODESYS Forge talk (Post)
Hi Im trying to setup a Weidmüller WL2000 to run with MODBUS, to get some data from a server. Codesys V3.5 SP20. The issue is, that whenever i attach an ethernet port and add MODBUS Master und also a Slave, codesys will compile the project, but there always seem to be some remaining errors, which or only visible, when setting the messages window to "Pre-Compiled". I tried a lot of stuff to get rid of these errors, but cant find to seem the reason. New installation of codesys, cleaned project, setup completely empty new project, manually adding libs. Nothing helps. Any help is apreciated. Maybe we are doing something wrong.. Example Project is available, if somebodey wants to take a look. Greetings and thanks alot
Last updated: 2024-04-15

Post by kazuhiro on Problems using MySql Library and SysProcessExecuteCommand2 together CODESYS Forge talk (Post)
I use fbMsSQL_compact(FUN) of the MySQL Library to write data to the database. There is no problem when writing data using only fbMsSQL_compact(FUN). However, when I try to write data obtained using SysProcessExecuteCommand2 to the database using fbMsSQL_compact(FUN), an error message "Dest server on ip address:xxx.xxx.xxx.xxx and port:1433 is unreachable" appears and writing is not possible. From what I have researched, it seems that writing is not completed in one cycle of fbMsSQL_compact(FUN), and when SysProcessExecuteCommand2 is executed first in the second cycle, the work done in one cycle of fbMsSQL_compact(FUN) is reset. Could you please give me some advice?
Last updated: 2024-06-18

Post by kazuhiro on Problems using MySql Library and SysProcessExecuteCommand2 together CODESYS Forge talk (Post)
I use fbMsSQL_compact(FUN) of the MySQL Library to write data to the database. There is no problem when writing data using only fbMsSQL_compact(FUN). However, when I try to write data obtained using SysProcessExecuteCommand2 to the database using fbMsSQL_compact(FUN), an error message "Dest server on ip address:xxx.xxx.xxx.xxx and port:1433 is unreachable" appears and writing is not possible. From what I have researched, it seems that writing is not completed in one cycle of fbMsSQL_compact(FUN), and when SysProcessExecuteCommand2 is executed first in the second cycle, the work done in one cycle of fbMsSQL_compact(FUN) is reset. Could you please give me some advice?
Last updated: 2024-06-18

Post by dekelec on The current baud rate could not be determined in CR0020 IFM with maintenance tool CODESYS Forge talk (Post)
It could be a problem with the cable pinout on either side: 9 pin D-SUB connector (male) - PC side Pin Potential: 1 n.c. 2 RxD 3 TxD 4 n.c. 5 n.c. 6 GND 7 n.c. 8 n.c. 9 n.c. Shell Shield Check if TxD and RxD cross between pins 2 and 3 (what is the Recive signal/wire to one device it's a Transmit signal/wire for the othe device) or with COM port settings: Bits per second: 9600 Data bits: 8 Parity: None Stop bits: 1 Flow controll: None
Last updated: 2024-07-09

Post by yannickasselin on codesys VLAN tagging CODESYS Forge talk (Post)
I ordered a cheap managed switch and tested it as soon as I received the switch. It works great! I even went a bit further. As you can see in the screenshot, I created 2 Codesys containers. Each one having 2 fieldbuses. The first one has EtherCAT and EtherNet/IP and the second one has EtherCAT and Modbus/TCP. All going through the same ethernet port from the PC to the switch. The switch splits it up into 4 different networks. The hardest part was to figure out how to configure the switch. @eschwellinger, thank you very much.
Last updated: 2024-09-17

Post by timvh on Modbus TCP & RTU with Control for Linux SL CODESYS Forge talk (Post)
It seems you have 2 network interfaces. Did you try eth1? Did you already configure the IP address for this interface in Linux? If yes, then maybe undo this. - or only set eth0 in the Nic configuration without anything else (so no IP address, because this is already set in Linux). For more information about the Nic settings, see (probably already read it?): https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_obj_deploy_control_sl_configuration.html PS, if you only want to run CODESYS Control SL, you don't necessarily need the Virtual PLC variant. You could also install and run the CODESYS Control SL Runtime in the Host operating system. This way you should also be able to access the serial port and directly access all ethernet ports. Maybe this is easier?
Last updated: 2024-10-23

Post by greenwood on CODESYS Control Raspberry Pi mit Servotreiber T6 von StepperOnline CODESYS Forge talk (Post)
Hallo, ich versuche, eine Modbus-RTU-Kommunikation zwischen meinem Raspberry Pi mit CODESYS Control für Raspberry Pi 64 SL und einem Servotreiber von StepperOnline, Typ T6, herzustellen. Die Verbindung ist wie folgt: RJ45-Stecker am Servotreiber -> Kabel mit RJ45 an einem Ende und USB-A-Stecker am anderen Ende -> Seriell-zu-USB-Konverter -> Raspberry Pi. Der Seriell-zu-USB-Konverter und die Kabel habe ich zusammen mit dem Motor und Treiber von StepperOnline gekauft und sie sind dafür gedacht, den Servotreiber mit einem Computer zu verbinden, auf dem deren Setup-Software läuft. dmesg | grep tty auf dem Pi sagt mir, dass der USB-zu-Seriell-Konverter auf ttyusb0 ist. Ich weiß nicht, wie man das in einen COM-Port übersetzt, ich habe COM 1 genommen. Ich habe ein Projekt in Codesys erstellt und ein Modbus_COM-Gerät hinzugefügt, einen Modbus_Master_COM_Port und einen Modbus_Slave_COM_Port angehängt. Auf der Registerkarte "Allgemein" des Modbus_COM habe ich die folgenden Werte eingestellt: Slave address 1 Baud rate 9600 Parity None Data bits 8 Stop bits 2 Ich habe den Servotreiber auf die gleichen Werte eingestellt. (Ich habe auch andere Werte getestet, aber mit dem gleichen Ergebnis). Auf der Registerkarte "Modbus Slave Channel" des Modbus_Slave_COM_Port habe ich einen Kanal hinzugefügt und die folgenden Werte eingetragen: Access type Read Holding Registers (Function Code 3) Read Register offset 0x0000 Length 1 Ich habe noch keinen Code geschrieben, weil ich noch nicht herausgefunden habe, wie man die Kommunikation programmiert. Wenn ich das Projekt zum Raspberry Pi herunterlade scheint der Modbus_Master_COM_Port zu laufen (grünes Symbol), aber der Modbus_Slave_COM_Port nicht (rotes Dreiecksymbol). Wenn ich einen anderen COM-Port eintrage, haben sowohl der Master als auch der Slave das rote Dreiecksymbol. Ich habe dies auch mit meinem Windows-PC unter Verwendung von Codesys Control Win 64 versucht und die gleichen Ergebnisse bekommen. Ich wäre dankbar für jede Hilfe oder Tipps, wie ich den Grund dafür herausfinden kann, warum der Servotreiberreiber nicht reagiert.
Last updated: 2024-05-31

Post by dantheman on Connecting to SoftPLC Only Works By Turning Off Modbus Ethernet Port CODESYS Forge talk (Post)
I have an IPC with 2 ethernet ports and 1 Wi-Fi. I'm using ModbusTCP with the ethernet port named "enp2s0" connected to my remote I/O. This works fine when testing with Python and also works with CODESYS, but CODESYS is only able to scan for the Linux SoftPLC when I turn off the "enp2s0" interface. In other words, I can't get online with the IDE if I want my ModbusTCP comms to run with CODESYS. I'm using a Linux SoftPLC that has the following entry in CODESYSControl.cfg, hoping that this will allow me to connect with "enp1s0" or "wlp3s0", and leave "enp2s0" for field comms, but this seems to only make the source IP of the ModbusTCP comms to be bound to "enp2s0". That last point is the case only if I don't restart the service, but if I do restart the service after changing the config file, the source IP for the ModbusTCP comms then becomes the one for "enp1s0", which is very confusing to me: [SysSocket] Adapter.0.Name="enp2s0" Adapter.0.EnableSetIpAndMask=1 On the device list, I only have "enp2s0" given as the ethernet device that has the ModbusTCP master & slave beneath it, shown in Screenshot 1. On the IPC, I can ping the ModbusTCP client (remote I/O) from "enp2s0", and I've attached a Wireshark capture of running ModbusTCP from the CODESYS runtime as Screenshot 2, 3 & 4 (again, I can't get online when this is running, I have to turn off "enp2s0" to connect even when it's idle and I don't have an active TCP session with my Python tests). Like I explained above, the source IP is "enp1s0", even though the ethernet device on the project is "enp2s0". I was lucky to catch the red message that showed the source IP that makes sense to me (the one for "enp2s0"), but for some reason that connection was reset and I never saw that packet again. I've also tried this with Auto-reconnect both enabled & disabled, for the ModbusTCP Master device. I also have to turn off "enp1s0" and then turn it on, just so that I can have the ModbusTCP comms running from "enp2s0" (which is not intuitive in any way to me, I'd love some help understanding that phenomenon as well) in the weird manner that I've described above. I would be very appreciative if someone can help me figure out this pickle. I'd love to just connect to CODESYS through my Wi-Fi interface and leave my ethernet ports for field comms.
Last updated: 2024-08-01

Post by ryandmg on Web Client (HMI) Disconnects from Webvisu (Weidmuller u-OS) CODESYS Forge talk (Post)
Thanks So Much for the reply! Were using the Weidmuller UV66-ADV-10-CAP-W The HMI is pointed to the URL which is assigned through u-OS. Basically when you log into the controller's webserver via browser you can view the installed apps. One of which is the Codesys runtime. When you click on that it takes you to the visualization. That corresponding url is what the HMI is looking for. I apologize I don't have that on hand as I'm in the office right now. I don't think I tried connecting using the port you mentioned and https in lieu of the u_OS URL. I can certainly try. Out of the box the u-OS is set for HTTP. Since we're isolated I havent changed that yet. When this has happened while logged on via chrome on my laptop, simply refreshing brings the visualization right back. In the case of the HMI in kiosk mode, we power cycle the HMI to force a reconnect, log back in u-OS and the visualization is back.
Last updated: 2023-09-06

<< < 1 .. 4 5 6 7 > >> (Page 6 of 7)

Showing results of 161

Sort by relevance or date