Search talk: data and time conversions

 
<< < 1 .. 99 100 101 102 103 .. 135 > >> (Page 101 of 135)

Post by alimans on Hex string CODESYS Forge talk (Post)
Hi kdkwhite, for Word you still can use suggested code by using a union structure and crack down your Word to two byte as bellow: TYPE CrackWordToByte : UNION InWord : WORD; OutBytes : ARRAY [0..1] OF BYTE; END_UNION END_TYPE then define your variable as this type: udInput : CrackWordToByte; now assign your Word variable input to InWord and send OutBytes[x] to the mentioned method: udInput.InWord := WordVariableInput; Input := udInput.OutBytes[x]; Regarding your question about the code: actually 48 is ascii code of "0" and while 65 is the ascii code of "A" so in above code 55 + 10 would be 65.
Last updated: 2023-09-20

Post by ggarcia94 on CANOPEN SDO configuration CODESYS Forge talk (Post)
Hello, I´m connected to two drives via CANOPEN. The connection seems to be ok. However, I´m not able to get the PDOs to work even tho they are configured as in the manual of the drives. Looking at the SDOs I´ve seen that for each PDO there is a "Disable PDO" SDO that does not exist in the manual or in the EDS file of the drives. This "Disable PDO" signal has the same Index and Subindex as another SDO used to set and enable the COB-ID of the PDO. I´m assuming this is normal but why is Codesys creating a "Disable PDO" SDO for each PDO and could that be the reason the PDOs are not working?
Last updated: 2023-09-25

Post by bahrt on Mapping GPIO and adding GPIO configurations CODESYS Forge talk (Post)
Hi I am about to configure ALL GPIOs on a Raspberry Pi 3 model B V1.2. It seems that I have limited understanding of why not all the IO’s become available with the corresponding mapped IO’s – the 'dwInUse' contains mapping of the inputs from GPIO0 to GPIO27. But 'dwInputs' are only showing GPIO0 to GPIO8 and GPIO15 as available inputs. These mentioned inputs work fine You will be able to watch the limited mapped IO activity here: https://drive.google.com/file/d/1zz4PBNBfRZBF2YkiJ2VQxw6L9MBVji7R/view?usp=sharing Can you please bring your best idea on why GPIO09 to GPIO14 and GPIO16 to GPIO27 state are zero in the dwInputs register? Thanks in advance. Best regards Andreas Bahrt
Last updated: 2023-11-16

Post by jegerjon on Testing of Codesys program CODESYS Forge talk (Post)
I have a simulation function that toggle xSimActive. I map all IO variables to "IO GVLs" when xSimActive=0. I map IO corresponding SimIO GVL to "IO GVLs" when xSimActive=1. Then I write code for the simulation program that runs when xSimActive=1. Typically increase flow corresponding to pump speed, simulate tankfilling corresponding to flow and so on. I made a FC that require a correct code to activate simulation to avoid unintended activation by service dept. When comissioned remove any possibility to activate simulation. Super when officetesting and supporting service dept. + cheap as it requires no additional equipment, and it is easier to support customer later on in the life cycle as you can test proposed changes without setting up a testlab.
Last updated: 2023-12-07

Post by jegerjon on Testing of Codesys program CODESYS Forge talk (Post)
I have a simulation function that toggle xSimActive. I map all IO variables to "IO GVLs" when xSimActive=0. I map IO corresponding SimIO GVL to "IO GVLs" when xSimActive=1. Then I write code for the simulation program that runs when xSimActive=1. Typically increase flow corresponding to pump speed, simulate tankfilling corresponding to flow and so on. I made a FC that require a correct code to activate simulation to avoid unintended activation by service dept. When comissioned remove any possibility to activate simulation. Super when officetesting and supporting service dept. + cheap as it requires no additional equipment, and it is easier to support customer later on in the life cycle as you can test proposed changes without setting up a testlab.
Last updated: 2023-12-07

Post by preimesbergert on Raspberry Pi 4 B HW 1.5 Codesys control 4.10.0 stopps after a few seconds CODESYS Forge talk (Post)
Wanted to play a bit with a raspberry Pi 4 Model B HW 1.5 and Codesys. Regardless of the image (tried 32bit / 64bit version from Raspberry Pi Imager) and with all tested Codesys Control versions (4.2.0, 4.8.0, 4.10.0) and regardless if single core / multicore / 64 bit variant, always is the runtime stopped after about 30sec with the nice message: ooops... this runtime was built for RASPBERRYPI. Hardware version or firmware version not supported! (-7, 0x00000BB8, 0xFFFFFFFB) Whats wrong with it?!?!? I read a lot about the issue in topics from 2020-2021 but it always was stated with new Codesys control version issue will be fixed (4.4 for example) but still it is there.
Last updated: 2023-12-21

Post by preimesbergert on Raspberry Pi 4 B HW 1.5 Codesys control 4.10.0 stopps after a few seconds CODESYS Forge talk (Post)
Wanted to play a bit with a raspberry Pi 4 Model B HW 1.5 and Codesys. Regardless of the image (tried 32bit / 64bit version from Raspberry Pi Imager) and with all tested Codesys Control versions (4.2.0, 4.8.0, 4.10.0) and regardless if single core / multicore / 64 bit variant, always is the runtime stopped after about 30sec with the nice message: ooops... this runtime was built for RASPBERRYPI. Hardware version or firmware version not supported! (-7, 0x00000BB8, 0xFFFFFFFB) Whats wrong with it?!?!? I read a lot about the issue in topics from 2020-2021 but it always was stated with new Codesys control version issue will be fixed (4.4 for example) but still it is there.
Last updated: 2023-12-21

Post by andrax on Save Recipe on Paspberry CODESYS Forge talk (Post)
Unfortunately not. The folder does not work. There are neither error messages nor any other indication that this may be due to missing rights. I have searched the entire forum and also tested the Codesys example. The simple recipe management generally does not work! The Raspi crashes with the extended recipe management from the example. I have now found another sample that works. https://forge.codesys.com/forge/talk/Engineering/thread/61c6a04b79/ Many thanks to mcodem. After some trial and error I have found out: xcreate must be called at least once at runtime. After that xload_write and xread_save work All other functions do not work. It is also possible to save to the /home/Documents folder. So it is not due to the rights. It would be nice if Codesys would check where the problem really lies.
Last updated: 2023-12-30

Post by jdjennings1962 on Trouble accessing Math functions in OSCAT library CODESYS Forge talk (Post)
Hi all, I am trying to utilize the ARRAY_SDV standard deviation function, part of the Math group in the OSCAT library downloaded from the CODESYS store. My Codesys version is 3.5.19.10. When I add the OSCAT to my Library, it shows a subset of the library (Standard) as fully installed and signed (see pic). However, the Math functions are not in this Standard group. The Math functions I need can be viewed as source code in the full OSCAT_BASIC, though this the symbol next to this library suggests it is source only and not fully installed. When I try to declare an instance of the ARRAY_SDV function in a program, it is not known. I have tried reinstalling and Building . . . Any help would be greatly appreciated. Jeff
Last updated: 2024-01-06

Post by toby on Ethercat Servo Setup CODESYS Forge talk (Post)
Hi everyone, so a little update to this, I've come back to this project in the new year, and got it working. Yeah!, However, now with the new licensing setup, I need a new SoftMotion license, but it doesn't seem to be compatible with the previous Raspberry Pi SL license. Has anyone had any luck with Raspberry Pi and SoftMotion_Lite? Specifically the licensing of such? My customers new installation needs to be rebooted every 30min which is causing headaches! Another option is to not use the SoftMotion function blocks, and control the EtherCat amplifier directly, but I'm not sure how to do so. Does anyone have a specific example project of how to control a servo without the use of the SoftMotion function blocks? Thanks everyone for any assistance rendered. It's very much appreciated! Toby
Last updated: 2024-01-10

Post by matthew on New Ladder Diagram conversion does not work due to missing features CODESYS Forge talk (Post)
Hi It looks like in the new ladder there is no way to remove unused FB call parameters or update the function block? It's quite often where you have a function block with multiple uses and not all the parameters are required. Need the ability to leave an input/output blank without getting an compile error Expression expected instead of '' Also double clicking on the FB no longer opens the underlying FB code and view what it was doing online. Dragging and dropping a variable does not work, only using the selection works. Will these be available in the V1.0 release or just best to stick to the old ladder until it's available? Thanks
Last updated: 2024-01-28

Post by ewi04 on How to upload application file to remote controller (offline) ? CODESYS Forge talk (Post)
Hi, I am looking for a good way to update a decice remotely. The devices are distributed worldwide and have normally no connection to the internet. The CODESYS Automation Server can't help here. So I want to update the decices via USB stick. I have written my own code* to update the files that are created with ‘Create boot application’. But sometimes strange things happen: visu elements are present, but are not found the application is no longer registered and therefore no longer starts I have not yet found out why these errors occur. Has anyone had similar problems or found a better way? Is there perhaps a CODESYS library or something else? Many thanks! *the code deletes the directories on the device and copies the new directories from the USB stick while the system is running (goes without saying)
Last updated: 2024-02-05

Post by arundara on OPC UA Server Stops after 5 consecutive disconnections of ethernet port CODESYS Forge talk (Post)
Hello Every one, During testing of OPC UA communication between UA Expert software and the CODESYS SoftPLC on a Linux environment, an observation was made. When the Ethernet cable was disconnected and reconnected with 2-minute intervals, on the 5th attempt, the OPC UA connection failed to establish in UA Expert software. At this juncture, restarting the CODESYS SoftPLC enabled the reestablishment of OPC UA communication. The same result was obtained when testing on a Raspberry Pi SoftPLC. What is the reason behind this phenomenon? and whether there are settings to stop this behavior? Please help. Thanks & Regards.
Last updated: 2024-02-13

Post by rh-pk on v3.5 SP19 - Modbus TCP Devices - Channel Limit? CODESYS Forge talk (Post)
Hi, i found a solution for me. I had installed a 'old' version of CoDeSys (3.5.18 P5). I tried to add channels there, which works fine. I created a new project, added an Ethernet-Port, added a Modbus-Master and then I copied the ModBus-Slave from my working project to the new project. Now I could add more channels. I add the channels 10 and 11. Then I deleted (please make a backup before :-) the original ModBus-Slave in my working project and copied the extended Slave back to my working project. Surprisingly it is now possible to add new channels. Maybe this will help you.
Last updated: 2024-02-14

Post by dhumphries on Toggling Visualizations using HMI Physical Buttons CODESYS Forge talk (Post)
Nothing wrong with ladder, in a lot of applications it is simpler than ST or CFC, you're a lot less likely to have syntax issues in a ladder diagram than in structured text as long as you stick with traditional ladder elements. Your attempt was almost valid, but you tried to change the currentvisu variable using a blend of structured text and ladder, which isn't allowed. You need to use the MOVE operator and define the visualization name as a string on the input side and the visuelems.currentvisu as the target on the output side.
Last updated: 2024-02-28

Post by riccardo on Web Browser special tools errors CODESYS Forge talk (Post)
Goodmoning everyone, I hope a codesys tecnichian will see this post. I serched on the forum and I found many topic about this tool but very few reaplies. I am tring to use the Web Browser tool, but it doesn't seem to work properly. I put several links in several forms: https://google.com http://google.com/ http://www.google.com http://www.google.com/ http://www.studiojomega.it/ . . . https://192.168.1.101/u-os-app-codesys/application/visualization/webvisu.htm But I obtain always errors; mainly 400 and 404 and in the normal visu this message appears "www.Google.com has refuse the connection". Is the codesys browser able to work as every other browser or has it some limitation? There is some particular precaution to consider when I pass the link to the codesys browser? Thanks in advance, Riccardo
Last updated: 2024-02-29

Post by mp9876 on Problems with simulation in Window 10 CODESYS Forge talk (Post)
Hi Automa, it seems the solution you were bringing up on 2022-04-06 could really help me as I did not remember the password I initially set. My problem though is that I am using Codesys Control Win V3.5 SP19/60 (64 bit) and I cannot locate any of the files you listed up there. I have been looking inside folder: C:\Program Files\CODESYS 3.5.19.60\CODESYS\ and they appear not to be present at all neither in the CODESYS folder or any sub-folders. Uninstalling and re-installing unfortunately does not do the trick. Any idea how I could get out of the ditch on this issue ? Anyone else maybe ? Thanks
Last updated: 2024-03-18

Post by valec on Connect local Asem HMI runtime to local Codesys Control Win V3 x64 CODESYS Forge talk (Post)
I have a project made on a PL700 PLC with Codesys and an Asem Premium HMI panel. I don't have access to the physical PLC right now, so I'm trying to use Codesys Control Win V3 x64. I created the application and loaded "Codesys Control Win V3 x64" without errors, then I activate "Start PLC" from the tray. Asem cannot connect. I tried to use "localhost" or the local IP address and it doesn't work (it's the "CoDeSys Soft PLC Communication Driver"). I need to connect my local Asem runtime to a virtual Codesys application on my PC. How can I do it?
Last updated: 2024-03-26

Post by niallel on Continuous MC_PositionProfile CODESYS Forge talk (Post)
Hi, Is it possible to have a MC_PositionProfile that runs continuously again and again without stopping the motor and starting again. I have a profile that contains about 50 steps that I want to repeat. At the end of each run the motor comes to a stop before the next one starts. My code checks for Done, then resets the Execute to False before setting Execute to True to run again, and I think this is causing the motor to go to standstill before starting again. There doesn't seem to be a BufferMode option like with MC_MoveAbsolute. Is it possible to do this? Many thanks,
Last updated: 2024-04-11

Post by esave on OPC UA Server with on Codesys + OPC UA Client on Labview CODESYS Forge talk (Post)
Hello everyone I want a communication between my PLC as an OPC UA Server and Labview on my PC as the OPC UA Client. I have an Festo CPX-E-CEC-C1-PN PLC and I have the OPC UA Toolkit from Labview. I created some Variables for testing (see picture 1) on Codesys. I tried to use this Labview block diagram (see picture 2) but I cant connect the PLC to it. What do I have to type in the Server Endpoint URL and what in the Node ID? Is this a good way for communication with a PLC to a PC? If not is there another way?
Last updated: 2024-04-12

Post by pethun on Upgrade from codesys 3.5.19 to 3.5.20 CODESYS Forge talk (Post)
Hi We upgraded our ptoject from 3.5.19 to 3.5.20 but we get an error message in the latest version. We made our own trend function and its related to this we get error message: Trend_Menu Device: PLC Logic: Application: C0032: Cannot convert type 'RTS_SYSTIMEDATE(systimertc, 3.5.20.0 (system))' to type 'RTS_SYSTIMEDATE(systimertc, 3.5.17.0 (system))' The variables are defined as follow: start : SysTimeRtc.SYSTIMEDATE; end : SysTimeRtc.SYSTIMEDATE; The code that creates the error is the variable start and end IF xAssign THEN xAssign := FALSE; xPanEnable := FALSE; xZoomEnable := FALSE; drs.liFrom := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(start, 0 (us)); drs.liTo := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(end, 0 (us)); drs.m_itfDateRangeSelectorClient.SetCurrentRange(drs.liFrom, drs.liTo); END_IF I cant understand really what the error message means and what can be the cause of the error? It compiles fine in dthe older codesys 3.5.19. If anyone has some experience of this please help us out? We must upgrade due to the new licenses. Thanks
Last updated: 2024-04-20

Post by pethun on Upgrade from codesys 3.5.19 to 3.5.20 CODESYS Forge talk (Post)
Hi We upgraded our ptoject from 3.5.19 to 3.5.20 but we get an error message in the latest version. We made our own trend function and its related to this we get error message: Trend_Menu Device: PLC Logic: Application: C0032: Cannot convert type 'RTS_SYSTIMEDATE(systimertc, 3.5.20.0 (system))' to type 'RTS_SYSTIMEDATE(systimertc, 3.5.17.0 (system))' The variables are defined as follow: start : SysTimeRtc.SYSTIMEDATE; end : SysTimeRtc.SYSTIMEDATE; The code that creates the error is the variable start and end IF xAssign THEN xAssign := FALSE; xPanEnable := FALSE; xZoomEnable := FALSE; drs.liFrom := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(start, 0 (us)); drs.liTo := VisuTrendStorageAccess.TrendStorageConvertToTimestamp(end, 0 (us)); drs.m_itfDateRangeSelectorClient.SetCurrentRange(drs.liFrom, drs.liTo); END_IF I cant understand really what the error message means and what can be the cause of the error? It compiles fine in dthe older codesys 3.5.19. If anyone has some experience of this please help us out? We must upgrade due to the new licenses. Thanks
Last updated: 2024-04-20

Post by reinier-geers on License problem gateway CODESYS Forge talk (Post)
Epis doesnt want Softmotion. I thought it was about the price. If it was possible it would be working already and i dont need an extra licence. Thats the problem of codesys. The software is running but hangs on its license. Epis made it posible to see the stick. I can see the license. Softmotion is there from 3.5.14.Xx Like is said And Motion control is alrady posible 15 year ago. And i only need a Sync of 2 drives. I want a good solution not a refund. Dont point to the manufacturer. The software is made by 3s not by epis .
Last updated: 2024-04-29

Post by viksym on Get text from textlist CODESYS Forge talk (Post)
Does anybody know how to get a specific text from a text list within a program. Obviously it works in a visualization, but because I will have an HMI that has it's own system and I will have to send variables to this HMI via an OPC UA connection, I need to be able to get a text into a string. I tried using the VisuElems like this, but it only returns an empty "" and nothing else. IF trig THEN sText := VisuElems.cmpDynamictext.DynamicTextGetDefaultText(ADR(sTextList), ADR(sAlarmID))^; //sText := VisuElems.cmpDynamictext.DynamicTextGetText(ADR(sTextList), ADR(sAlarmID))^; trig := FALSE; END_IF Any help and idea is highly appreciated because I am getting desperate here.
Last updated: 2024-05-31

Post by spice on WebVisu Recipe Save/Load CODESYS Forge talk (Post)
I'm currently reworking the controls on a cnc press brake and wanted to load various recipes as programs to run. I'm using a 2d array of REALs to store the X and Y coordinates as well as some other program parameters in a recipe. I'd like to store all of the recipes on a computer used as the HMI that way the text files can be edited and uploaded offline. I'm using Automation Directs P2CDS-622 Can this be done through webvisu? If not would a license for Codesys HMI SL on the computer allow me to accomplish this? I've attached the Project File Thanks, Spice
Last updated: 2024-05-31

<< < 1 .. 99 100 101 102 103 .. 135 > >> (Page 101 of 135)

Showing results of 3353

Sort by relevance or date