Post by davidbo on i2c How does CODESYS handle exception or error messages. CODESYS Forge talk (Post)
For Raspberry Pi I have made a python script which regularly read a bulk of data over the ic2 from a device. Sometimes I get an Exception an IOError. I assume similar things can happen in CODESYS. So how does CODESYS handle that? Can I get any info about such an event?
Last updated: 2024-02-07

Post by reinier-geers on SysFileOpen does not work after update to V3.5 SP19 Patch 5 CODESYS Forge talk (Post)
At 19.1 the hFile_test should be RTS_IEC_HANDLE and always open-write - close in one cycle udi_handle: RTS_IEC_HANDLE; //handle-number. Is created by SysFileOpen udi_handle:=SysFileOpen(sFileName,Sysfile.AM_WRITE_PLUS, ADR(udi_ErrorCode)); udi_RetValWrite:=SysFileWrite(udi_handle, pRemBuffer, szRemBufSize, ADR(udi_ErrorCode)); //closing file IF udi_RetValWrite < szRemBufSize THEN ui_Error:=cWriteError; END_IF//error writing data udi_ErrorCode_Close:=SysFileClose(udi_handle);
Last updated: 2024-02-19

Post by i-campbell on Not able to see input data coming from eip adapter on codesys CODESYS Forge talk (Post)
Hello, I think you can try to change the Connection from Multicast to Point to Point. Please also make sure your windows firewall is allowing the correct UDP ports inbound for ethernet IP. You might also need to increase the RPI, so it times out slower.
Last updated: 2024-03-07

Post by rjonker on codesys mqtt publish serialization CODESYS Forge talk (Post)
pbPayload is a pointer, which it expects to point at a STRING. If you point it at an address holding a different data type, it will just assume those bytes are part of a string and likely trundle along memory until it finds a null byte (0x00) that would normally signify the end of a string PublishMessage := BOOL_TO_STRING(boolVariable);
Last updated: 2024-06-05

Post by mos89p on how to use UseDataExpanding() in datasource CODESYS Forge talk (Post)
Hi I need to update by software some structures in my datasource, i found this example: https://content.helpme-codesys.com/en/CODESYS%20Communication/_cds_update_data_interface.html it seems that because i use complex variable structure i need to use UseDataExpanding() instead of use data, the question is how to get an instance of IDatasourcesMgr3 i have the global variable g_Datasources is instantiated automatically
Last updated: 2024-06-18

Post by koppit on SysComRead Timeout Parameter CODESYS Forge talk (Post)
Im using SysCom ver. 3.5.17.0 and seem to have the same issue on a Raspberry Pi. It's not waiting for the requested number of bytes, no matter if "ulTimeout := SYS_INFINITE" or any other value. The only solution I have found is to stall the program to allow the serial port to recieve the data.
Last updated: 2024-06-26

Post by tomast on Communication PLC with HMI - how to send DUT via NVL. CODESYS Forge talk (Post)
Hi everyone, I am working with project where i have DUT wihth struct. I would like to fill this data trough a form on HMI. I use NVL to communicate and i would like to know how is it possible to do this? Thanks for all your advice in advance.
Last updated: 2024-08-23

Post by janber on REFERENCE TO in an array CODESYS Forge talk (Post)
Hi all, in the online help it written, that array of reference to data type is not possible. Ok... but if I create array of struct of reference to - everything works fine - please see the screenshots: and it works this way OK. Is it intention or error in compiler 3.5.18.20 and we should avoid it? Thanks a lot, Jan.
Last updated: 2024-10-14

Post by yr00 on OPC UA datasource low read frequency CODESYS Forge talk (Post)
Hello everyone, I am trying to test the OPC UA client feature in Codesys. My setup is the following; I have a Codesys simulation/ visualization running on Control Win V3. My OPC UA server is hosted on a Siemens 1518 PLC using PLCSim Advanced. The setup is completely virtual so there are no really PLCs. Everything is on my laptop. Writing data from the Codesys simualtion to the server is very quick. I have a PLC program running on another 1500 PLC which reads data from simulation via the server, and changes in the simulation (e.g. button pressed) appear within hundreds of miliseconds if not tens of miliseconds in my PLC program. However, when it comes to reading data from the OPC UA Server by Codesys, it taks around 1-2s. I connected a UAExpert client and it gets update very quickly so I am fairly sure the problem is with Codesys. I have tried changing the update rate in datasource -> General and Diagnosis, but it doesn't seem to have an effect. Do you guys have any suggestion on what I can do?
Last updated: 2023-08-29

Post by egret on Issue with J1939, PGN 65267 (Vehicle Position) CODESYS Forge talk (Post)
I have a J1939 network (ISOBUS) connected to my PLC. I can receive various PGNs such as 65256 (Vehicle Direction/Speed) and 65254 (Time/Date). However, I cannot receive 65267 (Vehicle Position). PGN 65267 (VP) contains SPN 584 (Latitude) and SPN 585 (Longitude). On the network both SPNs return a value of -210 (meaning the CAN message payload is zero in both cases). The conversion settings are the default values and appear to be correct (see attached screenshot). Using a CAN analyser I can see that PGN 65267 (Vehicle Position) is being transmitted over the network with valid (non-zero) data that matches the latitude and longitude coordinates I would expect. I've created a program to read the raw J1939 data and this also returns valid data. It seems that the Codesys J1939 database has a problem with reading PGN 65267 messages. Can anybody else confirm this? I'm using Codesys Version 3.5 SP16 Patch 5.
Last updated: 2023-09-13

Post by andrej on Write to File on soft PLC winV3x64 CODESYS Forge talk (Post)
Hello all, I would like to store some data in text file. I use the soft PLC Win V3x64, on Windows 10. I use the SysFile Library 3.5.17.0. If I store the file directly in the in the directory of the PLC i.e. in '/CODESYSControlWinV3x64/E1FA7ABE/PlcLogic/LogAU.txt' the file is correctly filled with the data. However, If I use an absolute path to a different directory no data is stored in the respective file. Despite the fact that the respective file exists and the Filehandler is correctly opened (see in picture _fdSysFHandle <> -1). // sFileName : STRING := 'LogAU.txt'; // STORES FILE IN ../CODESYSControlWinV3x64/../PlcLogic/LogAU.txt' sFileName : STRING := 'C/Temp/LogAU.txt'// DOES NOT WORK --------------------- // FILE DESCRIPTOR _fdSysFHandle := SysFile.SysFileOpen( szFile:= sFileName,am:= SysFile.AM_APPEND,pResult := ADR(_Result)); Does some have an idea where the problem is, resp. how I can get store a file in an arbitrary directory. Thanks a lot and kind regards Andreas
Last updated: 2023-10-24

Post by smeitink on Timeout Error in Modbus Communication with WAGO PFC200 and iEM2050 Meter using 750-652 Module CODESYS Forge talk (Post)
Hi all, I'm looking for help with an issue I've come across while trying to facilitate Modbus communication between a WAGO PFC200 PLC using a 750-652 communication module and an iEM2050 Series Single Phase Energy Meter. I believe to have everything wired and setup correcty, but I keep running into a "Error time out" message, and by now I don't really know what else to try. My setup is as follows: A PFC200 Wago PLC, which has 2 750-652 Serial Interfaces extension modules connected to its field bus. I'm using one of these to talk to a Schneider iEM2050 - kWh-meter over modbus. I have connected terminal 23 (A) of the iEM2050 to connector 6 (A) on the 750-652. I have connected terminal 24 (B) of the iEM2050 to connector 2 (B) of the 750-652. I'm using 200mm of twisted together wires to connected them both, and I have placed a 120 ohm resistor between A and B at both ends. I've attached relevant pinout images to this post. I then wrote a simple program that configures the Mobus port, as per the datasheet of the iEM2050. You can find an image of the relavent page attached to this post too. This is my program: PROGRAM PLC_PRG VAR Master: FbMbMasterSerial; xIsConnected: BOOL; xError: BOOL; iIndex: INT := 1; xTrigger: BOOL; utQuery : typMbQuery := ( bUnitId := 1, // The Modbus unit or slave address bFunctionCode := 4, // Function code for reading input registers uiReadAddress := 1829, // adress for the Power on off counter uiReadQuantity := 1 // Quantity of registers to read ); iStep: INT; oStatusModbus: WagoSysErrorBase.FbResult; utResponseModbus: typMbResponse; xConnect: BOOL := FALSE; delayTimer: TON; END_VAR Master( xConnect:= xConnect, I_Port:= _750_652_24_1, udiBaudrate:= 9600, usiDataBits:= 8, eParity:= WagoTypesCom.eTTYParity.Even, eStopBits:= WagoTypesCom.eTTYStopBits.One, eHandshake:= WagoTypesCom.eTTYHandshake.None, ePhysical:= WagoTypesCom.eTTYPhysicalLayer.RS485_HalfDuplex, xIsConnected=> xIsConnected, xError=> xError, oStatus=> oStatusModbus, eFrameType:= WagoAppPlcModbus.eMbFrameType.RTU, tTimeOut:= T#5S, utQuery:= utQuery, xTrigger:= xTrigger, utResponse:= utResponseModbus); delayTimer(IN := TRUE, PT := T#3S); // Use the Q output of the timer to set xConnect after the delay IF delayTimer.Q THEN xConnect := TRUE; END_IF CASE iStep OF 0: //Wacht totdat de master de poort geopend heeft IF xIsConnected THEN iStep := 1; END_IF 1: //Stuur request naar de slave xTrigger := TRUE; iStep := 2; 2: //Wacht totdat de master klaar is met het afhandelen van de request IF NOT xTrigger THEN iStep := 3; END_IF END_CASE The TON delay before opening the port is due to a an error I encountered when opening it straight away. This seems to be a bug, as described here. However, the TON solved that particular issue. I tried reading multiple registers, but like I said, I still always end up with the "Error time out". What else can I test or try at this point?
Last updated: 2024-02-24

Post by alexgooi on Modbus writing on value change CODESYS Forge talk (Post)
The way I usally tackle this is by syncing only words (then you are able to use the FB above). If you then want to write a Boolean simply type it like this. Value[1].0 := Bool1; Value[1].1 := Bool2; Value[1].2 := Bool3; Uints have the same number of bits than a INT/WORD so these ones will work as well (they are only represented diffrently). A Real will work but you will loose some infomration in the conversion. If you want to keep the information you can convert 2 words to a float with a function (for example with the IEEE-754 standard) . In this way the syncing to the server is very simple and in the Codesys Program you decide what part of the word you want to use.
Last updated: 2024-04-03

Post by paro on Modbus Client Request Not Processed CODESYS Forge talk (Post)
Hi, works in my case if I increase the timeout! to_udint(t#100ms) -> 100 -> 100us.. FUNCTION_BLOCK MODBUS_master_example_ST VAR initDone : BOOL := FALSE; aIPAddress : ARRAY [0..3] OF BYTE := [127,0,0,1]; clientTcp: ModbusFB.ClientTcp; // buffer to read input registers aDataInputRegisters : ARRAY[0..9] OF UINT; // some client requests clientRequestReadInputRegisters: ModbusFB.ClientRequestReadInputRegisters; xExecute: BOOL; uistart: UINT := 100; udiTimeout1: UDINT; END_VAR IF NOT initDone THEN initDone := TRUE; // configure clientTcp clientTcp(aIPaddr:=aIPAddress, uiPort:=502, udiLogOptions := ModbusFB.LoggingOptions.All); // configure clientRequestReadInputRegisters clientRequestReadInputRegisters(rClient:=clientTcp, uiUnitId:=1, udiTimeout:=1000000); // 1sec END_IF // call the client FB's clientTcp(); clientRequestReadInputRegisters(rClient:=clientTcp,xExecute := xExecute AND NOT clientRequestReadInputRegisters.xBusy ,uiStartItem:=uistart, uiQuantity:=3, pData:=ADR(aDataInputRegisters[0]));
Last updated: 2024-05-30

Post by zer0g on Modbus Client Request Not Processed CODESYS Forge talk (Post)
I'm using the code bellow which is based on the Codesys example: FUNCTION_BLOCK MODBUS_master_example_ST VAR initDone : BOOL := FALSE; aIPAddress : ARRAY [0..3] OF BYTE := [127,0,0,1]; clientTcp: ModbusFB.ClientTcp; // buffer to read input registers aDataInputRegisters : ARRAY[0..9] OF UINT; // some client requests clientRequestReadInputRegisters: ModbusFB.ClientRequestReadInputRegisters; xExecute: BOOL; END_VAR IF NOT initDone THEN initDone := TRUE; // configure clientTcp clientTcp(aIPaddr:=aIPAddress, uiPort:=502, udiLogOptions := ModbusFB.LoggingOptions.All); // configure clientRequestReadInputRegisters clientRequestReadInputRegisters(rClient:=clientTcp, uiUnitId:=1, udiTimeout:=TO_UDINT(T#1000MS)); END_IF // call the client FB's clientTcp(); clientRequestReadInputRegisters(rClient:=clientTcp,xExecute := xExecute AND NOT clientRequestReadInputRegisters.xBusy ,uiStartItem:=2, uiQuantity:=3, pData:=ADR(aDataInputRegisters[0])); As you can see the clientTCP is called cyclically with the same result.
Last updated: 2024-05-30

Post by shrikantp007 on help to get codesys understand CODESYS Forge talk (Post)
Hello , I need some help on how to start with , 1) how to get test license to test codesys , 2) how to take a configuration backup or running process back and post file on fourm so people can understand and deploy same file and get idea what is missing or configure wrong 3) where i can get pdf for codesys admin or programmer 4) what is hardware recommand ,i am running on windows guest on kvm server .is it ok ? 5) i am trying to get ardunio porject working ,using ardunio board as a modbus slave but its not working some how https://forge.codesys.com/forge/talk/Engineering/thread/bf832569b8/ Thanks in advance . shrikant pune -india
Last updated: 2024-07-22

Post by yannickasselin on codesys VLAN tagging CODESYS Forge talk (Post)
I ordered a cheap managed switch and tested it as soon as I received the switch. It works great! I even went a bit further. As you can see in the screenshot, I created 2 Codesys containers. Each one having 2 fieldbuses. The first one has EtherCAT and EtherNet/IP and the second one has EtherCAT and Modbus/TCP. All going through the same ethernet port from the PC to the switch. The switch splits it up into 4 different networks. The hardest part was to figure out how to configure the switch. @eschwellinger, thank you very much.
Last updated: 2024-09-17

Post by timvh on Modbus TCP & RTU with Control for Linux SL CODESYS Forge talk (Post)
It seems you have 2 network interfaces. Did you try eth1? Did you already configure the IP address for this interface in Linux? If yes, then maybe undo this. - or only set eth0 in the Nic configuration without anything else (so no IP address, because this is already set in Linux). For more information about the Nic settings, see (probably already read it?): https://content.helpme-codesys.com/en/CODESYS%20Control/_rtsl_obj_deploy_control_sl_configuration.html PS, if you only want to run CODESYS Control SL, you don't necessarily need the Virtual PLC variant. You could also install and run the CODESYS Control SL Runtime in the Host operating system. This way you should also be able to access the serial port and directly access all ethernet ports. Maybe this is easier?
Last updated: 2024-10-23

Post by ben1 on How to write multiple coils (Modbus FC15) CODESYS Forge talk (Post)
If I am understanding what you are saying, then yes that would be your problem. I would create an array of bools on the client side for the transfer and try that. Or if client can't be changed then use words on server and unpack. But I am not sure if you or I are mis interpreting but it sounds a bit jumbled. I don't know what you have control of, but, if you are turning on BITS in the server, you should write to BITS in the client with a Function 15. If you are writing to WORDS in the server, you should write to WORDS in the client with a Function 16.
Last updated: 7 minutes ago

Post by ihatemaryfisher on Sorting array of any-sized structure CODESYS Forge talk (Post)
With that I could make an array of varying size, but would still have to define the array type in the function's declaration VAR_IN_OUT stArray: array [*..*] of <pre-defined data type> END_VAR I wanted a function that could take an array of any type (e.g., a structured VAR) as an input. That way I could call it in multiple POUs to handle different arrays structures.
Last updated: 2023-08-18

Post by docker on Canopen connection. Unknown node id. CODESYS Forge talk (Post)
hi, i am currently trying to adapt an i/o device for a project. the node id is unknown and there is no eds file available. no data is being emitted from the device as a giveaway, the baudrate is known but useless without the node id. is there an sdo request available to determine the id? i cannot get the device to leave pre op status even with a global nmt request. please help. no hair left.
Last updated: 2023-09-25

Post by timvh on Specify Input Configuration "OnDialogClosed" Action to only react to certain Dialogs CODESYS Forge talk (Post)
What maybe helps is the Visu Dialog ST demo project: https://store.codesys.com/en/visu-dialog-st.html This has an application IECOpenDialog where dialogs are opened using the VU.FbOpenDialogExtended function blocks. The fbOpenConfigurationDialog call has a reference (interface) to the "close listener" FB of which it's method is automatically called when the dialog is closed. This way you can create specific function blocks for each dialog when it is closed and do what you want with the data that might have been changed.
Last updated: 2023-09-28

Post by voffi on Converting UINT into bytes and converting 2Bytes into UINT CODESYS Forge talk (Post)
There are some ways. One is to use SHR and SHL and it depends on your byte order in the data array. For Motorola byte order: PROGRAM PLC_PRG VAR u : UINT; byte_array_in : ARRAY [1..8] OF BYTE := [16#11, 16#12, 16#13, 16#14, 16#15, 16#16, 16#17]; byte_array_out : ARRAY [1..8] OF BYTE; END_VAR u := SHL(TO_UINT(byte_array_in[2]), 8) + TO_UINT(byte_array_in[1]); byte_array_out[1] := TO_BYTE(u); byte_array_out[2] := TO_BYTE(SHR(u, 8)); If it's Intel byte order just change 1 and 2 in the array indexes.
Last updated: 2023-12-07

Post by tvm on VisuFbFrameBase.SetInputPositionData: The element id for the input position cannot be determined CODESYS Forge talk (Post)
I'm getting this error on one of my projects. Searching for it I came across this https://www.codesys.com/fileadmin/data/Images/System/Releaseinformation/Patch-Note-CODESYS-Visualization-4300.html which says it was a bug VIS-1394, fixed in Visualization 4.3.0.0. I'm using a previous visu version, what is the cause of this error, and what can be done to work around it?
Last updated: 2024-02-08

Post by dagsupport on CAA SerialCOM - hCom Reset max value 1023 CODESYS Forge talk (Post)
Hi everybody We are currently working on a project with an RS232 serial COM interface and using the CAA SerialCOM library. We have it working fine reading and writing data, although we have found an issue we cannot resolve and any suggestions would be helpful. We have noticed that after a while the RS232 stops working. We have tracked this down to the HANDLE hCom keeps increasing and when this reaches 1023 the COM returns an unknown error "5003". Is there a way to reset this hCom reference? Thanks Richard
Last updated: 2024-03-22